ADVERTISEMENT
19701610_WinCC_flexible_e.pdf
Siemens TP170B Color - jak wgrać backup z karty CF przy uszkodzonym dotyku?
Na stronach Siemensa jest wszystko opisane:
Download file - link to post
Cover sheet
Operating System Update with
WinCC flexible
WinCC flexible 2008
FAQ  October 2011
Service & Support
Answers for industry.
Question
This entry originates from the Service & Support Portal of Siemens AG, Sector
Industry, Industry Automation and Drive Technologies. The conditions of use
specified there apply (www.siemens.com/nutzungsbedingungen).
Go to the following link to download this document.
http://support.automation.siemens.com/WW/view/de/90701610
Question
How do you do an operating system update (OS update) on operator panels with
WinCC flexible?
Answer
Follow the instructions and notes listed in this document for a detailed answer to
the above question.
2
WinCC flexible 2008
Version V2.0, Entry ID: 19701610
Contents
Contents
1
1.1
1.2
1.3
Operating System Update with WinCC flexible.................................... 4
Operating System Update (OS Update)............................................... 5
Resetting the Operating System to the Factory Settings (Booting) ..... 7
Resetting the Operating System to the Factory Settings via Ethernet
Connection ........................................................................................... 9
2
2.1
2.1.1
2.1.2
2.2
2.3
Additional Information......................................................................... 11
Cable Connection between PC and Operator Panel ......................... 11
Operating System Update.................................................................. 11
Resetting the Operating System to the Factory Settings (Booting) ... 11
Set the Image Path / File in ProSave ................................................. 13
Determining the MAC Address........................................................... 14
3
3.1
Problem Analysis................................................................................ 15
Disconnected Connection when Using the RS232/PPI Multi-Master
Cable .................................................................................................. 15
Check Box Not Available in ProSave ................................................. 15
Check Box Cannot be Deselected in ProSave .................................. 15
Error Message During the Transfer of the Configuration ................... 15
MP 377 " Reset to factory settings " (booting) ..................................... 16
A Connection to the Operator Panel Cannot be Established............. 16
Check transmission type and address on the operator panel............ 16
Check Cable Connection and Connector........................................... 17
Check the PG/PC Interface on the Configuration Computer ............. 18
3.2
3.3
3.4
3.5
3.6
3.6.1
3.6.2
3.6.3
WinCC flexible 2008
3
1 Operating System Update with WinCC flexible
1
flexible
Below is a summary of how to do an operating system update (OS update) with
WinCC flexible.
If no operable operator panel image exists on the operator panel,
you can only update the operating system by means of a reset to factory
settings.
Information about this is described in sections 1.2 and 1.3.
Notes
The operating system of the operator panel depends on the version of WinCC
flexible used.
You should do always do an operating system update whenever the operating
system of the operator panel does not match the software version used.
Information about this is described in section 1.1.
If you have questions on establishing the connection or problems with the
operating system update, please refer to chapters 2 and 3.
Updating the operating system deletes all the data on the operator panel.
Therefore, first make a backup of the data below:
(using ProSave or Automation License Manager, for example)
4
User management.
Recipes.
Licenses
(if you reset the operating system to the factory settings.
Information about this is available in Entry ID: 27005215.)
WinCC flexible 2008
1.1
If you use WinCC flexible 2008 SP1 or higher to transfer a project to an operator
panel on which an incorrect version of the operating system is installed, WinCC
flexible recognizes this immediately.
You get a message via which you can do the operating system update
automatically.
Please proceed as follows to perform an operating system update " manually " .
Table 1-1
No.
1.
Procedure
Back up data:
Therefore, first make a backup of the data below, with ProSave, for example:
User management.
Recipes.
2.
Set the PG/PC interface:
3.
In the SIMATIC Manager, you select the menu command
" Tools & gt; Set PG/PC Interface... " .
There you set the interface parameters used,
CP5512 (PROFIBUS), for example.
Make transfer settings on the operator panel:
Make the corresponding transfer settings on the operator panel and then switch the
operator panel to Transfer mode.
4.
Establish cable connection:
Connect the operator panel to the PG/PC with an appropriate connection cable
(according to the transfer setting selected).
5.
Configure WinCC flexible:
Open the WinCC flexible configuration.
6.
Set transfer mode:
In the WinCC flexible menu bar, select the menu
" Project & gt; Transfer & gt; Transfer settings... " .
Make the following settings in the dialog displayed.
Then click the " Apply button " .
WinCC flexible 2008
5
No.
7.
Procedure
Update the operating system:
" Project & gt; Transfer & gt; Update operating system... " .
(Project & gt; Transfer & gt; OS update...).
The " SIMATIC ProSave [OS Update] " dialog opens.
The path with the image of the operating system is already preinstalled.
(You can also choose a different path for the image of the operating
system).
ProSave automatically adopts the transfer settings you made in Point 5.
Click the " Device status " button.
A connection is established between " ProSave " and the " operator panel " .
After the connection has been established successfully, the current image
version of the operator panel is displayed.
Click on the " Update OS " button. The operating system update is started.
Note:
Make sure that the correct image path is set.
(See also section 2.2)
8.
Transfer the project:
After updating the operating system, the operator panel switches to " Transfer
Mode " .
Now you can transfer the configuration.
Note:
For Touch operator panels, you should calibrate the screen beforehand under
" Control Panel & gt; OP & gt; Touch " .
6
WinCC flexible 2008
1.2
(Booting)
Proceed as follows to reset an operator panel to the factory settings.
Notes
If you reset the operating system to the factory settings, you cannot use all the
communication connections and cables.
Information on which cable you can use for which operator panel is available in
section 2.1.2.
If " Ethernet " is preset as transfer type for booting, then refer to section 1.3.
Table 1-2
No.
1.
Procedure
Back up licenses and authorizations:
Before resetting your operator panel to the factory settings, make sure that there are
no licenses or authorizations on the operator panel.
2.
For the " Reset to factory settings " function, the only setting you have to make in the
PG/PC interface is for the transfer type " Ethernet "
(see section 1.3).
3.
No transfer settings need to be made on the operator panel.
4.
Operator panel power supply:
Switch off the power supply for the operator panel.
5.
6.
7.
Set transfer mode:
Make the relevant settings in the dialog window displayed.
WinCC flexible 2008
7
No.
8.
Procedure
Reset to the factory settings:
system).
ProSave automatically adopts the transfer settings you made in " Point 7 " .
Check the " Reset to factory settings " option or " Boot " (in earlier versions of
ProSave).
If you have specified " Ethernet " as the connection parameter, then you
also enter the " MAC address " of the operator panel here.
Click " Update OS " button and depending on the operator panel used...
A dialog window opens with a safety note. Read the note.
Acknowledge the message with " Yes " and you will be requested to reboot
the operator panel.
The connection to the operator panel starts to be established.
Read the note. If necessary, you can abort the action with the " Cancel "
button.
Switch the operator panel’s power supply on again.
The operator panel is reset to the factory settings.
Note:
If the " Reset to factory settings " check box is not displayed, refer to section 3.2.
9.
Depending on the operator panel used, after transfer of the data, " ProSave "
requests you to reboot the operator panel (switch off and on).
The operator panel then performs additional installation steps.
10.
After completion of the installation, the " Control Panel " is displayed on the operator
panel.
For a subsequent project transfer, you first make the required transfer settings on
the operator panel.
8
WinCC flexible 2008
1.3
via Ethernet Connection
Below we take the example of an MP 377 Touch to show how to reset an operator
panel to the factory settings via Ethernet.
Notes
MP 377 operator panels with the Image version installed for WinCC flexible 2008
and higher (Image version as from V01.00.02.00_01.83) have the parameter
" Prepare for Reset " .
More information on this is available in
Entry ID: 35677293.
Table 1-3
No.
1.
Procedure
2.
3.
Set the interface parameters used to
" TCP/IP - & gt; Your network card " .
4.
MAC address of the operator panel:
To continue you need the MAC address of the operator panel.
Please refer to section 2.3 to determine the MAC address.
5.
6.
Connect the operator panel and the PG/PC using an Ethernet cable
(cross-over or patch cable).
7.
8.
Set transfer mode:
" Project & gt; Transfer & gt; Transfer settings... " and select " Ethernet " as the transfer type.
Specify a unique IP address and then click the " Apply " button.
WinCC flexible 2008
9
No.
9.
Procedure
system).
ProSave automatically adopts the transfer settings you made in " Point 9 " .
ProSave).
An input field is displayed for the MAC address.
Enter the operator panel's " MAC address " .
Refer to section 2.3 for how to determine the MAC address.
You will then receive a security warning.
Read the note. Acknowledge the message with " Yes " and you will be requested
to reboot the operator panel.
Switch the operator panel on again.
Note:
Make sure that the correct image path is set. This applies, in particular, if
multiple Engineering Systems
like ProTool, WinCC flexible or WinCC (TIA Portal), for example, are installed
jointly on your computer. (See also section 2.2).
10.
panel.
the operator panel.
10
WinCC flexible 2008
2 Additional Information
2
2.1
2.1.1
When performing an operating system update, you can use all the communication
connections supported by your operator panel.
2.1.2
Information about this is given in the table below.
The settings were made in ProSave version V9.0.0.0.
Table 2-1
Operator panel
RS 232
RS232/PPI
USB/PPI
PN PtP
PN
Zero modem
cable
Multi-master
cable
Multi-master
cable
Cross
Ethernet
6ES7 9011BF00-0XA0
6ES7 9013CB30-0XA0
6ES7 9013DB30-0XA0
6XV1 8701
3RH20 * )
Standard
Ethernet CAT5
C7-635
OP / TP
C7-636
Key / Touch
TP 177B
PN/DP
X )
*2
TP 177B
mono DP
X )
*2
TP 177B 4”
color PN/DP
OP 177B
PN/DP
X )
*2
OP 73 micro
OP 73
OP 77A
OP 77B
TP 170 micro
TP 170A
OP 170B
TP 170B
TP 177 micro
TP 177A
WinCC flexible 2008
11
Operator panel
RS 232
RS232/PPI
USB/PPI
PN PtP
PN
Zero modem
cable
Multi-master
cable
Multi-master
cable
Cross
Ethernet
X )
*2
X )
*2
X )
*2
X )
*2
X )
*2
Mobile Panel
170
Mobile Panel
177 DP
X )
*2
Mobile Panel
177 PN
X )
*2
Mobile Panel
277
X )
*2
Mobile Panel
277 IWLAN
Mobile Panel
277F IWLAN
KTP400
Basic mono PN
KTP600
Basic DP
KTP600
Basic PN
KTP600
Basic mono PN
KTP1000
Basic DP
KTP1000
Basic PN
TP1500
Basic PN
OP 177B
mono DP
OP 270
OP 277
TP 270
TP 277
MP177
MP 270
MP 277
MP 370
MP 377
*1) For the RS232/PPI multi-master cable you set DIP switches 1 to 3 according to
the baud rate selected in ProSave.
DIP switches 4 to 8 must all be set to ZERO.
*2
12
With this cable connection you cannot deselect the " Reset to factory settings "
option.
WinCC flexible 2008
2.2
In the following cases, you must change the image path or the image file
accordingly.
1. After you have set the ProTool image path for the operator panel displayed,
you must set the image path for
WinCC flexible if you now wish to use the same operator panel in WinCC
flexible.
2. If you need an earlier version of Image than the one currently displayed.
Notes
The image path setting is device-related. The setting is retained for the selected
panel type after ProSave is closed.
Beforehand, make sure that the correct Image path is set. This applies, in particular,
if, for example, WinCC flexible and ProTool
are installed jointly on your computer.
In order to set the image path in ProSave, click the button to the right of the image
path and browse through the folder tree to specify the folder path in which the
image files are located.
In the folders you find the image files required for the respective operator panel.
Figure 2-1
Sample image path in WinCC flexible
C:\Program Files\Siemens\SIMATIC WinCC flexible\WinCC flexible
Images\Operator Panel\xxxxx.img
WinCC flexible 2008
13
The Image version of the operator panels depends on the version of
WinCC flexible used.
Notes
Information about how these are interrelated is available at this link:
http://support.automation.siemens.com/WW/view/de/28263711
2.3
You can determine the operator panel's MAC address as follows.
When you switch on the operator panel, the MAC address is displayed during
startup.
14
The MAC address is printed on the back of the operator panel
(for example, MAC-ADD.: 00-0E-8C-F8-6A-18).
Via the " Control Panel " of the operator panel.
In the Control Panel you open the " OP " dialog and select the " Device " tab.
In this tab you find the device-specific data, like the MAC address.
WinCC flexible 2008
3 Problem Analysis
3
Problem Analysis
3.1
Multi-Master Cable
If the connection is disconnected when updating the operating system, set a lower
bit rate.
If you are using high bit rates, then you must implement the RS232/PPI multimaster cable with " E-Stand 03 " (development status 03) or higher.
3.2
If the " Reset to factory settings " check box is not displayed, then recheck the
connection settings made (Link). It is possible that the operator panel does not
support the transfer type required for this option.
Refer here to Table 2-1 under point 2.1.2.
3.3
If you use the " USB/PPI Multi-Master Cable " transfer type, then, depending on the
system, on some operator panels it might not be possible to deselect the " Reset to
factory settings " option.
In this case, you cannot make an operating system update (OS Update) using the
cable, but can only do a reboot ( " Reset to factory settings " ).
3.4
Configuration
You have changed the operating system of your operator panel and during transfer
of the configuration you receive the message that the operating system version of
In this case, prior to updating the operating system, check that the image path has
been set correctly and that you have selected the correct image file. See section
2.2 for this.
Example of an error message in WinCC flexible
Figure 3-1
or in older versions of WinCC flexible
Figure 3-2
WinCC flexible 2008
15
3 Problem Analysis
3.5
If the MP 377 operator panel cannot be reset to the factory settings, then check the
Image version of the MP 377.
and higher (Image version as from V01.00.02.00_01.83) have the new parameter
In this case refer to Entry ID: 35677293.
3.6
Established
Some points are given below, which you should check if no connection is
established between the operator panel and the configuration computer.
3.6.1
Compare the transfer settings on the operator panel with those on the configuration
computer.
Example
Specification of configuration computer...
Transfer via PROFIBUS
Panel address 10
Make sure that " Panel is the only master on the bus " is checked for the transfer
settings on the operator panel.
Figure 3-3
More information on the topic of " Transfer Settings " is available in Entry ID:
23802404
16
WinCC flexible 2008
3 Problem Analysis
3.6.2
MPI/PROFIBUS cable
Please check the points below.
Cable connection between the operator panel and the configuration computer.
Check the cable for damage.
Bus connector especially the connection of the terminating resistors.
Terminating resistors ON/OFF.
The following guideline value applies:
Bus terminating resistor OFF:
Bus connector with " two " cables connected.
Bus terminating resistor ON:
Bus connector with " one " cable connected.
More information on the topic of " Bus terminating resistor " is available in Entry ID:
187276.
When using an " RS232/PPI multi-master cable " , please note the switch settings.
More information on this topic is available in Entry ID: 16532946
Ethernet Cable
Use a " crossed " Ethernet cable for the connection between a PG/PC and an
operator panel.
If you use a " patch " cable, you need a switch in addition.
Notes
Operator panels with two " Ethernet interfaces " have an integrated switch.
WinCC flexible 2008
17
3 Problem Analysis
3.6.3
Check the PG/PC interface on your configuration computer.
In Windows XP
" Start & gt; SIMATIC & gt; SIMATIC NET & gt; Set PG-PC interface " .
In STEP 7
" Menu bar: Tools & gt; Set PG/PC interface... "
When setting the interface parameters in
MPI or PROFIBUS, make sure that the node address is set to " 0 " .
We also recommend that you select the " PG/PC is the only master on the bus "
option.
Figure 3-4
18
WinCC flexible 2008