Porter: kolega arwit pisal juz ze nie ma bezposredniego odwolania do tego wyjscia. W zasadzie z jezykiem STEP5 nie ma problemu bo przy instalacji wybralem angielski. Na jakiej zasadzie dziala "DO" ? (Digital/Data Out?) Czym jest slowo w argumencie? Wszystkim serdecznie dziekuje za pomoc mnie poczatkujacemu i cierpliwosc. Pozdrawiam. ps. Znalazlem w koncu spis instrukcji S5-100U, Oczywiscie co manual to manual.
Download file - link to post
SIMATIC S5
S5-100U
Programmable Controller
System Manual
CPU 100/102/103
EWA 4NEB 812 6120-02b
Edition 04
STEP ® SINEC ® and SIMATIC ® are registered trademarks of Siemens AG.
LINESTRA® is a registered trademark of the OSRAM Company.
Subject to change without prior notice.
The reproduction, transmission or use of this document or its contents is not
permitted without express written authority.
Offenders will be liable for
damages. All rights, including rights created by patent grant or registration of a
utility model or design, are reserved.
Copyright© Siemens AG 1992
Introduction
The SIMATIC S5 System Family
1
Technical Description
2
Installation Guidelines
3
Start-Up and Program Tests
4
Diagnostics and Troubleshooting
5
Addressing
6
Introduction to STEP 5
7
STEP 5 Operations
8
Integrated Blocks and Their Functions
9
Interrupt Processing
10
Analog Value Processing
11
The Integral Real-Time Clock, for CPU 103 and Higher
12
Connecting the S5-100U to SINEC L1
13
Module Spectrum
14
Function Modules
15
Appendices
A/B/C
D/E/F
Index
S5-100U
Contents
Contents
Page
How to Use This Manual
1
2
2.1
2.2
2.2.1
2.2.2
3
Programmable Controller Design
Principle of Operation for the Programmable Controller . . . . . . . . . . . . . .
Functional Units . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Mode of Operation for the External I/O Bus . . . . . . . . . . . . . . . . . . . . . .
xv
1 - 1
2 - 1
2 - 1
2 - 3
2 - 3
2 - 6
3 - 1
3.1
3.1.1
3.1.2
3.1.3
3.1.4
Installing S5-100U Components . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Assembling a Tier . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Multi-Tier Expansion . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Cabinet Mounting . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Vertical Mounting . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
3
3
3
3
3
1
1
5
7
8
3.2
3.2.1
3.2.2
3.2.3
3.2.4
Wiring . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Connection Methods: Screw-Type Terminals and Crimp Snap-in
Connecting the Power Supply to the S5-100U . . . . . . . . . . . . . . . . . . . .
Connecting Digital Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Connecting the Digital Input/Output Module . . . . . . . . . . . . . . . . . . . . . .
3
3
3
3
3
9
9
12
13
18
3.3
3.3.1
3.3.2
3.3.3
Electrical Configuration . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Electrical Configuration for the S5-100U . . . . . . . . . . . . . . . . . . . . . . . .
Electrical Configuration with External I/Os . . . . . . . . . . . . . . . . . . . . . . .
Non-Floating and Floating Configurations . . . . . . . . . . . . . . . . . . . . . . . .
3
3
3
3
20
20
21
25
3.4
Wiring Arrangement, Shielding, and Measures to
Guard against Electromagnetic Interference . . . . . . . . . . . . . . . . . . . . . .
Running Cables Inside and Outside a Cabinet . . . . . . . . . . . . . . . . . . . .
Running Cables Outside Buildings . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Equipotential Bonding . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Shielding Cables . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Special Measures for Interference-Free Operation . . . . . . . . . . . . . . . . .
3
3
3
3
3
3
29
29
30
31
32
33
3.4.1
3.4.2
3.4.3
3.4.4
3.4.5
v
Contents
S5-100U
Page
4
4 - 1
4.1
4.1.1
4.1.2
4.1.3
4
4
4
4
4.2
4.2.1
4.2.2
Starting Up a System . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Suggestions for Configuring and Installing the Product . . . . . . . . . . . . . .
Procedures for Starting Up the Programmable Controller . . . . . . . . . . . .
4 - 3
4 - 3
4 - 4
4.3
Loading the Program into the Programmable Controller . . . . . . . . . . . . . .
4 - 5
4.4
4.4.1
4.4.2
Backing Up the Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Backing Up the Program on a Memory Submodule
Function of the Back-Up Battery . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
4 - 7
4 - 7
4 - 8
4.5
Program-Dependent Signal Status Display “STATUS”
4 - 8
4.6
Direct Signal Status Display “STATUS VAR”
4.7
Forcing Outputs, “FORCE”, for CPU 103 and Higher
4.8
Forcing Variables, “FORCE VAR”
4.9
Search Function . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
4 - 11
4.10
5
Operating Instructions . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
CPU Operator Panel . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Operating Modes . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Performing an Overall Reset on the Programmable Controller . . . . . . . . .
Program Check, for CPU 103 and Higher
4 - 11
1
1
1
2
4 - 9
4 - 10
4 - 10
5 - 1
5.1
Indication of Errors by LEDs . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
5 - 1
5.2
5.2.1
5.2.2
5.2.3
5.2.4
CPU Malfunctions . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
“ISTACK” Analysis Function
Interrupt Analysis . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Errors during Program Copying . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Explanation of the Mnemonics Used in “ISTACK”
5
5
5
5
5
5.3
5.3.1
5.3.2
Program Errors . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Locating the Error Address . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Tracing the Program with the “BSTACK” Function . . . . . . . . . . . . . . . . .
5 - 8
5 - 8
5 - 11
5.4
I/O Faults . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
5 - 12
5.5
System Parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
5 - 12
5.6
vi
The Last Resort
5 - 13
1
1
4
5
6
S5-100U
Contents
Page
6
6 - 1
6.1
Slot Numbering . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6 - 1
6.2
Digital Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6 - 4
6.3
Analog Modules
6 - 5
6.4
6.4.1
6.4.2
Combined Input Modules and Output Modules . . . . . . . . . . . . . . . . . . . .
Output Modules with Error Diagnostics . . . . . . . . . . . . . . . . . . . . . . . . .
Digital Input/Output Module, 16 Inputs, 16 Outputs, 24 V DC
for All CPUs Version 8MA02 and Higher and
for CPU 102, Version 8MA01, Revision 5 and Higher . . . . . . . . . . . . . . .
Function Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6 - 6
6 - 6
6.4.3
6.5
6.5.1
6.5.2
The Structure of Process Image Input and Output Tables . . . . . . . . . . . .
Accessing the Process Image Input Table (PII) . . . . . . . . . . . . . . . . . . .
Accessing the Process Image Output Table (PIQ) . . . . . . . . . . . . . . . . .
6 - 8
6 - 10
6 - 11
6.6
6.6.1
6.6.2
Interrupt Process Images Tables and Time-Controlled Program
Processing in OB13 for CPU 103, Version 8MA02 and Higher . . . . . . . . .
Accessing the Interrupt PII . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Accessing the Interrupt PIQ . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6 - 12
6 - 12
6 - 14
6.7
7
Addressing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
RAM Address Assignments
6 - 15
6 - 7
6 - 7
7 - 1
7.1
7.1.1
7.1.2
7.1.3
Writing a Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Methods of Representation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Operand Areas . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Circuit Diagram Conversion . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7
7
7
7
7.2
7.2.1
7.2.2
Program Structure . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Linear Programming . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Structured Programming . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7 - 4
7 - 4
7 - 5
7.3
7.3.1
7.3.2
7.3.3
7.3.4
7.3.5
Block Types . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Organization Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Program Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Sequence Blocks, for CPU 103 and Higher
Function Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Data Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7
7
7
7
7
7
7
9
11
11
11
16
7.4
7.4.1
7.4.2
7.4.3
7.4.4
Program Processing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Program Processing with CPU 102 . . . . . . . . . . . . . . . . . . . . . . . . . . . .
START-UP Program Processing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Cyclic Program Processing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Time-Controlled Program Processing, for CPU 103
Version 8MA02 and Higher . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7
7
7
7
18
19
24
26
1
1
3
3
7 - 28
vii
Contents
S5-100U
Page
7.4.5
7 - 29
7.5
7.5.1
7.5.2
7.5.3
Processing Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Changing Programs . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Changing Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Compressing the Program Memory . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7
7
7
7
7.6
8
Interrupt-Driven Program Processing, for CPU 103
Number Representation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7 - 31
30
30
30
30
8 - 1
8.1
8.1.1
8.1.2
8.1.3
8.1.4
8.1.5
8.1.6
8.1.7
8.1.8
8.1.9
Basic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Boolean Logic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Set/Reset Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Load and Transfer Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Timer Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Counter Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Comparison Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Arithmetic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Block Call Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Other Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8
8
8
8
8
8
8
8
8
8
1
2
7
10
15
25
30
31
33
38
8.2
8.2.1
8.2.2
8.2.3
8.2.4
8.2.5
8.2.6
8.2.7
8.2.8
8.2.9
8.2.10
8.2.11
Supplementary Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Load Operation, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . . . . . .
Enable Operation, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . . . . .
Bit Test Operations, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . . . .
Digital Logic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Shift Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Conversion Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Decrement/Increment, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . .
Disable/Enable Interrupt, for CPU 103 Version 8MA02 and Higher . . . . . .
“DO” Operation, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . . . . . .
Jump Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Substitution Operations, for CPU 103 and Higher . . . . . . . . . . . . . . . . . .
8
8
8
8
8
8
8
8
8
8
8
8
39
40
41
42
44
48
50
52
53
54
56
58
8.3
8.3.1
8.3.2
8.3.3
8.3.4
System Operations, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . . . .
Set Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8
8
8
8
8
64
64
64
67
68
8.4
Condition Code Generation
8 - 69
8.5
8.5.1
8.5.2
8.5.3
viii
STEP 5 Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Sample Programs . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Momentary-Contact Relay/Edge Evaluation . . . . . . . . . . . . . . . . . . . . . .
Binary Scaler/Binary Divider . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Clock/Clock-Pulse Generator . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8
8
8
8
71
71
71
73
S5-100U
Contents
Page
9
9.1
9.1.1
9.1.2
9.1.3
9.1.4
9.1.5
9.1.6
9.1.7
9.1.8
9.2
9.2.1
9.2.2
9.2.3
9.2.4
9.2.5
9.3
9.3.1
9.3.2
9.3.3
10
10.2
9 - 1
Assigning Internal Functions to DB1,
for CPU 103 Version 8MA03 and Higher . . . . . . . . . . . . . . . . . . . . . . . .
Configuration and Default Settings for DB1 . . . . . . . . . . . . . . . . . . . . . .
Setting the Address for the Parameter Error Code in DB1 . . . . . . . . . . . .
Assigning Parameters in DB1 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Rules for Setting Parameters in DB1 . . . . . . . . . . . . . . . . . . . . . . . . . . .
How to Recognize and Correct Parameter Errors . . . . . . . . . . . . . . . . . .
Transferring DB1 Parameters to the Programmable Controller . . . . . . . . .
Reference Guide for Setting Parameters in DB1
Defining System Characteristics in DB1 . . . . . . . . . . . . . . . . . . . . . . . .
9
9
9
9
9
9
9
9
9
1
1
2
4
4
6
9
10
11
Integrated Function Blocks,
for CPU 102 Version 8MA02 and Higher . . . . . . . . . . . . . . . . . . . . . . . .
Code Converter : B4 - FB240 - . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Code Converter : 16 - FB241 - . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Multiplier : 16 - FB242 - . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Divider : 16 - FB243 - . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Analog Value Conditioning Modules FB250 and FB251 . . . . . . . . . . . . . .
9
9
9
9
9
9
11
12
12
13
13
14
Integrated Organization Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Scan Time Triggering OB31, for CPU 103 and Higher
Battery Failure OB34 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
OB251 PID Algorithm,
for CPU 103 Version 8MA02 and Higher . . . . . . . . . . . . . . . . . . . . . . . .
Interrupt Processing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
10.1
11
Interrupt Processing with OB2, for CPU 103
Calculating Interrupt Reaction Times . . . . . . . . . . . . . . . . . . . . . . . . . .
9 - 15
10 - 1
10 - 1
10 - 5
11 - 1
11.1
Analog Input Modules
11.2
11.2.2
11.2.3
11.2.4
11.2.5
Connecting Current and Voltage Sensors to Analog
Input Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Voltage Measurement with Isolated or
Non-Isolated Thermocouples . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Two-Wire Connection of Voltage Sensors . . . . . . . . . . . . . . . . . . . . . .
Two-Wire Connection of Current Sensors . . . . . . . . . . . . . . . . . . . . . .
Connection of Two-Wire and Four-Wire Transducers . . . . . . . . . . . . . .
Connection of Resistance Thermometers . . . . . . . . . . . . . . . . . . . . . .
11
11
11
11
11
11.3
Start-Up of Analog Input Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11 - 7
11.4
Analog Value Representation of Analog Input Modules
11 - 11
11.2.1
9 - 14
9 - 14
9 - 14
11 - 1
11 - 1
2
3
4
4
6
ix
Contents
S5-100U
Page
11.5
Analog Output Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11.5.1 Connection of Loads to Analog Output Modules . . . . . . . . . . . . . . . . . .
11.5.2 Analog Value Representation of Analog Output Modules . . . . . . . . . . . .
11.6
Analog Value Conversion: Function Blocks FB250 and FB251 . . . . . . . .
11.6.1 Reading in and Scaling an Analog Value - FB250 - . . . . . . . . . . . . . . . .
11.6.2 Outputting of Analog Values - FB251 - . . . . . . . . . . . . . . . . . . . . . . . .
12
11 - 19
11 - 19
11 - 20
11 - 22
11 - 22
11 - 25
The Integral Real-Time Clock, for CPU 103 Version 8MA02 and Higher
12 - 1
12.1
Function . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Setting Parameters in DB1, for CPU 103 Version 8MA03
and Higher . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12.2.1 Defaults . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12.2.2 Reading the Current Clock Time and the Current Date . . . . . . . . . . . . .
12.2.3 DB1 Parameters Used for the Integral Real-Time Clock . . . . . . . . . . . .
12 - 1
12.2
12
12
12
12
2
2
3
4
12.3.1
12.3.2
12.3.3
12.3.4
Programming the Integral Real-Time Clock in DB1,
Setting the Clock in DB1 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Setting the Prompt Time in DB1 . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Setting the Operating Hours Counter in DB1 . . . . . . . . . . . . . . . . . . . .
Entering the Clock Time Correction Factor in DB1 . . . . . . . . . . . . . . . .
12
12
12
12
12
5
5
6
7
7
12.4
Structure of the Clock Data Area
12 - 8
12.5
Structure of the Status Word and How to Scan It
12.6
Setting Parameters for the Clock Data Area and the Status Word
in the System Data Area . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12 - 15
Programming the Integral Real-Time Clock in the
User Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Reading and Setting the Clock . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming the Prompt Function . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming the Operating Hours Counter . . . . . . . . . . . . . . . . . . . . .
Entering the Clock Time Correction Factor . . . . . . . . . . . . . . . . . . . . .
12
12
12
12
12
12.3
12.7
12.7.1
12.7.2
12.7.3
12.7.4
x
12 - 12
21
21
25
30
35
S5-100U
Contents
Page
13
Connecting the S5-100U to SINEC L1, for CPU 102 and Higher
13.1
Connecting the Programmable Controllers to the
L1 Bus Cable . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
13 - 1
13 - 1
13.2
Setting Parameters in the Programmable Controller
for Exchanging Data . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
13.2.1 How to Program in a Function Block, for CPU 102 and Higher
13.2.2 Setting Parameters in DB1, for CPU 103 and Higher . . . . . . . . . . . . . .
13.3
13.3.1
13.3.2
13.3.3
14
13 - 1
13 - 2
13 - 5
13
13
13
13
Coordinating Data Exchange in the Control Program . . . . . . . . . . . . . . .
Sending Data
Receiving Data . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming the Messages in a Function Block . . . . . . . . . . . . . . . . .
7
8
9
11
Module Spectrum . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14 - 1
14.1
General Technical Specifications
14 - 3
14.2
Power Supply Modules
14.3
Central Processing Units
14.4
Bus Units . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14 - 10
14.5
Interface Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14 - 14
14.6
14.6.1
14.6.2
14.6.3
Digital Input Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Digital Output Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Digital Input/Output Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14
14
14
14
14 - 4
14 - 7
16
16
26
36
14.7
Analog Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14.7.1 Analog Input Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14.7.2 Analog Output Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15
14 - 38
14 - 38
14 - 56
Function Modules
15 - 1
15.1
Comparator Module 2×1 to 20 mA/0.5 to 10 V
15.2
Timer Module 2×0.3 to 300 s
15.3
Simulator Module
15.4
Diagnostic Module
15 - 1
15 - 4
15 - 7
15 - 9
xi
Contents
S5-100U
Page
15.5
Counter Module 2×0 to 500 Hz
15.6
15.6.1
15.6.2
15.6.3
15.6.4
15.6.5
15 - 12
Counter Module 25/500 kHz . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Installation Guidelines . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Data Transfer . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Functional Description of the Counter Mode . . . . . . . . . . . . . . . . . . . .
Functional Description of the Position Decoder . . . . . . . . . . . . . . . . . .
Entering New Setpoints for the Counter and
Position Decoder . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15.6.6 Addressing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15.7
Closed-Loop Control Module IP 262 . . . . . . . . . . . . . . . . . . . . . . . . . .
15 - 41
15.8
IP 263 Positioning Module
15 - 45
15.9
IP 264 Electronic Cam Controller Module
15.10
IP 265 High Speed Sub Control
15 - 52
15.11
Positioning Module IP 266 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15 - 55
15.12
Stepper Motor Control Module IP 267
15 - 59
15.13 Communications Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15.13.1 Printer Communications Module CP 521 . . . . . . . . . . . . . . . . . . . . . .
15.13.2 Communications Module CP 521 BASIC . . . . . . . . . . . . . . . . . . . . . .
xii
15
15
15
15
15
15 - 62
15 - 62
15 - 65
17
20
25
27
29
15 - 38
15 - 39
15 - 49
S5-100U
Contents
Appendices
A
Operations List, Machine Code and List of Abbreviations
A - 1
A.1
A.1.1
A.1.2
A.1.3
A.1.4
Operations List . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
System Operations, for CPU 102 and Higher . . . . . . . . . . . . . . . . . . . . .
Evaluation of CC 1 and CC 0 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
A
A
A
A
A
1
1
8
13
14
A.2
Machine Code Listing
A - 15
A.3
A - 18
B - 1
B
Dimension Drawings
C
Active and Passive Faults in Automation Equipment
D
Information for Ordering Accessories . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
D - 1
E
Reference Materials
E - 1
F
Siemens Addresses Worldwide . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
C - 1
F - 1
Index
xiii
S5-100U
How to Use This System Manual
The S5-100U is a programmable controller for lower and intermediate performance ranges. It meets
all the requirements for a modern programmable controller. To use this controller optimally, you
need detailed information.
In this system manual we have attempted to present this information as completely and as well
organized as possible. Certain information is repeated in various chapters so that you do not have
to leaf through the manual to find what you need.
This How to Use This System Manual section gives you information that will make it easier for you
to find what you need. This section explains how the manual is organized.
Contents of This System Manual
Hardware Description (Chapters 1, 2, and 3)
These chapters describe the controllers: how they fit into the SIMATIC® S5 family of
programmable controllers, how they function, and how you install them.
Start-Up Information (Chapters 4, 5, and 6)
These chapters summarize the information you need to start up your programmable controller.
These chapters describe how the hardware and software influence each other.
The Programming Language of the Programmable Controllers (Chapters 7, 8, and 9)
These chapters describe the structure, operations, and structuring aids of the STEP® 5 programming language.
Functions of the Programmable Controllers (Chapters 10, 11, 12, 13)
Each of these chapters contains a complete description of a particular function, from wiring to
programming. Subjects include analog value processing, counter and interrupt inputs, integral
clock, and the programmable controller as a SINEC® L1 slave.
Module Spectrum (Chapters 14 and 15)
These chapters contain information about all the currently available S5-100U modules that you
can use to expand your controller. Chapter 15, Function Modules, includes the modules that
require an extensive description (i. e., more than just technical specifications).
Overviews (Appendices)
In these chapters you will find not only a complete list of operations but also dimension
drawings, a description of errors that may occur during operation of the programmable controller,
maintenance and repair procedures, a list of accessories, and reference literature about
programmable controllers.
You will find correction pages at the end of the system manual. Use them to indicate any
corrections, additions, or suggestions for improvement you might have. Send these suggestions to
us. They will help us to improve the next edition of this system manual.
xv
S5-100U
Conventions
This system manual is organized in menu form to make it easier for you to find information. This
means the following:
Each chapter is marked with printed tabs.
At the front of the system manual is an overview page that lists the title of each chapter.
Following this page, you will find a table of contents.
At the beginning of each chapter is a table of contents for that chapter. Each chapter has three
level headings that are numbered. The fourth level heading is not numbered but appears in
boldface type.
Pages, figures, and tables are numbered separately for each chapter. On the back of the table
of contents for each chapter you will find a list of the figures and tables that appear in that
chapter.
This system manual employs the following specific structuring devices:
Specific terms have characteristic abbreviations (e. g., programmer is PG).
Appendix A contains a list of abbreviations.
Footnotes are marked with a raised number (e. g., “1”) or a raised asterisk (“ * ”). You will find
the corresponding explanations in the lower margin of the page or under a figure or table if the
footnote appears in one of these.
Lists are designated with bullets (• as in this particular listing) or with hyphens (-).
Cross references are indicated as follows: (see section 7.3.2). There are no references to
specific page numbers.
Dimensions in drawings are indicated in millimeters and inches.
Value ranges are indicated as follows: 17 to 21 or 17-21.
Especially important information appears in framed boxes such as the following:
Warning
You will find definitions for the terms “Warning,” “Danger,” “Caution,” and “Note” in the SafetyRelated Guidelines for the User at the end of the introduction.
xvi
S5-100U
Changes Made to the Second Edition of the S5-100U System Manual
(Order Number: 6ES5 998-0UB22)
S5-100U System Manual (Order Number 6ES5 998-0UB23) has been completely revised:
The format was adapted to the other system manuals in the SIMATIC S5 family.
The contents were updated and reorganized.
Some of the functions of CPU 103 have been expanded:
The default settings (default parameters) for DB1 have been integrated into CPU 103
version 8MA03. This feature makes it easier for you to use the internal CPU functions.
The following chapters were included or completely revised in the system manual:
- Chapter 9 “Integrated Blocks and Their Functions”
- Chapter 12 “Integral Real-Time Clock, for CPU 103 Version 8MA02 and Higher”
- Chapter 13 “Connecting the S5-100U to SINEC L1, for CPU 102 and Higher”
The execution times of some operations have been reduced considerably, compared to the
“old” CPU 103. For the new execution times refer to the list of operations in Appendix A.
The S5-100U system has been expanded to include an additional module:
The “Communications Module CP 521 BASIC” is described in section 15.10.2.
Changes Made to the Third Edition of the S5-100U System Manual
(Order Number: 6ES5 998-0UB23)
The contents were updated.
Training
Siemens offers a wide range of training courses for SIMATIC S5 users. Contact your Siemens
representative for more information.
xvii
S5-100U
Safety-Related Guidelines for the User
This document provides the information required for the intended use of the particular product. The
documentation is written for technically qualified personnel.
Qualified personnel as referred to in the safety guidelines in this document as well as on the product
itself are defined as follows.
• System planning and design engineers who are familiar with the safety concepts of automation
equipment.
• Operating personnel who have been trained to work with automation equipment and are
conversant with the contents of the document in as far as it is connected with the actual
operation of the plant.
• Commissioning and service personnel who are trained to repair such automation equipment and
who are authorized to energize, de-energize, clear, ground, and tag circuits, equipment, and
systems in accordance with established safety practice.
Danger Notices
The notices and guidelines that follow are intended to ensure personal safety, as well as protect the
products and connected equipment against damage.
The safety notices and warnings for protection against loss of life (the users or service personnel) or
for protection against damage to property are highlighted in this document by the terms and
pictograms defined here. The terms used in this document and marked on the equipment itself have
the following significance.
Danger
Warning
indicates that death, severe personal injury
or substantial property damage will result if
proper precautions are not taken.
Caution
indicates that death, severe personal injury or
substantial property damage can result if
Note
indicates that minor personal injury or
property damage can result if proper
contains important information about the
product, its operation or a part of the document to which special attention is drawn.
Proper Usage
Warning
xviii
The equipment/system or the system components may only be used for the
applications described in the catalog or the technical description, and only in
combination with the equipment, components, and devices of other manufacturers as far as this is recommended or permitted by Siemens.
The product will function correctly and safely only if it is transported, stored, set
up, and installed as intended, and operated and maintained with care.
1
Figures
1-1
Members of the SIMATIC S5 System Family
1 - 1
S5-100U
The S5-100U has the following features:
Modular Design
Depending on the CPU you use, the S5-100U allows you to have a maximum of 448 digital
inputs and outputs. It is suitable for machine control and for process automation and monitoring
on a medium scale. The S5-100U allows a broad expansion capability with various types of
modules to adapt optimally to a control task.
Rugged, Lightweight Design
All of the modules you can use with the S5-100U are block-type modules that are small, rugged,
and easy to use. The modules operate without fans. None of these modules has electromagnetically sensitive electronics. The modules are plugged into bus units and screwed tightly
so that they are vibration-proof.
The bus units snap onto a standard mounting rail. You can configure the S5-100U in one or
more tiers and configure it vertically or horizontally. The S5-100U offers such a wide range of
configuration possibilities that you can use it in rough and difficult operating conditions.
Simple Programming
The programming language is STEP 5 and its comprehensive operations set. It provides three
different methods of representation, - four, if you have a CPU 103 or higher.
You can use any of the U series programmers to program your S5-100U, or you can load
programs from memory submodules.
1-2
2
2.1
Programmable Controller Design . . . . . . . . . . . . . . . . . . . . . . . . .
2 - 1
2.2
2.2.1
2.2.2
2 - 3
2 - 3
2 - 6
Figures
2-1
2-2
2-3
2-4
2-5
2-6
The S5-100U . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Functional Units of the S5-100U . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Example of an Arithmetic Logic Unit’s Mode of Operation
Accumulator Design . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Structure of the External I/O Bus . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Data Cycle . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
2
2
2
2
2
2
1
3
5
5
6
7
Tables
2-1
2-2
Retentive and Non-Retentive Operands . . . . . . . . . . . . . . . . . . . . . . . . . .
Number of Bits per Module in the Shift Register . . . . . . . . . . . . . . . . . . . .
2 - 5
2 - 8
S5-100U
Input/output modules
Input/output modules transfer information between the CPU and such process peripherals as
sensors, actuators, and transducers. You can use the following types of input/output modules
with your S5-100U:
Digital input modules and digital output modules (4, 8, and 16/16 channel)
- Use these modules for simple control tasks involving signal states “0” and “1” only.
Analog input modules and analog output modules
- Use these modules to record and generate such variable quantities as currents and
voltages.
Timer module
- Use this module to set various times without having to change the program.
Counter module
- Use this module to count pulses up to 500 Hz. You can input comparison values without
High-speed counter/position detection module
- Use the high-speed counter to record high-speed counter pulses of 25/500 kHz. You can
use this module for position detection in a positioning task.
Comparator module
- This module makes it possible for you to monitor preset comparison values, such as for
current and voltage.
Simulator module
- Use this module to generate digital input signals or to display digital output signals.
Diagnostic module
- Use this module to check the function of the I/O bus.
Communications module (CP)
- Use this module to output message texts with the date and clock time to a connected
printer. You can also use this module to connect to external systems.
Intelligent I/O module (IP)
- Use these intelligent input/output modules for such special tasks as temperature control
and positioning tasks.
Bus units with terminal blocks (Crimp-snap-in or SIGUT, screw type)
Use bus units to connect the CPU to input/output modules. You can plug two input/output
modules into a single bus unit.
Interface modules (IM)
Use these modules to assemble your S5-100U in a multi-tier configuration.
Standard mounting rail
Mount your programmable controller on the standard mounting rail.
2-2
S5-100U
2.2
The remainder of this chapter explains how your S5-100U processes your program.
2.2.1
Functional Units
CPU
Program
memory
Timers
Counters
Flags
Process
I/O image
tables
Interrupt
process
I/O image
tables*
System
data
RAM
ROM
Memory
submodule
(operating
system)
Processor
ALU
(ACCU 1 and 2,
bit-ACCU (RLO))
Serial
port
I/O bus
Digital
modules:
- input
- output
Analog
modules:
- input
- output
Function
modules
I/O modules
* Beginning with CPU 103, version 8MA02
Figure 2-2. Functional Units of the S5-100U
2-3
S5-100U
Program Memory (EPROM/EEPROM)
In order to safely store the control program outside of your S5-100U, you must store it on an
EPROM or EEPROM memory submodule (see section 4.4).
Programs that are available on a memory submodule (EPROM or EEPROM) can be copied to the
internal program memory (see section 4.3). This internal program memory is a reserved area of the
CPU's internal RAM memory.
The internal RAM memory has the following characteristics:
The memory contents can be changed quickly.
Memory contents are lost when there is a supply voltage failure and there is no battery backup.
Operating System (ROM)
The operating system contains system programs that determine how the user program is executed,
how inputs and outputs are managed, how the memory is divided, and how data is managed.
The operating system is fixed and cannot be changed.
Process Image Tables (PII, PIQ)
Signal states of input and output modules are stored in the CPU in “process image tables”. Process
image tables are reserved areas in the RAM of the CPU.
Input and output modules have the following separate image tables:
Process image input table (PII)
Process image output table (PIQ)
Serial Interface
You can connect programmers, operator panels, and monitors to the serial port (cable connector).
You can use the serial port to connect your S5-100U as a slave to the SINEC L1 local area network.
Timers, Counters, Flags
The CPU has timers, counters, and flags available internally that the control program can use.
The program can set, delete, start, and stop the timers and counters. The time and count values are
stored in reserved areas of the RAM memory.
There is another area in the RAM memory where information such as intermediate results can be
stored as flags. You can address the flags by bits, bytes, or words.
If battery backup is available, then some of the flags and counters remain in the internal RAM
memory even if the supply voltage fails or your S5-100U is switched off. These flags and counters
are retentive.
2-4
S5-100U
Table 2-1 gives information about the number and retentive characteristics (the internal memory
contents are retained/are not retained) of these timers, counters, and flags.
Table 2-1. Retentive and Non-Retentive Operands
Retentive
Non-Retentive
Operand
CPU 100 to 103
CPU 100
CPU 102
CPU 103
Flags
0.0 to 63.7
64.0 to 127.7
64.0 to 127.7
64.0 to 255.7
Counters
0 to 7
8 to 15
8 to 31
8 to 127
0 to 15
0 to 31
0 to 127
Timers
Arithmetic Unit
The arithmetic unit (ALU) consists of two accumulators, ACCU 1 and 2. The accumulators can
process byte and word operations.
Load
information
from the PII.
Process
information
in ACCU 1 and ACCU 2.
Transfer
information
to the PIQ.
Figure 2-3. Example of an Arithmetic Logic Unit’s Mode of Operation
Accumulator Design
ACCU 2
15
8
7
High byte
ACCU 1
0
Low byte
15
8
High byte
0
7
Low byte
Figure 2-4. Accumulator Design
Processor
According to the control program, the processor calls statements in the program memory in
sequence and executes them. It processes the information from the PII and takes into consideration
the values of internal timers and counters as well as the signal states of internal flags.
External I/O Bus
The I/O bus is the electrical connection for all signals that are exchanged between the CPU and the
S5-100U modules in a programmable controller.
2-5
2.2.2
S5-100U
The S5-100U has a serial bus for the transfer of data between the CPU and the I/O modules. This
serial bus has the following characteristics:
The modular design permits optimal adaptation to the particular control task.
No addresses have to be set on the I/O modules.
A terminating resistor connector is not required.
Direct access to individual modules is not possible.
A number of shift registers moves the data (Figure 2-5).
Four data bits and one check bit for bus monitoring are assigned to each slot in the bus unit. All
modules requiring more than four data bits have their own shift register and therefore do not have to
use the shift register of the particular slot.
Slot number
CPU
Data ring bus
0
1
2
3
5 Bits
Shift register
of a slot
Shift register of an
8-channel digital module
or of an analog module
n x 5 Bits
n=2, 4, 6 to 16
Figure 2-5. Structure of the External I/O Bus
2-6
S5-100U
Data Cycle
Prior to a program scan, the external I/O bus transfers current information from the input modules to
the process image input table (PII). At the same time, information contained in the process image
output table (PIQ) is transferred to the output modules.
Data cycle
Shift
data
Program scanning
Shift
data
Time axis
Transfer data from the shift register to
the output modules.
Load data from the input
modules into the shift register.
Figure 2-6. Data Cycle
Interrupt Data Cycle, for CPU 103 version 8MA02 and higher
There is an interrupt input data cycle prior to each time-controlled or interrupt-driven program scan.
Before a time-controlled program scan, current information about the input modules is read into the
interrupt PII. Before an interrupt-driven program scan, interrupt inputs on slots 0 and 1 only are read
into the interrupt PII.
Following a time-controlled program scan, there is not an interrupt output data cycle until data has
been moved into the interrupt PIQ via a transfer operation (see section 6.6.2).
Information is output from the interrupt PIQ to the output modules during an interrupt output data
cycle. The PIQ is updated.
2-7
S5-100U
Length of the Shift Register
The total length of the shift register is obtained from the sum of the data bits of all plugged-in
modules and of the empty slots. The check bit is not counted.
You must know the length of the shift register to be able to determine the data cycle time. Data
cycle time is 25 µs x number of data bits.
Table 2-2. Number of Bits per Module in the Shift Register
Plugged-in Module
Number of Data Bits
Diagnostic module or vacant slot
4
4-channel digital input and output modules
4
500 Hz comparator module, 500 Hz timer module,
500 Hz counter module
4
25 KHz counter module
32
8-channel digital input and output modules
8
Digital input and output module, 16 inputs/16 outputs
16
Simulator module
8
Analog modules for each activated channel
16*
CP 521, IP 262, IP 266, IP 267
64
Refer to the individual manuals for information on other modules.
This does not apply to the 466-8MC11 analog input module (8 data bits).
The CPU specifies the maximum length of the shift register in a particular configuration.
CPU 100:
256 data bits, 128 (max.) of these from analog modules
CPU 102:
480 data bits, 256 (max.) of these from analog modules
CPU 103:
704 data bits, 512 (max.) of these from analog modules
Note
If the maximum expansion allowed is exceeded, the S5-100U goes into the STOP mode.
The “PEU” bit (I/O not ready) is set in the ISTACK.
2-8
S5-100U
Examples:
a) CPU 100:
This CPU lets you operate six digital modules (8-channel) and two analog modules
(4-channel):
[6 x 8+2 x (4 x 16)]=48+128 & lt; 256
b) CPU 100:
This CPU does not let you use three digital modules (8-channel) with three analog
modules (4-channel) because the maximum permissible number of analog data bits
would be exceeded:
[3 x 8+3 x (4 x 16)]=24+192 & lt; 256
c) CPU 102:
This CPU lets you operate seven digital modules (8-channel) and four analog
modules (4-channel):
[7 x 8+4 x (4 x 16)]=56+256 & lt; 480
d) CPU 102:
This CPU does not let you use 20 digital modules (8-channel) with 5 analog
would be exceeded:
[20 x 8+5 x (4 x 16)]=160+320=480
e) CPU 103:
This CPU lets you operate 24 digital modules (8-channel) and eight analog modules
(4-channel):
[24 x 8+8 x (4 x 16)]=192+512=704
f)
CPU 103:
This CPU does not let you use 31 digital modules (8-channel) with four analog
modules (2-channel) because the maximum permissible number of slots would be
exceeded:
[31 x 8+4 x (2 x 16)]=248+128 & lt; 704
2-9
3
3.1
3.1.1
3.1.2
3.1.3
3.1.4
3
3
3
3
3
1
1
5
7
8
3.2
3.2.1
3.2.2
3.2.3
3.2.4
Connection Methods: Screw-Type Terminals and Crimp Snap-in . .
3
3
3
3
3
9
9
12
13
18
3.3
3.3.1
3.3.2
3.3.3
3
3
3
3
20
20
21
25
3.4
Wiring Arrangement, Shielding, and Measures to . . . . . . . . . . . . .
3 - 29
3.4.1
3.4.2
3.4.3
3.4.4
3.4.5
3
3
3
3
3
29
30
31
32
33
Figures
3-1
3-2
3-3
3-4
3-5
3-6
3-7
3-8
3-9
3-10
3-11
3-12
3-13
3-14
3-15
3-16
3-17
3-18
3-19
3-20
3-21
3-22
3-23
3-24
3-25
3-26
3-27
3-28
Mounting the PS 930 Power Supply Module . . . . . . . . . . . . . . . . . . . . . . .
Removing Bus Units . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Coding System to Prevent an Inadvertent Interchange of Modules . . . . . . . .
Interconnecting Tiers with Interface Modules (6ES5 316-8MA12)
Multi-Tier Configuration in a Cabinet with the
IM 316 Interface Module (6ES5 316-8MA12) . . . . . . . . . . . . . . . . . . . . . . .
Cabinet Mounting with a Series of Devices . . . . . . . . . . . . . . . . . . . . . . . .
Vertically Mounting a Programmable Controller . . . . . . . . . . . . . . . . . . . . . .
SIGUT/Screw-Type Connection Method . . . . . . . . . . . . . . . . . . . . . . . . . .
Mounting the Crimp Snap-in Terminal
Disconnecting a Terminal . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Connecting a Power Supply Module and a CPU . . . . . . . . . . . . . . . . . . . . .
Two-Wire Connection of a Sensor to Channel 2 . . . . . . . . . . . . . . . . . . . . .
Two-Wire Connection of a Lamp to Channel 3 . . . . . . . . . . . . . . . . . . . . . .
Connecting a Sensor to Channel 4 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Connecting a Lamp to Channel 6 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Front View of the Digital I/O Module with a Crimp Snap-In Connector
(simplified view and not true to scale)
Connecting a Sensor and a Load to Digital Input/Output Module 482 . . . . . .
Configuration Possibility: S5-100U with 115/230 V AC Power Supply
for Programmable Controller, Sensors, and Actuators . . . . . . . . . . . . . . . . .
Configuration Possibility: S5-100U with 24 V DC Power Supply (with Safe
Electrical Isolation According to DIN VDE 0160) for Programmable
Controller, Sensors, and Actuators . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Non-Grounded Operation; 24 V DC Power Supply (with Safe Electrical Isolation According to DIN VDE 0160) for Programmable Controller and I/Os . . .
Example: Non-Floating Connection of I/Os to the S5-100U . . . . . . . . . . . . .
Simplified Representation of a Non-Floating I/O Connection . . . . . . . . . . . .
Simplified Representation of a Galvanically Isolated Connection
of the I/Os to the S5-100U . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
A Simplified Representation of a Floating I/O Connection . . . . . . . . . . . . . .
Laying Equipotential Bonding Conductor and Signal Label . . . . . . . . . . . . . .
Fixing Shielded Cables with Various Types of Cable Clamps . . . . . . . . . . . .
Wiring Coils . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Measures for Suppressing Interference from
Fluorescent Lamps in the Cabinet . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
3
3
3
3
2
3
4
5
3
3
3
3
3
3
3
3
3
3
3
7
8
8
9
10
11
12
14
15
16
17
3 - 18
3 - 19
3 - 22
3 - 23
3 - 24
3 - 25
3 - 26
3
3
3
3
3
27
28
31
33
33
3 - 34
Tables
3-1
3-2
3-3
Installing, Removing, and Changing S5-100U Components . . . . . . . . . . . .
Connecting the Load Voltage . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Rules for Common Running of Lines . . . . . . . . . . . . . . . . . . . . . . . . . . . .
3 - 1
3 - 13
3 - 29
S5-100U
3
3.1
Except for the I/O module, all of the S5-100U components are mounted on standard mounting rails
in accordance with DIN EN 50022-35x15. Mount the rails on a metal plate to obtain the same
reference potential.
Bus units with a SIGUT/screw-type, or crimp snap-in connection method have different heights.
If you install, remove, or change any parts of your S5-100U system, your system must be in the
state indicated in Table 3-1.
Table 3-1. Installing, Removing, and Changing S5-100U Components
Changing:
S5-100U
Power Status
S5-100U
Operating Mode
Load
Voltage
I/O modules
STOP
OFF
Bus units
Interface modules
Power OFF
CPU power supply
Power supply
voltage OFF
X=not relevant
3.1.1
Assembling a Tier
You need the following components to configure the S5-100U:
Power supply module
Central processing unit
Bus units
I/O modules
If you do not have a 24 V DC power supply, you must have a power supply module.
Mount the first module on the extreme left end of the standard mounting rail. Add other modules to
the right of the first module.
3-1
S5-100U
Installing an Interface Module
1.
2.
3.
4.
5.
Hook the interface module to the standard mounting rail.
Swing the interface module back until the slide on the bottom snaps into place on the rail.
Use the ribbon cable to connect the module to the last bus unit.
Use connecting cable 712-8 to join the two interface modules.
Connect the cable to the “out” socket on the programmable controller tier and to the “in” socket
on the expansion tier.
6. Securely screw the connecting cable plugs in place. Use two screws for each connecting cable
plug.
Removing an Interface Module
1. Only for the IM 316: Remove the hold-down screws from the plugs and remove the connecting
cable.
2. Remove the connecting ribbon cable from the adjacent bus unit.
3. Use a screwdriver to press down on the slide located on the bottom of the interface module.
4. Swing the module up and out of the standard mounting rail.
3-6
S5-100U
3.1.3
Cabinet Mounting
Make sure that the S5-100U, the power supply, and all modules are well grounded. Mount the
S5-100U on a metal plate to help prevent noise. There should be electrical continuity between the
grounded enclosure and the mounting rails. Make sure that the system is bonded to earth.
You can use the 8LW system or the 8LX system mounting plates (see Catalog NV 21).
Adequate ventilation and heat dissipation are important to the proper operation of the system. You
must have at least 210 mm (8.3 in.) between each mounting rail (see Figures in Appendix B) for
proper ventilation.
Always locate the power supply and the CPU on the lowest tier to ensure better heat dissipation.
To measure cabinet ventilation, define the total heat loss by calculating the sum of all typical heat
losses (see Catalog ST 52.1).
IM 316 interface module
Metal plate
At least 210 mm
(8.3 in.)
At least 210 mm
(8.3 in.)
CPU
Figure 3-5.
Multi-Tier Configuration in a Cabinet with the IM 316 Interface
3-7
S5-100U
Wiring devices
and/or cable duct
a
At least 45 mm
(1.77 in.)
210 mm+a
(8.3 in.+a)
CPU
Figure 3-6. Cabinet Mounting with a Series of Devices
3.1.4
Vertical Mounting
You can also mount the standard mounting rails vertically and then attach the modules one over the
other. Because heat dissipation by convection is less effective in this case, the maximum ambient
temperature allowed is 40 °C (104 °F).
Use the same minimum clearances for a vertical configuration as for a horizontal configuration.
You must install a clamp (see Catalog SA 2) on the lower end of the programmable controller tier to
hold the modules mechanically in position.
CPU
Clamp
Figure 3-7. Vertically Mounting a Programmable Controller
3-8
S5-100U
3.2
Wiring
3.2.1
SIGUT Screw-Type Terminal
When using screw-type terminals, you can clamp two cables per terminal. It is best to use a
3.5-mm screwdriver to tighten the screws.
Permissible cable cross-sections are:
A stranded conductor with a core end sleeve:
A solid conductor:
2 x 0.5 to 1.5 mm2
2 x 0.5 to 2.5 mm2
M3 screw
Wire clamp
Cables
Figure 3-8. SIGUT/Screw-Type Connection Method
3-9
S5-100U
3.2.3
All I/O modules are plugged into bus units. Connect the I/O modules to the terminal blocks of the
bus units. The connections illustrated in this section are of the screw terminal type (SIGUT
connection method).
You can also use the crimp snap-in connection method described in section 3.2.1. In both cases,
the terminal assignments are marked on the terminal blocks.
The assignments listed in Table 3-2 always apply for connecting the load voltage.
Table 3-2. Connecting the Load Voltage
Load Voltage
Terminal 2
24 V DC
L+
M
115/230 V AC
Terminal 1
L1
N
115/230 V AC digital modules can be operated with a load voltage of 120/230 V AC.
Note
For digital outputs, energy is temporarily stored in an internal capacitor for about
100 ms after the L+ supply is switched off.
Please note that this energy may be sufficient to activate low-rating loads (e.g., pulse
valves) for a triggered output.
3-13
S5-100U
Connecting Four-Channel Digital Modules
All of these modules are designed for a two-wire connection. You can therefore wire directly to the
sensor or output field device. An external distribution block is not required.
The four channels of a module are numbered from .0 through .3. (Numbers .4 through .7 are only
significant for the ET 100 distributed I/O system.) Each channel has a pair of terminals on the terminal block.
The terminal assignments and the connection diagram are printed on the front plate of the module.
Connecting Four-Channel Input Modules
Example: Connecting a sensor to channel 2 (address I 3.2) on the input module in slot 3
(see Figure 3-12)
L+
M
1
F
2
3
.0
.4
4
5
.1
.5
6
7
.2
.6
8
9
.3
.7
10
1
3
5
7
9
4
2
4
6
8
10
DIGITAL INPUT
4 x 24 - 60 V DC
6ES5 430-8MB11
1
2
3
4
5
6
L+
M
Sensor
Figure 3-12. Two-Wire Connection of a Sensor to Channel 2
3-14
S5-100U
Connecting Four-Channel Output Modules
Example: Connecting a lamp to channel 3 (address Q 1.3) on the output module in slot 1
(see Figure 3-13)
1
F
2
3
.0
.4
L+
M
4
5
.1
.5
6
7
.2
.6
8
9
.3
.7
10
1
3
5
7
9
5
2
4
6
8
10
DIGITAL OUTPUT
4 x 24 V DC/2 A
6ES5 440-8MA22
1
2
3
4
5
6
L+
M
Lamp
Figure 3-13. Two-Wire Connection of a Lamp to Channel 3
3-15
S5-100U
Connecting Eight-Channel Digital Modules
These modules do not have a two-wire connection. You therefore need an external distribution
block.
The eight channels of a module are numbered from .0 through .7. One terminal on the terminal
block is assigned to each channel. The terminal assignment and the connection diagram are printed
Connecting Eight-Channel Input Modules
The sensors must be connected to terminal 1 via the L+ terminal block.
Example: Connecting a sensor to channel 4 (address I 3.4) on an input module in slot 3
(see Figure 3-14)
1
L+
F
2M
.0
4
.1
3
.2
6
.3
5
.4
8
.5
7
.6
10
.7
9
1
4
DIGITAL INPUT
8 x 24 V DC
6ES5 421-8MA12
1
2
3
4
5
2
L+
5
3
4
7
6
9
8
10
Sensor
M
6
L+Terminal
Figure 3-14. Connecting a Sensor to Channel 4
3-16
S5-100U
Connecting Eight-Channel Output Modules
The actuators must be connected to terminal 2 via the M (negative) terminal block. This does not
apply to the digital output module 8× 5 to 24 V DC/0.1 A (see section 14.6.2).
Example: Connecting a lamp to channel 6 (address output Q 5.6) on an output module in slot 5
(see Figure 3-15)
1
2
L+
M
4
.0
3
.1
6
.2
5
.3
8
.4
7
.5
10
.6
1
3
5
7
9
9
.7
5
2
DIGITAL OUTPUT
8 x 24 V DC/0.5 A
6ES5 441-8MA11
1 2
3
4
5
L+
4
6
8
10
Lamp
M
6
M Terminal
Figure 3-15. Connecting a Lamp to Channel 6
3-17
3.2.4
S5-100U
Use only slots 0 through 7 when you plug the module into the bus unit. Use a 40-pin cable
connector with a screw-type connection or crimp snap-in connection for wiring. The module does
not have a two-wire connection. You must therefore use an external distribution block.
Every channel is assigned a terminal on the 40-pin connector. The channel numbers are printed on
the front plate.
The 16 channels on the input side (IN) are numbered from n.0 through n.7 and from n+1.0 through
n+1.7. The 16 channels on the output side (OUT) are numbered from n.0 through n.7 and from
n+1.0 through n+1.7. “n” is the start address of the slot. Slot 0, for example, has the start
address of n=64 (see chapter 6).
OUT
n+1
n
L+
.0
.1
.2
.3
.4
.5
.6
.7
M
L+
.0
.1
.2
.3
.4
.5
.6
.7
M
IN
1
b
1
2
3
4
5
5
6
6
7
7
8
0.5 A
3
4
8
9
9
10
10
11
11
12
12
13
13
14
0.5 A
n+1
2
14
15
15
16
16
17
17
18
18
19
19
20
20
n
L+
.0
.1
.2
.3
.4
.5
.6
.7
NC
NC
.0
.1
.2
.3
.4
.5
.6
.7
M
40-pin crimp
snap-in connector
Figure 3-16. Front View of the Digital I/O Module with a Crimp Snap-In Connector
3-18
S5-100U
Example:
The start address for the modules is 65.3. Inputs and outputs have the same address.
A sensor is to be connected to input I 64.4 and a lamp to output Q 7.3.
Figure 3-17 illustrates the wiring on the front connector.
OUT
IN
L+
L+
1
3
4
4
5
5
6
6
7
7
8
M
2
3
A 65.3
1
2
8
9
10
10
11
11
12
12
13
13
14
14
15
15
16
16
17
17
18
18
19
19
20
L+
9
20
E 64.4
M
Lamp
M
L+
M
M Terminal
Sensor
L+Terminal
Figure 3-17. Connecting a Sensor and a Load to Digital Input/Output Module 482
Note
Chapter 11 describes how to connect analog modules.
3-19
3.3
3.3.1
S5-100U
Power Supply
The entire control for the S5-100U consists of the following separate electrical circuits:
Control circuit for the S5-100U (24 V DC)
Control circuit for the sensors (24 V DC)
Load circuit for the actuators (24 V DC or 115/230 V AC)
Control Circuit
The power source for the control circuit supplies the CPU, the bus units, the programmer interface,
and the internal control circuits for the I/O modules. When the incoming supply is 24 V DC/1 A, the
PS 931 power supply module provides an internal supply of +9 V up to a total of 1 A current input
to the I/O modules. The grounding spring on the CPU forces the control circuit to be connected to
the standard mounting rail. The grounding spring must also be protected from interference. The
grounding spring must be grounded.
Load Circuit
The power source for the load circuit supplies the actuators of the process peripherals.
It is suggested that you use one of the following for a 24 V DC power supply:
The PS 931 power supply module (see Chapter 14)
A Siemens load power supply from the 6EV1 series (see Appendix D)
If you use load power supplies other than the recommended ones, make certain that the load
voltage is in the range of 20 to 30 V (including ripple).
Note
If you use a switched-mode power supply unit to supply floating analog modules and
BEROs, then this supply must be filtered through a network.
You can connect several mutually independent load circuits adjacent to each other on a single
programmable controller. These connections can either be non-floating or floating (see
section 3.3.3).
3-20
S5-100U
3.3.2
Figures 3-18, 3-19, and 3-20 display different configuration possibilities. Pay attention to the
following points when you design your configuration. The numbers appearing in parentheses in the
following points refer to the numbers in Figures 3-18 to 3-20.
You must have a main switch (1) in accordance with VDE 0100 for your S5-100U, the sensors,
and the actuators.
You do not need an additional fuse (2) to connect your S5-100U and the load circuit to power if
your radial lines are a maximum of 3 meters (9.84 feet) long and are inherently earth-fault proof
and short-circuit proof.
You need a load power supply (3) for 24 V DC load circuits.
- You need a back-up capacitor (rating: 200 µF per 1 A of load current) if you have nonstabilized load power supplies.
If you have AC load circuits, galvanic isolation via a transformer (4) is recommended.
You should ground the load circuit at one end. Provide a removable connection (5) to the
ground conductor on the load power supply (terminal M) or on the isolating transformer.
- You must provide earth-fault monitoring for any non-grounded load circuits.
You must separately fuse (6 and 7) the load voltage for sensor circuits and for actuator circuits.
You must connect the standard mounting rail of the S5-100U to the ground conductor through a
capacitor (8, to suppress high-frequency noise) for a non-grounded configuration.
You must have a low-resistance connection between the standard mounting rail and the
cabinet’s chassis ground (10) for a grounded configuration.
You need a power fuse (9) to protect against a short-circuit occurring in the power supply.
3-21
S5-100U
(1)
L1
L2
L3
N
PE
(9)
(2)
(5)
(4)
PS
(10)
CPU
DI
DI
1
2
1
2
DO DO
1
2
1
2
(6)
(7)
230 V AC
Figure 3-18. Configuration Possibility: S5-100U with 115/230 V AC Power Supply
3-22
EWA 4NEB 812 6120-02b
S5-100U
(1)
L1
L2
L3
N
PE
(2)
(3)
(5)
M
CPU
L+
L+
M
(10)
DI
DI
1
2
1
2
DO DO
1
2
1
2
(6)
(7)
M
Figure 3.19
L+
3-23
L1
S5-100U
(1)
L2
L3
N
PE
(2)
(8)
100 K
1 µF/
500 V AC
Install the standard mounting
rail electrically isolated
(3)
M
CPU
L+
L+
M
DI
DI
1
2
1
2
DO DO
1
2
1
2
(6)
(7)
M
L+
Figure 3-20. Non-Grounded Operation; 24 V DC Power Supply
Interference voltages are discharged to the ground conductor (PE) via a capacitor. You can prevent
static charges by connecting a high-ohmic resistor (approx. 100 k / W) parallel to the capacitor.
3-24
S5-100U
3.3.3
The S5-100U is powered by its own control circuit. The I/Os are powered by the load circuit.
The circuits can either be connected to the same grounding point (non-floating) or galvanically
isolated (floating).
Example of a Non-Floating Connection of Digital Modules
A 24 V DC load circuit has the same chassis grounding as the control circuit of the CPU.
Central
grounding point
PS
CPU
L+
M
Common
chassis ground
M
L+
Load power
supply
Figure 3-21. Example: Non-Floating Connection of I/Os to the S5-100U
3-25
S5-100U
The common chassis grounding connection makes it possible for you to use reasonably priced nonfloating I/Os. These modules function according to the following principles.
Input modules
- The ground line, line M (control circuit chassis) is the reference potential. A voltage drop V1
on line affects the input signal level VI.
Output modules
- Terminal 2 (M) of the terminal block is the reference potential. A voltage drop V2 on the
line raises the chassis potential of the output driver and thus reduces the resulting control
voltage VCV.
Figure 3-22 shows a simplified connection of the S5-100U with a non-floating external I/O.
+9 V
Data
GND
VCV
CPU
L+
M
VI
1
2
V1
L+
24 V DC supply
V2
M
Figure 3-22. Simplified Representation of a Non-Floating I/O Connection
3-26
S5-100U
When you have a non-floating configuration, you must make certain that the voltage drop on
cables and does not exceed 1 V. If 1 V is exceeded, the reference potentials could change
and the modules could malfunction.
Warning
If you use non-floating I/O modules, you must provide an external connection between
the chassis ground of the non-floating I/O module and the chassis ground of the CPU.
Example of a Floating Configuration with Digital Modules
Floating configuration is required in the following situations.
When you need to increase interference immunity in the load circuits
When load circuits cannot be interconnected
When you have AC load circuits
If you have a floating configuration, the PLC's control circuit and the load circuit must be galvanically
isolated.
Figure 3-23 shows a simplified connection of galvanically isolated I/Os.
Central
grounding point
PS
CPU
L+
M
L+
M
Load power
supply
Figure 3-23.
Simplified Representation of a Galvanically Isolated Connection of the
I/Os to the S5-100U
3-27
S5-100U
Figure 3-24 shows a simplified schematic for the connection of floating I/O modules.
+9 V
Data
GND
CPU
1L+
M
L1
N
2L+
2M
Figure 3-24. A Simplified Representation of a Floating I/O Connection
3-28
S5-100U
3.4
Wiring Arrangement, Shielding and Measures against
Electromagnetic Interference
This section describes the wiring arrangements for bus cables, signal cables, and power supply
cables that guarantee the electromagnetic compatibility (EMC) of your installation.
3.4.1
Running Cables Inside and Outside a Cabinet
Dividing the lines into the following groups and running the groups separately will help you to
achieve electromagnetic compatibility (EMC).
Group A:
Shielded bus and data lines (for programmer, OP, printer, SINEC L1, Profibus,
Industrial Ethernet, etc.)
Shielded analog lines
Unshielded lines for DC voltage 60 V
Unshielded lines for AC voltage 25 V
Coaxial lines for monitors
Group B:
Unshielded lines for DC voltage & gt; 60 V and 400 V
Unshielded lines for AC voltage & gt; 25 V and 400 V
Group C:
Unshielded lines for AC voltage & gt; 400 V
You can use the following table to see the conditions which apply to the running of the various
combinations of line groups.
Table 3-3. Rules for Common Running of Lines
Group A
Group B
Group C
Group A
Group B
Group C
Legend for table:
Lines can be run in common bundles or cable ducts
Lines must be run in separate bundles or cable ducts (without minimum distance)
Inside cabinets, lines must be run in separate bundles or cable ducts and outside cabinets but
inside buildings, lines must be run on separate cable trays with a gap of a least of 10 cm
between lines.
3-29
3.4.2
S5-100U
Running Cables Outside Buildings
Run lines outside buildings where possible in metal cable supports. Connect the abutting surfaces of
the cable supports galvanically with each other and ground the cable supports.
When you run cables outdoors, you must observe the regulations governing lightning protection and
grounding. Note the general guidelines:
Lightning Protection
If cables and lines for SIMATIC S5 devices are to be run outside buildings, you must take measures
to ensure internal and external lightning protection.
Outside buildings run your cables
either
In metal conduits grounded at both ends
or
In steel-reinforced concrete cable channels
Protect signal lines from overvoltage by using:
Varistors
or
Lightning arresters filled with inert gas
Install these protective elements at the point where the cable enters the building.
Note
Lightning protection measures always require an individual assessment of the entire
system. If you have any questions, please consult your local Siemens office or any
company specializing in lightning protection.
Grounding
Make certain that you have sufficient equipotential bonding between the devices.
3-30
S5-100U
3.4.3
Potential differences may occur between separate sections of the system if
• Programmable controllers and I/Os are connected via non-floating interface modules or
• Cables are shielded at both ends but grounded via different sections of the system.
Potential differences may be caused, for instance, by differences in the system input voltage. These
differences must be reduced by means of equipotential bonding conductors to ensure proper
functioning of the electronic components installed.
Note the following for equipotential bonding:
A low impedance of the equipotential bonding conductor makes equipotential bonding more
efficient.
If any shielded signal cables connected to earth/protective earth at both ends are laid between
the system sections concerned, the impedance of the additional equipotential bonding conductor
must not exceed 10 % of the shield impedance.
The cross-section of the equipotential bonding conductor must be matched to the maximum
compensating currents. The following cross-sections are recommendable:
- 16 mm2 copper wire for equipotential bonding line up to 200 m (656.2 ft).
- 25 mm2 copper wire for equipotential bonding line over 200 m (656.2 ft).
Use equipotential bonding conductors made of copper or zinc-plated steel. Equipotential bonding
conductors are to be connected to earth/protective earth via a large contact area and to be
protected against corrosion.
The equipotential bonding conductor should be laid in such a way as to achieve a relatively
small contact area between equipotential bonding conductor and signal cables (see Figure 3-25).
Signal line
Equipotential bonding conductor
Figure 3-25. Laying Equipotential Bonding Conductor and Signal Cable
3-31
S5-100U
3.4.4 Shielding Cables
Shielding is a measure to weaken (attenuate) magnetic, electric or electromagnetic interference
fields.
Interference currents on cable shields are discharged to ground over the shield bar which has a
conductive connection to the housing. So that these interference currents do not become a source
of noise in themselves, a low-resistance connection to the protective conductor is of special
importance.
Use only cables with shield braiding if possible. The effectiveness of the shield should be more than
80%. Avoid cables with foil shielding since the foil can easily be damaged by tension and pressure;
this leads to a reduction in the shielding effect.
As a rule, you should always shield cables at both ends. Only shielding at both ends provides good
suppression in the high frequency range.
As an exception only, you can connect the shielding at one end. However, this attenuates only the
lower frequencies. Shielding at one end can be of advantage in the following cases:
If you cannot run an equipotential bonding conductor
If you are transmitting analog signals (e.g. a few microvolts or microamps)
If you are using foil shields (static shields).
Always use metallic or metalized connectors for data lines for serial connections. Secure the shield
of the data line at the connector housing. Do not connect the shield to the PIN1 of the connector
strip!
In the case of stationary operation, you are recommended to insulate the shielded cable without
interrupt and to connect it to the shield/protective ground bar.
Note
If there are potential differences between the earthing points, a compensating current
can flow over the shielding that is connected at both ends. For this reason, connect an
additional equipotential bonding conductor.
3-32
S5-100U
Note the following when connecting the cable shield:
Use metal cable clamps for fixing the braided shield. The clamps have to enclose the shield over
a large area and make good contact (see Figure 3-26).
Connect the shield to a shield bar immediately at the point where the cable enters the cabinet.
Route the shield to the module; do not connect it to the module.
Figure 3-26. Fixing Shielded Cables with Various Types of Cable Clamps
3.4.5
Special Measures for Interference-Free Operation
Arc Suppression Elements For Inductive Circuits
Normally, inductive circuits (e.g. contactor or relay coils) energized by SIMATIC S5 do not require to
be provided with external arc suppressing elements since the necessary suppressing elements are
already integrated on the modules.
It only becomes necessary to provide arc supressing elements for inductive circuits in the following
cases:
• If SIMATIC S5 output circuits can be switched off by additionaly inserted contactors (e.g. relay
contactors for EMERGENCY OFF). In such a case, the integral suppressing elements on the
modules become ineffective.
• If the inductive circuits are not energized by SIMATIC S5.
You can use free-wheeling diodes, varistors or RC elements for wiring inductive circuits.
Wiring coils activated by alternating current
Wiring coils activated by direct current
with diode
with Zener diode
with RC element
with varistor
Figure 3-27. Wiring Coils
3-33
S5-100U
Mains Connection for Programmers
Provide a power connection for a programmer in each cabinet. The plug must be supplied from the
distribution line to which the protective ground for the cabinet is connected.
Cabinet Lighting
Use, for example, LINESTRA® lamps for cabinet lighting. Avoid the use of fluorescent lamps since
these generate interference fields. If you cannot do without fluorescent lamps, you must take the
measures shown in Figure 3.28.
Shielding grid over lamp
Shielded cable
Metal-encased switch
Mains filter or shielded mains cable
Figure 3-28. Measures for Suppressing Interference from Fluorescent Lamps
in the Cabinet
3-34
4
Start-up and Program Tests
4.1
4.1.1
4.1.2
4.1.3
Operating Instructions . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
CPU Operator Panel . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Operating Modes . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Performing an Overall Reset on the Programmable Controller . . . .
4-1
4-1
4-1
4-2
4.2
4.2.1
4.2.2
Starting Up a System . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Suggestions for Configuring and Installing the Product . . . . . . . . .
Procedures for Starting Up the Programmable Controller . . . . . . .
4-3
4-3
4-4
4.3
Loading the Program into the Programmable Controller
4-5
4.4
4.4.1
4.4.2
Backing Up the Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Backing Up the Program on a Memory Submodule . . . . . . . . . . . .
Function of the Back-Up Battery . . . . . . . . . . . . . . . . . . . . . . . . .
4-7
4-7
4-8
4.5
Program-Dependent Signal Status Display “STATUS”
4-8
4.6
Direct Signal Status Display “STATUS VAR”
4.7
Forcing Outputs, “FORCE”, for CPU 103 and Higher
4.8
Forcing Variables, “FORCE VAR”
4.9
Search Function
4.10
Program Check, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . .
4-9
4-10
4-10
4-11
4-11
Figures
4-1
4-2
4-3
4-4
4-5
4-6
CPU Operator Panel . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Procedure for Loading the Program Automatically . . . . . . . . . . . . . . . . . . .
Procedure for Loading the Program Manually . . . . . . . . . . . . . . . . . . . . . .
Procedure for Backing Up the Program on a Memory Submodule
“STATUS” Test Function . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
“STATUS VAR” Test Function . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
4
4
4
4
4
4
1
5
6
7
9
9
Starting Up the Programable Controller
4 - 4
Table
4-1
S5-100U
4
4.1
4.1.1
CPU Operator Panel
RUN
I
O
ON/OFF switch
Operating mode display
(green LED: RUN)
STOP
BATTERY
OFF/
LOW
Battery low
(yellow LED lights:
battery discharged or
not installed)
(red LED: STOP)
RUN
STOP
COPY
Operating mode switch
Figure 4.1 CPU Operator Panel
ON/OFF Switch
The ON/OFF switch turns on the CPU’s voltage regulators. This switch does NOT separate the
voltage regulator from the L+/M terminals.
Operating Mode Switch
Use the operating mode switch to select either the RUN or STOP operating mode. The CPU
automatically goes into the START-UP mode during the transition from STOP to RUN (see section
7.4.2).
4.1.2 Operating Modes
STOP Operating Mode
The program is not executed.
The current values for timers, counters, flags, and process image I/O tables are saved when the
STOP mode begins.
The output modules are disabled (signal status “0”).
The process image I/O tables, timers, and non-retentive flags and counters are set to “zero”
during the transition from STOP to RUN.
RUN Operating Mode
The program is processed cyclically.
Already started timers continue to run.
The signal states for the input modules are stored.
The output modules are addressed.
The RUN operating mode can also be set after an OVERALL RESET, that is, when the program
memory is empty.
4-1
S5-100U
START-UP Operating Mode
The operating system processes DB1 and accepts the parameters (see section 9.1).
Either the start-up organization block OB21 or OB22 is processed (see section 7.4.2).
The amount of time start-up requires is not limited since the scan time monitor is not activated.
Neither time-controlled program processing nor interrupt-driven program processing is possible.
The input modules and output modules are disabled during start-up.
Changing Operating Modes
A change in operating mode can be caused by the following:
The operating mode switch - when its position is changed.
A programmer - if the operating mode switch on the programmable controller is set to RUN.
Malfunctions - if one occurs that causes the programmable controller to go into the STOP
operating mode (see chapter 5).
4.1.3 Performing an Overall Reset on the Programmable Controller
You should perform an overall reset before you input a new program. An overall reset erases the
following:
The programmable controller's program memory
All data (flags, timers, and counters)
All error IDs
Note
If you do not perform an overall reset, then the information indicated above is retained
even if the program is overwritten.
Manual Reset
To perform a manual overall reset, you must:
1. Set the operating mode switch to STOP.
2. Remove the battery.
3. Set the ON/OFF switch to “0”.
4. Change the ON/OFF switch to “1”.
5. Insert the battery.
Performing an Overall Reset with the Programmer
You can select the overall reset function from the programmer's menu line. Refer to the
programmer manual.
4-2
S5-100U
4.2
The following section contains suggestions for configuring and starting up a system containing
4.2.1
A programmable controller is often used as a component in a larger system. The suggestions
contained in the following warning are intended to help you safely install your programmable
controller.
Warning
Adhere to any safety and accident-prevention regulations applicable to your
situation and system.
If your system has a permanent power connection (stationary equipment) that is
not equipped with an isolating switch and/or fuses that disconnect all poles,
install either a suitable isolating switch or fuses in the building wiring system.
Connect your system to a ground conductor.
Before start-up, if you have units that operate using the main power supply,
make sure that the voltage range setting on the equipment matches the local
main power voltage.
When using a 24 V supply, make sure to provide proper electric isolation
between the main supply and the 24-V supply. Power supply units must meet
the requirements of EN 60950 or be manufactured in accordance with
DIN VDE 0551/EN 60742 and DIN VDE 0160. The requirements of electromagnetic compatibility (EMC) must also be adhered to.
Fluctuations or deviations of the supply voltage from the rated value may not
exceed the tolerance limit specified in the technical data. If they do, functional
failures or dangerous conditions can occur in the electronic modules or
equipment.
Take suitable measures to make sure that programs that are interrupted by a
voltage dip or power failure resume proper operation when the power is restored.
Make sure that dangerous operating conditions do not occur even momentarily.
If necessary, force an EMERGENCY OFF.
EMERGENCY OFF devices must be in accordance with EN 60204/IEC 204
(VDE 0113) and be effective in all operating modes of the equipment. Make
certain to prevent any uncontrolled or undefined restart when the
EMERGENCY OFF devices are released.
Install power supply and signal cables so that inductive and capacitive
interference can not affect the automation functions.
Install your automation system and its operative components so as to prevent
unintentional operation.
Automation equipment can assume an undefined state in the case of a wire
break in the signal lines. To prevent this, take the proper hardware and software
safety measures when linking the inputs and outputs of the automation
equipment.
4-3
4.2.2
S5-100U
Table 4-1.
Prerequisites
Procedures
System and programmable
controller are off-load.
• Check the mechanical
configuration and wiring.
(see section 3.1 and 3.2).
Remarks
Displays
Check the mechanical assembly
(VDE 0100 and VDE 0160). Terminal “M” of the load power
supply and the ground terminal of
the programmable controller must
be connected to the central
grounding point (standard
mounting rail). For non-floating
modules, a module’s “M” terminal
must be connected to the
programmable controller’s “M”
terminal.
“0” and the operating mode
switch to ”STOP”.
• Switch on the power supply
and load power supply.
• Set ON/OFF switch to “1”.
• Connect programmer to
CPU.
• Reset the programmable
controller (see section 4.1.3).
• Set operating mode switch to
RUN.
• Switch on sensor power
supply.
• Actuate the sensors one after
the other.
• Switch on power supply for
output modules and
actuators.
• Force the outputs with the
“FORCE” programmer
function.
• Red fault LEDs on the I/O
modules lights.
• Red LED of the CPU lights;.
yellow LED lights if the battery is
low or not installed.
• Green LED on the CPU lights.
The input signals in the PII can be
observed with the “STATUS VAR”
programmer function.
• Red fault LEDs on the input
modules darken.
• Green LEDs on the input modules
light.
• Red fault LEDs on the output
modules darken.
The switching states of the
associated actuators change.
• Green LEDs of the output
modules light up.
Program is loaded.
• Red LED of the CPU lights.
The system is in operation.
• Green LED of the CPU lights.
Program on memory submodule
• Set ON/OFF switch to “0”.
• Plug in the memory
submodule.
“1”. *
• Test program and make any
necessary corrections.
STOP.
• Switch on the load.
RUN.
• Back up the program.
* For the CPU 102 only:
4-4
press the & lt; COPY & gt; key simultaneously (manual loading).
S5-100U
4.3
You can load a program from a connected programmer (online operation). When you load a
program, it is transferred to the programmable controller's program memory. There are specific
instructions in your programmer manual for doing this.
You can also load your program from a memory submodule, but only valid blocks can be loaded.
See section 7.5.2. The different memory submodules you can use are listed in Appendix D.
Section 4.3 describes how you can load a program from a memory submodule.
Warning
You can connect or disconnect memory submodules only in the Power OFF mode.
Automatic loading copies the program from a memory submodule into the program memory of the
CPU. You can only load valid blocks. See section 7.5.2.
Figure 4-2 shows how a program can be loaded automatically.
No battery is installed
(yellow LED lights).
PLC overall reset
Switch the S5-100U off.
Plug memory submodule
into the CPU.
Switch the S5-100U on.
Error
Red LED flashes.
CPU 100: red LED lights;
CPU 102/103: red LED flickers.
Perform error diagnostics
(see section 5.1).
Program is loaded.
Program is in the
S5-100U.
The CPU 102 is in
the Normal Mode.
Figure 4-2. Procedure for Loading the Program Automatically
4-5
S5-100U
Manual loading copies the program from a memory submodule into the program memory of the
CPU. If a back-up battery is installed, any program in the memory is completely erased.
Figure 4-3 shows how a program can be loaded manually.
Turn off the S5-100U.
Plug memory submodule into the CPU.
Press & lt; COPY & gt; key
and hold it down.
Turn on the S5-100U.
Error
Red LED flashes.
Release & lt; COPY & gt;
key.
Red LED flickers; release
& lt; COPY & gt; key.
Program is
loaded
Red LED
lights.
Red LED
flashes.
Red LED shows
steady light;
program is in the
S5-100U.
No valid program
is in submodule.
Perform error
diagnostics
(see section 5.1).
The CPU 102 is
in Test Mode
Figure 4-3. Procedure for Loading the Program Manually
4-6
S5-100U
4.4
A program can be backed up only if the back-up battery is connected. Backing up copies a program
from the program memory of the CPU to a memory submodule. Only valid blocks are backed up.
As soon as you have changed the integral, default DB1 data block, it is a valid block that can be
backed up. See section 7.5.2.
4.4.1
You can use various EEPROM memory submodules to back up a program. Appendix D contains a
list of the submodules you may use. Figure 4-4 illustrates how to back up a program on a memory
submodule.
Battery low LED (yellow)
lights.
Yes
Insert / replace
battery.
No
Plug EEPROM submodule into the CPU.
for at least 3 s.
Error
Red LED flickers;
Red LED flashes.
key.
Program is
loaded. 1)
Red LED
lights.
Red LED lights;
Program backed up
on EEPROM
submodule.
- No / wrong submodule plugged
in.
- No program is in
the S5-100U.
Red LED
flashes.
Perform error
diagnostics
(see section 5.1).
The CPU is in the
Normal Mode.
1) Program load time:
40 s/1024 statements
Figure 4-4. Procedure for Backing Up the Program on a Memory Submodule
4-7
4.4.2
S5-100U
If the power fails or the programmable controller is turned off, the contents of the internal (retentive)
memory are stored only if a back-up battery is connected. When power is recovered or when the
programmable controller is turned on, the following contents are available:
Control program and data blocks (see section 7.3.5)
Retentive flags and count values (see section 2.2.1)
ISTACK contents (see section 5.3]
Note
Insert and replace the battery while the programmable controller is turned on.
Otherwise, an OVERALL RESET is required when you turn the programmable
controller on.
The lithium battery in the programmable controller has a life expectancy of at least
one year.
The yellow LED on the operator panel lights up if the battery fails.
Warning
Do not charge lithium batteries. They could explode. Dispose of used batteries properly.
4.5
This test function displays the current signal states and the Result of Logic Operations (RLO) of the
individual operands during program processing.
You can use this test function to make corrections to the program.
Note
The current signal states are displayed only in the RUN operating mode.
4-8
S5-100U
Cycle trigger
STATUS
ontrol
ogram
= Q 2.0 1 1
Transfer data
Figure 4-5. “STATUS " Test Function
Refer to your programmer manual for information about the test function on your programmer.
4.6
This test function specifies the status of the operands (inputs, outputs, flags, data words, counters,
or timers) at the end of program processing. You can obtain information about inputs and outputs
from the process image I/O tables of the selected operands.
Cycle trigger
Control program
Transfer data
STATUS
VAR
Figure 4-6. “STATUS VAR” Test Function
4-9
4.7
S5-100U
Outputs can be set directly to a desired status even without the control program. This enables you
to control the wiring and functionality of output modules. This does not change the process I/O
image table, but the output disable condition is cancelled.
Note
The programmable controller must be in the STOP operating mode.
Refer to your programmer manual for information about calling up the test function on your
programmer.
4.8
The process image I/O table of the operands is changed regardless of the programmable controller's
operating mode. You can change the following variables: I, Q, F, T, C, and D.
The program is processed in the RUN operating mode using the changed process variables. They
can be changed again during program scanning without an acknowledgement being required. The
process variables are forced asynchronously to the program scanning.
Special characteristics
You can change the I, Q, and F variables in the process I/O image table by bits, bytes, or words.
For the T and C variables in KM and KH format, note the following:
- For programmers with screens, you must also enter “YES” in the system commands input
field in the presettings screen.
- You must be careful when you force edge trigger flags. You do not want to enable a higherorder byte inadvertently because this could give you a timer or counter value you did not set.
The signal status display breaks off if there is an error in the format entry or operand entry. The
programmer then displays the “NO FORCING POSSIBLE” message.
4-10
S5-100U
4.9
Search Function
This function allows you to search for specific terms in the program and list them on the programmer's display panel. You can perform program changes at this point.
You can have search runs in the following programmer functions:
INPUT
OUTPUT
STATUS
Some of the items you can search for are:
Statements
(e.g., A I 0.0)
Operands
(e.g., Q 3.5)
Labels
(e.g., X 01); possible only in function blocks
Addresses
(e.g., 0006 H)
Note
Search runs are handled differently by different programmers. The respective users
guides contain extensive information about search runs.
4.10
When this programmer function is called up, program scanning is stopped at a definite point. The
cursor indicates this breakpoint, which is a statement in the program. The programmable controller
scans the program up to the statement selected. The current signal states and the RLO up to the
statement selected are displayed (as in the “STATUS” test function).
The program can be scanned section by section by shifting the breakpoint. Program scanning takes
place as follows:
All jumps in the block called are executed.
Block calls are executed immediately. The program check is not resumed until control is
returned to the calling block.
The following applies during the program check:
The two mode LEDs are not lit.
The program writes to the PIQ and reads out the PII.
No process image (data cycle) is transferred.
All outputs are set to zero.
4-11
S5-100U
During the program check, you can execute the following additional test and programmable
controller functions from the programmer:
Input and output (program modification possible)
Direct signal status display (STATUS VAR)
Forcing of outputs and variables (FORCE, FORCE VAR)
Information functions (ISTACK, BSTACK)
If the function is aborted due to hardware faults or program errors, the programmable controller goes
into the STOP mode and the red LED on the control panel of the CPU lights.
Refer to your programmer manual for information about calling up these functions on your
programmer.
4-12
5
Diagnostics and Troubleshooting
5.1
Indication of Errors by LEDs
5.2
5.2.1
5.2.2
5.2.3
5.2.4
CPU Malfunctions . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
“ISTACK” Analysis Function . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Interrupt Analysis . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Errors during Program Copying . . . . . . . . . . . . . . . . . . . . . . . . . .
Explanation of the Mnemonics Used in “ISTACK” . . . . . . . . . . . . .
5
5
5
5
5
5.3
5.3.1
5.3.2
Program Errors . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Locating the Error Address . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Tracing the Program with the “BSTACK” Function
5 - 8
5 - 8
5 - 11
5.4
I/O Faults . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
5 - 12
5.5
System Parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
5 - 12
5.6
The Last Resort
5 - 13
5 - 1
1
1
4
5
6
Figures
5-1
5-2
5-3
5-4
5-5
Structured Program with an Illegal Statement . . . . . . . . . . . . . . . . . . . . . .
Addresses in the CPU’s Program Memory . . . . . . . . . . . . . . . . . . . . . . . .
Calculating the Error Address . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Tracing the Program with “BSTACK”
Analyzing the Cause of a Fault in the I/Os . . . . . . . . . . . . . . . . . . . . . . . .
5
5
5
5
5
8
9
10
11
12
5
5
5
5
5
5
1
2
4
5
6
7
Tables
5-1
5-2
5-3
5-4
5-5
5-6
Error Indication and Error Analysis . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
ISTACK Output (Bytes 1 to 16)
Interrupt Analysis . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Errors when Copying . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Meaning of the Remaining ISTACK Bits . . . . . . . . . . . . . . . . . . . . . . . . . .
Mnemonics Used for the Interrupt Display . . . . . . . . . . . . . . . . . . . . . . . .
S5-100U
5
5.1
The programmable controller's operator panel will show you if your device is not functioning
correctly (see Table 5-1).
Table 5-1. Error Indication and Error Analysis
Error Indication
Error Analysis
CPU in STOP
Red LED lights
CPU malfunction
Use the programmer to execute an interrupt analysis
(see section 5.2).
CPU in STOP
Red LED flashes
Error when loading or backing up the program
(see section 5.2).
CPU in RUN
Green LED lights
Faulty operation
Program error
(see section 5.3)
or
I/O fault
Execute a fault analysis
(see section 5.4).
If both LEDs light, your programmable controller is in the START-UP operating mode.
5.2
CPU Malfunctions
5.2.1
The interrupt stack is an internal CPU memory area where the causes of malfunctions are stored. If
there is a malfunction, a bit in the respective byte of the memory area is set. Using the programmer, you can read out the contents of this memory area byte-by-byte.
Calling the ISTACK
The call is made through the programmer menu in the STOP operating mode.
Refer to your programmer manual for the key sequence.
Note
Only ISTACK bytes 1 through 6 can be output in the RUN mode. There is no cause for
an interrupt to force the CPU to go into the STOP mode. The control bits are output in
bytes 1 through 6.
5-1
S5-100U
The following table shows which positions in the bit pattern are relevant for error diagnosis (grayshaded bits).
Table 5-2. ISTACK Output (Bytes 1 to 16)
Bit
Byte
7
6
5
3
BST
SCH
1
4
SCH
TAE
2
1
Abso- Syst. Dalute
ta Word
Addr. (SD)
0
ADR
BAU
EA0A
SD 5
EA0C
SD 6
EA0E
SD 7
EBAC
SD 214
(UAW)
EBAA
SD 213
EBA8
SD 212
EBA6
SD 211
2
3
STO
ZUS
STO
ANZ
NEU
STA
BAT
PUF
4
AF
KOPF
NI
5
6
KEIN
AS
SYN
FEH
UR
LAD
NINEU
7
IRRELEVANT
8
IRRELEVANT
9
10
STOPS
SUF
NAU
TRAF
ZYK
NNN
STS
STUEB
SYSFE
PEU
BAU
ASPFA
OR
STA
TUS
VKE
ERAB
OR
VKE
FKT
11
12
13
14
15
16
5-2
ANZ1
ANZ0
OVFL
6th nesting level
IRRELEVANT
4th nesting level
5th nesting level
OR
OR
VKE
VKE
FKT
FKT
S5-100U
Table 5-2. ISTACK Output (Bytes 17 to 32) [continued]
Bit
Byte
17
7
6
5
4
3
2nd nesting level
2
1
0
OR
VKE
Abso- Syst. Dalute
ta Word
Addr. (SD)
FKT
EBA4
EBA2
EB9A
FKT
Start address of the data block (low)
23
Block stack pointer (high)
24
Block stack pointer (low)
25
Step address counter (high)*
26
Step address counter (low)*
27
Operation register (high)
28
Operation register (low)
29
ACCU 2 (high)
30
ACCU 2 (low)
31
ACCU 1 (high)
32
SD 203
Start address of the data block (high)
22
VKE
SD 204
EB96
21
FKT
OR
SD 205
EB98
1st nesting level
SD 206
Nesting depth (0 to 6)
20
VKE
SD 207
EB9C
19
OR
SD 208
EB9E
3rd nesting level
SD 209
EBA0
18
SD 210
ACCU 1 (low)
The absolute memory address of the next statement to be processed from the faulty block is displayed.
If the step address counter displays a DB1 address, then there is a DB1 parameter setting error (see
section 9.1).
5-3
S5-100U
5.2.2 Interrupt Analysis
When there is an interrupt in program processing, you can use the following table to determine the
cause of the error. The CPU always goes into the STOP mode.
Table 5-3. Interrupt Analysis
ISTACK
Display
Byte
ASPFA and
KEIN AS
and NNN
and
SAZ=FFFF*
(CPU 102)
10
6
9
25 and 26
BAU
Cause of Error
Remedy
Error during program transfer from the PG to the
PLC:
Overflow of the internal program memory during
compilation
Shorten program.
Compress memory.
10
When automatically loading the program:
- Battery is missing or dead and there is no
valid program available on the memory
submodule
Replace the battery and
recreate the program, or
load the program again.
NAU
10
Interruption in the power supply voltage to the
CPU
NINEU
6
The program in the PLC memory is defective.
Cause:
• A power failure has interrupted one of the
following operations.
- Compress
- Block transfer from the PG to the PLC or
memory submodule to the PLC
- PLC overall reset
• Battery has been replaced while the power
was off.
Perform an overall reset
and load the program
again.
NNN
9
• Statement cannot be decoded.
• Nesting level is too high.
• Parameter exceeds permitted limits.
Eliminate program
errors.
PEU
10
• Check the power
supply in the
expansion unit.
• Check the
connections.
• Check the module
slots.
STOPS
9
Operating mode switch on STOP
STS
9
• Software stop by statement (STP)
• STOP requested by programmer
STUE
9
Block stack overflow: the maximum block call
nesting depth (16) has been exceeded.
Eliminate program
errors.
SYS** FEH
10
Correct DB1.
5-4
Expansion module not connected
I/O bus malfunction
Maximum length of shift register exceeded
Module unknown
Module in wrong slot
Set to RUN
SAZ = STEP address counter - The ISTACK bytes 25 and 26 read “1111 1111(FF)”.
Relevant only for the PG 605U and for the CPU 103, version 8MA03 and higher.
S5-100U
Table 5-3. Interrupt Analysis (continued)
ISTACK
Display
Byte
SUF*
9
Substitution error:
Function block called with an incorrect actual
parameter
Change actual
parameter.
TRAF
9
Transfer error
• Data block statement programmed with a
data word number larger than the data
block length
• Data block statement programmed without
previously opening a data block
Eliminate program error
(see your programmer
manual).
ZYK
10
Scan time exceeded:
The program processing time exceeds the
set monitoring time. Causes:
• Program too long
• Interrupts too frequent
Check the program for
continuous loops or
shorten program.
Cause of Error
Remedy
* Relevant for CPU 102, version 8MA02 and higher
5.2.3
Error message: after the & lt; COPY & gt; key is released, the red LED continues flashing.
Table 5-4. Errors when Copying
ISTACK
Display
ASPFA
Cause of Error
Loading the memory submodule into the PLC:
• Program on the memory submodule is too long
for the PLC's program memory.
Remedy
Check the program on the
memory submodule.
• Program on the module contains an invalid block
number.
ASPFA
ASPFA and
KEIN AS and
NNN
and SAZ=FFFF*
(CPU 102)
Saving from the PLC to the memory submodule:
EEPROM memory submodule is defective or too
small for the program in the PLC memory.
Replace the memory
submodule, or use a larger
EEPROM memory
submodule.
Internal program memory overflow during
compilation
Shorten program.
SAZ = STEP Address Counter
5-5
5.2.4
S5-100U
Table 5-5. Meaning of the Remaining ISTACK Bits
ISTACK
Display
Byte
Explanation
BST SCH
SCH TAE
ADR BAU
1
Shift block.
Execute shift operation.
Structure address list.
STO ANZ
STO ZUS
BAT PUF
NEU STA
3
PLC in STOP
Internal control bit for STOP/RUN change
Battery backup available
PLC not yet in cycle after Power ON
- See bytes 9 and 10 for cause.
AF*
4
Interrupt enable/enabling of time-controlled OB13 and interruptdriven OB3
KOPFNI
5
Program contains errors.
Block header cannot be interpreted.
KEIN AS**
6
Not enough S5 statement memory available
URLAD
SYNFEH
ANZ 1/ANZ 0
Overall reset, program defective
12
OV
OR
STATUS
VKE
ERAB
FKT
5-6
Condition code bits for arithmetic, logic, and shift operations.
Arithmetic overflow
ID bit of OR memory
Status ID of operand of last binary statement executed
Result of logic operation (RLO)
ID bit of first scan
13
0: O(
1: A(
OR parenthesis open
AND parenthesis open
relevant for CPU 103 only
for CPU 102: 0 = normal mode
1 = test mode
S5-100U
Table 5-6. Mnemonics Used for the Interrupt Display
Mnemonics Used
Explanation
ANZ1/ANZ0
ASPFA
Illegal memory submodule
BAU
Battery failure
ERAB
First scan
FKT
0 : O(
KE1...KE6
Nesting stack entry 1 to 6 entered for A( and O(
KEINAS
Insufficient S5 statement memory available
NAU
Power failure
NINEU
Cold restart not possible
NNN
Statement cannot be interpreted in the PLC
OR
OR memory (set by command “0”)
OVFL
Arithmetic overflow (+ or -)
PEU
I/Os not ready:
• First bus unit not connected
• Expansion module not connected
• I/O bus malfunction
• Maximum shift register length exceeded
• Unknown module
• Module in the wrong slot
STATUS
STATUS of the operand of the last binary statement executed
STOPS
STS
Operation interrupted by a programmer STOP request or
programmed STOP statements
STUE
Block stack overflow: The maximum block call nesting depth of 16
has been exceeded.
SUF
Substitution error
SYSFEH*
Error in DB1
TRAF
Transfer error for data block statements:
• When accessing a data word even though no corresponding data
block was opened or
• When the data word number is larger than the data block length
UAW
Interrupt display word
VKE
ZYK
Condition codes for various operations (see section A.1.4)
Scan time exceeded: the set maximum permissible program scan
time has been exceeded
1 : A(
Relevant only for CPU 103 version 8MA03 and higher
5-7
5.3
Program Errors
5.3.1
S5-100U
The SAZ (STEP address counter) in the ISTACK (bytes 25 and 26) contains the absolute address
of the STEP 5 statement in the programmable controller before which the CPU went into the STOP
mode.
Use the “DIR PC” programmer function to determine the associated block start address.
Example: You have entered a control program consisting of OB1, PB0 and PB7. An illegal
statement has been programmed in PB7.
OB1
PB0
JU PB0
JU PB7
PB7
Illegal
statement
L PB 0
BE
BE
BE
Figure 5-1. Structured Program with an Illegal Statement
When it reaches the illegal statement, the CPU interrupts program scanning and enters the STOP
mode with the “NNN” message. The STEP address counter is at the absolute address of the next
(but not yet scanned) statement in the program memory.
5-8
S5-100U
EE00
OB1 Header
Absolute addresses in
the CPU’s internal RAM
EE09
00
JU PB0
EE0A
EE0B
02
BE
EE0C
EE0D
EE0E
PB0 Header
EE17
EE18
EE19
00
i
JU PB7
EE2E
EE2F
i+2
BE
EE30
EE31
It is not possible to localize an error in
the program on the basis of the physical
address of the illegal statement.
The “DIR PC” function gives the
absolute start addresses of all
programmed blocks.
The error can then be localized by comparing these two addresses.
EE32
PB7 Header
EE3B
00
EE3C
EE3D
02
EE3E
EE3F
04
L PB 0
EE40
EE41
EE42
xx
Byte
Contents
25
EE
26
42
BE
F5FF
Figure 5-2. Addresses in the CPU’s Program Memory
5-9
S5-100U
Calculating the Address (necessary only when using the PG 605U)
In order to be able to make program corrections, it is necessary to have the address of the
statement that led to the fault referenced to the particular block (relative address).
The faulty block is found by comparing the SAZ (STEP address counter) contents and the
“DIR PC” display.
The relative error address gives the difference between the SAZ value and the block start address.
Figure 5-3 gives you an example of how to calculate the relative error address.
ISTACK byte
25
26
EE
42
Block
Start Address
PB0
EE18
PB7
EE3C
OB1
The absolute address EE42 is
greater than the start address for
PB7. The faulty statement is
therefore in PB7.
Calculating the relative address:
DIR PC
EE0A
EE42 - EE3C = 0006
“0006” is the relative address of the statement in PB7 following the statement that
caused the CPU to go into the STOP mode.
Figure 5-3. Calculating the Error Address
Output of an Error Statement
Use the “SEARCH” programmer function to find certain program locations and to look for the
relative error address. Refer to your programmer manual for additional information about this
5-10
S5-100U
5.3.2
Program trace with “BSTACK” is not possible on the 605U programmer.
During program processing, the following information about jump operations is entered in the block
stack (BSTACK):
The data block that was valid before program processing exited a block.
The relative return address
- It specifies the address where program processing will continue after the return from the
called up block.
The absolute return
- It specifies the memory address in the program memory where program processing will
continue after the return.
You can call up this information with the “BSTACK” programmer function in the STOP operating
mode if a fault caused the CPU to go into the STOP operating mode. “BSTACK” then reports the
status of the block stack at the time the interruption occurred.
Example:
Program scanning was interrupted at function block FB2. The CPU went into the STOP mode with
the error message “TRAF” (because of incorrect DB access, e.g., DB5 is two words long and DB3
is ten words long).
“BSTACK” lets you determine the path used to reach FB2 and lets you know which DB was open
at the time of call up. “BSTACK” contains the three (marked) return addresses.
PB1
00
xx
Interrupt with the
“TRAF” error
message
BE
PB4
OB1
PB2
00 JU PB1
02
02 JU PB4
04 JU PB2
04
00
00 C DB5
08 JC FB2
10
06
08 JC PB3
FB2
xx
BE
xx
BE
10
00
PB3
2A
xx
BE
L DW4
xx
BE
00 C DB3
16 JU FB2
18
BE
Figure 5-4. Tracing the Program with “BSTACK”
5-11
S5-100U
5.4 I/O Faults
Fault
Module with fault
indication
(red LED)
no
Power supply ok?
no
Check supply
leads.
yes
yes
Module addressable via
the process input image
(PII) and the process output image (PIQ) (STATUS VAR, FORCE VAR)
no
Red LED lights.
yes
no
Module power
supply ok?
Check
supply
leads.
yes
- Check module
(exchange).
- Check program.
no
Bus connection ok?
no
Replace bus unit.
yes
Short circuit at
the outputs?
yes
Eliminate
short
circuit.
no
no
Defective fuse
Defective
module
yes
Replace module with
simulator module.
Is a check with STATUS
VAR or FORCE VAR
possible?
yes
Replaced module
is defective.
no
yes
Check connections of
other bus units and
interface modules.
Replace fuse.
Figure 5-5. Analyzing the Cause of a Fault in the I/Os
5.5 System Parameters
The “SYSPAR” programmer function makes it possible to read out the system parameters (e.g.,
CPU software version) of the programmable controller (see programmer manual).
5-12
S5-100U
5.6
The Last Resort
The programmable controller will not go back to the RUN operating mode:
Possible cause:
The battery was installed or changed when the programmable controller
was turned off.
Remedy:
Perform an overall reset and load the program again.
How to perform an overall reset without a programmer
4. Set the ON/OFF switch to “1”.
5. Install a battery.
Contact your local Siemens representative if the above measures are ineffective.
5-13
6
Addressing
6.1
Slot Numbering . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6 - 1
6.2
Digital Modules
6 - 4
6.3
Analog Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6 - 5
6.4
6.4.1
6.4.2
6 - 6
6 - 6
6.4.3
Combined Input Modules and Output Modules . . . . . . . . . . . . . . .
Output Modules with Error Diagnostics . . . . . . . . . . . . . . . . . . . .
Digital Input/Output Module, 16 Inputs, 16 Outputs, 24 V DC
for All CPUs Version 8MA02 and Higher and
for CPU 102, Version 8MA01, Revision 5 and Higher . . . . . . . . . .
Function Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6.5
6.5.1
6.5.2
The Structure of Process Image Input and Output Tables
Accessing the Process Image Input Table (PII) . . . . . . . . . . . . . . .
Accessing the Process Image Output Table (PIQ) . . . . . . . . . . . . .
6 - 8
6 - 10
6 - 11
6.6
6.6.1
6.6.2
Interrupt Process Images and Time-Controlled Program
Processing in OB13 for CPU 103, Version 8MA02 and Higher . . . .
Accessing the Interrupt PII . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Accessing the Interrupt PIQ . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6 - 12
6 - 12
6 - 14
6.7
RAM Address Assignments
6 - 15
6 - 7
6 - 7
Figures
6-1
6-2
6-3
6-4
6-5
6-6
6-7
6-8
6-9
6-10
6-11
Address Assignment . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Consecutive Numbering of Slots in a Single-Tier Configuration . . . . . . . . .
Slot Numbering in a Multi-Tier Configuration . . . . . . . . . . . . . . . . . . . . . .
Expanding from 14 to 18 Slots . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Configuration of a Digital Address . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Address Assignment for Analog Modules . . . . . . . . . . . . . . . . . . . . . . . . .
Assignment of Process Images to the I/O Modules . . . . . . . . . . . . . . . . . .
Accesses to the PII . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Accesses to the PIQ . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Accesses to the Interrupt PII . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Accesses to the Interrupt PIQ . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
6
6
6
6
6
6
6
6
6
6
6
1
1
2
3
4
5
9
10
11
13
14
6
6
6
6
6
6
6
7
8
12
15
16
Tables
6-1
6-2
6-3
6-4
6-5
6-6
Error Messages for Output Modules with Error Diagnostics . . . . . . . . . . . .
Structure of the PII and the PIQ . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Structure of the Interrupt PII and the Interrupt PIQ . . . . . . . . . . . . . . . . . .
Important Addresses in the RAM . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
System Data Area Assignment . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
S5-100U
6
Addressing
Addressing
The inputs and the outputs have different assigned addresses so that you can access them
specifically. The I/O addresses are the same as the module slot addresses.
When you mount a module in a slot on a bus unit, the module is assigned a slot number and
consequently a fixed byte address in one or both process image I/O tables.
Connect the sensors and actuators to the terminal block. The terminal selected determines the
channel number.
Process image I/O
tables in the CPU
I/O module
Address in the process image input
table (PII)
Slot number
Channel number
Address in the process image output
table (PIQ)
Control
program
Address
in a
statement
Data direction: module - CPU
Figure 6-1. Address Assignment
6.1
Slot Numbering
The programmable controller can have a maximum of four tiers. You can use up to 16 bus units
(32 slots). The slots are numbered consecutively. Numbering begins with “0” at the slot beside
the CPU. Whether a module is plugged in or not has no effect on the numbering.
Slot numbers
CPU
0
1
2
3
30 31
Figure 6-2. Consecutive Numbering of Slots in a Single-Tier Configuration
6-1
Addressing
S5-100U
If the programmable controller consists of more than one tier, numbering of the expansion tiers is
continued at the slot on the extreme left.
Slot numbers
26 27 28 29 30 31
18 19 20 21 22 23 24 25
8
9 10 11 12 13 14 15 16 17
CPU
0
1
2
3
4
5
6
7
Figure 6-3. Slot Numbering in a Multi-Tier Configuration
When expanding your system, always add the new bus units to the topmost tier on the right. Otherwise, the slot numbers on the right of the new bus units will be changed, requiring address changes
in your control program.
Note
After every expansion, check to make certain that the addressing used in the control
program is the same as that in the actual configuration.
6-2
S5-100U
Addressing
Example:
Expanding from 14 to 18 slots
Existing configuration
8
9 10 11 12 13
New bus units
CPU 0
1
2
3
4
5
6
7
Correct expansion procedure
8
CPU 0
1
2
3
4
5
6
7
The new bus units are added at
the right. The interface module
is moved correspondingly to the
right. The old slot numbers are
retained. Continue numbering
the new slots sequentially.
Incorrect expansion procedure
8
8
9
10 11 12
13
The slot numbers of the old bus
units move to numbers 12 to 17.
The new slots are given the numbers 8 to 11.
CPU 0
1
2
3
4
5
6
7
Figure 6-4. Expanding from 14 to 18 Slots
6-3
Addressing
6.2
S5-100U
Digital Modules
Digital modules can be plugged into all slots (0 through 31).
Only two information states (“0” or “1”, OFF or ON) per channel can be transferred from or to a
digital module. The memory requirement is one bit.
Each channel of a digital module is displayed by a bit. This is the reason that every bit must be
assigned its own number. Use the following form for a digital address:
x
. y
Bit number (channel number)
Byte number (slot number)
Figure 6-5. Configuration of a Digital Address
The “X.Y” address consists of the following two components:
Byte Address X (Slot Number X)
- The byte address is the same as the number of the slot the module is plugged into.
Channel Number Y (Bit Address Y)
- The channel number comes from the connection of the actuators or sensors to the terminals
of the terminal block. The assignment for the channel number and the terminal number is
printed on the frontplate of the module.
Example:
Address Assignment
You are connecting a 2-wire BERO proximity limit switch to an 8 x 24-V DC digital input module
(6ES5 421-8MA11) at terminal 3. The other wire is routed to an L+ (positive supply voltage) terminal block (see section 3.2 for wiring). The module is plugged into slot 3.
This defines the address used by the control program to evaluate the signal states of the BERO.
The byte address is 3 since the module is plugged into slot 3.
As shown on the frontplate, channel number 1 is used.
The complete address for the BERO switch is 3.1.
Note
You can address 4-channel digital modules only with channel numbers 0 through 3. The
channel numbers 4 through 7 printed on the frontplate are relevant only for the ET 100U
system.
6-4
S5-100U
6.3
Addressing
Analog Modules
You can plug analog modules only into slots 0 through 7. Transfer of 65,536 different items of
information is possible per channel from or to an analog module. The memory requirement is
16 bits=2 bytes=1 word. The modules are addressed byte-by-byte or word-by-word with load or
transfer operations.
The programmable controller takes this increased address requirement into account when an analog
module is plugged in.
Eight bytes (=four words) are reserved per slot.
Two bytes (=1 word) are reserved per channel.
The slot addressing area is changed.
The permissible address space extends from byte 64 (slot 0, channel 0) to byte 127 (slot 7,
channel 3).
0
1
2
3
4
64+65
72...
80...
88...
96...
Slot number
5
6
7
Channel number
104... 112... 120...
CPU
0
66+67
1
68+69
2
70+71
...79
...87
...95 ...103 ...111 ...119
...127
3
Figure 6-6. Address Assignment for Analog Modules
Examples: 1)
2)
Bytes 88+89=analog module in slot 3, channel number 0
Channel 1 address of an analog module in slot 5?
Solution: bytes 106+107
Note
Any combination of analog and digital modules is possible in slots 0 through 7.
6-5
Addressing
6.4
S5-100U
With these modules it is possible to write data from the control program to the module and to read
in data from the module to the control program.
The byte addresses in the process image input table (PII) and process image output table (PIQ) are
identical. The meaning of the transferred data is usually different.
6.4.1
In addition to the fault LED (red LED), the following output modules can signal errors to the CPU.
4 x 24 V DC / 0.5 A
(6ES5 440-8MA12)
4 x 24 V DC / 2.0 A
(6ES5 440-8MA22)
4 x 24 to 60 V DC / 0.5 A
(6ES5 450-8MB11)
You can read the error messages on input channels I X.0 and I X.1 (not with CPU 100, version
8MA01).
The following error messages are possible.
Table 6-1. Error Messages for Output Modules with Error Diagnostics
Address
Type of Error
I X.0
Short circuit on an output channel / fuse blown
or
no-load voltage
I X.1
Defective module (output transistor shorted)
X is the byte address (slot number) of the output module
Signal state “1” indicates an error is present. The PII is set to “0” for output modules without error
diagnostics.
6-6
S5-100U
6.4.2
Addressing
Plug the module only into slots 0 through 7.
This module occupies the same address space as an analog module. However, only the first two of
the eight reserved bytes are used.
The address consists of byte address n or n+1 and channel number Y. “n” is the start address of
a slot, the first of the reserved bytes (e.g., byte 64 for slot 0). “n+1” is therefore the second of the
reserved bytes. The designations “n” and “n+1” are printed on the frontplate of the module.
The input and output information occupies the same addresses.
The channel number is defined by the connection of the actuators and sensors to the crimp
connector. The channel numbers are printed on the frontplate.
Table 6-2. Address Assignment
Slot Number
0
1
2
3
4
5
6
7
Address
Channel
64.0 to
72.0 to
80.0 to
88.0 to
96.0 to
104.0 to
112.0 to
120.0 to
PII (IN)
and
PIQ
n.0 to n.7
64.7
72.7
80.7
88.7
96.7
104.7
112.7
120.7
Channel
n+1.0 to
n+1.7
65.0 to
73.0 to
81.0 to
89.0 to
97.0 to
105.0 to
113.0 to
121.0 to
65.7
73.7
81.7
89.7
97.7
105.7
113.7
121.7
(OUT)
Examples: Determining the Address
1)
2)
6.4.3
You plugged the module into slot 4 and connected an actuator at byte n,
channel 4. The address is 96.4.
Address 113.3 indicates a sensor or an actuator is connected at byte n+1,
channel 3. The module is plugged into slot 6.
Function Modules
Function modules have module-specific addressing. Some function modules are addressed like
digital modules, and other function modules are addressed like analog modules. The addressing for
each function module is explained in chapter 15.
6-7
Addressing
6.5
S5-100U
Information about inputs is stored in the process image input table (PII). Information about outputs
is stored in the process image output table (PIQ).
The PII and the PIQ each have an area of 128 bytes in the RAM memory.
The PII and the PIQ have identical structures. The PII and the PIQ can be divided into three address
areas as shown in Table 6-3.
Table 6-3. Structure of the PII and the PIQ
Byte Address in the PII
and PIQ
Module
Slot Number
0 to 31
Digital modules
0 to 31
32 to 63
64 to 127
Unassigned address space
Analog modules
0 to 7
The address space for bytes 0 through 31 is reserved for information from or to modules that
are addressed like digital modules.
The unassigned address space in bytes 32 to 63 can be used to store intermediate results.
The address space in bytes 64 to 127 is reserved for information from or to modules that are
6-8
S5-100U
Addressing
Figure 6-7 shows a possible programmable controller configuration and storage of information in the
process I/O images.
Slot
0
1
2
CPU
AI
AQ
DI
3
4
27
DE
DI DQ
28
29
30
31
DQ
Bit
Bit
7 6 5 4 3 2 1 0
7 6 5 4 3 2 1 0
0
1
2
3
4
0
1
2
3
4
27
31
31
Unassigned
address area
Unassigned
address area
Unused areas
64
65
64
65
66
67
72
79
Byte
127
Byte
PII
PIQ
127
Figure 6-7. Assignment of Process Images to the I/O Modules
6-9
Addressing
6.5.1
S5-100U
During a data cycle, data is read into the process image input table (PII) from input modules (see
section 2.2.2 - Data Cycle). This data is available to the control program for evaluation in the next
program processing cycle.
Access to the PII is expressed by the operand identifiers “I”, “IB”, or “IW” in a statement in the
control program.
The letter “L” identifies the “Load” operation (see chapter 8). The letter “A” identifies the “AND
logic” operation (see chapter 8).
PII
Bit-by-bit reading “I & lt; bit address & gt; ”
Example: Reading in the signal state of
channel 2 of a 4-channel digital input module
in slot 2
Bit number
7 6 5 4 3 2 1 0
Byte 2
A I 2.2
Byte-by-byte reading “IB & lt; byte address & gt; ”
Example: Reading in the signal states of all
channels of an 8-channel digital input module
in slot 12
L IB 12
Byte 12
15
0
ACCU 1
High byte
Low byte
Word-by-word reading “IW & lt; word address & gt; ”
Example: Reading in the analog value of
channel 3 of a 4-channel analog input module in
slot 4
L IW 102
15
0
Byte 102
Byte 103
ACCU 1
High byte
Low byte
Always set to “0”
Figure 6-8. Accesses to the PII
6-10
S5-100U
6.5.2
Addressing
During a program cycle, data coming from the control program to the output modules is written into
the process image output table (PIQ). The data is transferred to the output modules in the following
data cycle.
Access to the PIQ is expressed by the operand identifiers “Q”, “QB”, or “QW” in a statement in
The letter “T” identifies the “Transfer” operation (see Chapter 8). The “=” character assigns the
result of a logic operation (RLO) to the operand that follows the character (see chapter 8).
PIQ
Bit number
Bit-by-bit writing
“Q & lt; bit address & gt; ”
Example: Writing the signal state to
channel 6 of an 8-channel digital output
module in slot 4
7 6
Q 4.6
5 4
3 2
1 0
Byte 4
Byte-by-byte writing
“QB & lt; byte address & gt; ”
Example: Writing the signal states to all
channels of an 8-channel digital output
module in slot 29
T QB 29
15
Byte 29
0
ACCU 1
High byte
Low byte
Word-by-word writing
“QW & lt; word address & gt; ”
Example: Writing an analog value to
channel 2 of a 4-channel analog output
module in slot 6
T QW 116
15
Byte 116
Byte 117
0
ACCU 1
High byte
Low byte
Figure 6-9. Accesses to the PIQ
6-11
Addressing
6.6
S5-100U
Interrupt Process Images and Time-Controlled Program Processing
In the event of a time-controlled or process interrupt, the CPU does not access the I/O modules
directly. The CPU stores its information in interrupt process images.
The interrupt process images are used only for time-controlled or interrupt-driven program
processing.
The interrupt process images and the “normal” process images have identical structures.
The interrupt process input image (interrupt PII) and interrupt process output image (interrupt
PIQ) take up an area of 128 bytes each in the RAM.
The interrupt PII and interrupt PIQ can be divided into three address areas as shown in Table 6-4.
Table 6-4. Structure of the Interrupt PII and the Interrupt PIQ
Byte address in interrupt
Module
Slot number
0 to 31
Digital modules
0 to 31
32 to 63
64 to 127
Analog modules
0 to 7
Note
The interrupt process images can be accessed by byte or word operations only.
6.6.1
The interrupt PII can only be accessed in connection with time-controlled or interrupt-driven
program processing.
Data from inputs is read into the interrupt PII only at the beginning of time-controlled program
processing. This data is available only to the time-controlled program for evaluation.
6-12
EWA 4NEB 812 6120-02b
S5-100U
Addressing
Access to the interrupt PII is expressed by the “PB” or “PW” operand identifiers in a statement in
the time-controlled program.
The letter “L” represents the “Load” operation (see chapter 8).
Interrupt PII
Byte-by-byte reading “PB & lt; byte address & gt; ”
in slot 21
L PY 21
Byte 21
15
0
ACCU 1
High byte
Low byte
Word-by-word reading “PW & lt; word address & gt; ”
channel 2 of a 4-channel analog input module
in slot 1
L PW 76
15
0
Byte 76
Byte 77
ACCU 1
High byte
Low byte
Figure 6-10. Accesses to the Interrupt PII
Interrupt-Driven Program Processing
When a process interrupt occurs, only the data of the interrupt inputs, slots 0 and 1, is read into
the interrupt PII.
Only this data of the interrupt PII is available to the interrrupt-driven program for evaluation.
In a statement in the interrrupt-driven program, access to the interrupt PII is possible only with
the following operands: PB0, PB1, and PW0.
If other parameters are specified, the CPU goes into the STOP mode and the “NNN” error
message is specified in the ISTACK. See section 5.2.
6-13
Addressing
6.6.2
S5-100U
When accessing the interrupt PIQ, the following rules apply.
Data can be written to the interrupt PIQ only within time-controlled or interrupt-driven program
processing.
Data from a time-controlled or interrupt-driven program to external outputs is written during timecontrolled or interrupt-driven program processing both to the “normal” PIQ and the interrupt
PIQ.
Data from the interrupt PIQ is read out to the outputs in the next interrupt output data cycle.
The PIQ is copied to the interrupt PIQ after the OB1 program cycle.
Note
The interrupt output data cycle is executed only after the interrupt PIQ has been written
to.
Access to the interrupt PIQ is expressed by the “PB” or “PW” operand identifiers in a statement in
the time-controlled or interrrupt-driven program.
The letter “T” identifies the “Transfer” operation (see chapter 8).
Interrupt PIQ
Example: Writing signal states to all
module in slot 13
T PY 13
Byte 13
15
0
ACCU 1
High byte
Low byte
Example: Writing an analog value to channel 3
of a 4-channel analog output module in slot 5
T PW 110
15
0
Byte 110
Byte 111
ACCU 1
High byte
Low byte
Figure 6-11. Accesses to the Interrupt PIQ
6-14
S5-100U
6.7
Addressing
The following table gives an overview of the major addresses in the RAM of the three CPUs (in
hexadecimal code).
Table 6-5. Important Addresses in the RAM
CPU
100
102*
103
Program memory
EE00 to FFFF
D000 to DFFF
8000 to CFFF
Memory submodule
C000 to DFFF
4000 to 5FFF
0000 to 7FFF
PII, digital
E400 to E41F
EF00 to EF1F
EF00 to EF1F
PII, analog
E440 to E47F
EF40 to EF7F
EF40 to EF7F
PIQ, digital
E480 to E49F
EF80 to EF9F
EF80 to EF9F
PIQ, analog
E4C0 to E4FF
EFC0 to EFFF
EFC0 to EFFF
Timers
E280 to E29F
EC00 to EC39
EC00 to ECFF
Retentive counters
E2A0 to E2AF
ED00 to ED0F
ED00 to ED0F
Non-retentive counters
E2B0 to E2BF
ED10 to ED3F
ED10 to ED3F
Retentive flags
E300 to E33F
EE00 to EE3F
EE00 to EE3F
Non-retentive flags
E340 to E37F
EE40 to EE7F
EE40 to EE7F
Module address list
OB
FC80 to FCFF
DC00 to DDFF
FB
E100 to E17F
FD00 to FEFF
DE00 to DFFF
PB
E180 to E1FF
FF00 to FF7F
E000 to E1FF
SB
E200 to E3FF
DB
E200 to E27F
FF80 to FFFF
E400 to E5FF
System data
E080 to E0FF
EA00 to EBFF
EA00 to EBFF
EA00 to EBFF
Program memory; block address list only in TEST mode.
6-15
Addressing
S5-100U
The following table gives an overview of the most important system data in the system data area.
Table 6-6. System Data Area Assignment
System data
word
Contents
Chapter/
Section Reference
5 to 7
ISTACK (Interrupt STACK)
5.2
8 to 12
Integral real-time clock
12
33
First free program memory address
35
Program memory starting address
37
Program memory end address
40 to 45
CPU version, software release
57 to 63
SINEC L1
13
96
Scan monitoring time (value . 10 ms)
97
Calling interval for OB 13 for time-controlled program
processing (value . 10 ms)
7.4.4
128 to 159
BSTACK (Block STACK)
5.3.2
203 to 214
6-16
5.2
7
Introduction to STEP 5
7.1
7.1.1
7.1.2
7.1.3
Writing a Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Methods of Representation . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Operand Areas . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Circuit Diagram Conversion . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7
7
7
7
7.2
7.2.1
7.2.2
Program Structure . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Linear Programming . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Structured Programming . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7 - 4
7 - 4
7 - 5
7.3
7.3.1
7.3.2
7.3.3
7.3.4
7.3.5
Block Types . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Organization Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Program Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Sequence Blocks, for CPU 103 and Higher . . . . . . . . . . . . . . . . .
Function Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Data Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7
7
7
7
7
7
7
9
11
11
11
16
7.4
7.4.1
7.4.2
7.4.3
7.4.4
Program Processing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Program Processing with CPU 102 . . . . . . . . . . . . . . . . . . . . . . .
START-UP Program Processing . . . . . . . . . . . . . . . . . . . . . . . . .
Cyclic Program Processing . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Time-Controlled Program Processing, for CPU 103
Version 8MA02 and Higher . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Interrupt-Driven Program Processing, for CPU 103
7
7
7
7
18
19
24
26
7.5
7.5.1
7.5.2
7.5.3
Processing Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Changing Programs . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Changing Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Compressing the Program Memory . . . . . . . . . . . . . . . . . . . . . . .
7
7
7
7
7.6
Number Representation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7 - 31
7.4.5
1
1
3
3
7 - 28
7 - 29
30
30
30
30
Figures
7-1
7-2
7-3
7-4
7-5
7-6
7-7
7-8
7-9
7-10
7-11
7-12
7-13
7-14
7-15
7-16
7-17
Compatibility of STEP 5 Methods of Representation . . . . . . . . . . . . . . . . .
Nesting Depth of Programmed Organization Blocks . . . . . . . . . . . . . . . . .
Structure of a Block Header . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Example of Organization Block Use . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming a Function Block Parameter, for CPU 103 and Higher . . . . . .
Programming a Function Block . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Example of Data Block Contents . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Validity Areas of Data Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programm Scanning with CPU 102 . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Mode Change for CPU 102 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Display of the Processing Mode in the ISTACK . . . . . . . . . . . . . . . . . . . .
Setting the Start-Up Procedure . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Cyclic Program Processing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Calculating the Response Time . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Compressing the Program Memory . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Bit Assignment of a 16-Bit Fixed-Point Binary Number . . . . . . . . . . . . . . .
BCD and Decimal Formats . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7
7
7
7
7
7
7
7
7
7
7
7
7
7
7
7
7
2
6
8
10
13
16
17
17
19
21
22
24
26
27
30
31
32
Tables
7-1
7-2
7-3
7-4
7-5
7-6
Comparison of Operation Types . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Comparison of Block Types . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Overview of Organization Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Block Parameter Types and Data Types with Permissible Actual
Parameters, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming Possibilities . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Comparison of Number Formats . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
7 - 2
7 - 7
7 - 9
7 - 14
7 - 18
7 - 32
S5-100U
7
Introduction to Step 5
This chapter explains how to program the S5-100U. It describes how to write a program, how the
program is structured, the types of blocks the program uses, and the number representation of the
STEP 5 programming language.
7.1
Writing a Program
A control program specifies a series of operations that tell the programmable controller how it has to
control a system. For example, a control program might be the series of operations that tell the
S5-100U how to use open-loop control or closed-loop control for a specific system. You must write
the program in a special programming language and according to specific rules so that the programmable controller can understand it. The programming language that has been developed for the
SIMATIC S5 family is called STEP 5.
7.1.1
The following methods of representation are possible with the STEP 5 programming language.
Statement List (STL)
STL represents the program as a sequence of operation mnemonics. A statement has the
following format:
Operation
Operand
002: A I 0.1
Parameter
Operand ID
Relative address of the statement
in a particular block
The operation tells the programmable controller what to do with the operand. The parameter
indicates the operand address.
Control System Flowchart (CSF)
CSF represents logic operations with graphics symbols.
Ladder Diagram (LAD)
LAD graphically represents control functions with circuit diagram symbols.
GRAPH 5, for CPU 103 and higher
GRAPH 5 describes the structure of sequence control systems.
You cannot use CSF, LAD, or GRAPH 5 with the PG 605 programmers.
7-1
S5-100U
Each method of representation has its own special characteristics. A program block that has been
programmed in STL cannot necessarily be output in CSF or LAD. The three methods of graphic representation are not compatible. However, programs in CSF or LAD can always be converted to
STL. Figure 7-1 illustrates these points in a diagram.
CSF
LAD
STL
Figure 7-1. Compatibility of STEP 5 Methods of Representation
The STEP 5 programming language has the following three operation types:
Basic
Supplementary
System
Table 7-1 provides further information about these operations.
Table 7-1. Comparison of Operation Types
STEP 5 PROGRAMMING LANGUAGE
Basic Operations
Supplementary
Operations
System Operations
Application
In all blocks
Only in function blocks
Methods of
representation
STL, CSF, LAD
STL
STL
Special features
For users with good
system knowledge
Refer to Chapter 8 for a description of all operations and for programming examples.
7-2
S5-100U
7.1.2
Operand Areas
The STEP 5 programming language has the following operand areas:
I
(inputs)
Interfaces from the process to the programmable controller
Q
(outputs)
Interfaces from the programmable controller to the process
F
(flags)
Memory for intermediate results of binary operations
D
(data)
Memory for intermediate results of digital operations
T
(timers)
Memory for implementing timers
C
(counters)
Memory for implementing counters
P
(peripherals)
K
(constants)
Defined numeric values
OB, PB, SB
FB, DB
(blocks)
Program structuring aids
Refer to Appendix A for a listing of all operations and operands.
7.1.3
If your automation task is in the form of a circuit diagram, you must convert it to STL, CSF, or LAD.
7-3
S5-100U
Example: Hard-Wired Control
A signal lamp (H1) is supposed to light up when a normally open contact (S1) is activated and a normally closed contact (S2) is not activated.
The signal lamp is connected to an output (i.e., Q 1.0). The signal voltages of the two
contacts are connected to two programmable controller inputs (i.e., I 0.0 and I 0.1).
The S5-100U scans to see if the signal voltages are present (signal state “1” at the
activated normally open contact or non-activated normally closed contact). Both signal
states are combined through logic AND. The result of logic operation (RLO) is assigned
to output Q 1.0 (the lamp lights).
Circuit Diagram
STL
CSF
LAD
S1
A
I 0.0
A
I 0.1
I 0.0
I 0.0
S2
I 0.1
I 0.1
Q 1.0
Q 1.0
Q 1.0
H1
7.2
Program Structure
An S5-100U program can be one of the two following types:
Linear
Structured
Sections 7.2.1 and 7.2.2 describe these program types.
7.2.1
Linear Programming
Programming individual operations in one section (block) is sufficient for handling simple automation
jobs. For the S5-100U, this is organization block 1 (see section 7.3.1). The S5-100U scans this
block cyclically. After the S5-100U scans the last statement, it goes back to the first statement and
begins scanning again. Please note the following rules:
When OB1 is called, five words are assigned to the block header in the program memory (see
section 7.3).
Normally, a statement takes up one word in the program memory.
Two-word statements also exist (e.g., with the operation “Load a constant”). Count these
statements twice when calculating the program length.
Like all blocks, OB1 must be terminated by a Block End statement (BE).
7-4
S5-100U
7.2.2
To solve complex tasks, it is advisable to divide a program into individual, self-contained program
parts (blocks). This procedure has the following advantages:
Simple and clear programming, even for large programs
Program parts can be standardized
Easy alterations
Simple program test
Simple start-ups
Subroutine techniques (block call from different locations)
The STEP 5 programming language has the following five block types:
Organization Block (OB)
Organization blocks manage the control program.
Program Block (PB)
Program blocks arrange the control program according to functional or technical aspects.
Sequence Block (SB)
Sequence blocks are special blocks that program sequence controls. They are handled like
program blocks. (This is available for CPU 103 and higher.)
Function Block (FB)
Function blocks are special blocks for programming frequently recurring or especially complex
program parts (e.g., reporting and arithmetic functions). You can assign parameters to them
(available for CPU 103 and higher). They have an extended set of operations (e.g., jump
operations within a block).
Data Block (DB)
Data blocks store data needed to process a control program. Actual values, limiting values, and
texts are examples of data.
7-5
S5-100U
The program uses block calls to exit one block and jump to another. You can therefore nest program, function, and sequence blocks randomly up to 16 levels (see section 7.3). Nesting can be up
to 32 levels for CPU 103 version 8MA03.
Note
When calculating the nesting depth, note that the system program in the programmable
controller can call an organization block automatically under certain circumstances
(e.g., OB2).
The total nesting depth is the sum of the nesting depths of call programmed organization blocks. If
nesting goes beyond 16 levels (32 levels for CPU 103 version 8MA03), the CPU goes into the
STOP mode with the error message “STUEB,” block stack overflow (see section 5.2). Figure 7-2
illustrates the nesting principle.
OB 1
Level 1
Level 2
Level 3
Level 16
Figure 7-2. Nesting Depth of Programmed Organization Blocks
7-6
S5-100U
7.3
Block Types
The following table lists the most important characteristics of the individual block types:
Table 7-2. Comparison of Block Types
OB1
Number
CPU 100
FB2
DB3
64
PB0 to PB63
64
FB0 to FB63
62
DB2 to DB63
64
OB0 to OB63
64
PB0 to PB63
64
FB0 to FB63
62
DB2 to DB63
Number
CPU 103
256
OB0 to OB255
256
PB0 to PB255
2562
FB0 to FB255
254
DB2 to DB255
Length (max.)
CPU 100
4 Kbytes
4 Kbytes
4 Kbytes
256 data words
Length (max.)
CPU 102
4 Kbytes
4 Kbytes
4 Kbytes
256 data words
Length (max.)
CPU 103
8 Kbytes
8 Kbytes
8 Kbytes
8 Kbytes
8 Kbytes
Operations
set
(contents)
Basic
operations
Basic
operations
Basic
operations
Basic,
supplementary,
system
operations
Bit patterns,
numbers,
texts
Representation methods
STL, CSF,
LAD
STL, CSF,
LAD
STL, CSF,
LAD
STL
Block header
length
1
64
OB0 to OB63
Number
CPU 102
2
3
PB
5 words
5 words
5 words
5 words
SB
256
SB0 to SB255
5 words
The operating system calls up particular OBs automatically (see section 7.3.1 and 9.3).
Function blocks are already integrated into the operating system (see section 9.2).
Data blocks DB0 and DB1 are reserved.
7-7
S5-100U
Block Structure
Each block consists of the following parts:
The block header that specifies the block type, number, and length
- Generated by the programmer when it transforms the block
The block body that has the STEP 5 program or data
Synchronization
pattern
Block type
Block number
Programmer ID
Absolute
byte
addresses
(in ascending
order)
Library number
Block length
Figure 7-3. Structure of a Block Header
Programming
Program your blocks as follows (does not apply to data blocks):
1. Specify the block type (e.g., PB).
2. Specify the block number (e.g., 27).
3. Enter the control program statements.
4. Terminate the block with the “BE” statement.
7-8
S5-100U
7.3.1
Organization Blocks
Organization blocks (OB) form the interface between the operating system and the control program.
Organization blocks are handled in one of the following three ways:
Organization block OB1 is called cyclically by the operating system.
Some organization blocks are event-driven or time-controlled. They can be called in response
to events or at certain times:
- By a switch from STOP to RUN (OB21)
- By a switch from Power OFF to Power ON (OB22 (see Table 7-3))
- By interrupts (OB2 and OB13)
Some other organization blocks represent operating functions (similar to the the integral function
blocks). They can be called by the control program (for CPU 103 and higher; see section 9.3).
Table 7-3 provides an overview of organization blocks.
Table 7-3. Overview of Organization Blocks
OB No.
OB integrated in
Function
CPU 100
CPU 102
CPU 103
You must program the OB. The operating system calls up the OB.
OB1
Cyclic program processing
Interrupt-driven program processing
OB2
OB13
Time-controlled program processing
Handling start-up procedures
OB21
When starting manually (STOP to RUN)
OB22
When power returns
Handling programming errors and device errors
OB34
Battery failure
The OB is already programmed. You must call up the OB.
OB31
Scan time triggering (resets scan time monitor)
OB251
PID control algorithm
OB is ready or is supported by the operating system
You can program all organization blocks using parameters from the permissible range. CPU 100
and CPU 102 use organization blocks OB0 to OB63. CPU 103 uses OB0 to OB255. However, you
must call the organization blocks from the control program.
7-9
S5-100U
Figure 7-4 shows how to set up a structured control program. It also illustrates the significance of
OB21/OB22
OB1
SB1*
FB2
System program
PB1
FB61
Control program
* For CPU 103 and higher
Figure 7-4. Example of Organization Block Use
7-10
S5-100U
7.3.2
Program Blocks
Self-contained program parts are programmed in program blocks (PB).
Special feature: Control functions can be represented graphically in program blocks.
Call
Block calls JU and JC activate program blocks. You can program these operations in all block types
except data blocks. Block call and block end cause the RLO to be reloaded. However, the RLO
can be included in the “new” block and be evaluated there.
7.3.3
Sequence blocks (SB) are special program blocks that process sequence controls. They are treated
like program blocks.
7.3.4
Function Blocks
Frequently recurring or complex control functions are programmed in function blocks (FB).
Function blocks have the following special features.
FBs can be assigned parameters (for CPU 103 and higher).
- Actual parameters can be assigned when the block is called (for CPU 103 and higher).
FBs have an extended set of operations not available to other blocks.
The FB program can be written and documented in STL only.
If you are using CPU 102 version 8MA02 or higher, you have the following types of function blocks
available:
FBs that you can program
FBs that are integrated in the operating system (see section 9.2)
FBs that are available as software packages (standard function blocks, see Catalog ST 57)
7-11
S5-100U
Block Header
Besides the block header, function blocks have organizational information that other blocks do not
have.
A function block's memory requirements consist of the following:
Block header (five words) as for other blocks
Block name (five words)
Block parameter for parameter assignment (three words per parameter)
Creating a Function Block, for CPU 103 and Higher
In contrast to other blocks, parameters can be assigned to FBs.
To assign parameters, you must program the following block parameter information.
Block Parameter Name (formal operand)
Each block parameter as a formal operand is given a designation (DES). Under this designation
it is replaced by an actual parameter when the function block is called.
The name can be up to four characters long and must begin with an alpha character. You can
program up to 40 block parameters per function block.
You can enter the following parameter types:
-I
input parameters
-Q
output parameters
-D
data
-B
blocks
-T
timers
-C
counters
In graphic representation, output parameters appear to the right of the function symbol. Other
parameters appear to the left.
Block Parameter Data Type
You can specify the following data types:
- BI
for operands with a bit address
- BY
for operands with a byte address
-W
for operands with a word address
-K
for constants
7-12
S5-100U
When assigning parameters, enter all block parameter specifications.
Block header
Name
DES:
Block
parameter
IN 1
I
BI
Block parameter
DES:
IN 2
I
BI
Name
DES:
OUT 1 Q
BI
Data type
Parameter type
: A = IN 1
Control
program
Memory assignment
: A = IN 2
: == OUT 1
Program example
Figure 7-5. Programming a Function Block Parameter, for CPU 103 and Higher
7-13
Table 7-4.
S5-100U
Parameter
Type
Data Type
Permissible Actual Parameters
I, Q
BI
for an operand with bit address
I
Q
F
x.y Inputs
x.y Outputs
x.y Flags
BY
for an operand with byte address
IB
QB
FY
DL
DR
PY
x
x
x
x
x
x
Input bytes
Output bytes
Flag bytes
Data bytes left
Data bytes right
Peripheral bytes*
W
for an operand with word address
IW
QW
FW
DW
PW
x
x
x
x
x
Input words
Output words
Flag words
Data words
Peripheral words*
KM
KY
for a binary pattern (16 digits)
Constants
for two absolute numbers, one byte each,
each in the range from 0 to 255
for a hexadecimal pattern (maximum 4
digits)
for a character (maximum 2
alphanumeric characters)
for a time (BCD-coded time) with time
base 1.0 to 999.3
for a count (BCD-coded) 0 to 999
for a fixed-point number in the range
from -32768 to +32767
D
KH
KS
KT
KC
KF
B
Type designation not permitted
DBx
OBx
FBx
PBx
SBx
Data blocks. The C DBx operation is
executed.
Organization blocks are called
unconditionally (JU ... x).
Function blocks (permissible without
parameters only) are called
unconditionally (JU..x).
Program blocks are called
Sequence blocks are called
T
T
Timer. The time should be assigned
parameters as data or be programmed
as a constant in the function block.
C
C
Counter. The count should be
assigned parameters as data or be
programmed as a constant in the
function block.
* Not permitted for integral FBs
Calling a Function Block
Like other blocks, function blocks are stored under a specific number in the program memory (e.g.,
FB47). The numbers 240 to 255 are reserved for the integral function blocks (in CPU 103 version
8MA02 and higher).
You can program function block calls in all blocks except data blocks.
7-14
S5-100U
A function block call consists of the following parts:
Call statement
- JU
FBx
unconditional call (Jump Unconditional)
- JC
FBx
call if RLO = 1 (Jump Conditional)
Parameter list (only if block parameters were defined in the FB)
Function blocks can be called only if they have been programmed. When a function block call is
being programmed, the programmer requests the parameter list for the FB automatically if block
parameters have been defined in the FB.
Setting Parameters for a Function Block
The program in the function block specifies how the formal operands (parameters defined as “DES”)
are to be processed.
As soon as you have programmed a call statement (for example JU FB2), the programmer displays
the parameter list. The parameter list consists of the names of the parameters. Each parameter
name is followed by a colon (:). You must assign actual operands to the parameters. The actual
operands replace the formal operands defined in the FB when the FB is called, so that the FB
operates with the actual operands.
A parameter list has a maximum of 40 parameters.
Example:
The name (DES) of a parameter is IN1, the parameter type is I (as in input), the data
type is BI (as in bit). The formal operand for the FB has the following structure:
DES:
IN1
I BI
Specify in the parameter list of the calling block which actual operand is to replace the
formal operand in the FB call. In our example it is : I 1.0.
Enter in the parameter list:
IN1:
I 1.0
When the FB is called, it replaces the formal operand “IN1” with the actual operand
“I 1.0”.
Figure 7-6 provides you with a detailed example of how to set parameters for a function block.
The FB call takes up two words in the internal program memory. Each parameter takes up an
additional memory word.
You can find the memory requirements for standard function blocks and the run times in the
specifications in Catalog ST 57.
The name of the function block is stored in the function block. The designations (DES) of the
function block inputs and outputs that appear on the programmer during programming are also
stored in the function block. Before you begin programming on the programmer, you must choose
one of the following two options:
Transfer all necessary function blocks to the program diskette (for off-line programming)
Input all necessary function blocks directly into the program memory of the programmable
controller
7-15
S5-100U
PB 3
Executed
program
FB 5
DES:
: JU
I
BI
X2
I
BI
DES:
FB5
X1
DES:
X3
Q BI
: A = X1
: A = X2
: = = X3
X1
: I 0.0
X2
: F 1.3
X3
I 0.0
A
F 1.3
Parameter list
for first call
A
: BE
Q 1.0
: Q 1.0
First call
Formal operands
Actual operands
: A I 0.1
: JC FB5
Second call
X1
: I 0.3
X2
: I 0.2
X3
: Q 1.0
A
I 0.3
A
I 0.2
Parameter list
for second call
Q 1.0
Formal operands
Figure 7-6. Programming a Function Block
7.3.5
Data Blocks
Data blocks (DB) store data to be processed in a program.
The following data types are permissible:
Bit pattern (representation of controlled system states)
Hexadecimal, binary or decimal numbers (times, results of arithmetic operations)
Alphanumeric characters (ASCII message texts)
7-16
S5-100U
Programming Data Blocks
Begin programming a data block by specifying a block number between 2 and 63 for CPU 100 or
CPU 102, and between 2 and 255 for CPU 103. DB0 is reserved for the operating system, DB1 for
setting parameters for internal functions (see section 9.1). Data is stored in this block in words.
If the information takes up less than 16 bits, the high-order bits are padded with zeros. Data input
begins at data word 0 and continues in ascending order. A data block can hold up to 256 data
words. You can call up or change the data word contents with load or transfer operations.
Input
0000
0001
0003
KH
KT
KF
Stored Values
A13C
100.2
+21874
DW0
DW1
DW2
A13C
2100
5572
Figure 7-7. Example of Data Block Contents
You can also create or delete data blocks in the control program (see section 8.1.8).
Program Processing with Data Blocks
A data block must be called in the program with the C DBx operation (x = DB number) before it
can be accessed.
Within a block, a data block remains valid until another data block is called.
When the program jumps back into the higher-level block, the data block that was valid before
the block call is again valid.
After OB1, 2, 13, 21, 22 have been called by the operating system, no DB is valid.
Valid
DB
PB7
PB20
Valid
DB
DB10
C DB10
DB10
C DB11
JU PB20
DB11
DB10
When PB20 is called, the valid data area is entered into memory.
When the program jumps back, this area is reopened.
Figure 7-8. Validity Areas of Data Blocks
The Function of DB1
DB1 is used for special functions. DB1 is already integrated into CPU 103 version 8MA03 and
higher and contains (default) values that you can either accept or change (see section 9.1). DB1 is
evaluated once during start-up: either after Power ON or after a transition from STOP to RUN.
7-17
7.4
S5-100U
Program Processing
Some of the organization blocks (OBs) are responsible for structuring and managing the control
program.
These OBS can be grouped according to the following assignments:
OBs for START-UP program processing
One OB for cyclic program processing
OBs for time-controlled program processing
OBs for (process) interrupt-driven program processing
The S5-100U has additional OBs whose functions are similar to those of integral function blocks
(e.g., PID control algorithm). These OBs are described in chapter 9.
Section 7.3.1 summarizes all of the OBs.
Comparing Programming Possibilities for CPU 100, CPU 102, and CPU 103
Table 7-5. Programming Possibilities
CPU
CPU 100
CPU 102
CPU 103
Cyclical
Yes
Yes
Yes
Interrupt-driven
No
No
Yes
(for 8MA02 and higher)
Time-controlled
No
No
Yes
Integral FBs
No
Yes
Yes
Graph 5
No
No
Yes
Programmable FBs
No
No
Yes
Beginning with section 7.4.2, you learn which special organization blocks each of the CPUs has
available to perform the programming tasks described in Table 7-5. You also learn which precautions you need to take when you program.
7-18
S5-100U
7.4.1
You can process the program in the following two modes:
Normal mode
Test mode
Program processing is faster in the normal mode, but you can not use the STATUS test function.
Transferring from one mode to the other is called a mode change.
Test Mode:
Scanning the STEP 5 program
Normal Mode:
The control program you have written in STEP 5 is not processed directly. What is processed is a
translated or runtime-optimized form of the program generated by the programmable controller.
Cycle trigger
Cycle trigger
Control
program
in STEP 5
Assemble
(compile)
Runtimeoptimized
program
Transfer
data
Transfer
data
Test mode
Figure 7-9.
Normal mode
Program Scanning with CPU 102
7-19
S5-100U
Special Features of the Normal Mode
Significance of the Memory Submodule
Normal mode is only possible if the memory submodule is plugged in.
This submodule contains only the STEP 5 program.
The CPU RAM contains the STEP 5 program and the compiled program to be processed.
Program Change
You can enter, modify, or erase PBs, OBs and FBs only in the test mode.
You can read out the STEP 5 program with the programmer.
Signal Status Display
You can monitor and control signals states with the “STATUS VAR” and “FORCE VAR” functions.
The “STATUS” function can be used only in the test mode.
Diagnostics
The “BSTACK” diagnostics function cannot be activated.
Fault Analysis
The ISTACK bytes 23 to 27 are not valid. Therefore, you cannot determine the point in a program
where an interruption took place (programmable controller in STOP, e.g., programmed loop with
timeout). However, when compiling the program, errors (e.g., illegal operations and parameters) are
detected and displayed by the STEP address counter in the ISTACK. This counter points to the
error in the STEP 5 program.
7-20
S5-100U
Mode Change
Load program
(manual)
Back up program
(without PG)
Load program
(automatic)
1. Turn off the PLC
2. Plug in memory sub-
Battery required
1. Turn off the PLC
1. Reset the PLC
2. Turn off the PLC
module
3. Press COPY key and
hold it down
2. Plug in EEPROM
submodule
3. Turn on the PLC
3. Plug in memory
submodule
4. Turn on the PLC
4. Turn on the PLC
- Red LED flickers
- Red LED lights when
4. Press COPY key for at
least 3 s
5. Release it as soon as
program is loaded
5. Release COPY key
Test
mode
- Red LED flickers
when program
loaded
the red LED starts
flickering
- Program is stored in
EEPROM submodule
and compiled in the
CPU’s RAM
- Red LED lights
Normal
mode
Load program
(with PG)
With or without battery
1. Turn on the PLC
2. Switch PLC to STOP
3. Perform an overall
reset with the PG
4. Enter the program
Reset PLC
(without PG)
5. Transfer the program
If program scanning is
interrupted
1. Remove the battery
2. Turn off the PLC
(fault, mode selector
at STOP or Power
OFF in the case of
3. Remove the memory
submodule
4. Turn on the PLC
battery backup), the
mode that was active
prior to the interruption
will be the operating
mode when RUN is
resumed.
Figure 7-10. Mode Change for CPU 102
7-21
S5-100U
Determining the Processing Mode in the ISTACK
Bit
7
Byte
6
1
2
KEIN
AS
6
7
Figure 7-11. Display of the Processing Mode in the ISTACK
You can use a programmer to check the current processing mode in the ISTACK. The ISTACK
display, byte 6, is possible in RUN and STOP (see section 5.2).
KEIN AS=1 : Test mode
Execution time is 70 ms/1024 binary statements. There are no limitations on the test or operator
functions.
KEIN AS=0: Normal mode
Execution time is 7 ms/1024 binary statements. There are limited test and operator functions.
7-22
S5-100U
Further Reduction in the Execution Time in Normal Mode
Logic operations executed in one input byte, output byte, or flag byte require only 2 µs per logic
operation. Program your control according to example 2.
Example 1:
Example 2:
STL
Time/ µs
A
AN
ON
I
I
I
0.0
1.1
2.3
O
I
Q
3.5
4.2
5
6
6
6
8
A
A
AN
F
F
F
15.1
16.3
17.7
Q
4.5
Execution time
5
6
6
8
56 µs
Approx. 6 µs/binary operation
STL
Time/ µs
A
AN
I
I
0.0
0.1
ON
O
I
I
Q
0.3
0.5
4.2
5
2
2
2
8
A
A
F
F
15.1
15.3
AN
F
Q
15.7
4.5
Execution time
5
2
2
8
36 µs
Approx. 4 µs/binary operation
7-23
7.4.2
S5-100U
In the START-UP mode, the operating system of the CPU automatically calls up a start-up OB if the
OB has been programmed.
OB21 is called up for a manual cold restart.
OB22 is called up for an automatic cold start after power recovery if the programmable controller
was previously in the RUN mode.
If you have programmed start-up OBs, they are processed before the cyclic program processing
occurs. The start-up OB program is appropriate, for example, for a one-time presetting of certain
system data. If the appropriate start-up OB is not programmed, the programmable controller jumps
directly to the RUN mode. See section 4.1.2.
Features of the start-up blocks (OB21, OB22):
The red and green LEDs light.
Timers are processed.
Scan monitoring is not activated.
Interrupts are not processed.
Operating mode switch set from STOP
to RUN; Programmer command RUN
Clear the process image I/O table,
the non-retentive timers,
counters, and flags.
Interpret DB12
Power recovery1
Interpret DB12
Processing OB21
Cold
restart
routine
Processing OB22
STARTUP
Enable the outputs
Read in the PII
Process OB1
RUN
Read out the PIQ
1
2
This is the procedure if the programmable controller was in the RUN mode when the power went off,
if the mode switch was still on RUN when the power was restored, and if the battery was inserted. If
the battery was not inserted, you must insert a memory submodule containing the valid blocks.
For CPU 103 version 8MA03 and higher
Figure 7-12. Setting the Start-Up Procedure
7-24
S5-100U
The following two examples show you how you can program a start-up OB.
Example 1: Programming OB22
STL
Example
After power recovery, you
want to be sure that the power
supply voltage for the I/Os has
attained its rated value before
the cyclic program is processed. A time loop is therefore programmed in OB22.
AN
L
SP
F001: A
JC
BE
Explanation
T
1
KT
T
T
500.0
1
1
=F001
A 5 s time value is loaded in
ACCU 1.
Timer 1 is started.
After 5 s, cyclic program
processing begins in OB1.
Example 2: Programming OB21
STL
Example
After the operating mode
switch causes a cold restart,
flag bytes 0 to 9 are preset
with “0”. The other flag bytes
are retained since they contain
important machine functions.
Explanation
L
T
T
KH
FW
FW
0
0
2
T
T
T
FW
FW
FW
Value “0” is loaded in
ACCU 1 and transferred into
flag words 0, 2, 4, 6, and 8.
4
6
8
BE
7-25
7.4.3
S5-100U
The operating system calls OB1 cyclically. If you want to
have structured programming, you should program only jump
operations (block calls) in OB1. The blocks you call up, PBs,
FBs, and SBs, should contain completed functional units in
order to provide a clearer overview.
A time monitor is triggered at the beginning of each program
processing cycle (scan cycle trigger). If the scan cycle time
trigger is not reset within the scan monitoring time, the CPU
automatically enters the STOP mode and disables the output
modules.
You can set the monitoring time (see Table 6-6). You could
have a control program that is so complex that it cannot be
processed within 300 ms. With CPU 103 and higher, you can
use OB31 (see section 9.3) to lengthen (retrigger) the scan
monitoring time in the control program.
Monitoring time is exceeded, for example, if you program
endless loops or if there is a malfunction in the programmable
controller.
Cycle trigger
Control
program
Transfer
data
Figure 7-13. Cyclic Program Processing
7-26
S5-100U
Response Time
Response time tR is defined as the time between a change in the input signal and the subsequent
change in the output signal.
Prerequisites for the following information:
No interrupts are running.
The programmer interface is not in use. (The load is very dependent on the function.)
The response time is influenced by the following factors:
The input module delay (see chapter 14)
The program processing time (see Appendix A)
The data cycle times (number of data bits x 25 µs - a bus configuration of 256 data bits results
in a data cycle time of approximately 8 ms)
The operating system run time (up to 3% of the program cycle)
The processing of the internal timers
T 0 to T15 for CPU 100
T 0 to T31 for CPU 102
T 0 to T127 for CPU 103
Calculating the maximum response time tRm:
With tG=
2 x program processing time + 3 x data cycle time + 3 x operating system run time
+ delay time of the input modules
Maximum processing time of the internal timers tTm
tTm = number of processed timers x 32 µs (number of processed timers for CPU 100:
number of processed timers for CPU 102:
number of processed timers for CPU 103:
16
32
128)
tTm = 103 µs for CPU 103 version 8MA03
tTm
tRm = tG ( 1 +
) + tTm.
10 ms
During the transition from STOP to RUN, there is a one-time increase in the response time to about
200 ms.
Response
Input
module
delay
I 0.0
1
0
1
Q 1.0
0
Time
Data
cycle
Program processing
A I 0.0 = Q 1.0
Data
cycle
Figure 7-14. Calculating the Response Time
7-27
7.4.4
S5-100U
Time-Controlled Program Processing, for CPU 103 Version 8MA02
and Higher
Time-controlled program processing can be defined as a (periodic) time signal causing the CPU to
interrupt cyclic program processing to process a specific program. Once this program has been
processed, the CPU returns to the interruption point in the cyclic program and resumes processing.
Prerequisites for time-controlled program processing
Time-controlled program processing is possible only if the following prerequisites have been fulfilled.
Organization block OB13 must be programmed.
The programmable controller must be set to Power ON and the RUN mode must be selected.
Interrupt processing may not be disabled (by the IA - disable interrupt - operation). See
section 8.2.8.
The OB13 call-up interval is set to & gt; 0.
OB13 is available for time-controlled program processing when using CPU 103 version 8MA02 and
higher. You determine the intervals at which you want the operating system to process OB13. It is
also possible to change the call-up intervals during cyclic program processing. Cyclical program
processing continues if OB13 is not programmed.
Setting the call-up interval
You can set the call-up interval in DB1 using the TFB: block ID. You can set the times from
10 ms to 655,530 ms (use 10-ms increments). The default for OB13 is 100 ms.
Interrupt possibilities
OB13 can interrupt the cyclical program after any STEP 5 statement. After the current STEP 5
statement is executed, you can use process interrupts to interrupt time-controlled program
processing. After interrupt processing, time-controlled program processing continues until it is
finished.
OB13 cannot interrupt the operating system, the process interrupts (OB2), or the current timecontrolled program processing (OB13).
Disabling/enabling the call-up
Use the IA command to disable, and the RA command to enable the OB13 call-up.
A call-up request can be stored during a call-up disable. The default is RA. See section 8.2.8.
7-28
S5-100U
Saving data
If a time-controlled OB uses scratchpad flags that are also used in the cyclic control program,
then these scratchpad flags must be saved in a data block during the processing of the timecontrolled OB.
Note
When processing OB13, you may not exceed the block nesting depth of 16 levels.
When processing with CPU 103 (6ES5 103-8MA03), you may not exceed the block
nesting depth of 32 levels.
Reading out the interrupt PII
When OB13 is called, the signals of the input modules are read into the interrupt PII. The
interrupt PII can be scanned in OB13 by means of the L PY 0 to 127 or L PW 0 to 126 load
operations (load byte x or word x of the interrupt PII in ACCU 1). There is an interrupt input data
cycle prior to time-controlled program processing. The interrupt data cycle time lengthens the
response time of the cyclical program processing.
If other operands are entered, the CPU goes in the STOP mode (see section 5.2.1). This error
is indicated in ISTACK by the “NNN” error message.
Writing to the interrupt PIQ
Data to the external I/Os can be written to the interrupt PIQ by means of transfer operations
T PY 0 to 127 or T PW 0 to 126. The “normal” PIQ is written to simultaneously. After OB13
has finished, the data that has been transferred to the interrupt PIQ is output to the peripheral
I/Os in an interrupt output data cycle (before “normal” program processing). The interrupt data
cycle time lengthens the response time of the cyclical program processing.
Note
The interrupt output data cycle is executed only if the interrupt PIQ has been written to.
7.4.5
Interrupt-Driven Program Processing, for CPU 103 Version 8MA02
and Higher
For CPU 103 version 8MA02 and higher, interrupt-driven program processing is initiated when a
signal from the process causes the CPU to interrupt the cyclic or time-controlled program
processing and execute a specific program. When this program has been scanned, the CPU returns
to the point of interruption in the cyclic or time-controlled program and resumes scanning at that
point. Chapter 10 contains detailed information about interrupt processing.
7-29
7.5
S5-100U
Processing Blocks
Earlier sections in this chapter described how to use blocks. Chapter 8 introduces all of the
operations required to work with blocks. You can change any block that has been programmed.
The following sections will deal only briefly with the different ways you can change blocks. Refer to
the operator‘s guide for your programmer for more detailed information on changing blocks.
7.5.1
Changing Programs
You can use the following programmer functions to make program changes with any block type.
INPUT
OUTPUT
STATUS (see section 4.5)
These three programmer functions make it possible for you to make the following types of changes:
Delete, insert, or overwrite statements.
Insert or delete segments.
7.5.2
Changing Blocks
Program changes refer to changing the contents of a block. You can also delete or overwrite a
complete block. When you delete a block, it is not deleted from the program memory but simply
becomes invalid. You cannot enter new information in the memory location of an invalid block. This
may cause new blocks not to be accepted. If a new block is not accepted, then the PG transmits
the “no space available” error message. You can make more space by compressing the
programmable controller memory.
7.5.3
Figure 7-15 illustrates what takes place in the program memory during a COMPRESS operation.
Internally, one block is shifted per cycle.
Program memory
RAM
Program memory
RAM
Valid
blocks
Invalid
Compress
Input not
possible
PB
Input
possible
PB
Available
memory space
Figure 7-15. Compressing the Program Memory
7-30
S5-100U
You can use the COMPRESS programmer function to clean up internal program memory.
If there is a power failure during the compress operation when a block is being shifted and block
shifting can not be completed, the CPU remains in the STOP mode. The “NINEU” error message
appears. Both the“BSTSCH” and the “SCHTAE” bits are set in the ISTACK.
Remedy: Overall reset.
7.6
With STEP 5 you can work with numbers in the following five representations:
Decimal numbers from -32768 to +32767 (KF)
Hexadecimal numbers from 0000 to FFFF (KH)
BCD-coded numbers (4 tetrads) from 0000 to 9999
Bit patterns (KM)
Constant byte (two-byte representation) from 0 to 255 for each byte (KY)
Number Formats
The programmable controller is designed to process binary signal states (only “0” and “1”).
Therefore the programmable controller represents all numbers internally as 16-bit binary numbers or
as bit patterns.
Four bits can be combined into a tetrad (BCD) to shorten the binary code representation. The value
of these tetrads can be displayed in hexadecimal representation.
Example:
16-bit binary coded number and shortened hexadecimal representation
n
Word no.
n
Byte no.
(high byte)
n+ 1 (low byte)
15 14 13 12 11 10 09 08 07 06 05 04 03 02 01 00
Bit no.
Binary code representation
0
0
0
1
1
1
1
1
0
1
1
0
0
0
1
1
215 214 213 212 211 210 29 28 27 26 25 24 23 22 21 20
Meaning
Hexadecimal representation
1
F
6
3
Figure 7-16. Bit Assignment of a 16-Bit Fixed-Point Binary Number
7-31
S5-100U
You can work with binary-coded decimals to program timers and counters in the decimal system.
BCD tetrads are defined in the range of 0 to 9.
Example:
12-bit timer or counter value in BCD and decimal formats
n
Word No.
n
Byte No.
Bit No.
(high byte)
n+ 1 (low byte)
BCD No.
0
0
0
0
1
0
0
1
0
0
1
1
0
0
0
1
Meaning
Decimal format
0
9
3
1
Figure 7-17. BCD and Decimal Formats
Table 7-6.
Binary
0000
0001
0010
0011
0100
0101
0110
0111
1000
1001
1010
1011
1100
1101
1110
1111
7-32
Decimal
0
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
BCD
0000
0000
0000
0000
0000
0000
0000
0000
0000
0000
0001
0001
0001
0001
0001
0001
0000
0001
0010
0011
0100
0101
0110
0111
1000
1001
0000
0001
0010
0011
0100
0101
Hexadecimal
0
1
2
3
4
5
6
7
8
9
A
B
C
D
E
F
S5-100U
You can use the “LC” operation to convert a binary number to a BCD number for timers and
counters.
Example:
Comparing a count in counter 1 with decimal number 499
The comparison value must be stored in the accunulator by means of a load
operation. Use the “LKF + 499” statement so that you do not have to convert the
value 499 into other numerical systems (binary or hexadecimal) for the input. The
number 1F3H is then stored in the accumulator.
The current count must also be loaded into the accumulator.
Incorrect Method:
Correct Method:
If you use the “LCC1”
statement, the current count will
be loaded in BCD. The “!=F”
comparison operation results in
a “not equal to” condition since
the comparison uses different
formats.
The formats are identical if the
“LC1” statement is input.
High Byte
0 0 0 0 0 0 0 1 1 1 1 1 0 0 1 1
L KF+499
0 0 0 0 0 1 0 0 1 0 0 1 1 0 0 1
LC C 1
Low Byte
L KF+499
L C1
7-33
8
STEP 5 Operations
8.1
8.1.1
8.1.2
8.1.3
8.1.4
8.1.5
8.1.6
8.1.7
8.1.8
8.1.9
Basic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Boolean Logic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Set/Reset Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Load and Transfer Operations . . . . . . . . . . . . . . . . . . . . . . . . . . .
Timer Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Counter Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Comparison Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Arithmetic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Block Call Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Other Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8
8
8
8
8
8
8
8
8
8
1
2
7
10
15
25
30
31
33
38
8.2
8.2.1
8.2.2
8.2.3
8.2.4
8.2.5
8.2.6
8.2.7
8.2.8
8.2.9
8.2.10
8.2.11
Supplementary Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Load Operation, for CPU 103 and Higher . . . . . . . . . . . . . . . . . . .
Enable Operation, for CPU 103 and Higher . . . . . . . . . . . . . . . . .
Bit Test Operations, for CPU 103 and Higher . . . . . . . . . . . . . . . .
Digital Logic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Shift Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Conversion Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Decrement/Increment, for CPU 103 and Higher . . . . . . . . . . . . . .
Disable/Enable Interrupt, for CPU 103 Version 8MA02 and Higher .
“DO” Operation, for CPU 103 and Higher
Jump Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Substitution Operations, for CPU 103 and Higher . . . . . . . . . . . . .
8
8
8
8
8
8
8
8
8
8
8
8
39
40
41
42
44
48
50
52
53
54
56
58
8.3
8.3.1
8.3.2
8.3.3
8.3.4
System Operations, for CPU 103 and Higher . . . . . . . . . . . . . . . .
Set Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8
8
8
8
8
64
64
64
67
68
8.4
Condition Code Generation . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8 - 69
8.5
8.5.1
8.5.2
8.5.3
Sample Programs . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Momentary-Contact Relay/Edge Evaluation . . . . . . . . . . . . . . . . .
Binary Scaler/Binary Divider . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Clock/Clock-Pulse Generator . . . . . . . . . . . . . . . . . . . . . . . . . . .
8
8
8
8
71
71
71
73
Figures
8-1
8-2
8-3
8-4
8-5
8-6
Accumulator Structure . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Execution of the Load Operation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Transferring a Byte . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Output of the Current Time (Example) . . . . . . . . . . . . . . . . . . . . . . . . . .
Outputting the Current Counter Status (Example) . . . . . . . . . . . . . . . . . .
Executing a “DO” Operation
8
8
8
8
8
8
10
12
12
18
27
55
8
8
8
8
8
8
8
8
8
2
7
11
15
25
30
31
33
38
8
8
8
8
8
8
8
8
8
8
8
8
8
8
8
8
8
40
41
42
42
44
48
50
52
53
54
56
58
59
60
61
63
64
8
8
8
8
8
8
8
8
65
67
68
69
69
70
70
70
Tables
Basic Operations
8-1
Overview of Boolean Logic Operations . . . . . . . . . . . . . . . . . . . . . . . . .
8-2
Overview of the Set/Reset Operations . . . . . . . . . . . . . . . . . . . . . . . . . .
8-3
Overview of Load and Transfer Operations . . . . . . . . . . . . . . . . . . . . . .
8-4
Overview of Timer Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-5
Overview of Counter Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-6
Overview of Comparison Operations . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-7
Overview of Arithmetic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-8
Overview of Block Call Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-9
Other Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-10
Load Operation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-11
Enable Operation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-12
Overview of Bit Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-13
Effect of “TB” and “TBN” on the RLO
8-14
Overview of Digital Logic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-15
Overview of Shift Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-16
Overview of Conversion Operations . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-17
Decrement/Increment Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-18
Disable/Enable Interrupt Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-19
Overview of the “DO” Operation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-20
Overview of Jump Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-21
Overview of Binary Logic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-22
Overview of Set/Reset Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-23
8-24
Overview of Timer and Counter Operations . . . . . . . . . . . . . . . . . . . . . .
8-25
“DO” Operation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-26
Overview of Set Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
System Operations
8-27
8-28
Overview of the “ADD” Operation . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
8-29
The “TAK” and “STS” Operations
8-30
Condition Code Settings for Comparison Operations . . . . . . . . . . . . . . . .
8-31
Condition Code Settings for Fixed-Point Arithmetic Operations . . . . . . . . .
8-32
Condition Code Settings for Digital Logic Operations . . . . . . . . . . . . . . .
8-33
Condition Code Settings for Shift Operations . . . . . . . . . . . . . . . . . . . . .
8-34
Condition Code Settings for Conversion Operations . . . . . . . . . . . . . . . .
S5-100U
8
STEP 5 Operations
STEP 5 Operations
Basic Operations include functions that can be executed in organization, program, sequence,
and function blocks. Except for the addition (+F), subtraction (-F), and organizational operations, the basic operations can be input and output in the statement list (STL), control system
flowchart (CSF), or ladder diagram (LAD) methods of representation.
Supplementary Operations include complex functions such as substitution statements, test
functions, and shift and conversion operations. They can be input and output in STL form only.
System Operations access the operating system directly. Only an experienced programmer
should use them. System operations can be input and output in STL form only.
8.1
Basic Operations
Sections 8.1.1 through 8.1.9 use examples to describe the basic operations.
8-1
STEP 5 Operations
8.1.1
S5-100U
Table 8-1 provides an overview of Boolean logic operations. Examples follow the table.
Table 8-1. Overview of Boolean Logic Operations
Operation
Operand
Meaning
O
Combine AND operations through logic OR
Combine the result of the next AND logic operation (RLO) with the previous
RLO through logic OR.
A(
Combine expression enclosed in parentheses through logic AND
Combine the RLO of the expression enclosed in parentheses with the
previous RLO through logic AND.
O(
Combine expression enclosed in parentheses through logic OR
previous RLO through logic OR.
Close parenthesis
Conclude the expression enclosed in parentheses.
A
Scan operand for “1” and combine with RLO through logic AND
The result is “1” when the operand in question carries signal state “1”.
Otherwise the scan results in “0”. Combine this result with the RLO in the
processor through logic AND1.
O
Scan operand for “1” and combine with RLO through logic OR
The result is “1” when the operand in question has signal state “1”.
processor through logic OR1.
AN
Scan operand for “0” and combine with RLO through logic AND
The result is “1” when the operand in question has signal state “0”.
ON
Scan operand for “0” and combine with RLO through logic OR
ID
Parameter
I
Q
F
T
C
1
8-2
CPU 100
0.0 to 127.7
0.0 to 127.7
0.0 to 127.7
0
to 15
0
to 15
CPU 102
0.0 to 127.7
0.0 to 127.7
0.0 to 127.7
0
to
31
0
to
31
CPU 103
0.0 to 127.7
0.0 to 127.7
0.0 to 255.7
0
to 127
0
to 127
If the scan follows an RLO limiting operation directly (first scan), the scan result is reloaded as a new
RLO.
S5-100U
STEP 5 Operations
AND Operation
The AND operation scans to see if various conditions are satisfied simultaneously.
Example
Circuit Diagram
Output Q 1.0 is “1” when all three inputs are “1”.
The output is “0” if at least one input is “0”.
The number of scans and the sequence of the logic
statements are at random.
I 0. 0
I 0.1
I 0.2
Q 1.0
STL
CSF
A
I
0.0
A
A
I
I
Q
0.1
0.2
1.0
LAD
I 0.0
I 0.1
I 0.1
Q 1.0
I 0.2
I 0.0
I 0.2
Q 1.0
OR Operation
The OR operation scans to see if one of two (or more) conditions has been satisfied.
Example
Circuit Diagram
Output Q 1.0 is “1” when at least one of the inputs is “1”.
Output Q 1.0 is “0” when all inputs are “0” simultaneously.
The number of scans and the sequence of their
programming are optional.
I 0.0
I 0.1
I 0.2
Q 1.0
STL
CSF
LAD
I 0.0
O
O
O
I
I
I
0.0
0.1
0.2
Q
1.0
Q 1.0
I 0.0
I 0.1
I 0.2
& gt; =1
I 0.1
Q 1.0
I 0.2
8-3
STEP 5 Operations
S5-100U
AND before OR Operation
Example
Circuit Diagram
Output Q 1.0 is “1” when at least one AND condition has
been satisfied.
Output Q 1.0 is “0” when neither of the two AND conditions
has been satisfied.
I 0.0
I 0.2
I 0.1
I 0.3
Q 1.0
STL
CSF
A
I
0.0
A
O
A
I
I
0.2
I
Q
0.3
1.0
I 0. 0
0 1
A
I 0.0
& gt; =1
I 0.2
I 0.1
I 0.2
I 0.1
Q 1.0
I 0.3
I 0.3
8-4
LAD
Q 1.0
S5-100U
STEP 5 Operations
OR before AND Operation
Example
Circuit Diagram
Output Q 1.0 is “1” when one of the following conditions
has been satisfied:
I 0.0
• Input I 0.0 is “1”.
I 0.2
I 0.3
• Input I 0.1 and either input I 0.2 or I 0.3 is “1”.
I 0.1
Output Q 1.0 is “0” when none of the AND conditions has
been satisfied.
Q 1.0
STL
CSF
O
I
0.0
O
A
A(
I
0.1
I 0.1
O
O
I
I
0.2
0.3
I 0.2
Q
1.0
I 0.0
LAD
& gt; =1
Q 1.0
I 0.0
I 0.2
I 0.1
& gt; =1
I 0.3
I 0.3
Q 1.0
8-5
STEP 5 Operations
S5-100U
Example
Circuit Diagram
Output Q 1.0 is “1” when both OR conditions have been
satisfied.
Output Q 1.0 is “0” when at least one OR condition has not
been satisfied.
I 0.0
I 0.1
I 0.2
I 0.3
Q 1.0
STL
CSF
I 0.0
A(
O
O
I
I
0.0
0.1
A(
O
O
I
I
0.2
0.3
Q
1.0
8-6
LAD
& gt; =1
I 0.3
I 0.2
I 0.1
I 0.1
I 0.2
I 0.0
Q 1.0
I 0.3
& gt; =1
Q 1.0
S5-100U
8.1.2
STEP 5 Operations
Set/reset operations store the result of logic operation (RLO) formed in the processor. The stored
RLO represents the signal state of the addressed operand. Storage can be dynamic (assignment)
or static (set and reset). Table 8-2 provides an overview of the set/reset operations. Examples
follow the table.
Table 8-2. Overview of the Set/Reset Operations
Operation
Operand
Meaning
S
Set
The first time the program is scanned with RLO = “1”, signal state
“1” is assigned to the addressed operand. An RLO change does
not affect this status.
R
Reset
“0” is assigned to the addressed operand. An RLO change does
Assign
Every time the program is scanned, the current RLO is assigned to
ID
Parameter
I
Q
F
CPU 100
0.0 to 127.7
0.0 to 127.7
0.0 to 127.7
CPU 102
0.0 to 127.7
0.0 to 127.7
0.0 to 127.7
CPU 103
0.0 to 127.7
0.0 to 127.7
0.0 to 255.7
8-7
STEP 5 Operations
S5-100U
Flip-Flop for a Latching Signal Output (reset dominant)
Example
Circuit Diagram
A “1” at input I 0.1 sets flip-flop Q 1.0 (signal state “1”). If
the signal state at input I 0.1 changes to “0”, the state of
output Q 1.0 is maintained, i.e., the signal is latched.
A “1” at input I 0.0 resets the flip-flop (signal state “0”).
When the “SET” signal (input I 0.1) and the “RESET”
signal (input I 0.0) are applied at the same time, the
scanning operation that was programmed last (in this case
A I 0.0) is in effect during processing of the rest of the
program.
In this example, resetting output Q 1.0 has priority.
STL
I 0.0
Q 1.0
CSF
A
S
A
I
Q
I
0.1
1.0
0.0
R
NOP
Q
0
I 0.1
LAD
1.0
I 0.1
Q 1.0
R
S
S
I 0.0
I 0.1
Q 1.0
Q
I 0.0
R
8-8
NOP 0
Q
“NOP 0” is necessary if the program is to be represented in LAD or CSF form on programmers
with a screen. During programming in LAD and CSF, such “NOP 0” operations are allotted
automatically.
EWA 4NEB 812 6120-02b
S5-100U
STEP 5 Operations
RS Flip-Flop with Flags (set dominant)
Example
Circuit Diagram
A “1” at input I 0.0 sets flip-flop F 1.7 (signal state “1”).
If the signal state at input I 0.0 changes to “0”, the state of
flag F 1.7 is maintained, i.e., the signal is latched.
A “1” at input 0.1 resets the flip-flop (signal state “0”). If
the signal state at input I 0.1 changes to “0”, flag F 1.7
retains signal state “0”.
If both inputs have a “1” signal state, the flip-flop is set (set
dominant).
The signal state of the flag is scanned and transferred to
output Q 1.0.
STL
I 0.0
F 1.7
CSF
A
R
A
I
F
I
0.1
1.7
0.0
S
A
F
F
Q
1.7
1.7
1.0
LAD
F 1.7
I 0.1
I 0.1
F 1.7
R
R
Q 1.0
I 0.0
S
I 0.0
S
I 0.1
Q
Q
Q 1.0
8-9
STEP 5 Operations
8.1.3
S5-100U
Use load and transfer operations to do the following tasks.
Exchange information between various operand areas
Prepare time and count values for further processing
Load constants for program processing
Information flows indirectly via accumulators (ACCU 1 and ACCU 2). The accumulators are special
registers in the programmable controller that serve as temporary storage. They are each 16 bits
long. The accumulators are structured as shown in Figure 8-1.
ACCU 2
15
8
High byte
7
ACCU 1
0
Low byte
15
8
High byte
0
7
Low byte
Figure 8-1. Accumulator Structure
You can load and transfer permissible operands in bytes or words. For exchange in bytes, information is stored right-justified, i.e., in the low byte.
The remaining bits are set to zero.
You can use various operations to process the information in the two accumulators.
Load and transfer operations are executed independently of condition codes. Execution of these
operations does not affect the condition codes.
You can program load and transfer operations graphically only in combination with timer or counter
operations; otherwise you can represent them only in STL form.
Table 8-3 provides an overview of the load and transfer operations. Examples follow the table.
8-10
S5-100U
STEP 5 Operations
Table 8-3. Overview of Load and Transfer Operations
Operation
Operand
Meaning
L
Load
The operand contents are copied into ACCU 1 regardless of the RLO.
The RLO is not affected.
T
Transfer
The contents of ACCU 1 are assigned to an operand regardless of the
RLO.
ID
Parameter
CPU 100
0 to 127
0 to 126
0 to 127
0 to 126
0 to 127
0 to 126
0 to 255
0 to 255
0 to 255
0 to 15
0 to 15
--------random bit
pattern (16 bits)
0 to FFFF
-32768 to+32767
0 to 255
per byte
0 to 255
any 2
alphanumeric
characters
0.0 to 999.3
0 to 999
IB
IW
QB
QW
FY
FW
DR
DL
DW
T1
C1
PY
PW
KM1
KH1
KF1
KY1
KB1
KS1
KT1
KC1
LD
CPU 102
0 to 127
0 to 126
0 to 127
0 to 126
0 to 127
0 to 126
0 to 255
0 to 255
0 to 255
0 to 31
0 to 31
--------random bit
pattern (16 bits)
0 to FFFF
-32768 to +32767
0 to 255
per byte
0 to 255
any 2
alphanumeric
characters
0.0 to 999.3
0 to 999
CPU 103
0 to 127
0 to 126
0 to 127
0 to 126
0 to 255
0 to 254
0 to 255
0 to 255
0 to 255
0 to 127
0 to 127
0 to 127
0 to 126
random bit
pattern (16 bits)
0 to FFFF
-32768 to +32767
0 to 255
per byte
0 to 255
any 2
alphanumeric
characters
0.0 to 999.3
0 to 999
Load in BCD
Binary times and counts are loaded into ACCU 1 in BCD code regardless
of the RLO.
ID
Parameter
T
C
CPU 100
0 to 15
0 to 15
CPU 102
0 to 31
0 to 31
CPU 103
0 to 127
0 to 127
1 These operands cannot be used for transfer.
8-11
STEP 5 Operations
S5-100U
Load Operation
During loading, information is copied from a memory area, e.g., from the PII, into ACCU 1.
The previous contents of ACCU 1 are shifted to ACCU 2.
The original contents of ACCU 2 are lost.
Example:
Two consecutive bytes (IB7 and IB8) are loaded from the PII into the accumulator.
Loading does not change the PII (see Figure 8-2).
Lost
information
ACCU 2
Byte d
Byte c
ACCU 1
Byte b
Information
from the PII
Byte a
L IB7
Byte d
Byte c
Byte b
Byte a
0
IB7
IB7
L IB8
Byte b
Byte a
0
IB7
0
IB8
IB
Figure 8-2. Execution of the Load Operation
Transfer Operation
During transfer, information from ACCU 1 is copied into the addressed memory area, e.g., into the
PIQ.
This transfer does not affect the contents of ACCU 1.
Example:
Figure 8-3 shows how byte a, the low byte in ACCU 1, is transferred to QB5.
ACCU 2
Byte d
Byte c
ACCU 1
Byte b
Information
in the PIQ
Lost
information
Byte a
T QB5
Byte d
Byte c
Byte b
Byte a
Byte a
Previous value
of QB5
Figure 8-3. Transferring a Byte
8-12
S5-100U
STEP 5 Operations
Loading and Transferring a Time (See also Timer and Counter Operations)
Example
Representation
During graphic input, QW62 is assigned to output BI of
a timer. The programmer automatically stores the
corresponding load and transfer operation in the
control program. Thus the contents of the memory location addressed with T 10 are loaded into ACCU 1.
Afterwards, the contents of the accumulator are
transferred to the process image addressed with
QW62. In this example, you can see timer T 10 at
QW62 in binary code.
Outputs BI and DE are digital outputs. The time at
output BI is in binary code. The time at output DE is
in BCD code with time base.
STL
A
L
SP
I
IW
T
NOP 0
L
T
T
QW
T 10
Load
Transfer
QW62
CSF
0.0
22
10
10
62
NOP 0
NOP 0
LAD
T 10
I 0.0
T 10
I 0.0
1
IW22
1
TV
R
BI
DE
Q
QW62
IW22
TV
R
BI
DE
Q
QW62
8-13
STEP 5 Operations
S5-100U
Loading and Transferring a Time (Coded)
Example
Representation
The contents of the memory location addressed with
T 10 are loaded into the accumulator in BCD code.
Then a transfer operation transfers the accumulator
contents to the process image memory location
addressed by QW50. A coding operation is possible
only indirectly for the graphic representation forms
LAD and CSF by assigning an address to output DE of
a timer or counter location. However, this operation
can be entered with a separate statement with STL.
STL
A
L
SP
I
IW
T
NOP 0
NOP 0
LD
T
T
QW
NOP 0
8-14
T 10
Load
Transfer
QW50
CSF
0.0
22
10
50
T 10
I0.0
T 10
1
I 0.0
1
IW22
10
LAD
TV
R
BI
DE
Q
IW22
TV
QW50
R
BI
DE
Q
QW50
S5-100U
8.1.4
STEP 5 Operations
Timer Operations
The program uses timer operations to implement and monitor chronological sequences. Table 8-4
provides an overview of timer operations. Examples follow the table.
Table 8-4. Overview of Timer Operations
Operation
Operand
Meaning
SP
Pulse Timer
The timer is started on the leading edge of the RLO.
When the RLO is “0”, the timer is set to “0”.
Scans result in signal state “1” as long as the timer is running.
SE
Extended Pulse Timer
When the RLO is “0”, the timer is not affected.
SD
On-Delay Timer
Scans result in signal state “1” when the timer has run out and the
RLO is still pending at the input.
SS
Stored On-Delay Timer
Scans result in signal state “1” when the timer has run out.
The signal state becomes “0” when the timer is reset with the “R”
operation.
SF
Off-Delay Timer
The timer is started on the trailing edge of the RLO.
When the RLO is “1”, the timer is set to its initial value.
Scans result in signal state ”1” as long as the RLO at the input is
“1” or the timer is still running.
R
Reset Timer
The timer is reset to its initial value as long as the RLO is “1”.
Scans result in signal state “0” as long as the timer is reset or has
not been started yet.
ID
Parameter
T
CPU 100
0 to 15
CPU 102
0 to 31
CPU 103
0 to 127
8-15
STEP 5 Operations
S5-100U
Loading a Time
Timer operations call internal timers.
When a timer operation is started, the word in ACCU 1 is used as a time value. You must therefore
first specify time values in the accumulator.
You can load a timer with any of the following data types:
KT
DW
IW
QW
FW
constant time value
or
data word
input word
output word
flag word
These data types must be
in BCD code.
Loading a Constant Time Value
The following example shows how you can load a time value of 40 s.
Operation
Operand
L KT
40.2
Coded time base (0 to 3)
Time (0 to 999)
Key for Time Base
Base
Factor
8-16
0
0.01 s
1
0.1 s
2
1s
3
10 s
S5-100U
STEP 5 Operations
Example: KT 40.2 corresponds to 40 x 1 s.
Tolerance:
The time tolerance is equivalent to the time base.
Examples
Operand
Time Interval
Possible
KT 400.1
400 x 0.1 s
- 0.1 s
39.9 s to 40 s
settings for
the time
KT 40.2
40
x 1s
- 1s
39 s to 40 s
40 s
KT 4.3
4
x 10 s
- 10 s
30 s to 40 s
Note
Always use the smallest time base possible.
Loading a Time as an Input, Output, Flag, or Data Word
Load Statement:
L
DW
2
The time 638 s is stored in data word DW2 in BCD code.
Bits 14 and 15 are insignificant for the time value.
15
0
11
1
0
0
1
1
0
0
0
1
1
1
0
0
Bit
0
DW2
Three-digit time value
(in BCD code)
Time base
Key for Time Base:
Base
00
01
10
11
Factor
0.01 s
0.1 s
1s
10 s
You can also use the control program to write to data word DW2.
Example: Store the value 270 x 100 ms in data word DW2 of data block DB3.
C
L
T
DB 3
KT 270.1
DW2
8-17
STEP 5 Operations
S5-100U
Output of the Current Time 1
You can use a load operation to put the current time into ACCU 1 and process it further from there
(see Figure 8-4).
Use the “Load in BCD” operation for digital display output.
Current time in T1
L T1
LD T1
ACCU 1
Binary time value
Time
base
in BCD code
indicates bit positions occupied by “0”.
Figure 8-4. Output of the Current Time (Example)
1
The current time is the time value in the addressed timer.
8-18
S5-100U
STEP 5 Operations
Starting a timer
In the programmable controller, timers run asynchronously to program scanning. The time that has
been set can run out during a program scanning cycle. It is evaluated by the next time scan. In the
worst case, an entire program scanning cycle can go by before this evaluation. Consequently,
timers should not activate themselves.
Example:
Schematic Representation
Program
Signal from
timer 17
0
L
1
The schematic shows the “nth + 1”
processing cycle since timer T 17* was
started. Although the timer ran out
shortly after the statement “= Q 1.0”,
output Q 1.0 remains set. The change is
not considered until the next program
scanning cycle.
KT 100.0
SP T
17
A
T
17
n:
tp:
Explanation
Q
1.0
1s - n · tp
number of program scanning cycles
program scan time
* KT 100.0 is equal to 1 s.
The following rules apply to timers:
Except for “Reset timer”, all timer operations are started only when there is an edge change.
The RLO alternates between “0” and “1”.
After being started, the loaded time is decremented in units corresponding to the time base until
it reaches zero.
If there is an edge change while the timer is running, the timer is reset to its initial value and
restarted.
The signal state of a timer can be scanned with Boolean logic operations.
8-19
STEP 5 Operations
S5-100U
Pulse
Example:
Output Q 1.0 is set when the signal state at input I 0.0 changes from “0” to “1”.
However, the output should not remain set longer than 5 s.
Timing Diagram
Circuit Diagram
Signal states
I 0.0
1
I 0.0
0
T1
1
Q 1.0
0
Q 1.0
Time in s
5
T 1:
STL
A
L
SP
I
KT
T
CSF
0.0
500.0
1
1
1.0
T1
I 0.0
I 0.0
1
TV
BI
DE
R
T
Q
LAD
T1
KT 500.0
NOP 0
NOP 0
NOP 0
A
Time relay with transitional
NO contact
1
Q
KT 500.0
Q 1.0
TV
BI
DE
R
Q
Q 1.0
Note
The time tolerance is equivalent to the time base. Always use the smallest time base
possible.
8-20
S5-100U
STEP 5 Operations
Extended pulse
Example:
Output Q 1.0 is set for a specific time when the signal at input I 0.0 changes to “1”. The time is
indicated in IW16.
Timing Diagram
Circuit Diagram
Signal states
1
I 0.0
0
1
I 0.0
Q 1.0
0
T2
Time
t
Q 1.0
t
T 2: Time relay with pulse shaper
STL
A
L
I
IW
SE
T
NOP 0
NOP 0
NOP 0
A
T
Q
CSF
0.0
16
T2
T2
I 0.0
I 0.0
1
IW16
2
LAD
TV
V
1
BI
IW16
TV
DE
2
1.0
R
Q
V
BI
DE
Q 1.0
R
Q
Q 1.0
8-21
STEP 5 Operations
S5-100U
On-Delay
Example:
Output Q 1.0 is set 9 s after input I 0.0 and remains set as long as the input carries signal “1”.
Timing Diagram
Circuit Diagram
Signal states
I 0.0
1
I 0.0
0
1
Q 1.0
0
T3
Time in s
9
9
STL
A
L
SD
I
KT
T
CSF
0.0
900.0
3
8-22
LAD
T3
T3
I 0.0
I 0.0
T
KT 900.0
NOP 0
NOP 0
NOP 0
A
Q 1.0
TV
0
T
BI
KT 900.0
TV
DE
T
Q
R
3
1.0
Q
0
BI
DE
Q 1.0
R
Q
Q 1.0
S5-100U
STEP 5 Operations
Stored On-Delay and Reset
Example:
Output Q 1.0 is set 5 s after I 0.0.
Further changes in the signal state at input I 0.0 do not affect the output.
Input I 0.1 resets timer T 4 to its initial value and sets output Q 1.0 to zero.
Timing Diagram
Circuit Diagram
Signal states
I 0.1
1
I 0.0
0
1
H1
I 0.1
0
1
Q 1.0
H1
I 0.0
T4
0
5
Time
in s
5
Q 1.0
H1
H 1: Auxiliary relay
STL
A
L
SS
I
KT
T
A
I
R
T
NOP 0
NOP 0
A
T
Q
CSF
0.0
500.0
4
0.1
4
LAD
T4
T4
I 0.0
I 0.0
T
KT 500.0
TV
T
s
R
KT 500.0
DE
I 0.1
BI
TV
I 0.1
Q
Q 1.0
4
1.0
s
BI
DE
R
Q
Q 1.0
Note
8-23
STEP 5 Operations
S5-100U
Off-Delay
Example:
When input I 0.0 is reset, output Q 1.0 is set to zero after a certain delay (t). The value in FW14
specifies the delay time.
Timing Diagram
Circuit Diagram
Signal states
I 0.0
1
I 0.0
0
1
Q 1.0
0
T5
Time in s
t
t
STL
A
L
I
FW
SF
T
NOP 0
NOP 0
NOP 0
A
T
Q
8-24
Q 1.0
CSF
0.0
14
T5
T5
I 0.0
I 0.0
0
FW14
5
LAD
TV
0
T
FW14
BI
TV
R
Q
BI
DE
DE
5
1.0
T
Q 1.0
R
Q
Q 1.0
S5-100U
8.1.5
STEP 5 Operations
Counter Operations
The programmable controller uses counter operations to handle counting jobs. Counters can count
up and down. The counting range is from 0 to 999 (three decades). Table 8-5 provides an
overview of the counter operations. Examples follow the table.
Table 8-5. Overview of Counter Operations
Operation
Operand
Meaning
S
Set Counter
The counter is set on the leading edge of the RLO.
R
Reset Counter
The counter is set to zero as long as the RLO is “1”.
CU
Count Up
The count is incremented by 1 on the leading edge of the RLO.
When the RLO is “0”, the count is not affected.
CD
Count Down
The count is decremented by 1 on the leading edge of the RLO.
ID
Parameter
C
CPU 100
0 to 15
CPU 102
0 to 31
CPU 103
0 to 127
Loading a Count
Counter operations call internal counters.
When a counter is set, the word in ACCU 1 is used as a count. You must therefore first store
counts in the accumulator.
You can load a count with any of the following data types:
KC
DW
IW
QW
FW
constant count
or
data word
input word
output word
flag word
The data for these words must
be in BCD code.
8-25
STEP 5 Operations
S5-100U
Loading a Constant Count
The following example shows how the count 38 is loaded.
Operation
Operand
L KC
38
Count (0 to 999)
Loading a Count as an Input, Output, Flag, or Data Word
Load statement:
L
DW
3
The count 410 is stored in data word DW3 in BCD code.
Bits 12 to 15 are insignificant for the count.
15
11
0
0
1
0
0
0
0
0
1
0
0
0
Bit
0
DW3
Three-digit count
(in BCD code)
Scanning the Counter
Use Boolean logic operations to scan the counter status (e.g., A Cx). As long as the count is not
zero, the scan result is signal state “1”.
8-26
S5-100U
STEP 5 Operations
You can use a load operation to put the current counter status into ACCU 1 and process it further
from there. The “Load in BCD” operation outputs a digital display (see Figure 8-5).
Current Counter Status in C2
L C2
LD C2
ACCU 1
Binary count
Three-digit count
in BCD code
Figure 8-5. Outputting the Current Counter Status (Example)
8-27
STEP 5 Operations
S5-100U
Setting a Counter “S” and Counting Down “CD”
Example:
When input I 0.1 is switched on (set), counter 1 is set to count 7. Output Q 1.0 is now “1”.
Every time input I 0.0 is switched on (count down), the count is decremented by 1.
The output is set to “0” when the count is “0”.
Timing Diagram
Circuit Diagram
I 0.1
1
0
I 0.0
1
0
I 0.1
KC 7
R
S
CI
C1
7
I 0.0
0
1
0
IIII
Q 1.0
Time
Count
Q 1.0
S C1
S C1
STL
A
CD
I
C
NOP
A
L
0
I
KC
S
NOP
NOP
C
0
0
NOP
A
0
C
Q
8-28
CSF
0.0
1
LAD
C1
I 0.0
0.1
7
CD
CD
CU
I 0.1
KC 7
C1
I 0.0
I 0.1
CU
S
S
1
CV
Q
KC 7
BI
DE
R
1
1.0
Binary
16 bits
CQ
0
Q 1.0
CV
BI
DE
R
Q
Q 1.0
S5-100U
STEP 5 Operations
Resetting a Counter “R” and Counting Up “CU”
Example:
When input I 0.0 is switched on, the count in counter 1 is incremented by 1. As long as a second
input (I 0.1) is “1”, the count is reset to “0”.
The A C 1 operation results in signal state “1” at output Q 1.0 as long as the count is not “0”.
Timing Diagram
Circuit Diagram
I 0.0
1
0
1
0
I 0.1
I 0.1
2
R
S
CI
C 1
0
I 0.0
IIII
Q 1.0
1
CQ
0
0
Binary
16 bits
Time
R
C1
Q 1.0
STL
A
CU
I
C
NOP
NOP
NOP
0
0
0
A
R
NOP
I
C
0
NOP
A
0
C
Q
CSF
0.0
1
LAD
C1
I 0.0
C1
I 0.0
S
CV
I 0.1
CD
S
1
1.0
CU
CD
0.1
1
CU
BI
DE
R
Q
CV
BI
DE
R
Q
I 0.1
Q 1.0
Q 1.0
8-29
STEP 5 Operations
S5-100U
8.1.6 Comparison Operations
Comparison operations compare the contents of the two accumulators. The comparison does not
change the accumulators' contents. Table 8-6 provides an overview of the comparison operations.
An example follows the table.
Table 8-6. Overview of Comparison Operations
Operation
Operand
Meaning
F
Compare for “equal to”
The contents of the two accumulators are interpreted as bit patterns
and scanned to see if they are equal.
& gt; & lt;
F
Compare for “not equal to”
and compared to see if they are not equal.
& gt;
F
Compare for “greater than”
The contents of the two accumulators are interpreted as fixed-point
numbers. They are compared to see if the operand in ACCU 2 is
greater than the operand in ACCU 1.
& gt; =
F
Compare for “greater than or equal to”
greater than or equal to the operand in ACCU 1.
& lt;
F
Compare for “less than”
less than the operand in ACCU 1.
& lt; =
F
Compare for “less than or equal to”
less than or equal to the operand in ACCU 1.
Processing Comparison Operations
To compare two operands, load them consecutively into the two accumulators. Execution of the
operations is independent of the RLO.
The result is binary and is available as RLO for further program processing. If the comparison is
satisfied, the RLO is “1”. Otherwise it is “0”.
Executing the comparison operations sets the condition codes (see section 8.4).
Note
When using comparison operations, make sure the operands have the same number
format.
8-30
S5-100U
STEP 5 Operations
Example:
The values of input bytes IB19 and IB20 are compared. If they are equal, output
Q 1.0 is set.
Circuit Diagram
IB19
STL
CSF/LAD
IB20
L
L
C1
19
20
!=F
C2
IB
IB
Q
1.0
IB19
C1
F
IB20
C2
Q
Q 1.0
Q 1.0
8.1.7
Arithmetic operations interpret the contents of the accumulators as fixed-point numbers and
manipulate them. The result is stored in ACCU 1. Table 8-7 provides an overview of the arithmetic
operations. An example follows the table.
Table 8-7. Overview of Arithmetic Operations
Operation
Operand
+F
-F
Meaning
Addition
The contents of both accumulators are added.
Subtraction
The contents of ACCU 1 are subtracted from the contents of
ACCU 2.
CPU 102 and higher have integral function blocks for multiplication and division (see section 9.2).
8-31
STEP 5 Operations
S5-100U
Processing an Arithmetic Operation
Before an arithmetic operation is executed, both operands must be loaded into the accumulators.
Note
When using arithmetic operations, make sure the operands have the same number
format.
Arithmetic operations are executed independently of the RLO. The result is available in ACCU 1 for
further processing. The contents of ACCU 2 are not changed.
These operations do not affect the RLO. The condition codes are set according to the results.
STL
Explanation
L
C 3
The value of counter 3 is loaded into ACCU 1.
L
C 1
The value of counter 1 is loaded into ACCU 1. The previous contents of
The contents of the two accumulators are interpreted as 16-bit fixed-point
numbers and added.
+ F
T
The result, contents of ACCU 1, is transferred to output word QW12.
QW12
Numeric Example
15
876
668
0
0 0 0 0 0 0 1 1 0 1 1 0 1 1 0 0
ACCU 2
+F
0 0 0 0 0 0 1 0 1 0 0 1 1 1 0 0
ACCU 1
0 0 0 0 0 1 1 0 0 0 0 0 1 0 0 0
ACCU 1
1544
8-32
S5-100U
8.1.8
STEP 5 Operations
Block call operations specify the sequence of a structured program. Table 8-8 provides an overview
of the block call operations. Examples follow the table.
Table 8-8. Overview of Block Call Operations
Operation
Operand
Meaning
JU
Jump unconditionally
Program scanning continues in a different block regardless of the
RLO.
JC
Jump conditionally
Program scanning jumps to a different block when the RLO is “1”.
Otherwise program scanning continues in the same block.
The RLO is set to “1”.
ID
Parameter
OB
PB
FB
SB
CPU 100
0 to 63
0 to 63
0 to 63
CPU 102
0 to 63
0 to 63
0 to 63
CPU 103
0 to 255
0 to 255
0 to 255
0 to 255
C
Call a data block
A data block is activated regardless of the RLO.
Program scanning is not interrupted.
G
Generate and delete a data block*
An area is set up in the RAM to store data regardless of the RLO.
ID
Parameter
DB
CPU 100
2 to 63**
CPU 102
2 to 63**
CPU 103
2 to 255**
BE
BEU
Block end, unconditional
The current block is terminated regardless of the RLO.
Program scanning continues in the block in which the call originated.
The RLO is “carried along” but not affected.
BEC
Block end
The RLO is “carried along” but not affected. BE is always the last
statement in a block.
Block end, conditional
When the RLO is “1”, the current block is terminated.
During the block change, the RLO remains “1”.
If the RLO is “0”, the operation is not executed.
The RLO is set to “1” and linear program scanning continues.
The length of the DB must be loaded into ACCU 1 before execution of the operation. A length of 0
makes the DB invalid.
Data blocks DB0 and DB1 are reserved for special functions.
8-33
STEP 5 Operations
S5-100U
Unconditional Block Call “JU”
One block is called within another block, regardless of conditions.
Example:
A special function has been programmed in FB26. It is called at several locations in
the program, e.g., in PB63, and processed.
Program Sequence
PB63
STL
FB26
JU
JU FB26
Explanation
The “JU FB26” statement in program
block PB63 calls function block FB26.
FB 26
Conditional Block Call “JC”
One block is called within another block when the previous condition has been satisfied
(RLO = “1”).
Example:
A special function has been programmed in FB63. It is called and processed under
certain conditions, e.g., in PB10.
Program Sequence
PB10
A
I 0.0
STL
FB63
S
A
JC
JC FB63
8-34
Explanation
F
I
FB
1.0
0.0
The “JC FB63” statement in program
block PB10 calls function block FB63
if input I 0.0 is “1”.
63
S5-100U
STEP 5 Operations
Call a Data Block “C DB”
Data blocks are always called unconditionally. All data processed following the call refers to the data
block that has been called. This operation cannot generate new data blocks. Blocks that are called
must be programmed or created before program scanning.
Example:
Program block PB3 needs information that has been programmed as data word DW1 in
data block DB10. Other data, e.g., the result of an arithmetic operation, is stored as
data word DW3 in data block DB20.
Program Sequence
STL
PB3
DB10
C
DB 10
C DB10
DW1
L
L DW1
DW 1
C DB20
DB20
C
The information from data word DW1
in data block DB10 is loaded into the
accumulator. The contents of ACCU 1
are stored in data word DW3 of data
block DB20.
DB 20
T
Explanation
DW 3
T DW3
DW3
Generating and Deleting a Data Block
The “G DB x” statement does not call a data block. Instead, it generates a new block. If you want
to use the data in this data block, call it with the “C DB” statement.
Before the “G DB” statement, indicate in ACCU 1 the number of data words the block is to have
(see the example below).
If you specify zero as the data block length, the data block in question is deleted, i.e., it is removed
from the address list. It is considered nonexistent.
Note
The block is stored in memory and is designated as invalid until the programmable
controller memory is compressed (see section 7.5.3).
If you try to set up a data block that already exists, the “G DB x” statement is not executed.
A data block can be a maximum of 256 data words (DW0 to 255) in length.
8-35
STEP 5 Operations
S5-100U
Generating a Data Block
Example
Generate a data block with 128 data
words without the aid of a programmer.
STL
Explanation
L
KF + 127
G
DB
5
The constant fixed-point number
+127 is loaded into ACCU 1. At
the same time, the old contents
Data block 5 is generated with a
length of 128 data words (0000)
in the RAM of the PLC and
entered in the block address list.
The next time the “G DB5”
operation is processed, it has no
effect if the contents of
ACCU 1 are not 0.
Example
Delete a data block that is no longer
needed.
8-36
STL
L
G
KF + 0
DB
5
Explanation
+0 is loaded into ACCU 1. At the
same time, the old contents of
Data block 5, which must be in
the RAM of the PLC, is declared
invalid and removed from the
block address list.
S5-100U
STEP 5 Operations
Block End “BE”
The “BE” operation terminates a block. Data blocks do not need to be terminated. “BE” is always
the last statement in a block.
In structured programming, program scanning jumps back to the block where the call for the current
block was made.
Boolean logic operations cannot be continued in a higher-order block.
Example:
Program block PB3 is terminated by the “BE” statement.
Program Sequence
STL
Explanation
OB1
PB3
JU PB3
The “BE” statement terminates
program block PB3 and causes
program scanning to return to
organization block OB1.
BE
BE
Unconditional Block End “BEU”
The “BEU” operation causes a return within a block. However, jump operations can bypass the
“BEU” operation in function blocks (see sections 8.2.10 and 8.3.4).
Binary logic operations cannot be continued in a higher-order block.
Example:
Scanning of function block FB21 is terminated regardless of the RLO.
Program Sequence
PB8
FB21
JC=
JU FB21
BEU
STL
JC=
BEU
Explanation
The “BEU” statement causes program
scanning to leave function block FB21
and return to program block PB8.
BE
BE
8-37
STEP 5 Operations
S5-100U
Conditional Block End “BEC”
The “BEC” operation causes a return within a block if the previous condition has been satisfied
(RLO = 1).
Otherwise, linear program scanning is continued with RLO “1”.
Example:
Scanning of program block FB20 is terminated if the RLO = “1”.
Program Sequence
PB7
STL
FB20
A
I
0.0
The “BEC” statement causes program
scanning to return to program block
PB7 from function block FB20 if input
I 0.0 is “1”.
BEC
A I 0.0
JU FB20
Explanation
BEC
8.1.9
Other Operations
Table 8-9 lists other basic operations. Explanations follow the table.
Table 8-9. Other Operations
Operation
Operand
STP
Meaning
Stop at the end of program scanning (in OB1)
Current program scanning is terminated.
The PIQ is read out. Then the PLC goes into the STOP mode.
NOP 0
“No” Operation
Sixteen bits in the RAM are set to “0”.
NOP 1
“No” Operation
Sixteen bits in the RAM are set to “1”.
BLD
Display Generation Operation
“BLD” means a display generation operation for the programmer.
ID
Parameter
130, 131, 132, 133, 255
Note
These operations can be programmed in STL form only.
8-38
S5-100U
STEP 5 Operations
STOP Operation
The “STP” operation puts the programmable controller into the STOP mode. This can be desirable
for time-critical system circumstances or when a programmable controller error occurs.
After the statement is processed, the control program is scanned to the end, regardless of the RLO.
Afterwards the programmable controller goes into the STOP mode with the error ID “STS”. You
can restart the programmable controller with the mode selector (STOP to RUN) or with a
programmer.
“NOP” (No Operations)
The “NOP” operations reserve or overwrite memory locations.
Display Generation Operations
“BLD” display generation operations divide program parts into segments within a block.
“NOP” operations and display generation operations are significant only for the programmer when
representing the STEP 5 program.
The programmable controller does not execute any operation when these statements are processed.
8.2
Supplementary operations extend the operations set. However, compared to basic operations,
which can be programmed in all blocks, supplementary operations have the following limitations.
They can be programmed in function blocks only.
They can be represented in STL form only.
The following sections describe the supplementary operations.
8-39
STEP 5 Operations
8.2.1
S5-100U
As with the basic load operations, the supplementary load operation copies information into the
accumulator. Table 8-10 explains the load operation. An example follows the table.
Table 8-10. Load Operation
Operation
Operand
L
Meaning
Load
A word from the system data is loaded into ACCU 1 regardless of the
RLO.
ID
Parameter
RS
0 to 255
Example
In order to set parameters for
SINEC L1 bus operation via the
system data, the programmer and
slave numbers from SD57 should
be input into ACCU 1.
8-40
STL
L
RS
57
Explanation
Load ACCU 1 with the programmer and slave numbers.
S5-100U
8.2.2
STEP 5 Operations
You can use the enable operation (FR) to execute the following operations even without an edge
change.
Start a timer
Set a counter
Count up and down
Table 8-11 presents the enable operation. An example follows the table.
Table 8-11. Enable Operation
Operation
Operand
Meaning
FR
Enable a Timer/Counter
Timers and counters are enabled on the leading edge of the RLO.
This operation restarts a timer, sets a counter, or causes a counter
to count up or down when the RLO “1” is pending at the “Start”
operation.
ID
Parameter
T
C
0 to 127
0 to 127
Example
Input I 0.0 starts a timer T 2 as an
extended pulse (pulse width 50 s).
This timer sets output Q 1.0 for the
duration of the pulse.
STL
A
I
L
SE
A
KT
T
T
Q
If output Q 1.1 is reset repeatedly, the
timer should also be restarted
repeatedly.
0.0
500.1
2
2
1.0
Start a timer T 2 as an extended
pulse.
Output Q 1.0 is set for 50 s.
A
Q
FR
T
BE
Explanation
1.1
2
If output Q 1.1 is set (positive
edge change of the RLO) during
the time in which input I 0.0 is
set, timer T 2 is restarted. Output
Q 1.0 therefore remains set at the
restarted time or is reset.
If input I 0.0 is not set during the
edge change of output Q 1.1, the
timer is not restarted.
8-41
STEP 5 Operations
8.2.3
S5-100U
Bit test operations scan digital operands bit by bit and affect them. Bit test operations must always
be at the beginning of a logic operation. Table 8-12 provides an overview of these operations.
Table 8-12. Overview of Bit Operations
Operation
Operand
Meaning
TB
Test a bit for signal state “1”
A single bit is scanned regardless of the RLO. The RLO is affected
according to the bit's signal state (see Table 8-13).
TBN
Test a bit for signal state “0”
SU
Set a bit unconditionally
The addressed bit is set to “1” regardless of the RLO. The RLO is
not affected.
RU
Reset a bit unconditionally
The addressed bit is set to “0” regardless of the RLO. The RLO is
not affected.
ID
Parameter
T
C
D
RS1
1
0.0 to 127.15
0.0 to 127.15
0.0 to 255.15
0.0 to 255.15
RS applies only to TB and TBN
Table 8-13 shows how the RLO is formed during the bit test operations “TB” and “TBN”.
example for applying the bit operations follows the table.
An
Table 8-13. Effect of “TB” and “TBN” on the RLO
Operation
TB
TBN
Signal state of the bit in
the operand indicated
1
0
1
Result of logic operation
8-42
0
0
1
1
0
S5-100U
STEP 5 Operations
Example
A photoelectric barrier that counts
piece goods is installed at input
I 0.0. After every 100 pieces, the
program is to jump to FB5 or FB6.
After 800 pieces, counter 10 is to
be reset automatically and start
counting again.
STL
Explanation
DB
10
A
CU
A
I
C
I
0.0
10
0.1
L
S
O
O
KC
C
I
F
000
10
0.2
5.2
R
LD
T
C
C
DW
10
10
12
TBN
D
12.8
JC
FB
5
TB
D
12.8
JC
FB
6
TB
D
12.11
I 0.3. After every 256 pieces, the
counter is supposed to be reset and
start counting again.
C
F
5.2
:A
I
0.3
:CU
:A
:L
:S
C
I
KC
C
2
0.4
000
20
:TB C
20.8
:JC =
:BEU
20.8
Input I 0.1 loads the count of
counter 10 with the constant 0. With
each positive edge change at I 0.0,
the counter is incremented by 1. The
counter is reset by either input I 0.2
or flag F 5.2.
The current count of the counter is
stored in data word DW12 in BCD
code.
As long as bit 8 of data word DW12
is zero, program processing jumps to
function block FB5. This is the case
for the first, third, fifth etc. batch of
100 pieces.
is “1”, program scanning jumps to
function block FB 6. This is the case
for the second, fourth, sixth, etc.
batch of 100 pieces.
When data bit 11 of data word DW12
becomes “1” (the count is then 800),
flag F 5.2 is set conditionally.
Input I 0.4 loads the count of counter
20 with the constant 0. The count is
incremented by 1 with each positive
edge change at input I 0.3. If the
count has reached 256 = 100H (bit 8
is “1”), program scanning jumps to
the label “FULL”. Otherwise the
FULL
FULL:RU C
:BE
Call data block 10.
Bit 8 of counter C 20 is set to “0”
unconditionally. Then the count is
again 000H.
Note
Times and counts are stored in the timer/counter word in hexadecimal notation in the
10 least significant bits (bits 0 to 9).
The time base is stored in bits 12 and 13 of the timer word.
8-43
STEP 5 Operations
8.2.4
S5-100U
Digital logic operations combine the contents of both accumulators logically bit by bit.
Table 8-14 provides an overview of these digital logic operations. Examples follow the table.
Table 8-14. Overview of Digital Logic Operations
Operation
Operand
Meaning
AW
Combine bit by bit through logic AND
OW
Combine bit by bit through logic OR
XOW
Combine bit by bit through logic EXCLUSIVE OR
Processing a Digital Logic Operation
A digital logic operation is executed regardless of the RLO. It also does not affect the RLO.
However, it sets condition codes according to the result of the arithmetic operation (see section 8.4).
Note
Make sure both operands have the same number format. Then load them into the
accumulators before executing the operation.
8-44
S5-100U
STEP 5 Operations
The result of the arithmetic operation is available in ACCU 1 for further processing. The contents of
ACCU 2 are not affected.
STL
Explanation
L
IW 92
Load input word IW92 into ACCU 1.
L
KH 00FF
Load a constant into ACCU 1. The previous contents of ACCU 1 are shifted
to ACCU 2.
Combine the contents of both accumulators bit by bit through logic AND.
AW
T
QW 82
Transfer the resulting contents from ACCU 1 to output word QW82.
Numeric Example
IW92
15
ACCU 2
0
0 1 1 1 0 0 0 1 1 0 0 1 1 1 0 0
KH 00FF
ACCU 1
AND
Set the 8 high-order bits in input
word IW92 to “0”.
Compare both words bit by bit. If
corresponding bits are both “1”, the
result bit is set to “1”.
0 0 0 0 0 0 0 0 1 1 1 1 1 1 1 1
Result
ACCU 1
0 0 0 0 0 0 0 0 1 0 0 1 1 1 0 0
8-45
STEP 5 Operations
S5-100U
STL
Explanation
L
IW 36
Load input word IW36 into ACCU 1.
L
KH 00FF
to ACCU 2.
Combine the contents of both accumulators bit by bit through logic OR.
OW
T
Transfer the result (contents of ACCU 1) to input word IW36.
IW 36
Numeric Example
15
ACCU 2
IW36
1 1 1 0 0 1 0 0 1 1 0 0 0 1 1 0
KH 00FF
ACCU 1
0
OR
Set the 8 low-order bits in input word
IW36 to “1”. Compare both words
bit by bit.
If either of the corresponding bits is
“1”, a “1” is set in the result word.
Result
ACCU 1
8-46
1 1 1 0 0 1 0 0 1 1 1 1 1 1 1 1
S5-100U
STEP 5 Operations
STL
Explanation
L
IW 70
Load input word IW70 into ACCU 1.
L
IW 6
Load input word IW6 into ACCU 1. The previous contents of ACCU 1 are
shifted to ACCU 2.
EXCLUSIVE OR.
XOW
T
Transfer the result (contents of ACCU 1) to output word QW86.
QW 86
Numeric Example
15
ACCU 2
IW70
0 0 0 1 1 0 1 1 0 1 1 0 1 1 0 0
IW6
ACCU 1
0
X-OR
Check to see if input words IW70
and IW6 are equal.
The result bit is set to “1” only if
corresponding bits in ACCU 1 and
ACCU 2 are unequal.
1 0 0 1 1 0 0 1 1 1 0 0 0 1 1 0
Result
ACCU 1
1 0 0 0 0 0 1 0 1 0 1 0 1 0 1 0
8-47
STEP 5 Operations
8.2.5
S5-100U
Shift Operations
Shift operations shift a bit pattern in ACCU 1. The contents of ACCU 2 are not affected. Shifting
multiplies or divides the contents of ACCU 1 by powers of two. Table 8-15 provides an overview of
the shift operations. Examples follow the table.
Table 8-15. Overview of Shift Operations
Operation
Operand
Meaning
SLW
Shift to the left.
The bit pattern in ACCU 1 is shifted to the left.
SRW
Shift to the right.
The bit pattern in ACCU 1 is shifted to the right.
Parameter
0 to 15
Processing a Shift Operation
Execution of shift operations is unconditional. The RLO is not affected. However, shift operations
set condition codes.
Consequently, the status of the last bit that is shifted out can be scanned with jump functions.
The shift statement parameter indicates the number of bit positions by which the contents of
ACCU 1 are to be shifted to the left (SLW) or to the right (SRW). Bit positions vacated during
shifting are assigned zeros.
The contents of the bits that are shifted out of ACCU 1 are lost. Following execution of the
operation, the state of bit 20 (SRW) or bit 215 (SLW) has an influence on the CC1 bit, which can
then be evaluated.
A shift operation with parameter “0” is handled like a “NOP” operation. The central processor processes the next STEP 5 statement with no further reaction.
Before executing a shift operation, load the operand to be processed into ACCU 1.
The altered operand is available there for further processing.
8-48
S5-100U
STEP 5 Operations
STL
L
Explanation
Load the contents of data word DW2 into ACCU 1.
DW 2
Shift the bit pattern in ACCU 1 three positions to the left.
SLW 3
T
Transfer the result (contents of ACCU 1) to data word DW3.
DW 3
Numeric Example
46410
15
ACCU 1
(DW2)
The value 46410 is stored in data
word DW2. Multiply this value by
23=8. Do so by shifting the bit
pattern of DW2 in ACCU 1 three
0
0 0 0 0 0 0 0 1 1 1 0 1 0 0 0 0
SLW 3
371210
15
ACCU 1
0
0 0 0 0 1 1 1 0 1 0 0 0 0 0 0 0
STL
L
Explanation
Load the value of input word IW124 into ACCU 1.
IW 124
Shift the bit pattern in ACCU 1 four positions to the right.
SRW 4
T
Transfer the result (contents of ACCU 1) to output word QW126.
QW 126
Numeric Example
15
ACCU 1
35210
(IW124)
0
0 0 0 0 0 0 0 1 0 1 1 0 0 0 0 0
SRW 4
15
ACCU 1
2210
The value 35210 is stored in IW124.
Shift the corresponding bit pattern in
ACCU 1 four positions to the right to
divide the value 35210 by 24 = 16.
0
0 0 0 0 0 0 0 0 0 0 0 1 0 1 1 0
8-49
STEP 5 Operations
8.2.6
S5-100U
Conversion operations convert the values in ACCU 1. Table 8-16 provides an overview of the
conversion operations. Examples follow the table.
Table 8-16. Overview of Conversion Operations
Operation
Operand
Meaning
CFW
One's complement
The contents of ACCU 1 are inverted bit by bit.
CSW
Two's complement
The contents of ACCU 1 are inverted bit by bit. Afterwards the word
0001H is added.
Processing Conversion Operations
Execution of these operations does not depend on the RLO nor does it affect the RLO.
The “CSW” operation sets the condition codes (see section 8.4).
STL
L
Explanation
Load the contents of data word DW12 into ACCU 1.
DW 12
Invert all bits in ACCU 1.
CFW
T
Transfer the new contents of ACCU 1 to output word QW20.
QW 20
Numeric Example
15
ACCU 1
DW12
0
CFW
15
ACCU 1
8-50
0
In a system, normally open contacts
have been replaced by normally
closed contacts. If the information in
data word DW12 is to maintain its
previous effect, DW12 must be
inverted.
1 0 0 0 1 1 1 0 0 1 1 0 0 0 1 1
S5-100U
STEP 5 Operations
STL
L
Explanation
Load the contents of input word IW12 into ACCU 1.
IW 12
Invert all bits and add a “1”.
CSW
T
Transfer the altered word to data word DW100.
DW 100
Numeric Example
15
ACCU 1
IW12
0 1 0 1 1 0 0 1 1 1 0 0 0 1 0 1
CSW
15
ACCU 1
0
Form the negative value of the value
in input word IW12.
+1
0
1 0 1 0 0 1 1 0 0 0 1 1 1 0 1 1
8-51
STEP 5 Operations
8.2.7
S5-100U
The decrement/increment operations change the data loaded into ACCU 1. Table 8-17 provides an
overview of the decrement/increment operations. An example follows the table.
Table 8-17. Decrement/Increment Operations
Operation
Operand
Meaning
D
Decrement
Decrement the contents of the accumulator.
I
Increment
Increment the contents of the accumulator.
The contents of ACCU 1 are either decremented or incremented by
the number indicated in the parameter.
Execution of the operation is unconditional and is limited to the
right-hand byte (without carry).
Parameter
0 to 255
Processing
Execution of the decrement and increment operations is independent of the RLO and does not affect
the RLO or the condition codes.
The parameter indicates the value by which the contents of ACCU 1 are to be changed.
The operations refer to decimal values; however, the result is stored in ACCU 1 in binary form.
Changes relate only to the low byte in the accumulator.
Example
Increment the hexadecimal constant
1010H by 16 and store the result in
data word DW8.
STL
16
T
DW
D
33
T
8-52
DB
KH
I
In addition, decrement the incrementation result by 33 and store the new
result in data word DW9.
C
L
DW
Explanation
6
1010
8
9
Call data block DB6.
Load hexadecimal constant 1010H
into ACCU 1.
Increment the low byte of ACCU 1
by 16. The result, 1020H, is
located in ACCU 1.
Transfer the contents of ACCU 1
(1020H) to data word DW8. Since
the incrementation result is still in
ACCU 1, you can decrement by 33
directly.
The result would be FFFH.
However, since the high byte of
ACCU 1 is not decremented along
with the low byte, the result in
ACCU 1 is 10FFH.
transferred to DW9 (10FFH).
S5-100U
8.2.8
STEP 5 Operations
The disable/enable interrupt operations affect interrupt-driven and time-controlled program scanning.
They prevent process or time interrupts from interfering with the processing of a sequence of statements or blocks. Table 8-18 lists the disable/enable interrupt operations. An example follows the
table.
Table 8-18. Disable/Enable Interrupt Operations
Operation
Operand
Meaning
IA
Disable interrupt
RA
Enable interrupt
Processing
Execution of the disable/enable interrupt operations does not depend on the RLO. These operations
do not affect the RLO or the condition codes. After the “IA” statement is processed, no more
interrupts are executed. The “RA” statement cancels the effect of “IA”.
Example
STL
Disable interrupt processing in a
specific program section and then
enable it again.
Explanation
Q
1.0
I
0.0
Disable interrupt.
IA
A
FB
If an interrupt occurs, the program
section between the “IA” and
“RA” is scanned without
interruption.
JU
Enable interrupt.
Interrupts that occurred in the
meantime are processed after the
“RA” operation.
RA
3
8-53
STEP 5 Operations
8.2.9
S5-100U
Use the “DO” operation to process STEP 5 statements as indexed operations. This allows you to
change the parameter of an operand during control program processing (see Table 8-19).
Table 8-19.
Operation
Operand
DO
Meaning
Processing a flag word or data word
ID
FW
DW
Parameter
0 to 254
0 to 255
“DO” Statements
“DO flag word or data word x” is a two-word statement that is unaffected by the RLO. “DO”
consists of the following two statements:
The first statement contains the “DO” operation and a flag word or data word.
The second statement defines the operation and the operand identifier you want the control
program to process. You must enter 0 or 0.0 as the parameter.
The control program works with the parameter that is stored in the flag word or data word. This
parameter is the one called up in the first statement. If you want to index binary operations, inputs,
outputs, or flags, you input the bit address in the high byte of this word. You input the byte address
in the low byte. In any other instance, the high byte must be “0”.
You can combine the following operations with the “DO” statement:
Operations
A1, AN, O, ON
S, R, =
FR T, RT, SF T, SD T, SP T, SS T, SE T,
FR C, RC, SC, CD C, CU C
L, LD, T
JU=, JC=JZ=, JN=, JP=, JM=, JO=
SLW, SRW
D, I
C DB, JU, JC, TNB
1
Explanations
Timer operations
Counter operations
Jump operations
Shift operations
Decrement and increment
Block calls
In combination with “DO FW,” the “A I” operation becomes the “A Q” operation if the byte address in
the data word or flag word is higher than 127.
Caution
Damage to the system.
Performing operations that are not listed in Table 8-20 will damage your system.
Perform only those operations that are listed in Table 8-20.
8-54
S5-100U
STEP 5 Operations
Figure 8-6 shows how the contents of a data word determine the parameter of the next statement.
DB6
FBx
:C
DW 12
KH = 0108
DW 13
DB
:DO DW
:A I
:DO DW
:FR T
KH = 0001
Actual program
6
:C
DB
:A I
:FR T
12
0.0
13
0
6
8.1
1
Figure 8-6. Executing a “DO” Operation
The following example illustrates how new parameters are generated in every program scan.
Example
STL
Set the contents of data words
DW20 to DW100 to signal state
“0”. The index register for the
parameter for the data words is
DW1.
Explanation
:C
:L
:T
DW 1
:L
KH 0
Call data block DB202.
Load constant number 20 in
ACCU 1.
Transfer contents from ACCU 1 to
data word DW1.
Load hex constant 0 in ACCU 1.
:DO
DW 1
DO data word DW1.
:T
DW 0
:L
DW 1
Transfer the contents from ACCU 1
to the data word whose address is
stored in data word DW1.
Load data word DW1 in ACCU 1.
:L
KB 1
Load constant number 1 in ACCU 1.
Data word DW1 is shifted to
ACCU 2.
ACCU 2 und ACCU 1 are added,
and the result is stored in ACCU 1
(data word address is higher).
:T
DW 1
:L
F 1
DB 202
KB 20
KB 100
Transfer contents of ACCU 1 to data
word DW1 (new data word address).
The constant number 100 is loaded
in ACCU 1 and the new data word
address is shifted to ACCU 2.
:+F
: & lt; =F
:JC = F 1
Compare the ACCUs for less than or
equal to: ACCU 2 ACCU 1.
Jump conditionally to label F1, if
ACCU 2 ACCU 1.
8-55
STEP 5 Operations
S5-100U
8.2.10 Jump Operations
Table 8.20 provides an overview of the jump operations. An example follows the table.
Table 8-20. Overview of Jump Operations
Operation
Operand
Meaning
JU =
The unconditional jump is executed independently of conditions.
JC=
Jump conditionally
The conditional jump is executed if the RLO is “1”. If the RLO is
“0”, the statement is not executed and the RLO is set to “1”.
JZ =
Jump if the result is “zero”
The jump is executed only if CC 1 = 0 and CC 0 = 0
The RLO is not changed.
JN =
Jump if the result is “not zero”
The jump is executed only if CC 1 CC 0
JP =
Jump if the result is positive
The jump is executed only if CC 1 = 1 and CC 0 = 0
JM =
Jump if the result is negative
The jump is executed only if CC 1 = 0 and CC 0 = 1
JO =
Jump on overflow
The jump is executed if an overflow occurs. Otherwise the jump is
not executed. The RLO is not changed.
ID
Jump label (up
to 4 characters)
8-56
S5-100U
STEP 5 Operations
Processing Jump Operations
A symbolic jump destination (jump label) must always be entered next to a jump operation. This
jump label can have up to four characters. The first character must be a letter of the alphabet.
When programming, please be aware of the following items:
The absolute jump displacement cannot exceed +127 or - 128 words in the program memory.
Some statements take up two words (e.g., “Load a constant”). For long jumps, insert an intermediate destination.
Jumps can be executed only within a block.
Jumping over segment boundaries (“BLD 255”) is not permitted.
Jump labels can be set only at the start of a series of scans for CPU 102.
Example
If no bit of input word IW1 is
set, program scanning jumps to
the label “AN 1”. If input word
IW1 and output word QW3 do
not agree, program processing
jumps back to the label “AN 0”.
Otherwise input word IW1 and
data word DW12 are compared.
If input word IW1 is greater than
or less than data word DW12,
program scanning jumps to the
“DEST” label.
STL
AN0
Explanation
:L
:L
:+F
IW 1
KH 0000
:JZ=
:A
AN 1
I 0.0
AN1
:L
:L
IW 1
QW 3
:XOW
:JN = AN 0
:L
:L
: & gt; & lt;
IW 1
DW12
F
:JC = DEST
DEST
1
Load input word IW1 into
ACCU 1. If the contents of
ACCU 1 equal zero1, jump to
the label “AN 1”. Otherwise
process the next statement
(I 0.0).
:A
Compare input word IW1 and
output word QW3. If they are
not equal, set individual bits in
ACCU 1.
If the contents of ACCU 1 are
not zero, jump to the label
“AN 0”. Otherwise process the
next statements.
data word DW12. If they are
not equal, set RLO to “1”.
If the RLO = “1”, jump to the
“DEST” label. If the RLO =
“0”, process the next
statement.
I 0.1
The “L...” statement does not affect the condition codes. An addition (+F) is executed with the constant
0000H so that the “JZ” operation can evaluate the contents of the accumulator.
8-57
STEP 5 Operations
S5-100U
8.2.11 Substitution Operations, for CPU 103 and Higher
If you plan to process a program with various operands and without a lot of changes, it is advisable
to assign parameters to individual operands (see section 7.3.4). If you have to change the operands, you only need to reassign the parameters in the function block call.
These parameters are processed in the program as “formal operands”.
Special operations are necessary for this processing. However, these special operations are no
different in their effect than operations without substitution. A brief description of these operations
and examples follows.
Table 8-21 provides an overview of binary logic operations.
Table 8-21. Overview of Binary Logic Operations
Operation
A
Operand
Meaning
AND operation
Scan a formal operand for “1”.
AN =
AND operation
Scan a formal operand for “0”.
O
OR operation
ON =
OR operation
Formal operand
Actual operands permitted
Inputs, outputs, and flags
addressed in binary form
Timers and counters
8-58
Parameter
type
Data
type
I, Q, F
BI
T, C
S5-100U
STEP 5 Operations
Table 8-22 provides an overview of the set/reset operations. An example follows the table.
Table 8-22. Overview of Set/Reset Operations
Operation
S
Operand
Meaning
Set a formal operand (binary).
RB =
Reset a formal operand (binary).
Assign
The RLO is assigned to a formal operand.
Formal operand
Parameter
type
Data
type
I, Q, F
BI
Example: FB30 is assigned parameters in OB1.
Call in OB1
Program in FB30
Executed Program
:JU FB 30
:A
=ON 1
:A
I
0.0
NAME
ON 1
ON 2
:COMBINE
I 0.0
I 0.1
:AN
:O
:S
=ON 2
=ON 3
=MOT 5
:AN
:O
:S
I
I
Q
0.1
0.2
1.2
ON 3
VAL1
OFF1
I 0.2
I 0.3
Q 1.0
:A
:A
=OFF 1
=VAL 1
=ON 2
:A
:A
Q
I
I
1.0
0.3
0.1
OFF2
MOT5
Q 1.1
Q 1.2
BE
:ON
:RB
=ON 3
=MOT 5
=OFF 2
:ON
:R
I
Q
Q
0.2
1.2
1.1
:BE
:BE
8-59
STEP 5 Operations
S5-100U
Table 8-23 lists the various load and transfer operations. An example follows the table.
Table 8-23. Overview of Load and Transfer Operations
Operation
Operand
Meaning
L
Load a formal operand.
LD
Load a formal operand in BCD code.
LW =
Load the bit pattern of a formal operand.
T
Transfer to a formal operand.
Formal operand
Parameter
type
Data
Timers and counters
For L
For LD
Timers and counters
For LW
Bit pattern
For T
Data
type
I, Q, F
PW*, PY*
DW, DR, DL
T, C
BY, W
T, C
D
I, Q
DW, DR, DL
F, PW*, PY*
Inputs, outputs, data (DW,
DR, DL) and flags
KF, KH, KM,
KY, KS, KT, KC
BY, W
* Not for integral function blocks
Example: FB34 is assigned parameters in PB1.
Call in PB1
Program in FB34
Executed Program
NAME
:A
:L
:S
=I 0
=L1
C
I0
I1
L1
I 0.0
I 0.1
FW 10
:A
:LW
:S
=I 1
=LW1
C
LW1 :
LC1
T1
KC 140
C 7
QW 4
:A
:CU
:CU
I
C
C
LW2 :
KC 160
:BE
:LD
:T
:A
:R
=LC1
=T1
I
C
:R
:LW
:LD
C
=LW2
=LC1
7
:!=F
:R
:BE
8-60
:JU FB 34
:LOAD/TRAN
6
:A
:L
:S
I
FW
C
0.0
10
6
7
:A
:L
:S
I
KC
C
0.1
140
7
0.2
6
7
:A
:CU
:CU
I
C
C
0.2
6
7
0.3
6
:LD
:T
:A
:R
C
QW
I
C
7
4
0.3
6
:R
:L
:LD
C
KC
C
7
160
7
C
7
:!=F
:R
:BE
C
7
S5-100U
STEP 5 Operations
Table 8-24 provides an overview of timer and counter operations. Examples follow the table.
Table 8-24. Overview of Timer and Counter Operations
Operation
FR
Operand
Meaning
Enable a formal operand for a cold restart. (For a description,
see “FT” or “FC”, according to the formal operand).
RD =
Reset a formal operand (digital).
SP
Start a pulse timer specified as a formal operand using the value
stored in the accumulator.
SD
Start an on-delay timer specified as a formal operand using the
value stored in the accumulator.
SEC =
Start an extended pulse timer specified as a formal operand
using the value stored in the accumulator or set a counter
specified as a formal operand using the count specified in the
accumulator.
SSU =
Start a stored on-delay timer specified as a formal operand using
the value stored in the accumulator or start the count up of a
counter specified as a formal operand.
SFD =
Start an off-delay timer specified as a formal operand using the
value stored in the accumulator or start the count down of a
1
Parameter
type
Timers and counters1
Formal operand
Data
type
T, C1
“SP” and “SD” do not apply to counters.
Specifying Times and Counts
As with the basic operations, you can specify a time or count as a formal operand. In this case, you
must distinguish as follows whether the value is located in an operand word or is specified as a
constant.
Operand words can be of parameter type “I” or “Q” and of data type “W”. Use the
“L=” operation to load them into the accumulator.
Constants can be of parameter type “D” and of data type “KT” or “KC”. Use “LW=” to load
these formal operands into the accumulator.
8-61
STEP 5 Operations
S5-100U
The following examples show how to work with timer and counter operations:
Example 1:
Function Block Call
:JU
FB 32
Program in Function Block (FB32)
:AN
:A
=I 5
=I 6
NAME
I 5
I 6
:TIME
I 0.0
I 0.1
:L
:SFD
:A
KT
=TIM5
=I 5
TIM5
TIM6
OFF6
:AN
:L
:SSU
=I 6
KT
=TIM6
:A
:O
:A
=TIM5
=TIM6
=OFF6
I
:RD
:RD
:BE
:AN
:A
:BE
005.2
005.2
0.2
I
I
0.0
0.1
:L
:SF
:A
KT
T
I
5.2
5
0.0
:AN
:L
:SS
I
KT
T
0.1
5.2
6
:A
:O
:A
T
T
Q
I
5
6
1.0
0.2
:R
:R
:BE
=TIM5
=TIM6
T 5
T 6
Q 1.0
Executed Program
T
T
5
6
Example 2:
Function Block Call
Program in Function Block (FB33)
:A
=I 2
NAME
I2
:JU
FB 33
:COUNT
I 0.0
:L
:SEC
:A
KC
=CNT5
=I 3
I3
I4
CNT5
I 0.1
I 0.2
C 5
:SSU
:A
:SFD
OFF3
:BE
Q 1.0
Executed Program
I
0.0
:L
:S
:A
KC
C
I
017
5
0.1
=CNT5
=I 4
=CNT5
:CU
:A
:CD
C
I
C
5
0.2
5
:A
:A
=CNT5
=OFF3
I
:A
:A
C
Q
I
5
1.0
0.3
:RD
:BE
8-62
:A
=CNT5
:R
:BE
C
5
017
0.3
S5-100U
STEP 5 Operations
“DO” Operation
Table 8-25 and the example that follows explain the processing operation.
Table 8-25. “DO” Operation
Operation
Operand
DO =
Meaning
Process formal operand
The substituted blocks are called unconditionally.
Formal operands
Parameter
type
DB, PB, SB, FB1
1
Data
type
B
As actual operands, function blocks cannot have block parameters.
Example:
Function Block Call
Program in Function Block FB35
Executed Program
STL
:JU
D5
DW2
D6
DW1
Q4
MOT5
:BE
FB 35
DB 5
:DO
:L
:DO
=D5
=DW2
=D6
:C
:L
:C
DB
DW
DB
5
2
6
DW 2
DB 6
DW 1
:T
:T
:DO
=DW1
=Q4
=MOT5
:T
:T
:JU
DW
QW
FB
1
4
36
QW 4
FB 36
:BE
:BE
8-63
STEP 5 Operations
8.3
S5-100U
System Operations, for CPU 103 and Higher
System operations and supplementary operations have the following limitations:
You can program them only in function blocks.
You can program them only in the STL method of representation.
Since system operations access system data, only users with system knowledge should use them.
If you want to program system operations, you must select “SYS: OPS. Y” in the programmer
presets menu.
8.3.1
Set Operations
Like the supplementary bit operations, these set operations can change individual bits. Table 8-26
provides an overview of the set operations.
Table 8-26. Overview of Set Operations
Operation
Operand
Meaning
SU
Set bit unconditionally
A specific bit is set to “1” in the system data area.
RU
Reset bit unconditionally
A specific bit is set to “0” in the system data area.
ID
RS
Parameter
0.0 to 255.15
Processing Set Operations
Execution of set operations does not depend on the RLO.
8.3.2
Use these load and transfer operations to address the entire program memory of the programmable
controller. They are used mainly for data exchange between the accumulator and memory locations
that cannot be addressed by operands. Table 8-27 provides an overview of the load and transfer
operations.
8-64
S5-100U
STEP 5 Operations
Table 8-27. Overview of Load and Transfer Operations
Operation
Operand
Meaning
LIR
Load the register indirectly
The contents of a memory word are loaded into the specified
register (ACCU 1, 2). The address is in ACCU 1.
TIR
Transfer the register indirectly
The contents of the indicated register are transferred to a memory
location. The address is in ACCU 1.
Parameter
0 (for ACCU 1), 2 (for ACCU 2)
TNB
Transfer a data field (byte-by-byte)
A memory area is transferred in the program memory as a field.
End address destination area:
ACCU 1
End address source area:
ACCU 2
T
Transfer
A word is transferred to the system data area.
ID
Parameter
RS
0 to 255
Loading and Transferring Register Contents
Both accumulators can be addressed as registers. Each register is 16 bits wide. Since the “LIR”
and “TIR” operations transmit data by words, the registers are addressed in pairs.
Loading and transferring register contents are independent of the RLO. The processor goes to
ACCU 1 to get the address of the memory location referenced during data exchange. Consequently, make sure that the desired address is stored in ACCU 1 before this system operation is
processed.
STL
Explanation
L
KH
LIR
6100
0
Load the address 6100H into ACCU 1.
Load the information from the memory location with the address 6100H into
ACCU 1.
8-65
STEP 5 Operations
S5-100U
Processing a Field Transfer
A field transfer is processed independently of the RLO. The parameter indicates the length of the
data field (in bytes) that is to be transferred. The field can be up to 255 bytes long.
The address of the source field is in ACCU 2. The address of the destination field is in ACCU 1.
The higher address of each field must be specified because a field transfer takes place by
decrementing. The bytes in the destination field are overwritten during the transfer.
Example
Transfer a 12-byte
data field from
address F0A2H to
address EE90H.
Representation
EE85
Destination
EE90
TNB
F097
Source
F0A2
STL
Explanation
:L
KH
F0A2
Load the end address of the source field into ACCU 1.
:L
KH
EE90
Load the end adress of the destination field into ACCU 1. The
source address is shifted to ACCU 2.
:TNB
12
8-66
Transfer the data field to the destination field.
S5-100U
STEP 5 Operations
Transferring to the System Data Area
Example: Set the scan monitoring time to 100 ms after each mode change from “STOP” to
“RUN”. You can program this time in multiples of 10 ms in system data word 96. The
following function block can be called from OB21, for example.
STL
Explanation
Block number and type
FB 11
L
KF
+10
T
RS
96
Load ACCU 1 with the factor 10.
Transfer this value to system data word 96.
BE
Caution
The TIR, TRS and TNB operations are memory-changing operations with which you can
access the user memory and the system data area. These accesses are not monitored
by the operating system. Improper use of the operations can lead to changes in the
program and to a programmable controller crash.
8.3.3
An arithmetic operation changes the contents of ACCU 1 by a specified value. The parameter represents this value as a positive or negative decimal number. Table 8-28 shows the essential
features of the “ADD” operation. An example follows the table.
Table 8-28. Overview of the “ADD” Operation
Operation
Operand
ADD
Meaning
Add a constant
Add byte or word constants.
ID
Parameter
BF
KF
-128
to
-32768 to
+127
+32767
Processing
An arithmetic operation is executed independently of the RLO. It does not affect the RLO or the
condition codes.
You can subtract by entering a negative parameter.
Even if the result cannot be represented by 16 bits, no carry is made to ACCU 2, i.e., the contents
8-67
STEP 5 Operations
S5-100U
Example
STL
Decrement the constant 1020H by 33
and store the result in flag word
FW28. Afterwards add the constant
256 to the result and store the sum in
flag word FW30.
Explanation
KH
1020
ADD
BF
-33
T
FW
28
ADD
KF
256
T
8.3.4
L
FW
30
The constant 1020H is loaded into
ACCU 1.
The constant -330D is added to
the ACCU contents.
The new ACCU contents (0FFFH)
are stored in flag word FW28.
The constant 2560D is added to
the last result.
The new ACCU contents (10FFH)
are stored in flag word FW30.
Other Operations
Table 8-29 provides an overview of the remaining system operations.
Table 8-29. The “TAK” and “STS” Operations
Operation
Operand
Meaning
TAK
Swap accumulator contents
Swap the contents of ACCU 1 and ACCU 2 regardless of the
RLO. The RLO and the condition codes are not affected.
STS
Stop immediately
The PLC goes into the STOP mode regardless of the RLO.
Processing the “STS” Operation
When the “STS” operation is executed, the programmable controller goes into the STOP mode
immediately. Program processing is terminated at this point. The STOP state can only be cancelled
manually (with the mode selector) or with the programmer function “PC START”.
8-68
EWA 4NEB 812 6120-02b
S5-100U
8.4
STEP 5 Operations
Condition Code Generation
The processor of the programmable controller has the following three condition codes:
• CC 0
• CC 1
• OV (overflow)
The following operations affect the condition codes.
• Comparison operations
• Arithmetic operations
• Shift operations
• Some conversion operations
The state of the condition codes represents a condition for the various jump operations.
Condition Code Generation for Comparison Operations
Execution of comparison operations sets condition codes CC 0 and CC 1 (see Table 8-30). The
overflow condition code is not affected. Comparison operations do affect the RLO. When a
comparison is satisfied, the RLO is 1. This allows you to use the “JC” conditional jump operation
after a comparison operation.
Table 8-30. Condition Code Settings for Comparison Operations
Contents of ACCU 2 as
Compared to Contents
of ACCU 1
Possible
Jump Operations
Condition Codes
CC 1
CC 0
OV
Equal to
0
0
JZ
Less than
0
1
JN, JM
Greater than
1
0
JN, JP
Condition Code Generation for Arithmetic Operations
Execution of arithmetic operations sets all condition codes according to the result of the arithmetic
operation (see Table 8-31).
Table 8-31. Condition Code Settings for Fixed-Point Arithmetic Operations
Result after
is Executed
Possible
Jump Operations
Condition Codes
CC 1
CC 0
OV
& lt; - 32768
1
0
1
JN, JP, JO
- 32768 to - 1
0
1
0
JN, JM
0
0
0
0
JZ
+1 to +32767
1
0
0
JN, JP
& gt; +32767
0
1
1
JN, JM, JO
(-) 65536*
0
0
1
JZ, JO
* This number is the result of the calculation -32768 - 32768
8-69
STEP 5 Operations
S5-100U
Condition Code Generation for Digital Logic Operations
Digital logic operations set CC 0 and CC 1. They do not affect the overflow condition code (see
Table 8-32). The setting depends on the contents of the ACCU after the operation has been processed.
Table 8-32. Condition Code Settings for Digital Logic Operations
Contents
of the
ACCU
Condition Codes
Possible
OV
Jump Operations
CC 1
CC 0
Zero (KH = 0000)
0
0
JZ
Not zero
1
0
JN, JP
Condition Code Generation for Shift Operations
Execution of shift operations sets CC 0 and CC 1. It does not affect the overflow condition code
(see Table 8-33). Code setting depends on the state of the last bit shifted out.
Table 8-33. Condition Code Settings for Shift Operations
Value of
the Last Bit
Shifted Out
Possible
Jump Operations
CC 1
CC 0
“0”
0
0
JZ
“1”
1
0
JN, JP
Condition Codes
OV
Condition Code Generation for Conversion Operations
The formation of the two's complement (CSW) sets all condition codes (see Table 8-34). The state
of the condition codes is based on the result of the conversion function.
Table 8-34. Condition Code Settings for Conversion Operations
Result after
is Executed
Condition Codes
Possible
Jump Operations
CC 1
CC 0
OV
- 32768 *
0
1
1
JN, JM, JO
- 32767 to - 1
0
1
0
JN, JM
0
0
0
0
JZ
+1 to +32767
1
0
0
JN, JP
* This number is the result of the conversion of KH = 8000.
8-70
S5-100U
8.5
STEP 5 Operations
Sample Programs
Sections 8.5.1 through 8.5.3 provide a few sample programs that you can enter and test in all three
methods of representation on a programmer.
8.5.1
Momentary-Contact Relay/Edge Evaluation
Example
Circuit Diagram
On each leading edge of the signal at input I 0.0, the AND
condition “A I 0.0 and AN F 64.0” is satisfied; the RLO is “1”.
This sets flags F 64.0 and F 2.0 (“edge flags”).
In the next processing cycle, the AND condition “A I 0.0 and
AN F 64.0” is not satisfied since flag F 64.0 has already been
set.
Flag 2.0 is reset.
Therefore, flag F 2.0 is “1” for only one program run.
When input I 0.0 is switched off, flag F 64.0 is reset.
This resetting prepares the way for evaluation of the next
leading edge of the signal at input I 0.0.
STL
I 0.0
F 2.0
CSF
A
I
F
F
F
64.0
2.0
64.0
AN
R
NOP
I
F
0
0.0
64.0
F 2.0
LAD
0.0
AN
S
I 0.0
F 64.0
8.5.2
I 0.0
I 0.0
F 2.0
F 64.0
S
I 0.0
R
F 2.0
F 64.0
F 64.0
F 64.0
S
I 0.0
R
Q
Q
Binary Scaler/Binary Divider
This section describes how to program a binary scaler.
Example: The binary scaler (output Q 1.0) changes its state each time I 0.0 changes its signal
state from “0” to “1” (leading edge). Therefore, half the input frequency appears at the
output of the flip-flop.
8-71
STEP 5 Operations
S5-100U
Timing Diagram
Circuit Diagram
Signal states
I 0.0
1
I 0.0
0
Q 1.0
1
Q 1.0
0
Time
STL
CSF
A
AN
I
F
0.0
1.0
A
S
F
1.1
F
F
1.1
1.0
AN
I
R
F
NOP 0
I 0.0
0.0
1.0
A
A
1.1
1.0
A
F
F 1.0
Q
F
Q
1.0
2.0
1.0
A
F
R
Q
NOP 0
2.0
1.0
F 1.1
F 1.0
F 1.1
F 1.1
F 1.0
S
S
R
Q
I 0.0
R Q
1.1
AN
AN
S
F 1.0
F 1.1
2.0
F
I 0.0
I 0.0
F
Q
LAD
F 1.1
F 1.1
Q 1.0
F 1.1
Q 1.0
F 2.0
F 2.0
F 1.1
Q 1.0
F 2.0
Q 1.0
S
Q 1.0
F 2.0
Q 1.0
F 2.0
S
R Q
F 2.0
R
Q
Note
Output in CSF or LAD is possible only if you enter the segment boundaries “***” when
programming in STL.
8-72
S5-100U
8.5.3
STEP 5 Operations
Clock/Clock-Pulse Generator
This subsection describes how to program a clock-pulse generator.
Example: A clock-pulse generator can be implemented using a self-clocking timer that is followed
in the circuit by a binary scaler. Flag F 2.0 restarts timer T 7 each time it runs down,
i.e., flag F 2.0 is “1” for one cycle each time the timer runs down. The pulses of flag
F 2.0 applied to the binary scaler result in a pulse train with pulse duty factor 1:1 at
output Q 1.0. The period of this pulse train is twice as long as the time value of the
self-clocking timer.
Timing Diagram
Circuit Diagram
Signal states
1
G
F 2.0
0
F 2.0
F 3.0
1
Q 1.0
0
Q 1.0
Time
T
T
STL
CSF
AN
F
L
SD
NOP
KT
T
0
NOP
NOP
A
0
0
T
7
A
F
2.0
F
2.0
AN
S
A
F
Q
F
3.0
1.0
2.0
A
R
NOP
F
Q
0
3.0
1.0
LAD
2.0
010.1
7
F 2.0
T 7
F 2.0
T
KT 10.1
TV
T 7
0
T
R
Q
BI
DE
R
KT 10.1
BI
DE
0
TV
Q
F 2.0
F 2.0
Q 1.0
F 2.0
S
F 2.0
F 3.0
R Q
F 2.0
F 2.0
Q 1.0
S
F 3.0
F 3.0
F 3.0
R Q
F 3.0
F 2.0
AN
A
F
Q
2.0
1.0
Q 1.0
S
AN
AN
F
F
Q
3.0
2.0
1.0
F 2.0
R
NOP
F
0
3.0
S
F 2.0
Q 1.0
F 3.0
S
Q 1.0
R Q
F 2.0
Q 1.0
R Q
8-73
9
Integrated Blocks and Their Functions
9.1
9.1.1
9.1.2
9.1.3
9.1.4
9.1.5
9.1.6
9.1.7
9.1.8
9.2
9.2.1
9.2.2
9.2.3
9.2.4
9.2.5
9.3
9.3.1
9.3.2
9.3.3
Assigning Internal Functions to DB1,
for CPU 103 Version 8MA03 and Higher . . . . . . . . . . . . . . . . . . . .
Configuration and Default Settings for DB1 . . . . . . . . . . . . . . . . . .
Setting the Address for the Parameter Error Code in DB1 . . . . . . . .
Assigning Parameters in DB1 . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Rules for Setting Parameters in DB1 . . . . . . . . . . . . . . . . . . . . . . .
How to Recognize and Correct Parameter Errors . . . . . . . . . . . . . .
Transferring DB1 Parameters to the Programmable Controller . . . . .
Reference Guide for Setting Parameters in DB1 . . . . . . . . . . . . . . .
Defining System Characteristics in DB1
9
9
9
9
9
9
9
9
9
- 1
- 1
- 2
- 4
- 4
- 6
- 9
- 10
- 11
Integrated Function Blocks,
for CPU 102 Version 8MA02 and Higher . . . . . . . . . . . . . . . . . . . .
Code Converter : B4 - FB240 ..........................
Code Converter : 16 - FB241 ..........................
Multiplier : 16 - FB242 ...............................
Divider : 16 - FB243 - . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Analog Value Conditioning Modules FB250 and FB251 . . . . . . . . . .
9
9
9
9
9
9
9
9
9
- 14
- 14
- 14
9
- 15
Integrated Organization Blocks . . . . . . . . . . . . . . . . . . . . . . . . . . .
Scan Time Triggering OB31, for CPU 103 and Higher . . . . . . . . . . .
Battery Failure OB34 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
OB251 PID Algorithm,
for CPU 103 Version 8MA02 and Higher . . . . . . . . . . . . . . . . . . . .
11
12
12
13
13
14
Figures
9-1
9-2
9-3
9-4
9-5
9-6
9-7
9-8
9-9
DB1 with Default Parameters . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Inputting the Address for the Parameter Error Code . . . . . . . . . . . . . . . . . .
Parameter Error Codes and Their Meaning . . . . . . . . . . . . . . . . . . . . . . . .
Erroneous Parameter Assignment in DB1 . . . . . . . . . . . . . . . . . . . . . . . . .
Inputting the System Data Parameter . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Calling Up the OB251 PID Algorithm . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Block Diagram of the PID Controller . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Principle of Interval Sampling . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Process Schematic . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
9
9
9
9
9
9
9
9
9
1
3
7
8
11
15
16
21
22
9
9
9
9
9
9
9
9
2
12
12
13
13
16
17
19
Tables
9-1
9-2
9-3
9-4
9-5
9-6
9-7
9-8
Parameter Blocks and Their IDs
Call and Parameter Assignments of FB240 . . . . . . . . . . . . . . . . . . . . . . . .
Call and Parameter Assignments of FB241 . . . . . . . . . . . . . . . . . . . . . . . .
Call and Parameter Assignments of FB242 . . . . . . . . . . . . . . . . . . . . . . . .
Call and Parameter Assignments of FB243 . . . . . . . . . . . . . . . . . . . . . . . .
Legend for the Block Diagram of the PID Controller . . . . . . . . . . . . . . . . . .
Description of the Control Bits in Control Word ”STEU”
Structure of the Controller DB . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
S5-100U
9
9.1
Assigning Internal Functions to DB1, for CPU 103 Version 8MA03 and
Higher
You can program the following CPU functions:
Using the integral real-time clock (see chapter 12)
Exchanging data via SINEC L1 (see chapter 13)
Changing polling interval for time-controlled program processing (OB 13) (see chapter 7)
Assigning system parameters (see chapter 9)
Setting the address for the parameter error code (see chapter 9)
To assign parameters to these functions, you must configure data block 1 (DB1).
9.1.1
To make it easier for you to assign parameters, data block 1 is already integrated in the CPU with
default parameters. After performing an overall reset, you can load the default DB1 from the
programmable controller into your programmer and display it on the screen (see Figure 9-1). The
character string “DB1” must remain before the parameter blocks and be followed by at least one
filler (such as a blank space or a comma).
0:
12:
24:
KS
KS
KS
= 'DB1 SL1: SLN 1
SF ';
= 'DB2 DW0
EF DB3 DW0 ';
= ' KBE MB100 KBS MB101
36:
48:
60:
KS
KS
KS
= 'PGN 1 ; #CLP: CF 0
= 'CLK DB5 DW0
STW
= 'MW102
STP Y SAV Y ';
72:
84:
96:
KS
KS
KS
= 'OHE N
SET 4 01.04.92 ';
= '12:10:00
TIS 4
= '01.04. 13:00:00
OHS ';
108:
120:
132:
KS
KS
KS
= '000000:00:00 # ; SDP: WD';
= ' 500 ; TFB: OB13 100 ';
= ' ; END
Figure 9-1. DB1 with Default Parameters
This preset DB1 has one parameter block for each function. Each parameter block begins with a
block ID (shown in Figure 9-1 in the shaded background). The block ID is followed by a colon. The
individual parameters for each function are contained in these parameter blocks.
Each parameter block begins with a block ID followed by a colon. This colon must be followed by
at least one filler (such as a blank space or a comma). A semicolon must be at the end of each
parameter block with at least one filler between the semicolon and the next block ID.
9-1
S5-100U
The parameter blocks listed in Table 9-1 are used for the S5-100U.
Table 9-1. Parameter Blocks and Their IDs
Block ID
Explanation/Default Setting
'DB1 ';
Start ID
'SL1:
SINEC L1: Parameter block for SINEC L1 configuration /
(see chapter 13)
’CLP: ’:
Clock-Parameters: Parameter block for integral time clock/
clock function not activated (see chapter 12)
'SDP: ';
System-Dependent Parameter: Parameter block for system specifications /
default setting for cycle time monitoring is 500 ms (see section 9.1.8)
'TFB: ';
Timer Function Blocks: Parameter block for time-controlled program
processing: OB13 is called up every 100 ms. (see chapter 7)
'ERT: ';
Error ReTurn: Address for parameter error code / no default setting (see
section 9.1.2)
'END ';
END block ID for DB1
The sequence of the parameters in DB1 is not fixed. A semicolon must be at the end of each
The structure of the following parameter blocks is described here in detail.
ERT:
(Error code position)
SDP:
(System specifications)
The parameter blocks that are not discussed here are explained in the chapters that describe their
functions.
9.1.2
For the following reasons, we recommend that you use this example when you start setting your
parameters:
Parameter block “ERT:” is the only block with no default parameters in DB1. You must therefore enter all the parameters. We will explain the rules for assigning parameters step by step,
so that you can learn the rules quickly.
The correctly input “ERT:” parameter block makes it easy for you to correct parameter setting
errors; therefore, you should complete this block in DB1 before you change or add other
parameters.
The error parameter block is only important during the start-up phase. You should erase it
during “normal” operation because it takes up a lot of memory space.
9-2
S5-100U
To help find parameter errors more easily and to help correct them, you can ask the programmable
controller to output error messages in a coded form. All you have to do is to tell the programmable
controller where it should store the error code. Make this input in parameter block “ERT:” of DB1.
The error code can be stored in either of the following locations:
In flagwords
In data words in a data block
How to Proceed:
1. Perform an overall reset on the programmable controller.
2. Display DB1 on the programmer.
3. Position the cursor on the E of the “END” ID at the end of the default DB1.
4. Enter the characters that are highlighted in Figure 9-2.
DB1
Explanation
0:
12:
KS
KS
= 'DB1 SL1: SLN 1
= 'DB2 DW0
EF DB3
SF ';
DW0 ';
24:
36:
48:
60:
KS
KS
KS
KS
72:
84:
96:
KS
KS
KS
= 'OHE N
SET 4 01.04.92 ';
= '12:10:00
TIS 4
= '01.04. 13:00:00
OHS ';
108:
120:
132:
KS
KS
KS
= ' ; ERT: ERR MW1 ; END
'PGN 1 ; #CLP: CF 0
'CLK DB5 DW0
STW
'MW102
STP Y SAV Y
The parameter error code is stored in flag
word MW1 after start-up.
Figure 9-2. Inputting the Address for the Parameter Error Code
5. Use the following check list to make sure your entries are correct.
- Is the block ID “ERT:” terminated by a colon?
- Is at least 1 filler (a blank space in Figure 9-2) added after the colon? . . . . . . . . . . . .
- Is the parameter name (ERR) entered correctly? . . . . . . . . . . . . . . . . . . . . . . . . . . .
- Does at least 1 filler (a blank space) follow the parameter name? . . . . . . . . . . . . . . .
- Is the argument (MW1) entered correctly? . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
- Does at least 1 filler (a blank space) follow the argument? . . . . . . . . . . . . . . . . . . . .
- Does a semicolon (;) indicate the block end? . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
- Does DB1 end with the end ID “END” followed by a space?
6. Transfer the changed DB1 to the programmable controller.
7. Switch the programmable controller from STOP to RUN.
- The programmable controller accepts the changed DB1.
If you did not store the parameter block “ERT:” in DB1, you can localize the error in the ISTACK if
there was an incorrect parameter setting. However, you will not know what type of error is present.
The same applies if you made an error when you input the parameter block “ERT:”
9-3
S5-100U
9.1.3 Assigning Parameters in DB1
As discussed in section 9.1.2, you use the following steps to change or expand the preset values of
DB1:
1. Display the default DB1, with its parameter block “ERT:” on the programmer.
2. Position the cursor on the desired parameter block.
3. Change or expand the parameters.
(for an explanation and possible parameter values see section 9.1.7)
4. Transfer the changed DB1 to the programmable controller.
5. Switch the programmable controller from STOP to RUN.
Changed DB1 parameters are accepted.
Note
If the CPU recognizes an error in DB1, then it remains in the STOP mode (red LED
lights up) even after a switch from STOP to RUN.
9.1.4
DB1 consists of the following:
A start ID . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
DB1
One or more parameter blocks . . . . . . . . . . . . . . . . . . . .
e.g.:
CLP:STW FW102
A block ID . . . . . . . . . . . . . . . . . . . . . . . . .
e.g.:
CLP:
One or more parameters
e.g.:
STW FW 102
A parameter name . . . . . . . . . . .
e.g.:
STW
One or more arguments . . . . . . .
e.g.:
FW 102
A parameter block consists of:
A parameter consists of:
A block end ID . . . . . . . . . . . . . . . . . . . . . . . . .
A block end symbol
9-4
: ; (Semicolon)
: END
S5-100U
In the following section are the rules for changing or expanding entire parameter blocks. Follow
these steps or the CPU will not understand what you have entered.
1. Enter the start ID “DB1”, followed by a filler.
- DB1 must begin with the start ID “DB1”. Do not separate the three characters from each
other. After the start ID, there must be at least one filler. Use a blank space or a comma
as a filler.
2. Enter the block ID for the parameter block, followed by a filler.
- The start ID and filler are followed by the block ID for the parameter block. The sequence
of the parameter blocks in DB1 is random. The block ID identifies a block and its
corresponding parameter. The block ID “SL1”, for example, stands for the SINEC-L1
parameter. You must enter a colon immediately after the block ID. If the colon is missing,
then the CPU skips this block and displays an error message. You must add at least one
filler after the colon of a block ID.
3. Enter the parameter name, followed by a filler.
- The parameter name comes next. Parameter names are names for single parameters within
a parameter block. Within a block, the first four characters of a parameter name must be
different from each other. After the parameter name, you must add at least one filler.
4. Enter the argument that is attached to the parameter name, followed by a filler.
- At least one argument is attached to each parameter name. An argument is either a
number or a STEP 5 operand that you must enter. If several arguments belong to a
parameter name, then every argument must be followed by at least one filler (even the last
one).
5. Enter a semicolon (; ) to identify the block end, followed by a filler.
- After the semicolon, you must enter at least one filler. Leaving out the semicolon leads to
misinterpretation in the CPU.
6. Enter additional parameter blocks after the semicolon.
- (Use steps 2 through 5 to create additional parameter blocks.)
7. Enter the end ID “END”.
- This identifies the end of DB1. If you forget to enter an end ID, this leads to errors in the
CPU.
9-5
S5-100U
The preceding steps present the minimal requirements for setting the parameters. Beyond that,
there are additional rules that make it easier for you to assign parameters.
For example:
You have the ability to add comments.
You can expand the German mnemonics used as parameter names by using plain English text.
Comments can be added anywhere a filler is allowed. The comment symbol is the pound (#) sign.
The comment symbol must be placed at the beginning and at the end of your comment. The text
between two comment symbols may not contain an additional #.
Example: #Comment# .
At least one filler must follow the comment.
If you wish to change the default settings in parameter blocks SL1: or CLP:, you must first of all
overwrite the two comment characters (#) with blanks. If you fail to do this, the changes are
ignored.
If you wish to retain the default settings for one of the two parameter blocks, you must place it
between comment characters (overwrite blanks with “#”).
In order to make it easier to read parameter names, you can add as many characters as you wish if
you add an underscore (_) after the abbreviated parameter name.
Example: SF becomes SF_SENDMAILBOX.
At the end of the input, you must add at least one filler.
There is a rule of thumb that will help you check DB1. You should include at least one filler in the
following instances:
After the start ID
Before and after the block ID, parameter name, argument, and semicolon
9.1.5
If an error occurs while assigning parameters and the programmable controller does not go to the
“RUN” mode, you have two possibilities for recognizing errors:
By using a parameter error code
By using the analysis function “ISTACK”
Both possibilities are described below.
Scanning the Parameter Error Code
If you have entered a start address for the parameter error code in parameter block “ERT:” of DB1
(see section 9.1.2), then you can retrieve the cause of the error, and the error location information
at this address.
The entire error code occupies 10 data words or 20 flag bytes. In the following examples and
tables, we assume that the error code is stored in a data block starting with data word 0. The error
code occupies DW0 through DW9. In the “Flag” operand area, this corresponds to FW0 through
FW19.
9-6
S5-100U
Example:
You entered the start address DB3 DW0 in parameter block “ERT:”. The parameters
set in DB1 have already been transferred to the programmable controller. Then you
continue to set parameters in DB1. While attempting to transfer the changed DB1
parameters to the programmable controller, you find out that the programmable
controller remains in the STOP mode. You suspect that the reason for this is a
parameter error. To find the error, display DB3 on the programmer. The entire
contents of DB3 appear on the screen. DW0 through DW9 contain the code for the
parameter error. In the following figure, you see how your screen could look. Below
the screen display is a complete list of parameter error codes and their meanings.
0:
1:
2:
KH=
KH=
KH=
0 6 0 3
0 0 0 0
0 0 0 0
3:
4:
5:
KH=
KH=
KH=
0 0 0 0
0 0 0 0
0 0 0 0
6:
7:
8:
KH=
KH=
KH=
0 0 0 0
0 0 0 0
0 0 0 0
9:
10:
KH=
0 0 0 0
Screen display with
CO DE
Cause of the error
(which error occurred?)
DL
DR
No error
Start or end ID is missing
Comment not closed off correctly
Before END; semicolon missing in front of
END
Syntax error - block ID
Syntax error - parameter
00
01
02
00
01
02
Syntax error - argument
Range exceeded
in an argument
Parameter combination is not allowed
05
06
Not defined
Not defined
DB is not present
Not enough space in DB
Error inputting weekday
Error in the date
Error in inputting time
Irregular time format in
parameter blocks (24h/12h mode)
08
09
10
11
12
13
14
Location of error
(in which parameter block did the error
occur?)
Error cannot be assigned
to any block
03
SL1:
SINEC L1
06
CLP:
Clock parameter
09
TFB:
Timer function block
11
03
04
SDP:
System data parameter
99
F0
FF
ERT:
Error return
07
15
Error can not be assigned
to any block
Figure 9-3. Parameter Error Codes and Their Meaning
9-7
S5-100U
Locating Parameter Errors in “ISTACK”
If the CPU recognizes an error in DB1 in the initial start-up, then the CPU remains in the STOP
mode and stores a message in “ISTACK” describing where the error happened. The “ISTACK”
contains the absolute error address as well as the relative error address.
The STEP Address Counter (SAC) in the ISTACK points either to the address that contains the
incorrect input or in front of the address that contains the incorrect input. These are byte
addresses.
Example: Your inputs into DB1 are as follows. The position shaded contains an error.
0:
12:
KS
KS
= 'DB1 SL1: SLN 40
= 'DB2 DW0
EF DB3
SF
DW0
24:
36:
48:
KS
KS
KS
= 'CLK DB5 DW0
STW
60:
72:
84:
KS
KS
KS
= 'MW102
STP Y SAV Y ';
= 'OHE N
SET 4 01.04.92 ';
= '12:10:00
TIS 4
96:
108:
120:
KS
KS
KS
= '01.04. 13:00:00
OHS ';
132:
KS
= ' ; END
The decimal numbers in front of each input line
represent the word address for the first
character that can be entered for that
respective line. Each word consists of two
characters (2 bytes).
Figure 9-4. Erroneous Parameter Assignment in DB1
The error causes ISTACK to display the following addresses.
The absolute (error) address:
82F2H
(absolute SAC)
The relative (error) address:
000CH
(relative SAC)
So that you can locate the error in DB1 exactly, you must convert the relative byte address that is
displayed in hexadecimal format into a decimal word address. Decimal format is required because
the programmer displays a DB in words.
000CH
Hexadecimal
byte address
12D
Decimal
byte address
12D
2D =
6D
Decimal
word address
The information displayed in the chart above shows that the error occurred after address 0 and
before address 12. In Figure 9-4, argument 40 occupies address 6; the “40” is an incorrect entry.
The error is due to a range violation.
9-8
S5-100U
9.1.6
Unlike other data blocks, DB1 is processed only one time. This occurs when a cold restart is
performed on the programmable controller. This was done so that DB1 could handle certain special
functions.
One such special function is the assignment of parameters in the programmable controller with the
help of DB1. Setting parameters means that you enter parameters in DB1 for those internal
functions that your programmable controller should work with.
The programmable controller's operating system accepts these inputs into DB1 only when there is a
cold restart. You must perform a cold restart anytime you make changes to DB1. You can perform a
cold restart by switching from Power OFF to Power ON or from STOP to RUN.
The programmable controller accepts the parameters from DB1 and stores them in the system data
area.
Note
The CPU remains in the STOP mode if a parameter assignment error is found during
start-up. The red LED lights up on the operator panel and ISTACK displays a DB1
addressing error.
9-9
9.1.7
S5-100U
Parameter
Argument
Meaning
Block ID: SL1:
SINEC L1 (SL1)
p
DBx DWy
DBxDWy
MBy
MBy
p
SLN
SF
EF
KBE
KBS
PGN
p=1 to 3
x=2 to 255
Block ID:SDP:
y=0 to 255
System-Dependent-Parameter (SDP)
p
WD
Slave number
Location of Send Mailbox
Location of Receive Mailbox
Location of Coordination Byte “Receive”
Location of Coordination Byte “Send”
Programmer bus number
Number of timers being processed(Watch-Dog-Timer)
p=1 to 2550
Block ID: TFB:
Timer-Funktions-Baustein (TFB)
p
OB13
Intervals (ms) at which OB13 is called up and is
processed
p=0 to 655350 (State in 10-ms steps)
Block ID: CLP:
STP
SAV
p
DBxDWy,MWz,EWv
or AWv
DBxDWy,MWz,EWv
or AWv
J/Y/N
J/Y/N
OHE
J/Y/N
SET
wd dd.mm.jj
hh:mn:ss1 AM/PM2
wd dd.mm.
hh:mn:ss1 AM/PM2
hhhhhh:mn:ss1
CF
CLK
STW
TIS
OHS
wd
dd
mm
yy
hh
mn
ss
hhhhhh
1
2
=1 to 7 (weekday = Sun..Sat)
=01 to 31 (day)
=01 to 12 (month)
=0 to 99 (year)
=00 to 23 (hours)
=00 to 59 (minutes)
=00 to 59 (seconds)
=0 to 999999 (hours)
ClockParameters (CP)
Inputting the correction factor (Correction Factor)
Location of the clock data (CLocK Data)
Location of the status word (STatus Word)
Updating the clock during STOP (SToP)
Saving the clock time after the last change from RUN
to STOP or Power OFF (SAVe)
Enabling the operating hours counter
(Operation Hour counter Enable)
Setting the clock time and date
Setting the prompting time (TImer Set)
Setting the operating hours counter
(Operation Hour counter Set)
p=– 400 to 400
v=0 to 126
x=2 to 255
y=0 to 255
z=0 to 254
j/J=ja(yes)
y/Y=yes
n/N=no
If an argument such as seconds, for example, is not to be entered, input XX. The clock continues to run
with the updated data. The TIS parameter block does not acknowledge this argument..
If you input AM or PM after the clock time, the clock runs in the 12-hour mode. If you omit this
argument, the clock runs in the 24-hour mode. You must use the same time mode in the SET and TIS
parameter blocks.
9-10
S5-100U
9.1.8
Each cyclical program processing triggers the beginning of a monitoring period. If the cycle trigger
is not retriggered during the monitoring period, the programmable controller is forced into the STOP
mode and disables the output modules. The default for the monitoring time is set to 500 ms in
DB1. You can increase the cycle time monitoring in the parameter block SDP.
Example: You wish to increase the monitoring time to 700 ms since your user program is very
large.
How to Proceed:
1. Display DB1 on the programmer.
2. Change the parameter block “SDP” as shown in Figure 9.5.
Position the cursor on the arguments for the parameter
Overwrite the arguments
3. Transfer the changed DB1 to the programmable controller.
4. Switch the programmable controller from STOP to RUN. The programmable controller now
accepts the changed parameters.
0:
12:
KS
KS
= 'DB1 SL1: SLN 1
= 'DB2 DW0
EF DB3
SF ';
DW0 ';
24:
36:
48:
KS
KS
KS
= 'CLK DB5 DW0
STW
60:
72:
84:
KS
KS
KS
= 'MW102
STP Y SAV Y ';
= 'OHE N
SET 4 01.04.92 ';
= '12:10:00
TIS 4
96:
108:
120:
KS
KS
KS
= '01.04. 13:00:00
OHS ';
= ' 700 ; TFB: OB13 100 ';
132:
KS
= ' ; END
Figure 9.5. Inputting the System Data Parameter
You can also set the cycle monitoring time in OB31 (see section 9.3.1).
9.2
Integrated Function Blocks, for CPU 102 Version 8MA02 and Higher
Some standard function blocks are integrated in your S5-100U. You can call up these blocks in
your control program with the commands “JU FB” or “JC FB x”. The character “x” stands for the
block number.
Overview:
Block No.
Block name
Call length
(in words)
Processing time
(in ms)
FB240
FB241
COD:B4 COD:16
5
6
FB242
MUL:16
7
FB243
DIV:16
10
& lt; 0.6
& lt; 0.9
& lt; 2.1
& lt; 1.0
FB250
RLG:AI
10
2.4
FB251
RLG:AQ
9
4.8
9-11
S5-100U
9.2.1 Code Converter : B4 - FB240 Use function block FB240 to convert a number in BCD (4 tetrads) with sign to a fixed-point binary
number (16 bits).
You must change a two-tetrad number to a four-tetrad number before you convert it.
If a tetrad is not in the BCD defined range, then FB240 displays the value “0”. An error bit
message does not follow.
Table 9-2. Call and Parameter Assignments of FB240
Parameter
Meaning
Type
BCD
BCD number
IW
SBCD
Sign of the
BCD number
I BI
DUAL
Fixed-point
number (KF)
QW
9.2.2
Code Converter : 16
Assignment
0 to 9999
“1” for “-”
“0” for “+”
16 bits “0”
or “1”
STL
: JU FB240
NAME
BCD
SBCD
: COD:B4
DUAL
- FB241-
Use function block FB 241 to convert a fixed-point binary number (16 bits) to a number in BCD code
with additional consideration of the sign. An eight-bit binary number must be transferred to a 16-bit
word before conversion.
Table 9-3. Call and Parameter Assignments of FB241
Parameter
Meaning
DUAL
Binary number
SBCD
Sign of the BCD
number
I BI
BCD number 4th and
5th tetrads
Q BY
BCD number tetrads
0 to 3
QW
BCD2
BCD1
9-12
Type
Assignment
W
-32768 to+32767
I
“1” for “-”
“0” for “+”
STL
: JU FB241
: COD:16
DUAL
SBCD
BCD2
BCD1
2 tetrads
NAME
4 tetrads
S5-100U
9.2.3
Multiplier : 16 - FB242 -
Use function block FB 242 to multiply one fixed-point binary number (16 bits) by another. The product is represented by two fixed-point binary numbers (16 bits each). The result is also scanned for
zero. An eight-bit number must be transferred to a 16-bit word prior to multiplication.
Table 9-4. Call and Parameter Assignments of FB242
Parameter
Meaning
Z1
Multiplier
Z2
Multiplicand
Type
Assignment
I
W
-32768 to+32767
I
W
-32768 to+32767
: MUL:16
“0” : product is zero
Z1
Z2
Z3=0
Z32
Z31
Scan for zero
Q BI
Z32
Product high-word
QW
16 Bits
Z31
Product low-word
QW
16 Bits
Divider : 16
: JU FB242
NAME
Z3=0
9.2.4
STL
- FB243 -
Use function block FB 243 to divide one fixed-point binary number (16 bits) by another. The result
(quotient and remainder) is represented by two fixed-point binary numbers (16 bits each).
The divisor and the result are also scanned for zero. An eight-bit number must be transferred to a
16-bit word prior to division.
Table 9-5. Call and Parameter Assignments of FB243
Parameter
Explanation
Type
Assignment
Z1
Dividend
IW
-32768 to+32767
Z2
Divisor
IW
-32768 to+32767
OV
Overflow bit
“1” : overflow
Q BI
FEH
Q BI
“1” : division by zero
Z3=0
Scan for zero
Q BI
“0”: quotient is zero
Z4=0
Scan for zero
Q BI
“0”: remainder is zero
Z3
Quotient
QW
16 bits
Z4
Remainder
QW
STL
: JU FB243
NAME
: DIV:16
Z1
Z2
OV
FEH
Z3=0
Z4=0
Z3
Z4
16 bits
9-13
9.2.5
S5-100U
Function block FB250 reads in an analog value from an analog input module and outputs a value XA
in the scale range specified by the user.
Function block FB251 allows you to output analog values to analog output modules. Values from the
range between the “UGR” (lower limit) parameters and the “OGR” (upper limit) parameters are
converted to the nominal range of the selected module.
You will find more information on the following topics in section 11.6:
Calling up and setting parameters in FB250.
Calling up and setting parameters in FB251.
An example of analog value processing with FB250 and FB251.
9.3
9.3.1 Scan Time Triggering OB31, for CPU 103 and Higher
A scan time monitor monitors the program scan time. If program scanning takes longer than the
specified scan monitoring time, the CPU goes into the STOP mode. This can happen when one of
the following errors occurs:
The control program is too long.
The program enters a continuous loop.
You can retrigger the scan time monitor at any point in the control program by calling up OB31.
Calling up this block restarts the scan time monitor.
Call up OB31
Prerequisite: SYSTEM COMMANDS “YES” has been specified on the programmer.
JU OB31 can be programmed at any point in the control program.
Programming
One statement in OB31 is sufficient, e.g. “BE” to make the retriggering effective. Other
statements are also possible.
9.3.2 Battery Failure OB34
The CPU constantly checks the status of the battery in the power supply. If a battery fails (BAU),
OB34 is processed before every cycle until the battery is replaced. You can program the reaction of
the programmable controller to battery failure in OB34. If OB34 is not programmed, there is no
reaction.
9-14
S5-100U
9.3.3
OB251 PID Algorithm, for CPU 103 Version 8MA02 and Higher
A PID algorithm is integrated in the operating system of the S5-100U. OB251 helps you use this
algorithm to meet your needs.
Before calling up OB251, you must first open a data block called the controller DB. It contains the
controller parameters and other controller specific data. The PID algorithm must be called up periodically to generate the manipulated variable. The more closely the scan time is maintained, the
more accurately the controller fulfills its task. The control parameters specified in the controller DB
must be adapted to the scan time.
You should always call OB251 from the time OB (OB13). You can set time OBs at a call up interval
ranging between 10 ms and 655,350 ms. The PID algorithm requires no more than 1.7 ms to
process.
OB13
Time-Controlled
Processing
C
JU
BE
DB
OB
N
251
DBN
Controller
Data Block
OB251
PID Control
Algorithm
DW
DW
1
49
Figure 9-6. Calling Up the OB251 PID Algorithm
The continuous action controller is designed for controlled systems such as those present in
process engineering for controlling pressure, temperature, or flow rate.
The “R” variable sets the proportional element of the PID controller. If proportional action is
required, most controller designs use the value R = 1.
The individual Proportional action, Integral action, and Derivative action elements can be deactivated
via their parameters (R, TI, and TD) by presetting the pertinent data words to zero. This enables
you to implement all required controller structures without difficulty, e.g., PI, PD, or PID controllers.
You can forward the system deviation XW or, using the XZ input, any disturbance variable or the
inverted actual value X to the derivative action element. Specify a negative K value for a reverse
acting controller.
When the manipulated information (dY or Y) is at a limit, the integral action component is
automatically deactivated in order not to impair the dynamic response of the controller.
The switch settings in the block diagram are implemented by setting the respective bits in control
word “STEU”.
9-15
S5-100U
Z
0
1
BGOG
STEU
Bit 5
STEU
Bit 2
0
W
Zk-Zk-1
R
TI
XW
K
dY
0
1
0
OG
Y
Summing
unit
1
UG
1
Manual
function
STEU
Bit 1
STEU
Bit 0
YH, dYH
0
YA,
dYA
dY
TD
XZ
Limiter
STEU
Bit 3
1
0
STEU
Bit 4
BGUG
Figure 9-7. Block Diagram of the PID Controller
Table 9-6. Legend for the Block Diagram of the PID Controller
Designation
Explanation
K
Proportional coefficient:
R
R parameter (usually 1000)
TA
Scan time
TN
Integral-action time
TV
Derivative-action time
TI
Constant TI
TI=Scan time TA/Integral action time TN
TD
Constant TD
TD=Derivative action time TV/Scan time TA
W
Setpoint
STEU
Control word
YH, dYH
Output value:
Z
Disturbance variable
XW
System deviation
Actual value
XZ
Substitute value for system deviation
Y, dY
Manipulated variable, manipulated increments
BGOG
Upper limit of the manipulated variable
BGUG
Lower limit of the manipulated variable
YA, dYA
Output word :
9-16
K & gt; 0
K & lt; 0
YH
dYH
YA
dYA
direct acting
reverse acting
Control Word Bit 3=0
Control Word Bit 3=1
S5-100U
Table 9-7. Description of the Control Bits in Control Word “STEU”
Control
Bit
Name
Signal
State
0
AUTO
0
Manual mode
The following variables are updated in Manual mode:
1) XK, XWK-1 and PWK-1
2) XZK, XZK-1 and PZK-1, when STEU bit 1=1
3) ZK and ZK-1, when STEU bit 5=0
Variable dDK-1 is set to 0: The algorithm is not computed.
1
Automatic mode
0
XWk is forwarded to the derivative action element. The XZ input
is ignored. A variable other than XWk is forwarded to the derivative
action element .
1
XZ EIN
1
2
REG AUS
0
1
Description
Normal controller processing
When the controller is called up (OB251), all variables (DW18 to
DW 48 ) with the exception of K, R, TI, TD, BGOG, BGUG, YHk
and Wk are reset in the controller DB. The controller is
deactivated.
3
GESCHW
0
1
Positioning algorithm
Correction rate algorithm
4
HANDART
0
When GESCHW=0:
Following the transfer to Manual mode, the specified manipulated
variable value YA is adjusted exponentially to the manual value in
four sampling steps. Additional manual values are then forwarded
immediately to the controller output.
When GESCHW=1:
The manual values are forwarded immediately to the controller
output. The limiting values are in force in Manual mode.
1
When GESCHW=0:
The manipulated variable last output is retained.
When GESCHW=1:
Correction increment dYK is set to zero.
0
1
With feedforward control
No feedforward control
5
NO Z
6 and 7
These bits are not assigned.
8 to 15
The PID algorithm uses these bits as auxiliary flags.
The control program can be supplied with fixed values or parameters. Parameters are input via the
assigned data words. The controller is based on a PID algorithm. Its output signal can be either a
manipulated variable (positioning algorithm) or a manipulated variable modification (correction rate
algorithm).
9-17
S5-100U
Correction Rate Algorithm
The relevant correction increment dYk is computed at instant t= k
formula:
TA according to the following
Without feedforward control (D11.5=1); XW is forwarded to the differentiator (D11.1=0)
dYk = K[(XWk - XWk-1) R+TI • XWk+ (TD (XWk - 2XWk-1 + XWk-2) + dDk-1)]
= K (dPWkR + dIk + dDk)
With feedforward control (D11.5=0); XW is forwarded to the differentiator (D11.1=0)
dYk = K[(XWk - XWk-1) R+TI • XWk+ (TD (XWk - 2XWk-1 + XWk-2) + dDk-1)]+(Zk-Zk-1)
= K (dPWkR + dIk + dDk)+dZk
Without feedforward control (D11.5=1); XZ is forwarded to the differentiator (D11.1=1)
dYk = K[(XWk - XWk-1) R+TI • XWk+ (TD (XZk - 2XZk-1 + XZk-2) + dDk-1)]
With feedforward control (D11.5=0); XZ is forwarded to the differentiator (D11.1=1)
dYk = K[(XWk - XWk-1) R+TI • XWk+ (TD (XZk - 2XZk-1 + XZk-2) + dDk-1)]+(Zk-Zk-1)
P element
I element
D element
Z element
k:
kth element
When XWk is applied:
XWk
PWk
QWk
W k - Xk
XWk - XWk-1
PWk - PWk-1
XWk-2XWk-1+XWk-2
When XZ is applied:
PZk
QZk
XZk - XZk-1
PZk - PZk-1
XZk-2XZk-1+XZk-2
The result is:
dPWk
dIk
(XWk- XWk-1)R
TI•XWk
dDk
(TD•QWk+dDk-1) when XW is applied
(TD•QZk+dDk-1) when XZ is applied
Zk - Zk-1
dZk
Positioning Algorithm
The formula used to compute the correction rate algorithm is also used to compute the positioning
algorithm.
In contrast to the correction rate algorithm, however, the sum of all correction increments computed
(in DW 48), rather than the correction increment dYk is output at sampling instant tk.
9-18
S5-100U
At instant tk , manipulated variable Yk is computed as follows:
m=k
Y k=
dYm
m=0
Initializing the PID Algorithm
OB251's interface to its environment is the controller DB. All data needed to compute the next
manipulated variable value is stored in this DB. Each controller has its own controller data block.
The controller-specific data are initialized in a data block that must comprise at least 49 data words.
The CPU goes to STOP with a transfer error (TRAF) if no DB is open or if the DB is too short.
Caution
Make sure that the right controller DB is open before calling control algorithm OB251.
Table 9-8. Structure of the Controller DB
Data Word
Name
Comments
1
K
Proportional coefficient (-32 768 to + 32 767) for controllers
without a derivative-action element
Proportional coefficient (- 1500 to +1500) for controllers with a
derivative-action element*
K is greater than zero when the control is direct acting, and less
than zero when the control is reverse acting; the specified value is
multiplied by a factor of 0.001**.
3
R
R parameter (- 32 768 to + 32 767) for controllers without
aderivative-action element
R parameter (- 1500 to + 1500) for controllers with a derivativeaction element*
Normally 1 for controllers with P element; the specified value is
multiplied with a factor of 0.001**
5
TI
Constant TI (0 to 9999)
TI=
Sampling interval TA
The specified value is multiplied by a factor of 0.001
3
Constant TD (0 to 999)
TD=
Derivative-action time TV
9
STEU
Control word (bit pattern)
12
YH
14
BGOG
Upper limit value (- 2047 to +2047)
16
Setpoint (- 2047 to +2047)
11
W
BGUG
Lower limit value (- 2047 to +2047)
Value for Manual operation (- 2047 to +2047)
It is possible to have larger gains, if sudden incremental changes to the system deviation are small
enough. This is the reason you have to divide larger deviations into smaller ones such as adding
the setpoint via a ramp function.
The factor 0.001 is an approximate value. The exact value of the factor is 1/1024 or 0.000976.
9-19
S5-100U
Table 9-8. Structure of the Controller DB (continued)
Data
Word
Name
22
Actual value (- 2047 to +2047)
24
Z
Disturbance variable (- 2047 to +2047)
29
XZ
Derivative time (- 2047 to +2047)
48
YA
Output variable (- 2047 to +2047)
Comments
All parameters (with the exception of the control word STEU) must be specified as 16-bit fixed point
numbers.
Caution
The PID algorithm uses the data words that are not listed in Table 9-8 as auxiliary flags.
9-20
S5-100U
Initialization and Call Up of the PID Controller in a STEP 5 Program
Several different PID controllers can be implemented by calling up OB251 repeatedly. A data block
must be initialized prior to each OB251 call up. These DBs serve as data interface between the
controllers and the user.
Note
Important controller data are stored in the high-order byte of control word DW11 (DL11).
Therefore make sure that only T DR 11/SU D11.0 to D11.7 or RU D 11.0 to D11.7
operations are used to modify user-specific bits in the control word.
Selecting the Sampling Interval
In order to be able to use the known analog method of consideration for digital control loops, do not
select a sampling interval that is too large.
Experience has shown that a TA sampling interval of approximately 1/10 of the time constant
TRK, dom* produces a control result comparable to the equivalent analog result. Dominant system
time constant TRK, dom determines the step response of the closed control loop.
TA = 1/10 • TRK, dom
In order to ensure the constancy of the sampling interval, OB251 must always be called up in the
service routine for time interrupts (OB13).
x
t
TA
TRK,dom=
x
TRK,dom
w
w
xd
xd
Control variable
Time
Sampling interval
Dominant system
time constant of
the closed control
loop
Reference
variable / Setpoint
Control deviation
t
TA
Figure 9-8. Principle of Interval Sampling
* TRK, dom = dominant system time constant of the closed control loop
9-21
S5-100U
Example for the Use of the PID Controller Algorithm:
A PID controller is supposed to keep an annealing furnace at a constant temperature.
The temperature setpoint is entered via a potentiometer.
The setpoints and actual values are acquired using an analog input module and forwarded to the
controller. The computed manipulated variable is then output via an analog output module.
The controller mode is set in input byte 0 (see control word DW11 in the controller DB).
You must use the well-known controller design procedure to determine how to tune the controller
for each controlled system.
IB32
Control byte (DR11)
Channel0
Channel1
Setpoint
adjuster
W
Y
PID
control
algorithm
Manipulated
variable
Channel 0
S5-100U
OB251 with
controller DB
(call in OB13)
Analog input module
(e.g. 6ES5 460)
Analog output module
(e.g. 6ES5 470)
Controlled
system
Actual
value
Temperature sensor
Annealing furnace
Final control
element
Transducer
Fuel gas flow
Figure 9-9. Process Schematic
The analog signals of the setpoint and actual values are converted into corresponding digital values
in each sampling interval (set in OB13). OB251 uses these values to compute the new digital
manipulated variable, from which, in turn, the analog output module generates a corresponding
analog signal. This signal is then forwarded to the controlled system.
9-22
S5-100U
Calling the Controller in the Program:
OB 13
STL
Description
NAME
: JU FB 10
: CONTROLLER 1
PROCESS CONTROLLER
THE CONTROLLER'S SAMPLING INTERVAL
DEPENDS ON THE TIME BASE USED
TO CALL OB13 (SET IN DB1).
THE DECODING TIME OF THE ONBOARD
ANALOG INPUTS MUST BE TAKEN
INTO ACCOUNT WHEN SELECTING
THE SAMPLING INTERVAL.
: BE
9-23
FB10
NAME
STL
Description
:CONTROLLER 1
:C
DB
30
:L
:T
:T
SELECT CONTROLLER'S DB
READ CONTROLLER'S CONTROL BITS
PY
FY
DR
0
10
11
READ CONTROLLER'S
CONTROL BITS
AND STORE IN DR11
NOTE CAREFULLY:
DR11 CONTAINS IMPORTANT CONTROL
DATA FOR OB251
THE CONTROL BITS MUST
THEREFORE BE TRANSFERRED WITH
T DR11 TO PREVENT
CORRUPTING DL11
READ ACTUAL VALUE AND SETPOINT
:A
F
12.0
:R
: AN
:S
F
F
F
12.0
12.1
12.1
NAME
: JU
FB250
: RLG: AI
BG
KNKT
OGR
KF
KY
KF
+8
0,6
+2047
UGR
EINZ
XA
KF
F
DW
- 2047
12.0
22
FB
BU
9-24
S5-100U
F
F
12.2
12.3
FLAG 0 (FOR UNUSED FUNCTIONS
IN FB 250)
FLAG 1
READ ACTUAL VALUE
MODULE ADDRESS
CHANNEL NO. 0, FIXED-POINT BIPOLAR
UPPER LIMIT FOR ACTUAL VALUE
LOWER LIMIT FOR ACTUAL VALUE
NO SELECTIVE SAMPLING
STORE SCALED ACTUAL VAL. IN CONTR. DB
ERROR BIT
RANGE VIOLATION
S5-100U
FB10 (continued) STL
NAME
: JU
FB250
: RLG: AI
BG
KNKT
OGR
KF
KY
KF
+8
1,6
+2047
UGR
EINZ
XA
FB
KF
F
DW
F
- 2047
12.0
9
13.1
BU
:A
F
13.2
F
10.0
: JC
:L
:T
=WEIT
DW 22
DW 9
WEIT
JU OB251
Explanation
READ SETPOINT
MODULE ADDRESS
CHANNEL NO. 1, FIXED-POINT BIPOLAR
UPPER LIMIT FOR SETPOINT
LOWER LIMIT FOR SETPOINT
STORE SCALED SETPOINT IN CONTR. DB
ERROR BIT
RANGE VIOLATION
IN MANUAL MODE, THE SETPOINT IS
SET TO THE ACTUAL VALUE TO FORCE
THE CONTROLLER TO REACT
TO A SYSTEM DEVIATION, IF ANY,
WITH A P STEP
ON TRANSFER
TO AUTOMATIC
MODE
CALL CONTROLLER
OUTPUT MANIPULATED VALUE
NAME
XE
: JU FB251
: RLG:AQ
DW 48
BG
KNKT
OGR
KF
KY
KF
+8
0,1
+2047
UGR
FEH
BU
KF
F
F
- 2047
13.5
13.6
: BE
MODULE ADDRESS
CHANNEL 0, FIXED-POINT BIPOLAR
UPPER LIMIT FOR ACTUATING SIGNAL
LOWER LIMIT FOR ACTUATING SIGNAL
ERROR BIT WHEN LIMITING VAL. DEFINED
MANIPULATED VARIABLE Y TO ANALOG
OUTPUT
RANGE VIOLATION
9-25
DB 30
0:
1:
2:
3:
4:
5:
6:
7:
8:
9:
10:
11:
12:
13:
14:
15:
16:
17:
18:
19:
20:
21:
22:
23:
24:
25:
26:
27:
28:
29:
30:
31:
32:
33:
34:
35:
36:
37:
38:
39:
40:
41:
42:
43:
44:
45:
46:
47:
48:
49:
50:
9-26
STL
KH
KF
KH
KF
KH
KF
KH
KF
KH
KF
KH
KM
KF
KH
KF
KH
KF
KH
KH
KH
KH
KH
KF
KH
KF
KH
KH
KH
KH
KF
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KH
KF
KH
S5-100U
Explanation
0000;
+01000;
0000;
+01000;
0000;
+00010;
0000;
+00010;
0000;
+00000;
0000;
00000000 00100000;
+00500;
0000;
+02000;
0000;
-02000;
0000;
0000;
0000;
0000;
0000;
+00000;
0000;
+00000;
0000;
0000;
0000;
0000;
+00000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
0000;
+00000;
0000;
K PARAMETER (HERE=1), FACTOR 0.001
(VALUE RANGE: - 32768 TO 32767)
R PARAMETER (HERE=1), FACTOR 0.001
TI=TA/TN (HERE=0.01), FACTOR 0.001
(VALUE RANGE: 0 TO 9999)
TD=TV/TA (HERE=10), FACTOR 1
(VALUE RANGE: 0 TO 999)
SETPOINT W, FACTOR 1
(VALUE RANGE: - 2047 TO 2047)
CONTROL WORD
MANUAL VALUE YH, FACTOR 1
UPPER CONT. LIMIT BGOG, FACTOR 1
LOWER CONT. LIMIT BGUG, FACTOR 1
ACTUAL VALUE X, FACTOR 1
DISTURBANCE VARIABLE Z, FACTOR 1
FEEDFORWARD XZ FOR DIFF.,
FACTOR 1, (- 2047 TO 2047)
CONTROLLER OUTPUT Y, FACTOR 1
10
Interrupt Processing
10.1
10.2
Interrupt Processing with OB2, for CPU 103
Version 8MA02 and Higher . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Calculating Interrupt Reaction Times . . . . . . . . . . . . . . . . . . . . . . .
10 - 1
10 - 5
Figures
10-1
10-2
10-3
Possible Configuration of the Programmable Controller
with Bus Units Having Interrupt Capability . . . . . . . . . . . . . . . . . . . . . . . .
Program Interruptions by Process Interrupts . . . . . . . . . . . . . . . . . . . . . . .
Accessing the Process Image Tables from OB2
10 - 1
10 - 2
10 - 4
Additional Reaction Times
10 - 5
Tables
10-1
S5-100U
10
Interrupt Processing, for CPU 103 Version
8MA02 and Higher
Interrupt-driven program processing starts when a signal from the CPU causes the programmable
controller to interrupt cyclic or time-controlled program scanning in order to process a specific
program. Once this program has been scanned, the CPU returns to the point of interruption in the
cyclic or time-controlled program and resumes processing at that point.
Prerequisites for Interrupt-Driven Program Processing
Interrupt-driven program processing is possible only if the following conditions are met:
The bus unit with interrupt capability is directly adjacent to the CPU (slots 0 and 1).
Four-channel digital input modules or comparator modules must be mounted on the bus unit to
transfer process interrupts.
- You may plug other modules in, but these modules will have no interrupt handling capability.
The programmable controller is in the Power ON state and in the RUN operating mode.
Interrupt processing is not disabled by an IA operation in your program. See section 8.2.8.
OB2 has been programmed.
Slot
Interrupts are handled
only by this module
Figure 10-1.
10.1
1
2
3
4
DI
CPU
0
8
DI
4
DI
8
DI
Bus unit with interrupt capability (but
acts only like a “normal” bus unit)
Possible Configuration of the Programmable Controller with Bus Units
Interrupt Processing with OB2, for CPU 103 Version 8MA02 and
Higher
For interrupt-driven processing, OB2 must have been programmed. OB2 is called up by a process
interrupt and interrupts in turn the cyclic or time-controlled program scanning. Other blocks can be
called from OB2. After the interrupt-driven program has been processed, the CPU resumes cyclic
10-1
S5-100U
Triggering an Interrupt
Interrupts can only be triggered by four-channel digital input modules and comparator modules that
are plugged into slots 0 and 1 on a bus unit with interrupt capability.
Interrupts are triggered by a change in the signal state (0 1=positive edge; 1 0=negative edge)
at the respective interrupt input. Then the programmable controller automatically branches to OB2.
If you have not programmed OB2, either the cyclic or time-controlled program resumes immediately
after the interrupt.
The cyclically processed program can be interrupted after every STEP 5 statement.
The processing of integral FBs can be interrupted at certain points (see section 9.2). The data cycle
(see section 2.2.2) can be interrupted after each data packet consisting of four data bits and a check
bit.
Cyclic or time-controlled
program processing
Interrupt-driven
program processing
A I 0.2
INTERRUPT!
Interrupt PII
OB2
S Q 14.0
L PY2
BE
BE
Interrupt PIQ
Figure 10-2. Program Interruptions by Process Interrupts
Use the IA command to disable interrupt processing. Use the RA command to enable interrupt
processing. The default setting is RA (see section 8.2.8).
Note
Even for interrupt processing, you may not exceed the general block nesting depth of 16
levels.
Interrupt Priorities
If a second interrupt is triggered during an interrupt processing, the second interrupts is processed
at the end of the first interrupt processing.
Note
If both a positive and negative pulse edge occur at an interrupt input while the IA
operation is valid (disable interrupt), it is no longer possible to determine the channel that
has triggered the interrupt.
But after an RA operation, OB2 is still called up.
10-2
S5-100U
Reading Out the Interrupt PII
If a process interrupt occurs, only the signal states of the interrupt inputs in slots 0 and 1 are read
out to the interrupt PII.
This data in the interrupt PII is the only data provided to the interrupt-driven program for evaluation.
The interrupt PII can be scanned in OB2 by means of the following load operations:
Overview:
Operation
Operand
Description
L
PY 0
Load byte 0 of the interrupt PII into ACCU 1
L
PY 1
Load byte 1 of the interrupt PII into ACCU 1
L
PW 0
Load word 0 of the interrupt PII into ACCU 1
If you enter other parameters, the CPU goes into the STOP mode and enters the “NNN” error
message in the ISTACK (see section 5.2). When data is read into the interrupt PII, the normal PII is
not written to simultaneously.
Writing to the Interrupt PIQ
Data from time-controlled or interrupt-driven programs to I/O modules are written to the interrupt PIQ
and simultaneously to the “normal” PIQ.
After OB2 is finished, the data that has been transferred to the interrupt PIQ is output to the
peripheral I/Os in an interrupt output data cycle (before “normal” program processing).
After the OB1 program cycle, the PIQ is copied to the interrupt PIQ.
The interrupt output data cycle is executed only if the interrupt PIQ has been written to. Use
transfer statements to write data for I/O modules to the interrupt PIQ. When data is written to the
interrupt PIQ, data is written simultaneously to the normal PIQ.
Overview:
Operation
Operand
Description
T
PY 0 to 127
Transfer contents of ACCU 1 into the interrupt PIQ
T
PW 0 to 126
10-3
S5-100U
Possibilities of Accessing Process I/O Image Tables
The following figure shows how data transfer between the process I/O image tables and ACCU 1
takes place when using various load and transfer statements in OB2.
Interrupt
PII
PII
T IBX/T IW X
L IBX/L IW X
L PYX/L PY1/L PW0
ACCU 1
T QBX/T QW X
T PYX/T PW X
Interrupt
PIQ
PIQ
X=byte or word address
Figure 10-3. Accessing the Process Image Tables from OB2
Example of How OB2 Can Be Programmed
Binary statements can access only the normal PII and PIQ. In order to determine the channel that
triggered an interrupt, transfer the I/O byte or word, for example, to a flag byte or word and then
evaluate using binary statements.
Example
Two sensors are
connected on channels 0
and 1 on a four-channel
digital input module on
slot 0.
Branch to FB12 if sensor 1
(channel 0) triggers an
interrupt.
STL OB2
L PY 0
T FY 0
A F 0.0
AN I 0.0
Explanation
Load byte 0 of the interrupt PII into ACCU 1 and
transfer it to flag byte 0.
Did a positive edge occur on channel 0?
OR
O
AN F 0.0
A I 0.0
Did a negative edge occur on channel 0?
JC FB 12
If a pulse edge has occurred, a branch is made
to FB12.
Caution
Be sure to save the flags (in a data block, for example) if these flags are to be
overwritten during interrupt processing and are needed again in the cycle.
10-4
S5-100U
10.2
The total reaction time is is the sum of the following times:
Signal delay of the module triggering the interrupt (= time from the input signal change
triggering the interrupt to the activation of the interrupt line)
Interrupt reaction time of the CPU
Execution time of the interrupt program (= sum of all STEP 5 statements in the interrupt
evaluation program)
Calculate the interrupt reaction times as follows:
CPU’s interrupt reaction time = basic reaction time + additional reaction times
The basic reaction time is 0.6 ms and is valid if the following conditions exist:
No integrated FBs were used.
No parameters for the integral clock are set.
No programmer/OP functions are present.
OB13 has not been programmed.
No SINEC L1 is connected.
The additional reaction times are variable. They are listed in Table 10-1.
Table 10-1. Additional Reaction Times
Additional Running Functions of the
Interrupt Reaction
Times
Integrated FBs
0.5 ms
Parameters set for clock
0.2 ms
SINEC L1 bus to the programmer interface
8.0 ms
OP functions
Depending on the number of bytes used
for loading the memory
Programmer functions:
Status block/Transfer block
Output address
Compress
• If no blocks are moved
• If blocks are moved
0.5 ms
18 ms per kbyte
Depending on the number of blocks
present (after overall reset 31 ms)
• 600 ms per each 1kword of
instructions in the block to be
moved
10-5
11
Analog Value Processing
11.1
Analog Input Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11.2
11.2.2
11.2.3
11.2.4
11.2.5
Connecting Current and Voltage Sensors to Analog
Input Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Voltage Measurement with Isolated/Non-Isolated
Thermocouples . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Two-Wire Connection of Voltage Sensors . . . . . . . . . . . . . . . . . . .
Two-Wire Connection of Current Sensors . . . . . . . . . . . . . . . . . . .
Connection of Two-Wire and Four-Wire Transducers . . . . . . . . . . . .
Connection of Resistance Thermometers . . . . . . . . . . . . . . . . . . . .
11.3
Start-Up of Analog Input Modules
11.4
Analog Value Representation of Analog Input Modules
11.2.1
11 -
1
11 -
1
11
11
11
11
11
2
3
4
4
6
11 -
7
11 - 11
11.5
Analog Output Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11.5.1 Connection of Loads to Analog Output Modules . . . . . . . . . . . . . . .
11.5.2 Analog Value Representation of Analog Output Modules . . . . . . . . .
11 - 19
11 - 19
11 - 20
11.6
Analog Value Conversion: Function Blocks FB250 and FB251 . . . . .
11.6.1 Reading in and Scaling an Analog Value -FB250- . . . . . . . . . . . . . .
11.6.2 Output of Analog Value -FB251- . . . . . . . . . . . . . . . . . . . . . . . . . .
11 - 22
11 - 22
11 - 25
Figures
11-1 Voltage Measuring with Isolated Thermocouples
(6ES5 464-8MA11/8MA21) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-2 Voltage Measuring with Non-Isolated Thermocouples
(6ES5 464-8MA11/8MA21) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-3 Two-Wire Connection of Voltage Sensors
(6ES5 464-8MB11, 464-8MC11, 466-8MC11) . . . . . . . . . . . . . . . . . . . . . .
11-4 Two-Wire Connection for Current Sensors (6ES5 464-8MD11) . . . . . . . . . .
11-5 Connection of Two-Wire Transducers (6ES5 464-8ME11) . . . . . . . . . . . . .
11-6 Connection for Four-Wire Transducers (6ES5 464-8ME11)
11-7 Wiring Method for PT 100 (6ES5 464-8MF11/8MF21) . . . . . . . . . . . . . . . .
11-8 Wiring Possibilities for Input Modules (6ES5 464-8MF11) . . . . . . . . . . . . . .
11-9 Load Connection via a Four-Wire Circuit
(6ES5 470-8MA11, 6ES5 470-8MD11) . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-10 Load Connection via a Two-Wire Circuit
(6ES5 470-8MB11, 6ES5 470-8MC11) . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-11 Scaling Schematic for FB250 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-12 Schematic for “Display of Tank Make-Up Quantity”
11-13 Conversion of the Nominal Range into the Defined Range
11-14 Schematic for “Display of Tank Contents” . . . . . . . . . . . . . . . . . . . . . . . . .
11-15 Transformation of the Analog Value to the Nominal Range . . . . . . . . . . . . .
11 -
2
11 -
2
11
11
11
11
11
11
3
4
4
5
6
6
11 - 19
11
11
11
11
11
11
20
22
23
23
25
26
Tables
11-1 Operating Mode Switch Settings for Analog Input Modules 464-8 to 11
11-2 Operating Mode Switch Settings for Analog Input
Module 464-8MA21 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-3 Operating Mode Switch Settings for Analog Input
Module 464-8MF21 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-4 Representation of an Analog Input Value as Bit Pattern . . . . . . . . . . . . . . . .
11-5 Analog Input Module 464-8MA11, -8MF11, -8MB11
(Bipolar Fixed-Point Number) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-6 Analog Input Module 464-8MC11, -8MD11
11-7 Analog Input Module 464-8ME11, 4x4 to20 mA
(Absolute Value Representation) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-8 Analog Input Module 464-8MF11, 2x PT 100 (Unipolar)
Analog Input Module 464-8MF21, 2x PT 100 “No Linearization”
(Unipolar) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-9 Analog Input Module 464-8MF21, 2x PT 100 “with Linearization”
(Bipolar) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-10 Analog Input Module 464-8MA21, 4x±50 mV “with Linearization” and
“with Temperature Compensation” (Bipolar); Thermoelement Type K
(Nickel-Chromium/Nickel-Aluminium, according to IEC 584) . . . . . . . . . . . . .
11-11 Analog Input Module 464-8MA21, 4x±50 mV “with Linearization” and
“with Temperature Compensation” (Bipolar); Thermoelement Type J
(Iron/Copper-Nickel (Konstantan), according to IEC 584) . . . . . . . . . . . . . . .
11-12 Analog Input Module 464-8MA21, 4x±50 mV “with Linearization” and
“with Temperature Compensation” (Bipolar); Thermoelement Type L
(Iron/Copper-Nickel (Konstantan) according to DIN 43710) . . . . . . . . . . . . .
11-13 Analog Input Module 466-8MC11, 4x 0 to10 V . . . . . . . . . . . . . . . . . . . . . .
11-14 Representation of an Analog Output Value as a Bit Pattern
11-15 Output Voltages and Currents for Analog Output Modules
(Fixed-Point Number Bipolar) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
11-16 Output Voltages and Currents for Analog Output Modules (Unipolar) . . . . . .
11-17 Call and Parameter Assignments of FB250 . . . . . . . . . . . . . . . . . . . . . . . .
11-18 Call and Parameter Assignments of FB251 . . . . . . . . . . . . . . . . . . . . . . . .
EWA 4NEB 812 6120-02b
11 -
7
11 -
8
11 - 10
11 - 11
11 - 11
11 - 12
11 - 12
11 - 12
11 - 13
11 - 14
11 - 15
11 - 16
11 - 16
11 - 20
11
11
11
11
21
21
22
25
S5-100U
11
11.1
Analog input modules convert analog process signals to digital values that the CPU can process (via
the process image input table, PII). In the following sections, you will find information about the
operating principle, wiring methods, and start-up and programming of analog input modules.
11.2
Connecting Current and Voltage Sensors to Analog Input Modules
Observe the following rules to connect current and voltage sensors to analog input modules:
When you have multi-channel operations, assign the channels in ascending order. This shortens
the data cycle.
Use terminals 1 and 2 for the connection of a compensating box (464-8MA11 ) or for the supply
of two-wire transducers (464-8ME11).
- Terminals 1 and 2 cannot be used with the remaining analog input modules.
Short-circuit the terminals of unused inputs.
Set the reference potentials of the sensors to a common reference potential. Do this to prevent
the potential difference between the common references from exceeding 1 V.
11-1
S5-100U
11.2.1 Voltage Measurement with Isolated/Non-Isolated Thermocouples
Module 464-8MA11/8MA21 is recommended for voltage measurement with thermocouples. With
floating sensors (e. g., isolated thermocouples), the permissible potential difference VCM between
terminals of the inputs and the potential of the standard mounting rail must not be exceeded. To
avoid this, the negative potential of the sensor must be connected to the central ground point (see
Figure 11-1). Jumper terminals 1 and 2 together if you do not use compensation boxes.
1
Reference junction
3
2
4
5
7
6
9
8
10
Compensating box
Thermal
coupling
Figure 11-1. Voltage Measuring with Isolated Thermocouples (6ES5 464-8MA11/8MA21)
With non-floating sensors (e. g., non-isolated thermocouples), the permissible potential difference
VCM must not be exceeded (see maximum values of the individual modules).
1
Reference junction
3
2
Compensating box
5
4
7
6
9
8
10
VCM
Thermal
coupling
Figure 11-2. Voltage Measuring with Non-Isolated Thermocouples
(Module 6ES5 464-8MA11/8MA21)
11-2
S5-100U
Connection of Thermocouples with Compensating Box to Module 464-8MA11/8MA21
The influence of the temperature on the reference junction (e. g., terminal box) can be compensated
for with a compensation box. Observe the following rules:
The compensation box must have a floating supply.
The power supply must have a grounded shielding winding.
The compensation box must be connected to terminals 1 and 2 of the terminal block.
11.2.2 Two-Wire Connection of Voltage Sensors
You can use the following three modules for the connection of voltage sensors:
Analog Input Module 464-8MB11 for voltages of±1 V
Analog Input Module 464-8MC11 for voltages of±10 V
Analog Input Module 466-8MC11 for voltages from 0 to 10 V
Figure 11-3 shows the two-wire connection of voltage sensors.
1
5
3
2
4
V
7
6
9
8
V
10
V
V
Figure 11-3. Two-Wire Connection of Voltage Sensors
11-3
S5-100U
11.2.3 Two-Wire Connection of Current Sensors
You can use module 464-8MD11 for the two-wire connection of current sensors.
Figure 11-4 shows the two-wire connections of current sensors.
1
3
2
5
7
4
9
10
6
8
Figure 11-4. Two-Wire Connection for Current Sensors (6ES5 464-8MD11)
11.2.4 Connection of Two-Wire and Four-Wire Transducers
Use the 24-V inputs 1 and 2 of analog input module 464-8ME11 to supply the two-wire transducers.
The two-wire transducer converts the supplied voltage to a current of 4 to 20 mA.
For wiring connections, see Figure 11-5.
1
3
2
4
L+
M
5
Two-wire
transducer
7
6
9
8
10
Two-wire
transducer
Figure 11-5. Connection of Two-Wire Transducers (6ES5 464-8ME11)
11-4
S5-100U
If you use a four-wire transducer connect it as shown in Figure 11-6.
1
3
2
U
5
4
7
6
9
8
10
Four-wire transducer
Figure 11-6. Connection for Four-Wire Transducers (6ES5 464-8ME11)
Four-wire transducers require their own power supply. Connect the “+” pole of the four-wire
transducer to the corresponding “-” pole of the terminal block (a connection technique that is the
opposite of the two-wire transducer). Connect negative terminals of the four-wire transducer to
terminal two of the terminal block.
Inputs 4, 6, 8, and 10 of the analog input module 464-8ME11 are connected internally via shunt
resistors. Because of the internal shunt resistors, broken wire signaling is not possible.
11-5
11.2.5
S5-100U
Analog input module 464-8MF11/8MF21 is suited for the connection of resistance thermometers
(e.g., PT 100).
The resistance of the PT 100 is measured in a four-wire circuit. A constant current is supplied to
the resistance thermometer via terminals 7 and 8 as well as via terminals 9 and 10, so that voltage
drops in these “constant current circuits” do not affect the measurement results. The measuring
inputs have a high resistance so that only a negligible current loss develops in the measuring
circuits.
M0+
IC0+
IC1+
3
1
M1+
5
7
9
Terminal assignments:
4
6
8
10
Measuring circuit M0
Measuring circuits M1
Constant current circuit IC 0
(9/10):
2
(3/4):
(5/6):
(7/8):
Constant current circuit IC 1
Figure 11-7. Wiring Method for PT 100 (6ES5 464-8MF11/8MF21)
If you use only one channel for PT 100 measurement (e.g., channel 0), then you can use the other
channel for voltage measurement (± 500 mV). In this case, use terminals M+/M- for the signal
connection and short circuit the terminals IC+ and IC-.
1
3
2
5
4
7
6
8
10
V
9
V
Figure 11-8. Wiring Possibilities for Input Modules (6ES5 464-8MF11)
11-6
S5-100U
11.3
Set the intended operating mode using the switches on the front panel of analog input modules
464-8 through 11. These switches are located on the right side at the top of the front panel of the
module.
Power supply
frequency:
Set the switch to the available power supply frequency. This selects the integration time of the A/D converters for optimal interference voltage suppression.
Power frequency 50 Hz: Integration time 20 ms
Power frequency 60 Hz: Integration time 16.66 ms
Operation:
Set the number of channels you wish to assign on the input module. If there are
fewer than four channels, less address space will be assigned and measured
values will be updated faster.
Broken wire:
Once the broken wire signal has been activated, a break on one of the lines to
the sensor (thermocouple or PT 100) or of the sensor itself causes the red LED
above the function selection switch to light up. At the same time, the broken wire
error bit F (bit 1, byte 1) for the faulty channel is set.
The module “recognizes” a wire break by applying a conventional tripping current
to the input terminals and by comparing the resulting voltage to a limit value. If
there is a wire break in the sensor or the lines, the voltage exceeds the limit value
and a “wire break” signal is sent. When the signal at the input is measured with
a digital voltmeter, the tripping current pulses cause apparent fluctuations of the
signal. Deactivation of the wire break signal does not turn off the tripping current.
Table 11-1. Operating Mode Switch Settings for Analog Input Modules 464-8 to 11
Function
Settings for Operating Mode Switch
50 Hz
60 Hz
4
3
2
1
Power supply
frequency
1 channel
(channel 0)
Operation
4
3
2
1
2 channels (channel 0
and channel 1)
4
3
2
1
4
3
2
1
With wire break signal
Wire break
4 channels (channel 0
- channel 3)
4
3
2
1
4
3
2
1
No wire break signal
4
3
2
1
11-7
S5-100U
Additional operating mode switch selections possible with analog module 464-8MA21:
Linearization:
With this function, you can obtain a characteristic linearization of the thermocouples of type J, K, and L or of the resistance thermometer PT 100. With module
464-8MA21, the linearization must always be activated together with the
corresponding compensation of the reference point temperature.
Thermocouples:
Type J: - 200° C to +1200° C
Type K: - 200° C to +1369° C
Type L: - 199° C to + 900° C
(-328° F to 2192° F)
(-328° F to 2497° F)
(-326° F to 1652° F) in steps each of 1° C (1.8° F)
Temperature
For the thermocouples of type J, K, and L, you can compensate, on the one hand,
compensation: the temperature of the reference point using a compensating box.
(See Figure 11-1). On the other hand, it is possible to move the reference point to
the front of the module by activating the “temperature compensation” function.
When thermocouples are directly connected, an internal circuit on the module
causes the digital value “0” to be displayed independently of the temperature of
the terminal when the temperature at the measuring junction is 0° C (32° F). In
order to accomplish this, the terminals of the sensors have to be connected
directly to the module, i.e., without a copper extension cable.
Table 11-2. Operating Mode Switch Settings for Analog Input Module 464-8MA21
Function
60 Hz
50 Hz
8
7
6
5
4
3
2
1
Power supply
frequency
1 channel
(channel 0)
Operation
and channel 1)
8
7
6
5
4
3
2
1
11-8
- channel 3)
8
7
6
5
4
3
2
1
Wire break
8
7
6
5
4
3
2
1
8
7
6
5
4
3
2
1
8
7
6
5
4
3
2
1
8
7
6
5
4
3
2
1
S5-100U
Table 11-2.
(continued)
Function
without
linearization
Characteristic
linearization of
thermocouples
Linearization
type K
8
7
6
5
4
3
2
1
8
7
6
5
4
3
2
1
without temperature
compensation
Temperature
compensation
Linearization
type J
8
7
6
5
4
3
2
1
Linearization
type L
8
7
6
5
4
3
2
1
Temperature compensation for type K
8
7
6
5
4
3
2
1
8
7
6
5
4
3
2
1
Temperature compensation for types J and L
8
7
6
5
4
3
2
1
If you have set “Characteristic linearization” and “Temperature compensation” with the operating
mode switches on module 464-8MA21 for the thermocouple used, then the reference temperature
is 0° C (32° F). This means that with 0° C (32° F) at the measuring junction, the value “0” is displayed.
If you equip several channels with thermocouples, use the same type of thermocouple. If you select
mixed thermocouples, or if you use thermocouples other than type J, K, or L, then you must choose
the following two settings:
“No linearization”
“No temperature compensation”
Compensation is then not possible even with a compensating box because the compensating box is
designed only for a certain type of thermocouple. It is possible to use a thermostat in the terminal
box if you use the thermostat temperature in the application software to adjust the thermocouple
input offset.
When you set the switches to “no linearization” and “no temperature compensation”, then module
464-8MA21 functions just like module 464-8MA11.
11-9
S5-100U
Set the switches on analog module 464-8MF21 as illustrated in Table 11-3.
Table 11-3. Operating Mode Switch Settings for Analog Input Module 464-8MF21
Function
50 Hz
60 Hz
8
7
6
5
4
3
2
1
Power supply
frequency
8
7
6
5
4
3
2
1
1 channel
(channel 0)
Operation
2 channels (channel 0 and
channel 1)
8
7
6
5
4
3
2
1
8
7
6
5
4
3
2
1
Wire break
8
7
6
5
4
3
2
1
8
7
6
5
4
3
2
1
No linearization
Characteristic
linearization
for the PT 100
Linearization for PT 100
8
7
6
5
4
3
2
1
8
7
6
5
4
3
2
1
Position 1 and 2 on the operating mode switch have no function.
If you set the switch to “no linearization” and “no temperature compensation”, module 464-8MF21
functions just like module 464-8MF11.
The characteristic linearization is possible for the following temperature ranges.
PT 100:
11-10
-100° C to+850° C (-148° F to 1569° F)
(in steps of 0.5° C (0.9° F))
S5-100U
11.4
Each analog process signal has to be converted into a digital format, to be stored in the process
image input table (PII). The analog signals are converted into a binary digit that is written in one of
the following ways:
In one byte (466-8MC11)
In two bytes (the remaining analog input modules)
Each bit position has a fixed value in powers of two (see Tables 11-4 and 11-14). Analog values
are represented in two's complement.
The following tables show the analog value representations of the different analog inputs in 2-byte
format. You will need this information to program FB250 and FB251 (see section 11.6).
Table 11-4. Representation of an Analog Input Value as Bit Pattern
High Byte
Low Byte
Bit Number
7
6
5
4
3
2
1
0
7
6
5
4
3
2
1
0
Analog Value Represent.
S
211
210
29
28
27
26
25
24
23
22
21
20
E
OV
Key:
S
E
OV
Sign bit
Irrelevant bits
Error bit
Overflow bit
0= " + " , 1= " - "
0= no wire break; 1=wire break
0= Measured value 4095 units at the most
1= Measured value greater than or equal to 4096 units
Analog value representation for analog input modules 464-8...
Table 11-5. Analog Input Module 464-8MA11, -8MF11, -8MB11 (Bipolar Fixed-Point Number)
Units
Measured Value
in mV
High Byte
Low Byte
Range
& gt; 4095
4095
100.0
99.976
1000.0
999.75
2000.0
1999.5
0 1 1 1 1 1 1 1 1 1 1 1 1 0 0 1
0 1 1 1 1 1 1 1 1 1 1 1 1 0 0 0
Overflow
2049
2048
1024
50.024
50.0
25.0
500.24
500.0
250.0
1000.48
1000.0
500.0
0 1 0 0 0 0 0 0 0 0 0 0 1 0 0 0
0 1 0 0 0 0 0 0 0 0 0 0 0 0 0 0
0 0 1 0 0 0 0 0 0 0 0 0 0 0 0 0
Overrange
1
0
-1
0.024
0.0
- 0.024
0.24
0.0
-0.24
0.48
0.0
-0.48
0 0 0 0 0 0 0 0 0 0 0 0 1 0 0 0
0 0 0 0 0 0 0 0 0 0 0 0 0 0 0 0
1 1 1 1 1 1 1 1 1 1 1 1 1 0 0 0
-1024
-2048
-2049
- 25.0
-50.0
-50.024
- 250.0
-500.0
-500.24
- 500.0
-1000.0
-1000.48
1 1 1 0 0 0 0 0 0 0 0 0 0 0 0 0
1 1 0 0 0 0 0 0 0 0 0 0 0 0 0 0
1 0 1 1 1 1 1 1 1 1 1 1 1 0 0 0
Overrange
-4095
& lt; -4095
-99.976
-100.0
-999.75
-1000.0
-1999.5
-2000.0
1 0 0 0 0 0 0 0 0 0 0 0 1 0 0 0
1 0 0 0 0 0 0 0 0 0 0 0 1 0 0 1
Overflow
464-8MA11/-8MA21 “No linearization”
464-8MF11
(2x±500 mV)
464-8MB11
(4x±1 V)
Nominal range
(4x±50 mV)
11-11
S5-100U
Table 11-6. Analog Input Module 464-8MC11, -8MD11 (Bipolar Fixed-Point Number)
Units
Measured Value
in V
in mA
& gt; 4095
4095
2049
20.000
19.995
10.0048
40.0
39.9902
20.0098
2048
1024
1
10.000
5.000
0.0048
20.0
10.0
0.0098
0
-1
-1024
0.0
-0.0048
- 5.000
0.0
-0.0098
-10.0
-2048
-2049
-4095
& lt; -4095
-10.000
-10.0048
-19.995
-20.000
-20.0
-20.0098
- 39.9902
-40.0
1
1
1
1
464-8MC11
464-8MD11
High Byte
1
0
0
0
0
1
0
0
0
1
0
0
0
1
0
0
0
1
0
0
Low Byte
0
1
0
0
0
1
0
0
0
1
0
0
0
1
0
0
0
1
0
0
0
1
0
0
0
1
1
1
0
0
0
0
Range
0
0
0
0
0
0
0
1
Overflow
Overrange
Nominal range
Overrange
Overflow
(4x±10 V)
(4x±20 mA)
Table 11-7. Analog Input Module 464-8ME11, 4x4 to 20 mA (Absolute Value Representation)
Units
Measured Value
High Byte
Low Byte
Range*
in mA
& gt; 4095
& gt; 32.769
Overflow
4095
2561
2560
31.992
20.008
20.0
0 1 0 1 0 0 0 0 0 0 0 0 1 0 0 0
0 1 0 1 0 0 0 0 0 0 0 0 0 0 0 0
Overrange
2048
512
511
16.0
4.0
3.992
0 0 0 1 0 0 0 0 0 0 0 0 0 0 0 0
0 0 0 0 1 1 1 1 1 1 1 1 1 0 0 0
Nominal range
384
0
-1
3.0
0.0
-0.008
0 0 0 0 1 1 0 0 0 0 0 0 0 0 0 0
& lt; -32.769
& lt; -4095
Transducer
failure?
Because of tolerances of components used in the module, the converted value can also be negative
(e.g. FFF8H Unit: -1).
Table 11-8.
Units
Analog Input Module 464-8MF21, 2x PT 100 “No Linearization” (Unipolar)
Resistance
High Byte
Low Byte
Range
in
& gt; 4095
400.0
Overflow
4095
2049
2048
399.90
200.098
200.0
Overrange
1024
1
0
100.0
0.098
0.0
Nominal range
11-12
S5-100U
Table 11-9. Analog Input Module 464-8MF21, 2x PT 100 “with Linearization” (Bipolar)
Units
& gt; 1766
Resistance in
& gt; 400
Temperature in
°C
& gt; 883
& gt; 1531
High Byte
Low Byte
Range
°F
0 0 1 1 0 1 1 1 0 0 1 1 0 0 0 1 Overflow
390.26
883
851
850
1531
1564
1562
0 0 1 1 0 1 1 1 0 0 1 1 0 0 0 1 Overrange*
0 0 1 1 0 1 0 1 0 0 1 1 0 0 0 1
0 0 1 1 0 1 0 1 0 0 1 0 0 0 0 0
345.13
280.90
212.02
700
500
300
1292
932
572
0 0 1 0 1 0 1 1 1 1 0 0 0 0 0 0
0 0 0 1 1 1 1 1 0 1 0 0 0 0 0 0
0 0 0 1 0 0 1 0 1 1 0 0 0 0 0 0
300
200
2
157.31
138.50
100.39
150
100
1
302
212
34
0 0 0 0 1 0 0 1 0 1 1 0 0 0 0 0
0 0 0 0 0 1 1 0 0 1 0 0 0 0 0 0 Nominal range
0 0 0 0 0 0 0 0 0 0 0 1 0 0 0 0
0
-40
-80
100.00
92.16
84.27
0
-20
-40
32
-4
-40
1 1 1 1 1 1 1 0 1 1 0 0 0 0 0 0
1 1 1 1 1 1 0 1 1 0 0 0 0 0 0 0
-200
-202
-494
60.25
-100
-101
-247
-148
-150
-413
1766
1702
1700
1400
1000
600
& lt; -494
& lt; -247
& lt; -403
1 1 1 1 1 0 0 1 1 1 0 0 0 0 0 0
1 1 1 1 1 0 0 1 1 0 1 1 0 0 0 1 Overrange*
1 1 1 1 0 0 0 0 1 0 0 1 0 0 0 1
1 1 1 1 0 0 0 0 1 0 0 1 0 0 0 1 Overflow
In the overrange area, the current slope of the characteristic curve is maintained when leaving the linearized nominal range.
11-13
S5-100U
Table 11-10. Analog Input Module 464-8MA21, 4x±50 mV “with Linearization”
and “with Temperature Compensation” (Bipolar); Thermoelement Type K
Units
Thermal
Voltage
in mV*
Temperature
°C
High Byte
Low Byte
Range
°F
& gt; 2359
0 1 0 0 1 0 0 1 1 0 1 1 1 0 0 1 Overflow
Overrange**
1370
1369
54.773
1370
1369
2498
2496
0 0 1 0 1 0 1 0 1 1 0 1 0 0 0 1
0 0 1 0 1 0 1 0 1 1 0 0 1 0 0 0
1000
500
150
41.269
20.640
6.137
1000
500
150
1832
932
302
0 0 0 0 1 1 1 1 1 0 1 0 0 0 0 0
0 0 0 0 0 1 0 0 1 0 1 1 0 0 0 0
100
1
0
4.095
0.039
0
100
1
0
212
34
32
-1
-100
-101
-0.039
-3.553
-3.584
1
-100
-101
-30
-148
-150
1 1 1 1 1 1 0 0 1 1 1 0 0 0 0 0
1 1 1 1 1 1 0 0 1 1 1 0 0 0 0 0 Accuracy
-150
-200
-201
-273
-4.912
-5.891
-150
-200
-201
-238
-328
-330
1
1
1
1
0 0 0 0 0 0 1 1 0 0 1 0 0 0 0 0 Nominal range
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
0
0
0
0
0
1
0
0
0
1
1
1
0
0
1
1
1
1
1
0
0
0
0
1
0
1
0
1
1
0
0
1
0
0
0
0
0
0
0
0
0
0 2K
0
1 Overrange**
1 Overflow
X X X X X X X X X X X X X 0 1 0 Wire break
This value corresponds to the terminal temperature at wire break
11-14
For a reference temperature of 0° C (32° F)
S5-100U
Table 11-11.
Units
and “with Temperature Compensation” (Bipolar); Thermoelement Type J
Thermal
Temperature
Voltage
High Byte
Low Byte
Range
°C
°F
in mV*
1485
0 0 1 0 1 1 1 0 0 1 1 0 1 0 0 1 Overflow
Overrange**
1201
1200
69.536
1201
1200
2194
2192
0 0 1 0 0 1 0 1 1 0 0 0 1 0 0 1
0 0 1 0 0 1 0 1 1 0 0 0 0 0 0 0
1000
500
100
57.942
27.388
5.268
1000
500
100
1832
932
212
1
0
-1
0.05
0
-0.05
1
0
-1
34
32
-30
-100
-150
-199
-4.632
-6.499
-7.868
-100
-199
-200
-148
-238
-326
1 1 1 1 1 0 1 1 0 1 0 1 0 0 0 0
1 1 1 1 1 0 0 1 1 1 0 0 1 0 0 0
-200
-201
-273
-7.890
-200
-201
-328
-330
1 1 1 1 1 0 0 1 1 0 1 1 1 0 0 1 Overrange**
1 1 1 1 0 1 1 1 0 1 1 1 1 0 0 1 Overflow
0 0 0 0 0 0 0 0 0 0 0 0 1 0 0 0 Nominal range
X X X X X X X X X X X X X 0 F 0 Wire break
11-15
S5-100U
Table 11-12. Analog Input Module 464-8MA21, 4x±50 mV “with Linearization”
and “with Temperature Compensation” (Bipolar); Thermoelement Type L
(Iron/Copper-Nickel (Konstantan), according to DIN 43710)
Thermal
Temperature
Units
Voltage
High Byte
Low Byte
Range
°C
°F
in mV*
1361
0 0 1 0 1 0 1 0 1 0 0 0 1 0 0 1 Overflow
Overrange**
901
900
53.14
901
900
1654
1652
0 0 0 1 1 1 0 0 0 0 1 0 1 0 0 1
0 0 0 1 1 1 0 0 0 0 1 0 0 0 0 0
500
27.85
500
932
250
13.75
250
482
0 0 0 0 0 1 1 1 1 1 0 1 0 0 0 0
100
1
0
+5.37
0.05
0
100
1
0
212
34
32
-1
-100
-150
-0.05
-4.75
-6.60
-1
-100
-150
-30
-148
-238
-190
-199
-200
-7.86
-8.12
-190
-199
-200
-310
-326
-328
1 1 1 1 1 0 1 0 0 0 0 1 0 0 0 0
1 1 1 1 1 0 0 1 1 1 0 0 0 0 0 1 Overrange**
-273
break
Analog value representation of analog input module 466-8MC11
The 466-8MC11 analog input module stores each analog value in a single byte. The other analog
input modules store the analog values in words (see Table 11-4).
Table 11-13. Analog Input Module 466-8MC11, 4x 0 to 10 V
Units
Bit Representation
255
9961
1 1 1 1 1 1 1 1
254
9922
1 1 1 1 1 1 1 0
128
5000
1
39
0 0 0 0 0 0 0 1
0
11-16
Voltage in mV
0
0 0 0 0 0 0 0 0
1 0 0 0 0 0 0 0
S5-100U
If you want to read in the analog value with function block FB250 (analog value reading), you have to
pre-process the analog value before calling up FB250.
Example 1:
Analog input module 466-8MC11 is inserted in slot 1, which means that the module's start address
is 72.
The analog values are stored in four consecutive bytes:
1st analog value
2nd analog value
3rd analog value
4th analog value
(channel 0)
(channel 1)
(channel 2)
(channel 3)
in IB72
in IB73
in IB74
in IB75
Function block FB72, pictured below, reads in the analog values and pre-processes them for
function block FB250 (analog value reading).
FB72
Explanation
READ IN ALL CHANNELS
OF AI 466
0005
0006
0007
0008
:L
:T
:L
IW
FW
IW
72
72
74
0009
000A
000B
:T
:L
FW
74
FY
72
PROCESS EACH ANALOG VALUE
000C
000D
000E
:SLW
:T
IW
6
72
AND REWRITE THEM IN
THE PII SO THAT FB250
CAN ACCESS THEM
000F
0010
0011
:L
FY
:SLW
:T
IW
73
6
74
WITHIN THAT SCAN.
0012
0013
0014
:L
FY
:SLW
74
6
0015
0016
0017
0018
:T
IW
:L
FY
:SLW
76
0019
001A
001B
:T
:BE
78
IW
READ ALL FOUR CHANNELS
AND REARRANGE
75
6
11-17
S5-100U
Example 2:
Analog input module 466-8MC11 is inserted in slot 0, which means that the module’s start address
is 64.
The analog values that are read in are stored in four consecutive bytes:
1st analog value
2nd analog value
3rd analog value
4th analog value
(channel 0)
(channel 1)
(channel 2)
(channel 3)
in IB64
in IB65
in IB66
in IB67
Function block 73, pictured below, reads in the analog values and pre-processes them for FB250.
The additional processing with FB250 is done just like module 464, however without an overflow bit.
FB73
Explanation
000A
000C
000E
:L
IB
:SLW
:T
IW
67
6
70
Read in channel 3
0010
0012
0014
:L
IB
:SLW
66
6
Read in channel 2
0016
0018
001A
:T
:L
001C
001E
0020
0022
0024
0026
:L
IB
:SLW
:T
IW
64
6
64
0028
002A
002C
:JU FB 250
IW
68
IB
65
:SLW
:T
IW
6
66
Read in channel 1
Read in channel 0
002E NAME :RLG:AI
0030 BG
KF +0
0032 KNKT :
KY 0,4
Module on slot 0
Channel/No. 0, unipolar representation
0034 OGR :
0036 UGR :
0038 EINZ :
KF +1000
KF +0
F
0.0
Upper limit 1000 (1000 mV)
Lower limit 0
No meaning
003A XA
003C FB
003E BU
0040
FW 100
F 102.0
F 102.1
Output, 0 to 1000 mV in KF
Error bit for parameter assignment
Range overflow
(always 0 with this module)
0042
:BE
11-18
S5-100U
11.5
Analog output modules convert the bit patterns that are output by the CPU into analog output
voltages or currents.
No adjustments are necessary if you want to connect loads to the analog outputs.
Check the following items before connecting loads:
The load voltage 24 V DC must be connected to terminals 1 and 2.
The maximum permissible potential difference between the outputs is 60 V AC.
Unused outputs must be left open-circuited.
Figure 11-9 shows how to connect loads to the voltage outputs of the following modules:
470-8MA12 (2x±10 V)
470-8MD12 (2x+1 to 5 V)
The sensor lines (S+ and S-) must be directly connected to the load, so that the voltage is
measured and regulated directly at the load. In this manner, voltage drops of up to 3 V per line can
be compensated for.
The sensor lines can be left out if the resistances of the QV and M lines are negligible compared to
the load resistance. In such a case, connect terminal S+to terminal QV, and terminal S- to MANA.
S+
S+
S-
3
1
S-
5
7
9
QV
2
4
MANA
QV
6
8
MANA
10
Key:
QV:
S±:
MANA:
RL:
L+
Analog output " Voltage "
Sensor line
Chassis ground terminal
of the analog unit
Load resistor
M
24 V DC
(4/8) (3/7)
QV
(5/9) (6/10)
S+
S- MANA
Terminal assignment
Terminals
RL
Figure 11-9. Load Connection via a Four-Wire Circuit (6ES5 470-8MA12 or 6ES5 470-8MD12)
11-19
S5-100U
Figure 11-10 shows how to connect loads to the current outputs of the following modules.
470-8MB12 (2x±20 mA)
470-8MC12 (2x+4 to 20 mA).
1
3
2
L+
5
4
7
9
6
8
Key:
QI:
MANA:
10
Analog output " Current "
of the analog unit
M
24 V DC
(4/8)
(6/10)
QI
Terminal assignment
MANA
Terminals
RL
Figure 11-10. Load Connection via a Two-Wire Circuit (6ES5 470-8MB12 or 6ES5 470-8MC12)
Table 11-14 shows how the analog output value has to be stored in the process image output table
(PIQ).
Table 11-14. Representation of an Analog Output Value as a Bit Pattern
High Byte
Low Byte
Bit number
7
6
5
4
3
2
1
0
7
6
5
4
3
2
1
0
Analog value represent.
S
210
29
28
27
26
25
24
23
22
21
20
Key:
11-20
S
sign bit
irrelevant bits
S5-100U
Table 11-15 and 11-16 show the voltage and currents assigned to the bit patterns.
Table 11-15.
Units
Output Values
High Byte
Low Byte
in V
1280
1025
12.5
10.0098
25.0
20.0195
1024
512
1
10.0
5.0
0.0098
20.0
10.0
0.0195
0 1 0 0 0 0 0 0 0 0 0 0 x x x x
0 0 1 0 0 0 0 0 0 0 0 0 x x x x
0 0 0 0 0 0 0 0 0 0 0 0 x x x x
0
-1
-512
0.0
-0.0098
-5.0
0.0
-0.0195
-10.0
1 1 1 1 1 1 1 1 1 1 1 1 x x x x
1 1 1 0 0 0 0 0 0 0 0 0 x x x x
-1024
-1025
-1280
-10.0
-10.0098
-12.5
-20.0
-20.0195
-25.0
1 1 0 0 0 0 0 0 0 0 0 0 x x x x
1 0 1 1 1 1 1 1 1 1 1 1 x x x x
1 0 1 1 0 0 0 0 0 0 0 0 x x x x
Range
in mA
2x±10 V
2x±20 mA
x x x x
x x x x
Overrange
Nominal range
Overrange
6ES5 470-8MA12
6ES5 470-8MB12
Table 11-16. Output Voltages and Currents for Analog Output Modules (Unipolar)
Units
Output Values
High Byte
Low Byte
in V
1280
1025
6.0
5.004
24.0
20.016
0 1 0 0 0 0 0 0 0 0 0 1
1024
512
1
5.0
3.0
1.004
20.0
12.0
4.016
0 0 0 0 0 0 0 0 0 0 0 1 x x x x
0
-1
-256
1.0
0.996
0.0
4.0
3.984
0.0
1 1 1 1 0 0 0 0 0 0 0 0 x x x x
-512
-1024
-1280
-1.0
-3.0
-4.0
-4.0
-12.0
-16.0
Range
in mA
2x 1 to 5 V
2x 4 to 20 mA
x x x x
x x x x
Overflow
Nominal range
Overrange
6ES5 470-8MD12
6ES5 470-8MC12
11-21
11.6
S5-100U
- FB250 -
Specify the type of analog value representation for the module (channel type) in the KNKT
parameter (see Table 11-17). Define the desired range using the “upper limit” (OGR) and " lower
limit” (UGR) parameters.
Table 11-17. Call and Parameter Assignments of FB250
Parameter
Explanation
Type
Assignment
BG
Slot number
D KF
0 to 7
KNKT
Channel number
Channel type
D KY
KY = x,y
x = 0 to 3
y = 3 to 6
3: Absolute value
representation
(4 to 20 mA)
4: Unipolar representation
5: Bipolar absolute value
6: Bipolar fixed-point
number
OGR
Upper limit of the output
value
D KF
-32767 to +32767
UGR
Lower limit of the output
value
D KF
-32767 to +32767
EINZ
Single scan
I BI
Not relevant
XA
Output value
QW
Scaled analog value is “0”
on wirebreak
FB
Error bit
Q BI
“1” on wirebreak, illegal
channel or slot number or
illegal channel type
BU
Range violation
Q BI
“1” when nominal range is
exceeded
Scaled range
STL
NAME
BG
KNKT
OGR
UGR
EINZ
XA
FB
BU
: JU FB 250
: RLG:AI
Representation of
the analog input
module
User scaled range
UGR
OGR
Figure 11-11. Scaling Schematic for FB250
11-22
S5-100U
Example: Display of Tank Make-Up Quantity
The make-up of a cylindrical tank holding 30 m3 is to be shown on a 3-digit display. The individual
digits must be set in BCD.
The level of the liquid in the tank is sensed by a SONAR-BERO®, range 80 to 600 cm, with analog
output (see Catalog NS3).
SONAR-BERO
I=4 to 20 mA
PS
CPU
AI AQ DQ DQ
80 cm
Gap
1 0. 5 m3
600 cm
Tank
Tank level
3-digit BCD display
Figure 11.12 Schematic for “Display of Tank Make-Up Quantity”
The analog output of the SONAR-BERO delivers a constant current in the range 4 to 20 mA
proportional to the gap between sensor and liquid. This current is routed to the 4 to 20 mA
analog input module in slot 0, channel 0.
FB250 converts the range 4 to 20mA to the range 0 to 30.0 m3.
The value is stored in flag word 1 as a fixed-point number. Initialization takes place in the
calling block. FB241 converts the fixed-point number into a BCD number.
4 mA
0 m3
12 mA
15.0 m3
20 mA
30.0 m3
Nominal range of the
analog module
Range set by
user
Figure 11-13. Conversion of the Nominal Range into the Defined Range
11-23
STL
JU FB 250
NAME
: RLG:AI
BG
: 0
KNKT
OGR
UGR
: 0.3
: 300
: 0
EINZ
XA
FB
: FW1
:F0.0
BU
:F0.1
JU FB 241
S5-100U
Explanation
Unconditional call FB250
Slot 0
Channel 0, channel type 3
Upper limit: 30.0 m3
Lower limit: 0.0 m3
No meaning
Make-up quantity stored in flag word 1 as fixed-point number
“1”, if wire break
“1”, if tank too full
Conversion of fixed-point number into
BCD number
The BCD number is stored in flag bytes 11 to 13. Output is via two 8-channel digital output
modules in slots 2 and 3. The BCD tetrads 5 and 6 stored in flag word 11 need not be output
since the number has only three digits.
STL
L FW12
T QW2
Explanation
Read tetrads 0 to 3 of the BCD number
and transfer to output modules.
BE
11-24
S5-100U
11.6.2
Output of Analog Value - FB251 -
Analog values can be output to analog output modules using this function block. In doing so, values
from the range between the lower limit (UGR) and high limit (OGR) parameters are converted to the
nominal range of the module in question.
Table 11-18.
Parameter
Explanation
Type
Assignment
: JU FB 251
NAME
: RLG:AQ
XE
Analog value to be
output
IW
Input value (two's
complement) in the
range UGR to OGR
XE
BG
KNKT
BG
Slot address
D KF
0 to 7
KNKT
Channel number
Channel type
D KY
OGR
UGR
FEH
BU
OGR
value
D KF
-32767 to +32767
UGR
value
D KF
-32767 to +32767
FEH
Error in limit value
setting
Q BI
“1” if UGR = OGR,
invalid channel or slot,
or invalid channel type
BU
Input value exceeds
UGR or OGR
Q BI
“1” if XE lies outside
limits (UGR; OGR).
XE assumes the limit
value
KY = x,y
x = 0;1
y = 0;1
0: unipolar representation
1: bipolar fixed-point
number
Example: Display of Tank Contents on an Analog Measuring Instrument
The make-up quantity of a 30 m3 tank is stored in flag word 1 as a fixed-point number (see example
FB250). The ± 20 mA analog output module in slot 1, channel 0, transfers the standardized value
to the measuring instrument. The value is displayed within the range 0 to 20 mA.
PS
CPU
AQ
Figure 11-14. Schematic for “Display of Tank Contents”
11-25
S5-100U
The tank contents are determined from the make-up quantity.
STL
L KF +300
L FW 1
-F
T FW 20
Explanation
Maximum tank capacity
Make-up quantity
Calculate difference
Store tank contents in FW20
The UGR and OGR parameters of FB 251 refer to the nominal range of the analog output module.
For this reason, the UGR parameter must be assigned the value -30.0.
- 30.0 m3
- 20 mA
Tank contents
0.0 m3
30.0 m3
0 mA
20 mA
Figure 11-15. Transformation of the Analog Value to the Nominal Range
STL
JU FB251
NAME
:RLG:AQ
XE
BG
KNKT
:FW20
:1
:0.1
OGR
UGR
FEH
BU
:300
:-300
:F0.2
:F0.3
Explanation
Unconditional call-up FB251
Tank contents
Slot 1
Channel 0, channel type 1
High limit 30.0 m3
Low limit - 30.0 m3
“1”, if wire break
BE
11-26
12
The Integral Real-Time Clock, for CPU 103 Version 8MA02 and Higher
12.1
Function . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12 -
1
12
12
12
12
2
2
3
4
12.3.1
12.3.2
12.3.3
12.3.4
Programming the Integral Real-Time Clock in DB1,
for CPU 103 Version 8MA03 and Higher . . . . . . . . . . . . . . . . . . . .
Setting the Clock in DB1 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Setting the Prompt Time in DB1 . . . . . . . . . . . . . . . . . . . . . . . . . .
Setting the Operating Hours Counter in DB1 . . . . . . . . . . . . . . . . .
Entering the Clock Time Correction Factor in DB1
12
12
12
12
12
5
5
6
7
7
12.4
Structure of the Clock Data Area . . . . . . . . . . . . . . . . . . . . . . . . . .
12 -
8
12.5
Structure of the Status Word and How to Scan it
12 - 12
12.6
Setting Parameters for the Clock Data Area and the Status Word
in the System Data Area . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12 - 15
Programming the Integral Real-Time Clock in the
User Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Reading and Setting the Clock . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming the Prompt Function . . . . . . . . . . . . . . . . . . . . . . . .
Programming the Operating Hours Counter . . . . . . . . . . . . . . . . . .
Entering the Clock Time Correction Factor . . . . . . . . . . . . . . . . . . .
12
12
12
12
12
12.2
Setting Parameters in DB1, for CPU 103 Version 8MA03
and Higher . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12.2.1 Defaults . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12.2.2 Reading the Current Clock Time and the Current Date . . . . . . . . . .
12.2.3 DB1 Parameters Used for the Integral Real-Time Clock . . . . . . . . . .
12.3
12.7
12.7.1
12.7.2
12.7.3
12.7.4
21
21
25
30
35
Figures
12-1 DB1 with Default Parameters for Integral Real-Time Clock . . . . . . . . . . . . .
12-2 Example: Setting the Clock in DB1 to Monday, November 9, 1992, 15:30 . . .
12-3 Example: Setting the Prompt Time in DB1 to
Thursday, December 17, 1992, 8:00 o'clock
12-4 Setting the Operating Hours Counter in DB1 to 1600 Hours
12-5 Entering a Correction Factor of +90s in DB1 . . . . . . . . . . . . . . . . . . . . . . .
12-6 How DB1 or the Control Program and the Clock Access the Clock
Data Area . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12-7 Flowchart - Transferring Time and Date Settings to the Clock . . . . . . . . . . .
12-8 Flowchart - Transferring a New Prompt Time . . . . . . . . . . . . . . . . . . . . . . .
12-9 Flowchart - Transferring Settings to the Operating Hours Counter . . . . . . . .
12 12 -
2
5
12 12 12 -
6
7
7
12
12
12
12
- 8
- 20
- 26
- 31
12
12
12
12
12
12
- 3
- 4
- 9
- 10
- 13
- 13
Tables
12-1
12-2
12-3
12-4
12-5
12-6
12-7
12-8
12-9
12-10
12-11
12-12
12-13
12-14
Reading the Current Clock Time and Current Date . . . . . . . . . . . . . . . . . . .
DB1 Parameters for the Integral Real-Time Clock . . . . . . . . . . . . . . . . . . . .
Clock Data in the Clock Data Area . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Range Definitions for Clock Data . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Significance of Bits 0, 1, 2, and 3 of the Status Word . . . . . . . . . . . . . . . . .
Significance of Bits 4 and 5 of the Status Word . . . . . . . . . . . . . . . . . . . . .
Significance of the Operating Hours Counter Flags Bits 8, 9, and 10
of the Status Word . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Significance of the Prompting Time Flags Bits 12, 13, and 14 of the
Status Word . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
The System Data Area for the Integral Real-Time Clock . . . . . . . . . . . . . . .
FB1 Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
OB21 Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
OB22 Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
DB75 Program . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
FORCE VAR Function . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
12 - 14
12
12
12
12
12
12
12
14
15
17
18
18
18
19
S5-100U
12
12.1
Function
The integral real-time clock offers the following possibilities of controlling the process sequence:
Clock and calendar function
- Used to configure clock-time dependent control, for example
Prompt and alarm function
- Used to monitor the duration of a process, for example
Operating hours counter
- Used to monitor inspection intervals, for example
The clock begins running when you supply voltage to the programmable controller. The default is
April 1, 1992, 12:00 o’clock. You set the clock by setting its parameters.
There are two possibilities.
With CPU 103 version 8MA03, you can set the clock parameters in DB1 (see section 12.2).
With CPU 103 version 8MA02 and higher, you can set the clock parameters in the system data
area (see section 12.6) and program the clock in the user program (see section 12.7).
The hardware clock requires a clock data area and a status word in order to function. The location
of both the clock data area and the status word must be stored in system data 8 to 10.
Operating Principle of the Clock
Data exchange between the integral real-time clock and the control program always goes through
the clock data area. The clock stores current values for time, date, and operating hours counter in
the clock data area. You can transfer into the clock data area the values for the time, date, prompt
time, and operating hours counter that you want the clock to use.
You can scan the status word to identify setting errors, for example. Or you can change certain
status word bits to deliberately disable or enable transfer or read operations.
Refer to sections 12.4 and 12.5 for additional information about the clock data area and the status
word. These sections are especially important if you want to set clock parameters in the system
data. If you are new to SIMATIC, you may prefer to set clock parameters in DB1.
12-1
12.2
S5-100U
Setting Parameters in DB1, for CPU 103 Version 8MA03 and Higher
Set the clock parameters in DB1 to be able to use the clock functions. Follow the same rules you
used in setting parameters for other functions. Refer to section 9.1.
Procedures for Setting Parameters in DB1
1. Perform an overall reset.
2. Output default DB1 to the programmer.
3. Use the cursor to jump into the clock parameter block.
4. Change the parameters.
5. Transfer the changed DB1 to the programmable controller.
6. Switch the programmable controller from STOP to RUN.
Every time there is a change from STOP to RUN, the programmable controller accepts the new
clock data.
Note
The system data contents are deleted during an overall reset. The clock continues to run
internally with the current values.
The clock time is updated one second after the next cycle starts.
12.2.1 Defaults
The following values are preset in the parameter block when you output the default DB1.
36:
48:
KS
KS
60:
72:
84:
KS ='MW102
KS ='OHE N
KS ='12:00:00
96:
108:
KS
KS
='PGN 01 ; #CLP: CF 0
='CLK DB5 DWO
STW
STP Y SAV Y ';
SET 4 01.04.92 ';
TIS 4
='01.04. 13:00:00
OHS ';
='000000:00:00 # ; SDP: WD';
Figure 12-1. DB1 with Default Parameters for Integral Real-Time Clock
After the CLP block ID for the integral real-time clock, the CLK parameter defines the location of the
clock data (in DB5 beginning with DW0, for example). The STW parameter specifies the location of
the status word (in flag word MW102, for example). You must specify both parameters if you want
to read the clock.
Section 12.2.2 describes the procedures you must follow to read the clock.
Section 12.2.3 lists all of the parameters that you can use for the integral clock.
12-2
S5-100U
Proceed as follows to see how and with which values the clock runs.
2. Output DB1 to the programmer.
3. Overwrite both (#) comment characters with a blank space.
4. Generate DB5 with DW0 to DW21. See Table 12-3 for information about storing the current
clock time and current date.
5. Switch the programmable controller from STOP to RUN. The clock accepts the values present
in DB1.
6. Enter DB5 and DW0 to DW3 on the programmer by using the FORCE VAR function.
7. Press the “ENTER” key twice. The clock runs using the current values.
Table 12-1. Reading the Current Clock Time and Current Date
Operand
Signal States
Explanation
DW 0
KH = 0004
DW 1
DW 2
DW 3
KH = 0104
KH = 9212
KH = 0000
Wednesday
October 1
1992, 12:00
DB 5
12-3
S5-100U
Table 12-2.
Parameters
Argument
Meaning
Block ID: CLP:
Clock Parameters
Entering the correction factor (Correction Factor)
CF
p
CLK
DBxDWy, MWz,EWv
or AWv
Location of the clock data (CLocK Data)
STW
DBxDWy, MYz,EWv
or AWv
Location of the status word (STatus Word)
STP
J/Y/N
Updating the clock during STOP (SToP)
SAV
J/Y/N
Saving the clock time after the last change
from RUN to STOP or Power OFF (SAVe)
OHE
J/Y/N
Enabling the operating hours counter
(Operating Hours counter Enable)
SET
wd dd.mm.yy
hh:mn:ss1 AM/PM2
Setting the clock time and date
TIS
wd dd.mm.
hh:mn:ss1 AM/PM2
Setting the prompt time (TImer Set)
OHS
hhhhhh:mn:ss1
Setting the operating hours counter
(Operating Hours counter Set)
wd
dd
mm
yy
hh
mn
ss
hhhhhh
1
2
1 to 7
01 to 31
01 to 12
0 to 99
00 to 23
00 to 59
00 to 59
0 to 999999
(weekday = Sun. - Sat.)
(day)
(month)
(year)
(hours)
(minutes)
(seconds)
(hours)
p = – 400
v =
0
x =
2
y =
0
z =
0
j/J = yes
y/Y = yes
n/N = no
to
to
to
to
to
400
126
255
255
254
If an argument such as seconds, for example, is not to be entered, enter XX. The clock continues to run
with the current data. The TIS parameter block does not acknowledge this argument.
If you enter AM or PM after the clock time, the clock runs in the 12-hour mode. If you omit this argument,
the clock runs in the 24-hour mode. You must use the same time mode in the SET and TIS parameter
blocks.
12-4
S5-100U
12.3
Programming the Integral Real-Time Clock in DB1, for CPU 103
Sections 12.3.1 to 12.3.4 contain examples for programming the clock in DB1. Adhere to the rules
described in chapter 9 for setting parameters when you enter these examples into the programmable
controller.
Note
If the programmable controller recognizes a parameter setting error in DB1, the
programmable controller remains in the STOP mode even after it has been switched
from STOP to RUN. The red LED is lit.
12.3.1 Setting the Clock in DB1
How to set the clock in DB1
1. Perform an overall reset on the programmable controller.
2. Generate DB5 with DW0 to DW21.
3. Output default DB1 to the programmer.
4. Overwrite the comment characters (#) with a blank space.
5. Use the cursor to jump to the CLP parameter block.
6. Enter the example.
- Set the clock to the following date: Monday, November 9, 1992, 15:30.
Setting the Clock
Explanation
36:
48:
KS
KS
='PGN 01 ; CLP: CF 0
='CLK DB5 DW0
STW
60:
KS
='MW102
STP Y SAV Y ';
72:
KS
='OHE N
SET 2 09.11.92 ';
84:
KS
='15:30:00
TIS 4
The clock data is stored in data block 5 beginning
with data word DW0. The status word is located in
flag word MW 102.
The clock is updated when the programmable
controller is in the STOP mode. The clock time is
saved in the clock data area. See Table 12-3.
After the SET parameter, enter the weekday, the
date, and the clock time you want the clock to use
when it begins running. Be certain to include the
blank spaces.
The clock runs in the 24-hour time mode since
you do not enter either AM or PM.
Figure 12-2. Example: Setting the Clock in DB1 to Monday, November 9, 1992, 15:30
7. Transfer the changed DB1 to the programmable controller.
8. Switch the programmable controller from STOP to RUN.
Each time the programmable controller is switched from STOP to RUN, it accepts the new clock
data.
12-5
S5-100U
12.3.2 Setting the Prompt Time in DB1
How to set the prompt time in DB1
5. Use the cursor to jump into the CLP parameter block.
- Set the clock to the following prompt time: Thursday, December 17, 1992, 8:00 o’clock.
Setting the Prompting Time
Explanation
36:
48:
KS
KS
='CLK DB5 DW0
STW
60:
KS
='MW102
84:
KS
='12:00:00
TIS 5
96:
KS
='17.12. 08:00:00 PM
OHS ';
STP Y SAV Y ';
flag word MW 102.
After the parameter for TIS, enter the weekday,
date and time to initiate the prompt time.
You can enter the parameter for the clock mode.
The clock runs in the 24-hour time mode.
Figure 12-3. Example: Setting the Prompt Time in DB1 to Thursday, December 17,
1992, 8:00 o’clock
data.
12-6
S5-100U
12.3.3
How to set the operating hours counter in DB1
- You are setting the start value for the operation hours counter to 1600 hours.
Explanation
36:
48:
KS
KS
='CLK DB5 DW0
STW
60:
KS
='MW102
STP Y SAV Y ';
72:
KS
='OHE Y
SET 4 01.04.92 ';
96:
KS
='01.04. 13:00:00
108:
KS
='001600:00:00
OHS ';
; SDP: WD';
flag word MW 102.
The operating hours counter is enabled.
After the OHS parameter, enter the start value for
the operating hours counter.
Figure 12-4. Setting the Operating Hours Counter in DB1 to 1600 Hours
Each time the programmable controller is changed from STOP to RUN, it accepts the new clock
data.
12.3.4
The exactness of the clock is temperature-dependent. You can configure a correction value to
increase the clock’s exactness. The correction value is output in s/month. You must measure how
many seconds per month the clock runs fast or slow. A month is defined as 30 days.
Example: Your measurements indicate the clock is 12 s too slow in 4 days. That would be 90 s
too slow in 30 days. The correction value is +90 s/month.
In addition to the changed clock parameters, enter the example into DB1 as follows:
Enter the Clock Time Correction Factor
36:
KS
='PGN 01 ;
CLP: CF +90
Explanation
The correction value of +90 s is loaded into the
clock.
Figure 12-5. Entering a Correction Factor of +90 s in DB1
12-7
12.4
S5-100U
You need only to change the default values in DB1 to program the clock in DB1. See section 12.2.
During start-up, the DB1 interpreter writes all information into the system data area.
TIP:
Do not attempt to set parameters in the system data, or to access directly from the user
program unless you have extensive knowledge of the system.
You must store the location of the clock data area in system data 8 and 9.
Data exchange between DB1 or the control program and the integral real-time clock is always
through the clock data area.
The integral real-time clock stores current time, date, and operating hours counter values in the
clock data area (flag area, data block, input area, or output area).
DB1 and the control program store the settings for prompt times and operating hours counters in
the same data area.
The control program can only read from or write to the clock data area. The control program can
never access the clock directly. Figure 12-6 illustrates the relationship between DB1 or the control
program, the clock data area, and the integral real-time clock.
Clock data area
Current clock
time/date
(words 0 to 3)
Settings
clock time/date
(words 4 to 7)
DB1/
Control
program
Prompt time
(words 8 to 11)
Integral realtime clock
Current operating
hours count
(words 12 to 14)
Settings operating
hours counter
(words 15 to 17)
Clock time/date of
the last switch from
RUN to STOP
(words 18 to 21)
Reading clock data
The clock writes clock data
Transferring settings
The clock accepts the settings
from the clock data area
Figure 12-6. How DB1 or the Control Program and the Clock Access the Clock Data Area
12-8
S5-100U
When you set the clock, you have to transfer only the data needed to implement a particular
function. For example, if you want to change only the clock function data, you do not have to enter
data for the time prompt function or for the operating hours counter.
The clock data area has the same structure wherever it is located: in the data block area, the flag
area, the input area, or the output area. Table 12-3 provides you with information about where
specific clock data is located within the clock data area. The explanations for Table 12.3 follow the
table.
Table 12-3. Clock Data in the Clock Data Area
Clock Data
Area
(Data Word)
Left Flag Word
Right Flag Word
Weekday
1
Day
Month
2
Year
AM/PM (Bit 7) Hour
3
Minute
Second
Leap year*
Weekday
Day
Month
6
Year
AM/PM (Bit 7)** Hour
7
Minute
Second
Weekday
9
Day
Month
10
AM/PM (Bit 7)**Hour
11
Minute
Second
Second
Minutes
Hour
Hours · 100
Hours · 10,000
Second
Minutes
Hours
Hours · 100
Hours · 10,000
Weekday
Day
Month
Year
Minute
Second
0
4
5
8
12
13
Meaning
Current clock
time/date
Settings for clock
time/date
Time prompt
Current operating
hours
14
15
16
Settings for
operating hours
counter
17
18
19
20
Clock time/date after
a switch from RUN to
STOP or Power OFF
(only if bit 5 in the
status word = 1)
21
Relevant when programming the clock in the user program (see Table 12-4)
Significant only in the 12-hour mode
Bit 7=1 means PM, bit 7=0 means AM
12-9
S5-100U
Make certain you are aware of the following points when you make inputs into the clock data area.
Entries into the clock data area must be in BCD code.
The clock runs either in the 12-hour mode or the 24-hour mode depending on how you set bit 1
in the status word. See section 12-5 for additional information.
The AM/PM flag (0 = AM, 1 = PM) is significant only for the 12-hour mode of the hardware
clock. The AM/PM flag corresponds to bit 7 in words 2, 6, 10, and 20.
In the 12-hour mode, you have to set the hours and the AM/PM flag for both the clock and
prompt functions.
In the 24-hour mode, if you set an AM/PM flag when you enter the values for the clock and
prompting time, then the program sets the relevant error bit.
Leap year settings are only relevant when the clock is programmed in the user program. If DB1
is used, the leap year settings are carried out automatically by the system.
The clock settings you enter must be within the range defined in Table 12-4.
Table 12-4.
Variable
Permissible Parameters
Variable
Seconds
0 to 59
Day
1 to 31
Minutes
0 to 59
Month
1 to 12
Hours
In the 24-hour mode:
0 to 23
In the 12-hour mode:
for AM: 1 to12
(12 = 12 o’clock noon)
for PM: 81 to 92
(81 = 1 o’clock PM)
0 to 999999 when
entering the operating
hours
Year
0 to 99
Leap Year
0 to 3
Weekday
12-10
1 to 7
1=Sunday
2=Monday
3=Tuesday
4=Wednesday
5=Thursday
6=Friday
7=Saturday
0 = Leap year is current
year
1 = Leap year was last year
2 = Leap year was two
years ago
3 = Leap year was three
years ago
S5-100U
If your inputs differ from the ones described, the operating system outputs error messages that are
displayed in the status word. The operating system resets error messages displayed in the status
word the next time you set the clock, prompt time, or the operating hours counter, if the new
settings are within the definition range. See section 12.5.
If you do not wish to modify one of the setting values, you can enter at its place XX (ASCII code) in
DB1, or FF (hexadecimal code) when you are programming in the system data.
If the clock data area is located at the end of other areas (flags, data blocks, inputs, and outputs)
and there is insufficient memory space available for the clock data area, the amount of clock data
transferred is only as much as will fit in the area available. Settings are not accepted if they lie
outside of the available space.
If clock data is located in the non-retentive flag area, then the following two events occur:
- All the settings are lost after Power OFF and cold restart.
- The time the last switch from RUN to STOP occurred is lost.
Remember that you can decide where to locate the clock data area. The word numbers listed in
Table 12-3 are relative.
- If your clock data area is located in a data block and does not begin with data word DW0 but
DWX, then you must add the value X to the word number shown in Table 12-3.
Example:
Your clock data area begins with DW124. The data for the time and date is then
stored in DW124 to DW127.
- If you locate your clock data area in the flag area beginning with flag word 0, then you must
multiply the appropriate data word number listed in Table 12-3 by a factor of 2 to obtain the
appropriate flag word address.
Example:
You locate your clock data area in the flag operand area beginning with flag
word 0. Data for the operating hours counter is then stored beginning with the
FW24 address.
- If your clock data area does not begin at flag word 0, you have to add the beginning value to
12-11
12.5
S5-100U
You can scan the status word to identify errors in the entered settings. You can deliberately change
certain bits in the status word to enable or disable transfer or read operations. You can use
designated flag bits to govern the clock’s behavior when the programmable controller is switched
from the RUN to the STOP mode or during Power OFF.
The status word can be located in the flag area or in a data block. You must define the location
of the status word in DB1 or directly in system data 9 and 10. See section 12.6.
The integral real-time clock runs independently of the set operating mode. Access to the clock
data area depends on the set operating mode and the signal states of bits 4 and 5 in the status
word. You can set or reset these bits using the “S” or “R” operations in the control program.
If you use an operator panel, such as the OP 396, to monitor the program, it is an
advantage to have the programmable controller update the clock time (the current date)
even in the STOP mode.
The operating system resets the “transfer settings” bits (bits 2, 10, and 14 in the status word)
under the following conditions.
The settings have been transferred.
The settings have not been transferred because they were outside of the permissible
range. The corresponding error bits (bits 0, 8, and 12 in the status word) are set.
The operating system does not reset the “transfer settings” bits (bits 2, 10, and 14 in the status
word) under the following conditions.
The clock data area is too small.
The system data for the clock is either incorrect or not available.
The clock is defective (hardware error).
There are four types of bits in the status word.
Clock flags
Operating system flags
Operating hours counter flags
Prompt time flags
12-12
S5-100U
Tables 12-5 through 12-8 provide you with information about the significance of the signal states of
the respective flags.
Clock Flags
Table 12-5.
Bit Number
Significance of Bits 0, 1, 2 and 3 of the Status Word
Signal State
Meaning
1
24-hour clock mode
1
Transfer settings
0
Do not transfer settings
1
The clock time can be read
0
3
12-hour clock mode
0
2
No error in setting entry
1
1
Error in setting entry
0
0
The clock time cannot be read
Operating System Flags
Table 12-6.
Operating
Mode
STOP
Bit Number
Status
Word
4
Signal
State
Meaning
1
The clock updates only words 0 to 3 (current time/date) in
the clock data area. You can set the clock by using the
FORCE VAR programmer function.
0
The clock does not update the clock data area. Words 0
to 3 contain the time at which the last switch from RUN to
STOP occurred.
1
Words 18 to 21 contain the time at which the last RUN to
STOP switch occurred or the time at which the last
Power OFF occurred if bit 4 is also set.
0
Words 18 to 21 are not used.
4
1/0
The clock continually updates the clock data area
(Words 0 to 17).
5
1
Words 18 to 21 contain the time at which the last switch
from RUN to STOP occurred or the time at which the last
Power OFF occurred.
0
5
RUN
12-13
S5-100U
Table 12-7.
Bit Number
Significance of the Operating Hours Counter Flags Bits 8, 9, and 10 of the
Status Word
Signal State
Meaning
1
Enable the operating hours counter
0
Disable the operating hours counter
1
Transfer the settings
0
10
1
9
0
8
Do not transfer the settings
Prompt Time Flags
Table 12-8.
Bit Number
12
13
14
Significance of the Prompt Time Flag Bits 12, 13, and 14 of the Status Word
Signal State
Meaning
1
0
1
The set prompting time is reached
0
The set prompting time is not reached
1
0
The operating system requires bit numbers 6, 7, 11, and 15. You can not use these bits.
Scanning the Status Word
In a data block, you can use the “P & lt; data word number & gt; & lt; bit number & gt; ” operation to scan the
individual bits of a data word. In the flag area, you can scan the individual bits if you enter the
& lt; byte address & gt; and the & lt; bit number & gt; .
Example: The status word is stored in DW13. You are checking to see if the set prompt time has
been reached. The “P D 13.13” instruction triggers a scan. If the status word is stored
in FW12, then the same scan would be “A F 12.5”.
Backup of the Hardware Clock
If there is a backup battery, the clock continues to run even after Power OFF. If the programmable
controller does not have a backup battery, the clock values will be set at “April 1, 1992, 12.00.00
o’clock, weekday: 4” when the clock is initialized after a Power ON. The default is the 24-hour time
mode. You should install a battery only during Power ON; otherwise, you would lose the clock data.
12-14
S5-100U
12.6
Setting Parameters for the Clock Data Area and the Status Word in
Table 12-9.
Absolute
Address RAM
System
Data Word
EA10
8
ASCII characters
I, Q, F, D
Start address for the clock data
Operand area D
Operand Areas I, Q, F
DB number
DB2 to DBFFH
Byte address
Relevant only for operand area D
DB word number
DW0 to DWFFH
Operand area for the status word
ASCII characters
I, Q, F, D
Start address for the status word
Operand area D
Operand areas I, Q, F
DB number
DB2 to DBFFH
Byte address
DB word number
DW0 to DWFFH
11
Status for hardware1
(only bits 0 and 1 are relevant)
• If either bit 0 or bit 1 is set, the
clock chip is defective
• If no bit is set, the clock chip is
running
“0”, “1”
11
Incorrect correction value?
(only bit 15 is relevant)
• If bit 15 is set, the correction value
is incorrect ( & gt; +400 or & lt; - 400)
• If bit 15 is not set, the correction
value is correct
“0”, “1”
12
Correction value2
- 400 to 400
9
EA13
EA14
10
EA15
EA16
EA16
EA18
Permissible
Parameters
Operand area for the clock data
EA11
EA12
Meaning
1 You can scan SD11 during start-up. You must call up an FB in OB21 or OB22 by using “L RS 11” to read
out and then continue processing SD11.
2 Always use the “L KF X” instruction to load the correction value in ACCU 1 since negative values can
also be specified.
12-15
S5-100U
The following section is intended to help you to start running the integral real-time clock as quickly
as possible by setting parameters in the system data. You need to be familiar with the clock data
area described in sections 12.4 and 12.5 in order to understand this section.
Note
The clock time is updated one second after the start of the next cycle.
Task:
You want to set the clock to the following values:
Wednesday, 12.02.92; 10:30:00
The status word is assigned to flag word FW12. Clock data is stored in DB75 beginning with DW0.
The two ways to transfer clock settings are as follows:
Use the STATUS VAR programmer function when the programmable controller is in the RUN
mode.
Use the FORCE VAR programmer function when the programmable controller is in the STOP
mode and status word bit 4 = 1.
The following example uses the first method. Proceed as follows:
1. Set the programmable controller to Power OFF.
2. Set the operating mode switch to STOP.
3. Set the programmable controller to Power ON.
4. Perform an overall reset on the programmable controller. See section 4.1.3.
5. Use the following program to program the programmable controller.
6. Set the operating mode switch to RUN.
The integral real-time clock is running.
Program Structure:
OB21
FB1
The system data is defined during the change from
STOP to RUN.
OB22
FB1
The system data is defined when the programmable
controller is switched on.
FB1
12-16
DB75
Set the new date and time.
S5-100U
The Block Entry Sequence and a Programming Example:
The following procedure is suggested:
1. Program FB1
- Defining system data for the integral real-time clock
2. Program OB21
- Calling up FB1 during a change from STOP to RUN
3. Program OB22
- Calling up FB1 when the programmable controller is switched on
4. Generate DB75
- Storing clock data
5. Transfer new data to the clock using the FORCE VAR programmer function (programmable
controller in the RUN mode) .
The respective programming examples are shown in Tables 12-10 to 12-14.
Table 12-10.
STL
FB1 Program
Meaning
Explanation
FB 1
NAME:
CLOCK
L KH
4 4 4 B
ASCII Code for the “D” character
Block number “75D”
T
Storing in system data word 8
RS 8
Clock data is
located in
DB75
beginning
with DW0
DW0 is the start address for clock data
L KH
0 0 4 D
ASCII Code for the “M” Character
T
Storing in system data word 9
RS 9
Flag word Number “12D”
L KH
0 C
The status
word is
located in
FW12
0 0
ASCII Code is irrelevant
T
RS 10
Storing in system data word 10
BE
12-17
S5-100U
Table 12-11.
STL
OB 21
JU FB 1
NAME:
CLOCK
OB21 Program
Explanation
The function block is called up once during a switch from STOP to
RUN.
BE
Table 12-12.
STL
OB 22
JU FB 1
NAME:
CLOCK
OB22 Program
Explanation
The function block is called up once when the programmable
BE
Table 12-13.
STL
DB 75
0: KH = 0000;
1: KH = 0000;
2:
3:
4:
KH = 0000;
KH = 0000;
KH = 0000;
5:
6:
7:
DB75 Program
Explanation
Define the number of data words. (Data words 0 to 7 are used in
the example. See Table 12-3) . Define the numerical
representation. Hex is used in the examples.
KH = 0000;
KH = 0000;
KH = 0000
12-18
S5-100U
Reading and Setting the Time and Date
After you enter the program, you can test it as follows.
1. Switch the programmable controller to the RUN mode.
2. Use the FORCE VAR programmer function to enter the following.
Data block number
Data words DW0 to DW7
Clock data
Status word
Table 12-14.
Operand
FORCE VAR Function
Signal States
Explanation
DB 75
DW 0
KH = 0003
DW 1
DW 2
DW 3
KH = 0110
KH = 9112
KH = 0000
DW 4
DW 5
DW 6
KH = 0002
KH = 0212
KH = 9210
DW 7
KH = 3000
FW 12
KM = 00000000 00000100
Tuesday
October 1
1991, 12 o’clock
(reading current clock data)
Monday
December 2
1992, 10.30 o’clock
(writing new settings)
If you set bit 2 in the status word to
“1”, the new settings are transferred
to the clock.
3. Begin status processing by pressing the ENTER key twice. Bit 2 in the status word is reset. The
clock runs with the new settings
Note
Besides using the method described in Table 12-14 (with the FORCE VAR function), you
can also enter the new settings directly into the data block. In that case, store the new
settings in data words DW4 to DW7 of data block DB75.
See Table 12-13.
EWA 4NEB 812 6120-02b
12-19
S5-100U
Write the settings into the
clock data area
Set transfer bit 2 in the
control program
Wait approximately two seconds
(entering a wait program)
Possible errors:
- Clock is not
available.
- Clock system data
is incorrect or not
available.
- Clock data area is
too small.
- Clock is defective.
yes
Status Word
Bit 2=1
no
Status Word
Bit 0=1
yes
Incorrect settings
no
The clock cannot be
used.
Eliminate the errors.
The clock runs with
the new settings.
The clock continues
running with the old
values.
* The lower portion of the flowchart has only a diagnostic function. There is nothing you must perform.
You can also implement the upper portion of the flowchart using the FORCE VAR programmer function
(programmable controller in the RUN mode) or using the FORCE function (the programmable controller
is in the STOP mode and bit 4 = 1 in the status word).
Figure 12-7. Flowchart - Transferring Time and Date Settings to the Clock
If you do not want a value (for example the minutes) in the settings to be transferred, enter the value
for relevant byte as either 255D or FFH. When you set the clock, the old value present in the clock is
retained.
Incorrect settings are displayed by a set bit 0 in the status word. The clock continues to run with the
old values.
In a similar manner, you can program new settings for the time prompt function and the operating
hours counter. However, the settings are located in other data words in the clock data area. See
section 12-4. You must set the respective bit to 1 in the status word so that the clock can accept
the new settings. See section 12-5.
12-20
S5-100U
12.7
Programming the Integral Real-Time Clock in the User Program
The programming of the clock in the user program should be performed only by users with extensive
knowledge of the system. For all other users, use of DB1 is recommended (see sections 12.2
and 12.3).
The following section provides you with information on how to access the clock through the user
program.
12.7.1 Reading and Setting the Clock
Example:
Program for setting the time and date
Transfer of the settings for the time and date is triggered by input I 0.0. Before you set input I 0.0
(see OB1), you must transfer these settings to flag bytes FY120 to FY127. Values that you do not
want to change must be preset with “FFH”. You can define the clock mode with input I 1.0(1= 12hour mode). Input I 0.1 is the AM/PM bit that you use for setting the 12-hour mode.
The clock data area is in DB2 beginning with DW0, and the status word is FW10.
OB1 STL
Explanation
SETTING THE TIME AND DATE
FIRST TRANSFER TIME AND DATE VALUES
INTO FB120 TO FB127.
:A
:S
:JU
I
F
FB
0.0
20.0
10
CLOCK SETTING TRIGGERED
BY SETTING F 20.0 (RESET IN FB10)
WDAY :
FY 121
DAY :
FY 122
(SETTING THE TIME AND DATE)
WEEKDAY
DAY
MON :
YEAR :
HOUR :
FY 123
FY 124
FY 125
MONTH
YEAR
HOUR
AMPM
MIN
SEC
ERR
I
0.1
FY 126
FY 127
F
12.1
AMPM-BIT (ONLY IMPORTANT IN 12-HOUR MODE)
MINUTES
SECONDS
ERROR BIT
I
12-HOUR MODE: I 1.0 = 1
MODE :
:BE
1.0
12-21
S5-100U
FB10 STL
Description
SETTING THE CLOCK
DES
DES
DES
:WDAY
:DAY
:MON
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
BI/BY/W/D: BY
BI/BY/W/D: BY
BI/BY/W/D: BY
DES
DES
DES
:YEAR
:HOUR
:AMPM
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
BI/BY/W/D: BY
BI/BY/W/D: BY
BI/BY/W/D: BI
DES
DES
DES
:MIN
:SEC
:ERR
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
I/Q/D/B/T/C: Q
BI/BY/W/D: BY
BI/BY/W/D: BY
BI/BY/W/D: BI
DES
:MODE
I/Q/D/B/T/C: I
BI/BY/W/D: BI
:A
=MODE
24HR-MODE = 0, 12HR-MODE = 1
:AN
:JC
F
11.1
F
20.0
=M001
(CLOCK MODE STATUS WORD BIT 1)
FLAG IS RESET IF SETTINGS ALREADY
READ INTO CLOCK DATA AREA
:R
:C
F
20.0
DB
2
:L
:T
:L
=WDAY
DR
4
=DAY
:T
:L
:T
DR
5
=MON
DR
5
:L
:T
:L
= YEAR
DL
6
=HOUR
STORE VALUE FOR YEAR
:ON
:ON
:JC
=AMPM
=MODE
=MORN
IF 12-HOUR MODE IS SET, AND
AM/PM BIT = 1 (AFTERNOON), THE
RELEVANT BIT IN THE CLOCK AREA
KH 0080
IS SET
:L
:OW
MORN :T
DR
CLOCK DATA AREA
STORE VALUE FOR WEEKDAY
STORE VALUE FOR DAY
STORE VALUE FOR MONTH
STORE VALUE FOR HOUR
6
:L
:T
:L
:T
=MIN
DL
7
=SEC
DR
7
STORE VALUE FOR MINUTES
:AN
:S
:L
F
11.2
F
11.2
KT 020.1
TRANSFER SETTINGS
(STATUS WORD IS FW10)
START MONITORING TIME
:SE T
M001 :A
T
:BEC
10
10
STORE VALUE FOR SECONDS
BEC, IF MONITORING TIME
NOT YET ELAPSED
12-22
S5-100U
FB10 STL (continued)
:AN
F
11.2
:JC =M002
:S
=ERR
:BEU
M002 :AN F
11.0
:RB =ERR
:BEC
:S
=ERR
Explanation
HAVE SETTINGS BEEN TRANSFERRED?
IF YES, JUMP TO M002
SET ERROR BIT IF THERE ARE ERRORS
WERE THERE ERRORS WHILE ENTERING SETTINGS?
IF NO, RESET ERROR BIT
IF NO ERROR, THEN BEC
IF AN ERROR, SET ERROR BIT
:BE
Example:
Program for reading the current time and the current date
The time is stored in flag bytes FY30 to FY36, depending on an external event, simulated here by a
positive edge at input I 0.5. Flag F 13.1 indicates which mode the clock is operating in. Flag F 13.0
is the AM/PM bit in the 12-hour mode
OB1 STL
Explanation
:A
I
0.5
READING TIME AND DATE
TIME AND DATE ARE
:AN
:A
F
F
I
0.1
0.0
32.5
STORED IN FY30 TO FY36 IN CASE OF A
POSITIVE EDGE AT I 32.5.
(EXTERNAL EVENT)
:A
F
0.1
F
0.0
EDGE TRIGGER FLAG
:JC FB 13
WDAY :
FY 30
(READING TIME AND DATE)
WEEKDAY
DAY :
MON :
YEAR :
FY
FY
FY
31
32
33
DAY
MONTH
YEAR
HOUR :
AMPM :
MIN :
FY
F
FY
34
13.0
35
HOUR
F 13.0 = 1, AFTERNOON IN 12H-MODE
MINUTES
SEC :
MODE :
:BE
FY
F
36
13.1
SECONDS
F 13.1 = 1, IN 12-HOUR MODE
12-23
S5-100U
FB13 STL
Explanation
READING THE CLOCK
DES
DES
DES
:WDAY
:DAY
:MON
I/Q/D/B/T/C:
I/Q/D/B/T/C:
I/Q/D/B/T/C:
Q
Q
Q
BI/BY/W/D/:BY
BI/BY/W/D/:BY
BI/BY/W/D/:BY
DES
DES
DES
:YEAR
:HOUR
:AMPM
I/Q/D/B/T/C:
I/Q/D/B/T/C:
I/Q/D/B/T/C:
Q
Q
Q
BI/BY/W/D/:BY
BI/BY/W/D/:BY
BI/BY/W/D/:BI
DES
DES
DES
:MIN
:SEC
:MODE
I/Q/D/B/T/C:
I/Q/D/B/T/C:
I/Q/D/B/T/C:
Q
Q
Q
BI/BY/W/D/:BY
BI/BY/W/D/:BY
BI/BY/W/D/:BI
:C
DR
0
=WDAY
DL
1
:T
:L
:T
=DAY
DR
1
=MON
:L
:T
:L
DL
2
=YEAR
DR
2
YEAR
:L
:AW
:T
KH 007F
ERASE AM/PM BIT
(ONLY RELEVANT IN 12-HOUR MODE)
:TB
:L
D
2.7
=AMPM
DL
3
DISPLAY AM/PM BIT
MINUTE
:T
:L
:T
=MIN
DR
3
=SEC
SECOND
:A
:BE
12-24
DB
:L
:T
:L
2
F
11.1
=MODE
DISPLAY CLOCK MODE
MODE = 1, IN 12-HOUR MODE
WEEKDAY
DAY
MONTH
HOUR
=HOUR
S5-100U
Storing the Updated Time/Date after a RUN to STOP Switch
Note
This clock data area is only written to if the following requirements are met.
• Bit 5 in the status word is set to “1”.
• A RUN to STOP switch or a Power OFF has taken place.
• The necessary memory space is available in the operand area.
This enables you to detect a RUN to STOP switch or a Power OFF even if the programmable
controller has since gone back to RUN mode. The time and date of the last RUN to STOP switch or
Power OFF are in words 18 to 21 (see Table 12-3)
If several RUN to STOP switches have occurred before you read out this clock data area, you will
only be able to determine the time of the last switch.
If you do not have sufficient memory for this clock data area, you either cannot use this area or use
only part of it. This has no impact on anything else.
12.7.2 Programming the Prompt Function
Transferring Settings to the Clock
You can store the settings in the clock data area by using transfer operations (see Table 12-3).
The AM/PM flag (bit number 7) is only significant in 12-hour mode.
Bit 7=1 means PM
Bit 7=0 means AM
You must transfer the clock data in BCD code.
TIP: The “KC” data format loads a BCD constant into ACCU 1 and is therefore especially
suitable.
If you enter the value “255D” or “FFH” in a byte as the prompt time, this byte will be ignored
when evaluating “Prompt time reached”. This makes it easy to program, for example, an alarm
that is repeated daily by entering the value in the “255D” or “FFH”in the “Weekday”, “Date”
and “Month” settings.
You can transfer the prompt time settings to the clock by initiating bit 14 in the status word.
The settings are transferred 1 second after the start of the next cycle.
Bit 12 in the status word displays incorrect settings.
12-25
S5-100U
the clock data area
Set transfer bit 14
Wait about two seconds
(entering wait program)
Possible errors:
- Clock is not
available.
- Clock system data
is incorrect or not
available.
too small.
yes
Bit 14=1
no
yes
Bit 12=1
Settings
incorrect
no
The clock cannot
be used.
Correct the error.
Clock runs with
the new settings
for prompt time.
Prompt time
function is turned
off.
The lower part of the flow chart has only a diagnostic function.
Figure 12-8. Flowchart - Transferring a New Prompt Time
12-26
S5-100U
Prompt Time Sequence
Bit 13 in the status word is set after the prompt time has elapsed.
Bit 13 remains set until you reset it in the control program.
The prompt time can be read at any time.
Caution
If the prompt time is reached in the STOP mode or during Power OFF, the prompt time
cannot be evaluated. It is always deleted on restart.
Example:
Setting and evaluating the prompt time
In the example program, the status of input I 0.6 determines whether the settings for the prompt time
are transferred. Before setting input I 0.6, you must transfer the settings to flag bytes FY130 and
FY135. Enter values that you do not wish to be evaluated as FFH.
You set the clock mode with input I 1.0. Use input I 0.1 to specify the the AM/PM bit for 12-hour
mode.
If the preset prompt time has been reached, set flag F 13.2. If errors are made while entering the
prompt time, the error bit, flag F 12.2, is set.
The clock data is stored in DB2 beginning with data word DW0, and the status word is flag word
FW10.
OB1 STL
Explanation
SETTING AND EVALUATING THE PROMPT TIME
LOAD VALUES INTO FY130 TO FY135
FIRST.
:A
:S
:JU
I
F
FB
0.6
20.1
11
TRIGGER SETTING OF PROMPT TIME
BY SETTING F 20.1 (RESET IN FB11)
NAME :SET PROMPT TIME
WDAY :
FY 130
DAY :
FY 131
(SET AND EVALUATING PROMPT TIME)
WEEKDAY
DAY
MON :
HOUR :
AMPM :
FY 132
FY 133
I
0.1
MONTH
HOUR
MIN
SEC
ERR
FY 134
FY 135
F
12.2
MINUTES
SECONDS
ERROR BIT
F
I
DISPLAYS THAT PROMPT TIME IS REACHED.
12-HOUR MODE: I 33.0 = 1
ALRM :
MODE :
:BE
13.2
1.0
12-27
S5-100U
FB11 STL
Explanation
SETTING THE PROMPT TIME
DES
DES
DES
:WDAY
:DATE
:MON
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
BI/BY/W/D: BY
BI/BY/W/D: BY
BI/BY/W/D: BY
DES
DES
DES
:HOUR
:AMPM
:MIN
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
I/Q/D/B/T/C: I
BI/BY/W/D: BY
BI/BY/W/D: BI
BI/BY/W/D: BY
DES
DES
DES
:SEC
:ERR
:ALRM
I/Q/D/B/T/C: I
I/Q/D/B/T/C: Q
I/Q/D/B/T/C: Q
BI/BY/W/D: BY
BI/BY/W/D: BI
BI/BY/W/D: BI
DES
:MODE
I/Q/D/B/T/C: I
BI/BY/W/D: BI
:A
24 HOUR MODE = 0, 12 HOUR = 1
F
11.1
F
10.5
=ALRM
(SET CLOCK MODE)
DISPLAY PROMPT TIME REACHED
(BIT 13 IN STATUS WORD)
:R
:AN
F
10.5
RESET BIT AFTER EVALUATION
F
20.1
FLAG IS RESET IF SETTINGS HAVE ALREADY
:JC
:R
=M001
F
20.1
BEEN READ INTO THE CLOCK DATA AREA
:C
:L
:T
DB
2
=WDAY
DR
8
CLOCK DATA AREA
:L
:T
:L
=DAY
DL
9
=MON
STORE VALUE FOR DATE
:T
12-28
=MODE
:A
:S
DR
9
S5-100U
FB11 STL (continued)
Description
:L
:ON
=HOUR
=AMPM
STORE VALUE FOR HOURS
IF AM/PM = 1 (AFTERNOON) AND
:ON
:JC
:L
=MODE
=MORN
KH 0080
12-HOUR MODE IS SET, THE
CORRESPONDING BIT IN THE CLOCK
DATA AREA IS SET
DR 10
=MIN
:OW
MORN :T
:L
:T
:L
:T
DL 11
=SEC
DR 11
:AN
:S
:L
F
10.6
F
10.6
KT 020.1
TRANSFER SETTINGS
(BIT 14 IN STATUS WORD FW10)
:SE T
M001 :A
T
:BEC
11
11
:AN F
10.6
:JC =M002
:S
=ERR
:BEU
M002 :AN F
10.4
:RB =ERR
:BEC
:S
:BE
=ERR
BEC, IF MONITORING TIME NOT YET
ELAPSED
IF ERROR, SET ERROR BIT
ERROR WHEN ENTERING SETTINGS?
BEC, IF NO ERROR
12-29
S5-100U
12.7.3 Programming the Operating Hours Counter
You can enable the operating hours counter with bit 9 of the status word. This allows you to
establish, for example, the number of hours a motor has been in operation. The operating hours
counter is active only in the RUN mode.
You can preset the operating hours counter with a certain start value (e.g. after exchanging the
CPU).
The clock data must be transferred in BCD code.
suitable for entering the settings.
If you do not want a value (for example minutes) to be transferred, entering the relevant byte as
“255D” or “FFH”. The current value for this variable is then retained.
After you have transferred the settings to the clock data area, you must set bit 10 in the status
word for the clock to accept the clock data.
Bit 8 in the status word displays incorrect settings.
12-30
S5-100U
the clock data area
Set transfer bit 10
Possible errors:
- Clock is not
available.
- Clock system data
is incorrect or not
available.
too small.
yes
Status word
Bit 10=1
no
Status word
Bit 8=1
yes
Settings
incorrect
no
The operating
hours counter
cannot be used.
Correct the errors.
The operating
hours counter
runs with the new
settings.
The operating
hours counter
continues to run
with old values.
* The lower part of the flow chart has only a diagnostic function.
Figure 12-9. Flowchart - Transferring Settings to the Operating Hours Counter
12-31
S5-100U
Example: Setting the operating hours counter
The status of input I 0.7 determines whether the operating hours counter values are transferred.
You must transfer these values to flag bytes FY136 to FY140 before setting input I 0.7 (not
implemented in the example program). Values that are not to be changed should be preset
with FFH.
Errors are displayed in flag F 12.3. The clock data area is in data block DB2 beginning with data
word DW0, and the status word is flag word FW10.
OB1 STL
Explanation
SETTING THE OPERATING HOURS COUNTER
:A
LOAD VALUES INTO FY136 TO FY140
I
:S
F
:JU FB
0.7
TRIGGER TRANSFER OF SETTINGS FOR
20.2
OPERATING HOURS COUNTER BY SETTING
F 20.2
12
NAME :SET OPER. HOURS COUNTER
SEC :
FY 136
MIN :
FY 137
(SETTING THE OPERATING HOURS COUNTER)
SECONDS
MINUTES
HOUR0:
HOUR2:
HOUR4:
FY 138
FY 139
FY 140
HOURS
HOURS X 100
ERRORS X 10000
ERR
F
ERROR BIT
12-32
:BE
12.3
S5-100U
FB12 STL
Explanation
DES
DES
DES
:SEC
:MIN
:HOUR0
I/Q/D/B/T/C:
I/Q/D/B/T/C:
I/Q/D/B/T/C:
I
I
I
BI/BY/W/D:
BI/BY/W/D:
BI/BY/W/D:
BY
BY
BY
DES
DES
DES
:HOUR2
:HOUR4
:ERR
I/Q/D/B/T/C:
I/Q/D/B/T/C:
I/Q/D/B/T/C:
I
I
Q
BI/BY/W/D:
BI/BY/W/D:
BI/BY/W/D:
BY
BY
BI
:AN
:JC
F
20.2
=M001
ALREADY READ INTO THE
:R
:C
F
20.2
CLOCK DATA AREA
DB
2
CLOCK DATA AREA
:L
:T
:L
=SEC
DR 15
=MIN
:T
:L
:T
DL 16
=HOUR0
DR 16
:L
:T
:L
=HOUR2
DL 17
=HOUR4
:T
:AN
:S
DR
F
F
17
10.2
10.2
:S
:L
F
10.1
KT 020.1
:SE T
M001 :A
T
:BEC
:AN F
12
12
10.2
:JC =M002
:S
=ERR
:BEU
M002 :AN F
10.0
:RB =ERR
:BEC
:S
:BE
=ERR
STORE VALUE FOR HOURS X 100
STORE VALUE FOR HOURS X 1000
TRANSFER SETTINGS
(BIT 10 IN STATUS WORD FW 10)
ENABLE OPERATING HOURS COUNTER
IF NOT ALREADY ENABLED
BEC IF MONITORING TIME NOT YET
ELAPSED
BEC IF NO ERROR
12-33
S5-100U
Reading the Current Operating Hours Counter
The current data is stored in words 12 to 14 of the clock data area. You can use load operations to
read out the data.
Example:
Reading the operating hours counter
You need to switch off a machine for inspection after every 300 hours of operation. Flag F 12.4 is
set when the machine is switched off. After 300 hours of operation, a jump is made to PB5 to switch
the machine off (not programmed in the example).
The clock data area is in DB2 beginning with flag word FW0, and the status word is flag word FW10.
OB1 STL
:JU FB 14
Explanation
EVALUATE OPERATING HOURS COUNTER
:BE
FB14 STL
:C
:A
DB
F
:BEC
:L
DL
Explanation
READING THE OPERATING HOURS COUNTER
2
12.4
DB IN WHICH THE CLOCK DATA IS LOCATED.
IF AUXILIARY FLAG 12.4 IS SET, OFF.
14
THE MACHINE IS ALREADY
BLOCK END
LOAD HOUR VALUE X 100 IN ACCU 1
:L
KC 003
: & gt; & lt; F
COMPARE TO 3 (=300 HOURS)
:BEC
:S
F
END IF 300 HOURS NOT YET
REACHED
SET AUXILIARY FLAG
:JU
PB
12.4
5
JUMP TO PB5 WHEN 300 OPERATING
HOURS REACHED
:BE
12-34
S5-100U
12.7.4 Entering the Clock Time Correction Factor
You can configure a correction value that increases the exactness of the integral real-time clock.
The correction value is displayed in seconds/month. The month is defined as 30 days.
Absolute Address
RAM Memory
EA 18
Example:
Range
- 400D to + 400D
System Data Word
seconds/month
12
You determined that the clock runs 12 seconds slow in a four day period. That would
be 90 seconds in 30 days. The correction value is+ 90 seconds/month.
Note
Use the data KF format to enter the correction value. You then do not have to convert
the value to other numbering systems.
STL
FB10
L
KF
T
RS
+ 90
12
Explanation
LOAD THE + 90 SECONDS CORRECTION VALUE INTO ACCU 1 AND STORE IT
IN SYSTEM DATA WORD 12.
BE
Note
The correction value you have entered is read in after the next minute change. If an
error occurs when a setting is entered, bit 15 in system data word 11 is set.
12-35
13
Connecting the S5-100U to SINEC L1, for CPU 102 and Higher
13.1
Connecting the Programmable Controllers to the
L1 Bus Cable . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
13 - 1
13.2
Setting Parameters in the Programmable Controller
for Exchanging Data . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
13.2.1 How to Program in a Function Block, for CPU 102 and Higher . . . .
13.2.2 Setting Parameters in DB1, for CPU 103 and Higher . . . . . . . . . . .
13 - 1
13 - 2
13 - 5
13.3
13.3.1
13.3.2
13.3.3
13
13
13
13
Coordinating Data Exchange in the Control Program . . . . . . . . . . .
Sending Data . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Receiving Data . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming the Messages in a Function Block . . . . . . . . . . . . . .
7
8
9
11
Figures
13-1
13-2
13-3
13-4
13-5
13-6
13-7
13-8
13-9
Connection of the Bus Cable . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming Example for Setting Parameters in FB1 . . . . . . . . . . . . . . . .
Data Exchange between Sender and Receiver (Principle) . . . . . . . . . . . . .
Structure of the Send Mailbox . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Structure of the Coordination Byte Send (KBS) . . . . . . . . . . . . . . . . . . . .
Structure of the Receive Mailbox . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Structure of the Coordination Byte Receive (KBE) . . . . . . . . . . . . . . . . . .
Organization of Program Execution . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Programming “Message Processing” in FB2 . . . . . . . . . . . . . . . . . . . . . .
13
13
13
13
13
13
13
13
13
1
4
7
8
8
9
10
11
12
Tables
13-1 SINEC L1 Parameter Block . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
13-2 Setting Parameters in the Coordination Byte . . . . . . . . . . . . . . . . . . . . . .
13-3 Setting Parameters for the SINEC L1 Interface . . . . . . . . . . . . . . . . . . . . .
13 - 2
13 - 3
13 - 6
S5-100U
13
SINEC L1 is a local area network that enables SIMATIC S5 programmable controllers to communicate with each other. This option is available when you are using CPU 102 or higher. It operates
on the master-slave principle.
You will find more exact information on the SINEC L1 in the SINEC L1 manual. You need to
understand the SINEC L1 operating system before continuing with this chapter.
The S5-100U can be connected directly to the SINEC L1 as a slave. The information you need to
perform this operation is explained in this chapter.
13.1
Connecting the Programmable Controller to the L1 Bus Cable
Bus terminal BT 777 is the signal level converter that connects the programmable controller to the
L1 bus cable. The procedure is as follows:
1. Connect the L1 bus cable to bus terminal BT 777.
0A
0B
0A
0B
0A
0B
1A
1B
1A
1B
1A
1B
2A
2B
2A
2B
2A
2B
3A
3B
3A
3B
3A
3B
4A
4B
4A
4B
4A
4B
Figure 13-1. Connection of the Bus Cable
2. Insert the connector of the bus terminal cable into the PG/OP/SINEC L1 port.
13.2
Setting Parameters in the Programmable Controller for Exchanging
Data
The programmable controller requires the following information for the handling of data exchange via
the L1 bus:
Location of the data to be sent (data block or flag area)
Name: Send Mailbox, abbreviated: SF
Location of the data to be received (data block or flag area)
Name: Receive Mailbox, abbreviated: EF
Storage location of the coordinating information for sending data (e.g., the message:
“Send Mailbox is enabled”)
Name: Coordination Byte Send, abbreviated: KBS
13-1
S5-100U
Storage location of the coordinating information for receiving data (e.g., the message:
“Receiving data can be read”)
Name: Coordination Byte Receive, abbreviated: KBE
Programmer number (necessary if you want to transmit programmer functions over the SINEC
L1 local area network), abbreviated: PGN
You can set parameters for the programmable controller for the CPU 102 in the function block, and
for the CPU 103 version 8MA03 in the integrated data block (DB1).
You can program the SINEC L1 local area network by first setting the parameters and then
programming the “messages” in the control program (see section 13.3.3)
Setting Parameters in the Function Block
You must define the following in the program:
Your own programmer number for the programmer bus functions
Your own slave number
The data or flag areas reserved by the send and receive mailboxes
The location of the coordination bytes
You program in the function block by calling up one of the two restart organization blocks (OB21 or
OB22). You store the corresponding parameters in the system data area of the programmable
controller by using the “TNB” block transfer statement. The SINEC L1 parameter block begins at
system data word 57.
Table 13-1. SINEC L1 Parameter Block
System Data
Word
High Byte
Low Byte
Address in
System Data Area
SD57
Programmer number
(1 through 30)
Slave number
(1 through 30)
EA72H
EA73H
SD58
KBE
Data identifier
KBE
DB or flag byte
EA74H
EA75H
SD59
KBE
Data word
KBS
Data identifier
EA76H
EA77H
SD60
KBS
DB or flag byte
KBS
Data word
EA78H
EA79H
SD61
SF
Data identifier
SF
DB or flag byte
EA7AH
EA7BH
SD62
SF
Data word
EF
Data identifier
EA7CH
EA7DH
SD63
EF
DB or flag byte
EF
Data word
EA7EH
EA7FH
You define the position of the coordination bytes and the starting addresses of the send and receive
mailboxes in each case by three bytes.
13-2
S5-100U
Table 13-2. Setting Parameters in the Coordination Byte
Meaning
Parameters
Address in System Data Area
“Flag” data identifier
(“F”) 4D
EA74H
Flag byte
0 to 127
EA75H
EA76H
“Data word” identifier
(“D”) 44
EA77H
Data block
2 to 63
EA78H
Data word
0 to 255
EA79H
The data identifier is in ASCII code.
Overflow
If data packets longer than 64 bytes are received, the information is not written beyond the end of
the receive mailbox. There is no overflow message. The end of the receive mailbox is flag byte
127 in the flag area or the last present data word (in the data block).
Example:
Setting parameters in the S5-100U as slave 1 in function block 1
Definitions:
“Receive” coordination byte (KBE)
Flag byte
FY100
“Send” coordination byte (KBS)
Flag byte
FY101
Send mailbox (SF)
Data block
DB2 from DW0
Receive mailbox (EF)
Data block
DB3 from DW0
Flag bytes FY 64 to 77 are used as buffer areas.
13-3
STL
S5-100U
Explanation
L
KF
1
- Load slave number and
T
L
T
FY
KH
FW
65
4D00
66
L
T
L
KY
FW
KH
100,0
67
4D00
T
L
T
FW
KY
FW
69
101,0
70
L
T
L
KH
FW
KY
4400
72
2,0
T
L
T
FW
KH
FW
73
4400
75
L
T
KY
FW
3,0
76
L
L
KH
KH
EE4D
EA7F
store it in flag byte 65
- Load “Flag” data identifier and store it
in flag byte 66
- Load flag byte 100 and store it
in flag byte 67
in flag byte 69
- Load flag byte 101 and store it
in flag byte 70
- Load “Data word” identifier and store it
in flag byte 72
- Store DB number “2” and DW number “0”
in flag bytes 73 and 74
in flag byte 75
- Store DB number “3” and DW “0”
in flag bytes 76 and 77
- Transfer flag area FY64 to 67 to the system
data area:
- Load upper source address
- Load upper destination address
- Transfer a block of data 14 bytes long
Erase all buffer areas
- Load hexadecimal number “0000”
- Set all bits of FY64 to 77 to “0”
TNB
14
L
KH
0000
T
T
T
T
FW
FW
FW
FW
64
66
68
70
T
T
T
FW
FW
FW
72
74
76
L
KH
0080
T
FY
100
L
T
BE
KH
FY
0000
101
Default setting of the KBE;
Data can be received from the bus.
- Load binary number 1000 0000
- Set bit 7 to “1” and bits 6 to 0 to “0”
Default setting of the KBS;
Program has access to the send mailbox
- Load binary number 0000 0000
- Set bits 7 to 0 to “0”
Block end
Figure 13-2. Programming Example for Setting Parameters in FB1
13-4
S5-100U
Set the parameters in DB1 as follows:
1. Display the default DB1 on the programmer (Transfer function, source: PC, target: FD (PG)
- A default DB1 is integrated into the programmable controller's operating system; it contains
default parameters for the data exchange via SINEC L1.
2. Look for the SINEC L1 parameter block with the block ID “SL1:” for the PG/OP/SINEC L1 port.
3. Overwrite the comment character (#) with a space.
SL1:
SLN 1
PGN 1
Beginning of the L1 parameter block
for PG/ OP/ SINEC L1 port
Last parameter
4. Edit the default parameters according to your requirements. Do not change the syntax.
Example:
The S5-100U participates in the SINEC L1 network as a slave with the slave number 2.
Send Mailbox (SF) in DB2 beginning with data word 0
Receive Mailbox (EF) in DB2 beginning with data word 10
Coordination Byte Send (KBS) is flag byte 0 (MB0)
Coordination Byte Receive (KBE) is flag byte 2 (MB2)
Programmer bus number (PGN) is 1.
13-5
S5-100U
Table 13-3 shows how to change default parameters for the example given above and which
parameter settings are permitted.
Table 13-3. Setting Parameters for the SINEC L1 Interface
Default DB1:
Block: SINEC L1 to
PG/ OP/ SINEC L1
Port
Explanation
Modifications
Necessary for the
Example
Valid
Parameters for
CPU 103 and
Higher
SL1:
Block ID “SINEC L1 to
Interface SL1”
no modification
necessary
SLN 1
Slave number of the
PLC; default to 1
SLN 2
Location of the Send
Mailbox; default
beginning with DW0
SF DB2DW0
SF DB2DW0
SLN x
(x=1 to 30)
SF DBxDWy
(x=2 to 255;
y=0 to 255) or
SF MBz
(z=0 to 255)
EF DB3DW0
Location of the
Receive Mailbox;
default location: DB3
beginning with DW0
EF DB2DW10
EF DBxDWy
(X=2 to 255;
y=0 to 255) or
EF MBz
(z=0 to 255)
KBE MB100
KBS MB101
PGN 1
Location of the
Coordination Byte
Receive; default
location flag byte 100
(MB100)
KBE MB2
Location of the
Coordination Byte
Send; default location
flag byte 101 (MB101)
KBS MB0
Programmer bus number (necessary if you
want to transmit
over SINEC L1;
default 1)
PGN 1
PGN x
no modification
necessary
(x=1 to 30)
KBE MBx
(x=0 to 255)
or
KBE DByDWx*
(y=2 to 255;
z=0 to 255)
KBS MBx
(x=0 to 255)
or
KBS DByDWz*
(y=2 to 255;
z=0 to 255)
The KBE/KBS is in the high-order byte of the given data word.
13-6
S5-100U
5. Transfer the changed DB1 to the programmable controller. The default DB1 is overwritten.
If you now go from STOP to RUN or from Power OFF to Power ON (with a battery inserted), the
programmable controller accepts the changed parameters and stores them in the system data area.
13.3
After you set the parameters, the control program for data exchange has to be created. The control
program relies on the coordination information that the operating system makes available in the
coordination bytes (see Figure 13-3).
Sender (source)
Receive (destination)
RAM
RAM
KBS
KBE
KBS
KBE
Control program
for data exchange
Control program
for data exchange
Send Mailbox
Receive Mailbox
Data
area or
flag area
Send Mailbox
Receive Mailbox
Data
area or
flag area
L1 bus
Figure 13-3.
In the following paragraphs, you will learn how to control the sending and receiving of data after you
have set the parameters in DB1.
There is an example in section 13.3.3 of how you must program the data exchange in a function
block.
13-7
S5-100U
13.3.1 Sending Data
The prerequisites for sending data are as follows:
The parameters are set in DB1 for the location of the Send Mailbox (see section 13.2.2).
The data to be sent, additional information (length of the send data “net data”), and destination
slave number are then transferred to the Send Mailbox.
Figure 13-4 shows which information has to be stored in what part of the Send Mailbox.
Example:
Example:
Send Mailbox in the flag area
(beginning with flag byte 1)
Send Mailbox in the data block
(beginning with data word DW1)
DL
DR
Flag byte 1
Length of the “net data”
(0 to 64 bytes)
DW1
Length of the “net
data”
Number of the
destination slave*
Flag byte 2
Numb. of the dest. slave*
DW2
1st data byte
2nd data byte
Flag byte 3
Data (“net data”)
maximum of 64 bytes
DW33 63rd data byte
Flag byte 66
Number of the receiver:
64th data byte
0 = Master
1 to 30 = Slaves
31 = Broadcast
Figure 13-4. Structure of the Send Mailbox
Figure 13-5 shows the structure of the Coordination Byte Send (KBS).
KBS
Bit
7
6
5
4
3
2
1
0
0:
1:
No error
Error during last data transfer
0:
1:
No express transmission
Request a bus interrupt for this
transmission (express transmission)
0:
Program is able to process Send
Mailbox (operating system has no
access)
Send Mailbox is enabled (program has
no access)
1:
Figure 13-5. Structure of the Coordination Byte Send (KBS)
13-8
S5-100U
The control program for sending data should be structured as follows:
1. Check bit 7 in the KBS to see if data is currently being sent.
- If the programmable controller is sending data, bit 7 is set. During this phase, the Send
Mailbox can not be modified and no transmission can be started.
2. When bit 7 in the KBS has been reset, you can start the transmission by setting bit 7.
3. When bit 7 has been reset by the operating system after data has been sent, you can evaluate
possible errors.
You achieve the following by setting bit 4 in the KBS (express transmission):
The sending programmable controller treats this message preferentially (possibly by overwriting
a telegram not yet sent).
The receiver treats the message as an express transmission.
In case of an error, the operating system sets bit 0 of the KBS. The error message is not valid until
bit 7 has been reset in the KBS.
13.3.2 Receiving Data
The prerequisites for receiving data are as follows:
The parameters for the location of the Receive Mailbox and the Coordination Byte Receive (KBE)
(see section 13.2.2) have been set in DB1. Figure 13-6 shows you which information has to be
stored in what part of the Receive Mailbox.
Example:
Example:
Receive Mailbox in the flag area
Receive Mailbox in a data block
(beginning with data word 1)
DL
DR
Flag Byte 1
Length of " net data " (in
bytes)
DW1 Length of the " net
data "
Source slave
number *
Flag Byte 2
Source slave number*
DW2 1st data byte
2nd data byte
DW3 3rd data byte
4th data byte
Flag Byte 3
Data ( " net data " )
Number of the sender:
0 = Master
1 to 30 = Slave
Figure 13-6. Structure of the Receive Mailbox
13-9
S5-100U
Figure 13-7 shows the structure for receiving data (KBE).
KBE
Bit
7
6
5
4
3
2
1
0
0:
1:
No error
0:
1:
No slave failed
At least one slave failed
0:
1:
Bus in STOP mode
Bus in RUN mode
0:
1:
No message
Data arrives as express transmission
0:
Program can access the Receive
Mailbox
(operating system can not access)
Operating system accepts data into the
Receive Mailbox
(program can not access)
1:
Figure 13-7. Structure of the Coordination Byte Receive (KBE)
Structure of the Control Program for Receiving Data:
1. Check bit 7 of the KBE to see if it is possible to read the data from the Receive Mailbox. Bit 7
must be set to “0” so that the Receive Mailbox can be read.
2. In addition, you can scan through the KBE for the following errors and operating conditions:
- At least one slave has failed.
- The bus is in RUN (STOP) mode.
- The received data pack comes as an express transmission.
Special Features
If you have reserved too little memory for the Receive Mailbox, the available memory area is filled
up completely (flag area FY0 to FY255, DW0 to DW255). Therefore, the remaining receive data
cannot be stored. In this case, the programmable controller does not generate an overflow
message.
You can find sample programs for sending and receiving data in the SINEC L1 manual (in the
chapter on “Programming”).
13-10
S5-100U
13.3.3 Programming the Messages in a Function Block
The control program must execute the following tasks:
Enable the send and receive mailboxes and process the data contained in them.
Manage the coordination bytes (e.g. send request, error evaluation).
Example:
Data traffic with the master as slave 1
Definitions:
Slave 1 receives three bytes from Master 0.
The information is stored in the process output image table (QB0, QB1, QB2).
Slave 1 sends three bytes (IB0, IB1, IB2) to the master.
Parameters are set in FB1 as shown in Figure 13-2.
Programming the individual blocks:
STL
Explanation
OB22:
JU
FB1
OB22 is processed once only following power up. It calls FB1,
which assigns the parameters to the slave.
BE
OB1:
JU
FB2
OB1 is scanned cyclically, and calls FB2, which services the send
and receive mailboxes.
BE
Figure 13-8. Organization of Program Execution
13-11
STL
S5-100U
Explanation
C
A
DB3
F100.7
JC
=M001
L
L
& gt; & lt; F
DR0
KF+0
Receive mailbox (DB3)
Check whether access to receive mailbox is permissible.
KBE/Bit 7=0: Access permitted
KBE/Bit 7=1: Access not permitted
Skip receive mailbox evaluation if access not permitted
Check whether the number of the source (master 0) is in
byte 2 of the receive mailbox
JC
=M002
Skip receive mailbox evaluation if source No. 0
L
DL1
T
L
T
L
QB0
DR1
QB1
DL2
M2:
T
AN
QB2
M100.7
M1:
S
A
F100.7
F101.7
JC
C
=M003
DB2
L
T
L
KF+3
DL0
KF+0
T
L
T
DR0
IB3
DL1
L
T
L
IB4
DR1
IB5
T
AN
S
DL2
F101.7
F101.7
NOP
0
M3:
BE
Transfer receive mailbox
to the PIQ
Set KBE/Bit 7=1, i.e. permit PLC access.
Program access is not permitted again until the
PLC has reset this bit.
Check whether access to the send mailbox is permitted.
KBS/Bit 7=0: Access permitted
KBS/Bit 7=1: Access not permitted
Skip send mailbox evaluation if access not permitted.
Set send mail box (DB2)
Specify length of the data packet in byte 1
of the send mailbox
Load destination number 0 (master) into byte 2 of the
send mailbox
Load input bytes 3, 4 and 5
into the send mailbox
Set KBS/bit 7, i.e. programmable controller has access to the send
mailbox
Figure 13-9. Programming “Message Processing” in FB2
13-12
14
Module Spectrum
14.1
General Technical Specifications . . . . . . . . . . . . . . . . . . . . . . . . . .
14 -
3
14.2
Power Supply Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14 -
4
14.3
Central Processing Units
14 -
7
14.4
Bus Units
14.5
Interface Modules
14.6
14.6.1
14.6.2
14.6.3
Digital Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Digital Input Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Digital Output Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Digital Input/Output Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14.7
Analog Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14.7.1 Analog Input Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14.7.2 Analog Output Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
14 - 10
14 - 14
14
14
14
14
16
16
26
36
14 - 38
14 - 38
14 - 56
S5-100U
14
Module Spectrum
Module Spectrum
The following section describes the standards and test values the S5-100U meets and fulfills and the
test criteria with which the S5-100U has been tested.
UL/CSA approvals
The following approvals exist for the S5-100U:
UL Recognition Mark
Underwriters Laboratories (UL) in accordance with Standard UL 508, File E 116536
CSA Certification Mark
Canadian Standard Association (CSA) in accordance with Standard C 22.2 No. 142, File LR 48323
CE marking
Our products meet the requirements and protection objectives of the following EC Directives and
comply with the harmonized European standards (EN) published in the Official Gazettes of the
European Communities with regard to programmable controllers:
• 89/336/EC " Electromagnetic Compatibility " (EMC Directive)
• 73/23/EC " Electrical Equipment Designed for Use between Certain Voltage Limits "
(Low-Voltage Directive)
The EC declarations of conformity are held at the disposal of the competent authorities at
the address below:
Siemens Aktiengesellschaft
Bereich Automatisierungstechnik
AUT E 14
Postfach 1963
D-92209 Amberg
Federal Republic of Germany
Area of Application
SIMATIC products have been designed for use in industrial environments.
With indiivdual approval, SIMATIC products can also be used in residential environments (residential,
commercial and light industry).
You must acquire the individual approval from the respective national authority or testing board.
Requirements in respect of
Area of Application
Emitted interference
Immunity
Industry
EN 50081-2 : 1993
EN 50082-2 : 1995
Residential
Individual approval
EN 50082-1 : 1992
Oberserving the Installation Guidelines
S5 modules meet the requirements, if installed and operated in accordance with the Installation
Guidelines (see chapter 3).
14-1
Module Spectrum
S5-100U
Notes for the machine manufacturer
The SIMATIC automation system is not a machine in the sense of the EC Directives Machines.
Therefore a declaration of conformity with regard to the EC Directive Machines 89/392/EC does not
exist for SIMATIC.
The EC Directive Machines 89/392/EC regulates the requirements on a machine. A machine in this
sense is a group of interconnected parts or devices (see also EN 292-1, para. 3.1).
The SIMATIC is part of the electrical equipment of a machine and must therefore be included in the
declaration of conformity procedure by the machine manufacturer.
The standard EN 60204-1 (safety of machines, general requirements for the electrical equipment of
machines) applies for the electrical equipment of machines.
The following table is intended to help you with the declaration of conformity and shows which
criteria apply to SIMATIC in accordance with EN 60204-1 (June 1993).
EN 60204-1
Topic/criterion
Remarks
Para. 4
General requirements
Requirements are fulfilled if the devices
are assembled/installed in accordance
with the Installation Guidelines.
Please also observe the section on CE
marking.
Para. 11.2
Digital input/output interfaces
Para. 12.3
Programmable equipment
are installed in lockable cabinets to
protect them from memory modifications
through unauthorized persons.
Para. 20.4
Voltage tests
14-2
S5-100U
14.1
Module Spectrum
Climatic Environmental Conditions
Temperature
Operating
- horizontal design
- vertical design
Nonoperating
Temperature change
- operating
- nonoperating
Relative humidity
Atmospheric pressure
- operating
- nonoperating
Pollutants
- SO2
- H2S
0 to+60° C (32 to 140° F)
0 to+40° C (32 to 104° F)
(Air-intake temperature,
measured on the underside
of the module)
- 40 to +70° C
(- 40 to +150° F)
max. 10° C/h (50° F/h)
max. 20° C/h (68° F/h)
to DIN 40040
15 to 95% (indoors),
noncondensing
860 to 1060 hPa
660 to 1060 hPa
0.5 ppm,
(rel. humidity 60%,
noncondensing)
0.1 ppm,
(rel. humidity 60%,
noncondensing)
Mechanical Environmental Conditions
Vibration*
- tested to IEC 68-2-6
10 to 57 Hz,
57 to 150 Hz,
Mode of vibration
Vibration period
Shock*
- tested to IEC 68-2-27
Type of shock
Strength of shock
Direction of shock
Free-fall
- tested with
Electromagnetic Compatibility (EMC)
Noise Immunity
Static electricity
to IEC 801-2
(discharge on all parts that are accessible to the operator
during normal operation)
- Test voltage
2.5 kV
(relative humidity
30 to 95%)
Radiated electromagnetic
to IEC 801-3
field test
field strength 3 V/m
Fast transient burst
to IEC 801-4,
class III
Power supply
modules
- Supply voltage 24 V DC
1 kV
- Supply voltage 115/230 V AC
2 kV
- Analog input/output modules
1 kV
- Digital input/output modules
for V = 24 V
1 kV
for V & gt; 24 V
2 kV
Communications
interface
1 kV
to VDE 0871
Limit value class A
IEC/VDE Safety Information
Degree of protection
- Type
Const. ampl. 0.075 mm
- Class
Const. accel. 1 g
Insulation rating
- between electrically
Frequency sweeps with
independent circuits
a sweep rate of
and
1 octave/min
with circuits connected
to a central grounding
10 frequency sweeps per
axis in each of the 3 axes
point
vertical to each other
- between all circuits
and
a central grounding point
(standard mounting rail)
Half sine
15 g peak value, 11 ms
Test voltage
duration
for a rated voltage
2 shocks in each of the
Vinput of the circuits (AC/DC)
3 axes vertical to each
other
0 to 50 V
Vinput=
Vinput=
50 to 125 V
to IEC 68-2-31
125 to 250 V
Vinput=
height of fall 50 mm
to IEC 529
IP 20
to IEC 536
to VDE 0160
(05. 1988)
to VDE 0160
(05. 1988)
to VDE 0160
(05. 1988)
Sine, 50 Hz
500 V
1250 V
1500 V
Appropriate measures must be taken to avoid vibration, shock and repetitive shock.
14-3
Module Spectrum
14.2
S5-100U
Power Supply Module PS 930 115/230 V AC; 24 V DC/1 A
(6ES5 930-8MD11)
Input voltage
- rated value
- permiss. range
SIMATIC S5-100U
PS 930
VOLTAGE
SELECTOR
115/230 V AC
92 to 132 V/
187 to 264 V
Line frequency
- rated value
- permiss. range
50/60 Hz
47 to 63 Hz
Input current at
115/230 V
- rated value
0.35/0.18 A
- Input current
max. 6/3 A
Power consumption
115/230V AC
24V DC 1A
6ES5 930-8MD11
33 W
Output voltage
- rated value
- Permiss. range
- Open-circuit voltage
24 V DC
18 to 34 V1)
max. 39 V
24V DC
none
class 1
Galvanic isolation
L+
3A fast fuse
Protection class
N
1A
Fault LED
115/230V AC
Output current
- rated value
Short-circuit
L1
yes
Conductor cross sectional area
- stranded 2)
2×0.5 to 1.5 mm2
M
- solid
2×0.5 to 2.5 mm2
Insulation rating
VDE 0160
Rated insulation voltage
(+24 V to L1)
- insulation group
- tested with
F
3A
250 V AC
2×B
1500 V AC
Ri specification
Dimensions
W×H×D in mm
in.
A to VDE 0871
45.4×135×120
1.8 x 5.3 x 4.7
Power loss of the
module
Weight
L1
typ. 7.5 W
approx. 1040 g (2.4 lbs)
N
2×4,7 nF
1)
For this reason, can only be used with the S5-100U
CPUs
L+
2) With
core end sleeves
M
14-4
S5-100U
Module Spectrum
Power Supply Module PS 931 115/230 V AC; 24 V DC/2 A
(6ES5 931-8MD11)
Technical specifications
Input voltage
- rated value
- permiss. range
SIMATIC S5-100U
PS 931
VOLTAGE
SELECTOR
115/230 V AC
92 to 132 V/
187 to 264 V
Line frequency
- rated value
- permiss. range
Input current at
115/230 V
- rated value
Efficiency
Power consumption
50/60 Hz
47 to 63 Hz
0.9/0.6 A
approx.
approx.
85%
60 W
L1
24 V DC
22.8 to 25.2 V
yes
Output current
- rated value
115/230V AC
24V DC 2A
6ES5 931-8MD11
Output voltage
- rated value
- permiss. range
- open-circuit voltage
2A
Permiss. ambient
temperature of PLC
- horizontal arrangement
115/230V AC
N
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
- vertical arrangement
Buffering of line
voltage dips
- duration of voltage dips
- repetition rate
L+
24V DC
M
20 ms at 187 V/2 A
1s
Short-circuit protection
power limiting,
electronic cutoff,
non-latching
Fault LED
no
Protection class
class 1
Galvanic isolation
yes
Conductor cross-sectional area
- stranded *
- solid
2×0.5 to 1.5 mm2
2×0.5 to 2.5 mm2
Insulation rating
1,6 A
L1
N
2×4,7 n
L+
M
VDE 0160 and
VDE 0805
(transformer)
(+24 V to L1)
- insulation group
- tested with
250 V AC
2×B
2830 V AC
Dimensions
W×H×D in mm
in.
45.4×135×120
1.8 x 5.3 x 4.7
Power loss of the
module
typ.
8.5 W
Weight
approx.
500 g (1.1 lbs.)
* with core end sleeves
14-5
Module Spectrum
S5-100U
Power Supply Module PS 935 (not with CPU 100)
(6ES5 935-8ME11)
Number of inputs
(only internal)
Input voltage
- rated value
- permissible range
2×4 bits
dyn.
stat.
- Polarity reversal protection
Radio interference level
SIMATIC S5-100U
Input current at 24 V DC
- rated value
- inrush current limitation
- efficiency
approx.
Power input
approx.
Output voltage
- rated value
- permissible range
PS 935
ON
OFF
DC 24V
DC 9V 2,5A
6ES5 935-8ME11
24 V DC
18.5 to 30.2 V DC
20.4 to 28.8 V DC
yes
A to VDE 0871
1.25 A
15 times rated current
75%
30 W
9 V DC
8.55 to 9.45 V
yes
Output current
- rated value
- permissible range
- overload recognition
Buffering during mains
voltage dips
- repeat rate
L+
DC 24V
2.5 A
0.0 to 2.5 A
2.5 to 2.7 A
20 ms at 20.4 V/2.5 A
1s
(output side)
yes
electronic switch-off,
non-retentive
Diagnostics
yes (24 V DC input
voltage, 9 V output
voltage)
Fault indication
yes
Class of protection
Galvanic isolation
- stranded*
- solid
Dimensions
W×H×D mm
in.
Class 1
no
DC 9V
FAULT
Power loss of the
module
-- & gt;
CPU
I/Os
Weight
2×0.5 to 1.5 mm2
2×0.5 to 2.5 mm2
45.4×135×120
1.8×5.3×4.7
typ. 7.5 W
approx. 500 g (1.1 lbs)
9 V CPU
Interface
9V
FAULT
9V
M
ON
OFF
9 V=
L+
24V DC
14-6
24 V=
S5-100U
14.3
Module Spectrum
Central Processing Units (CPUs)
CPU 100
(6ES5 100-8MA02)
Memory configuration
- internal memory
RAM 1024 statements
- memory submodule
EPROM/EEPROM
Execution times
- per binary operation approx. 70 µs
- per word operation
approx. 125 µs
Scan monitoring time approx. 300 ms
Flags
1024; 512 retentive
SIEMENS
SIMATIC S5-100U
CPU 100
BATTERY
OFF/
LOW
Timers: Number/range approx. 16; 0.01 to 9990 s
Counters: Number/range
16; 8 retentive
0 to 999 (up/down)
Digital inputs,
Digital outputs
together max.
Analog inputs,
Analog outputs
together max.
Organization blocks
Program blocks
Function blocks
- programmable
- integrated
Sequence blocks
Data blocks
RUN
STOP
RUN
STOP
COPY
Number of operations approx.
Power supply (internal)
Input voltage
- nominal value
- permiss. range
Current consumption from +24 V
L+
24 V DC
M
Output voltage
- V 1 (for I/Os)
- V 2 (for programmer)
Output current
- from V 1
- from V 2
Protection class
6ES5 100-8MA02
256
8
OB1, 21, 22, and 34
0 to 63
0 to 63
none
none
2 to 63
60
24 V DC
18 to 34 V
1A
+9 V
+5.2 V
1A
0.65 A
electronic
class 1
Galvanic isolation
Backup battery
+9 V
Data
GND
+5,2 V
5,0 V
PS
18 ...
34 V
L+
M
CPU
no
Lithium Battery
(3.4 V/ 850 mAh)
- Backup time
min. 1 year (at 25 °C
[77 °F] and
uninterrupted
backup of CPU)
- Service life
approx. 5 years (at 25 °C
[77 °F])
Permissible ambient temperature
0 to 60 °C (32 to 140 °F)
0 to 40 °C (32 to 104 °F)
Connector cross-sectional area
- stranded, with core end sleeves 2×0.5 to 1.5 mm2
- solid
2×0.5 to 1.5 mm2
Power losses of the
module
typ. 10.7 W
Dimensions (WxHxD) in mm
91.5×135×120
in.
(3.6 x 5.3 x 4.7)
Weight
- CPU module
approx.
0.65 kg (1.4 lbs)
- memory submodule approx.
0.1 kg (0.2 lbs)
14-7
Module Spectrum
S5-100U
CPU 102
(6ES5 102-8MA02)
- internal memory
- memory submodule
RAM 2048 statements
EPROM/EEPROM
Execution times Normal/Test
approx.
Flags
SIEMENS
SIMATIC S5-100U
CPU 102
BATTERY
OFF/
LOW
RUN
STOP
RUN
STOP
COPY
7/70 µs
40/125 µs
350 ms
1024; 512 retentive
Timers: Number/range approx. 32; 0.01 to 9990 s
32; 8 retentive
0 to 999 (up/down)
Digital inputs,
Digital outputs
together max. 256
Analog inputs,
Analog outputs
together max. 16
Organization blocks
OB1, 21, 22, and 34
Program blocks
0 to 63
Function blocks
- programmable
0 to 63
- integrated
240 to 243, 250,
and 251
Sequence blocks
none
Data blocks
2 to 63
Number of operations approx. 60
Input voltage
- nominal value
24 V DC
- permiss. range
18 to 34 V
Current consumption from +24 V 1 A
L+
24 V DC
M
Output voltage
- V 1 (for I/Os)
Output current
- from V 1
- from V 2
Protection class
6ES5 102-8MA02
+9 V
+5.2 V
1A
0.65 A
electronic
class 1
Galvanic isolation
Backup battery
+9 V
Data
GND
+5,2 V
5,0 V
PS
18 ...
34 V
L+
M
14-8
CPU
- Backup time
- Service life
no
Lithium Battery
(3.4 V/ 850 mAh)
[77 °F] and
uninterrupted
backup of CPU)
approx.
5 years (at 25 °C
[77 °F])
Permissible ambient temperature of PC
- solid
2×0.5 to 2.5 mm2
Power losses of the
module
typ.
in.
Weight
- CPU module
approx.
- memory submodule
approx.
11.4 W
91.5×135×120
(3.6 x 5.3 x 4.7)
0.65 kg (1.4 lbs)
0.1 kg (0.2 lbs)
S5-100U
Module Spectrum
CPU 103
(6ES5 103-8MA03)
SIEMENS
SIMATIC S5-100U
CPU 103
BATTERY
OFF/
LOW
RUN
Processor
Byte/bit processor
- internal memory
RAM 10240 statements
- memory submodule
EPROM/EEPROM
Real-time clock
- Accuracy
±2s/day
- Variation due to temperature changes
(TA ambient temperature
in °C)
-3.5x(TA-15)2ms/day
- e.g. tolerance at 40 °C
±2s-3.5x(40-15)2ms/day
approx. 0 to -4s/day
Execution times
- per binary operation approx. 0.8 µs
approx. 100 µs
500 ms, selectable
Flags
2048; 512 retentive
Timers: Number/range approx. 128; 0.01 to 9990 s
128; 8 retentive
0 to 999 (up/down)
Digital inputs,
Digital outputs
together max. 256
Analog inputs,
Analog outputs
together max. 32
Organization blocks
OB1, 2, 13, 21, 22,
31, 34, and 251
Program blocks
0 to 255
Function blocks
- programmable
- integrated
STOP
RUN
STOP
COPY
Sequence blocks
Data blocks
L+
24 V DC
M
Input voltage
- nominal value
- permiss. range
6ES5 103-8MA03
Output voltage
- V 1 (for I/Os)
Output current
- from V 1
- from V 2
+9 V
Data
GND
+5,2 V
5,0 V
PS
18 ...
34 V
L+
M
CPU
0 to 255
240 to 243, 250 and
251
0 to 255
2 to 255
180
24 V DC
18 to 34 V
1A
+9 V
+5.2 V
1A
0.65 A
electronic
Protection class
Galvanic isolation
Backup battery
class 1
no
Lithium Battery
(3.4 V/ 850 mAh)
- backup time
[77 °F] and
uninterrupted backup
of CPU)
- service life
[77 °F])
0 to 55 °C (32 to 131 °F)
- solid
2×0.5 to 2.5 mm2
Power losses of the
module
typ. 11.6 W
91.5×135×120
in.
(3.6 x 5.3 x 4.7)
Weight
- CPU module
approx. 0.65 kg (1.4 lbs)
- memory submodule
approx. 0.1 kg (0.2 lbs)
14-9
Module Spectrum
14.4
S5-100U
Bus Units
Bus Unit (SIGUT Screw-type Terminals)
(6ES5 700-8MA11)
Type of connection
Number of plug-in modules
2
Number of bus units
per programmable
controller
SIEMENS
SIGUT screw-type
terminals
16
max.
Connection between two
bus units
flat ribbon
Number of terminals
10 per slot
Insulation rating
VDE 0160
(+9 V to
- insulation group
- tested with
12 V AC
1×B
500 V AC
Conductor cross
sectional area
- stranded *
- solid
2×0.5 to 1.5 mm2
2×0.5 to 2.5 mm2
Current consumption
- from +9 V (CPU)
typ.
1 mA
Dimensions
W×H×D in mm
in.
2
4
6
8 1 0
2
4
6
8 1 0
1
3
5
7
1
3
5
7
91.5×162×39
3.6×6.4×1.5
Weight
9
approx.
300 g (10.6 oz.)
9
1
3
2
5
4
7
6
9
8
1
10
3
2
5
4
7
6
9
8
10
+9V
GND
Data
1 nF
14-10
S5-100U
Module Spectrum
Bus Unit (Crimp Snap-in Connections)
(6ES5 700-8MA22)
Type of connection
2
Number of bus units
per programmable
controller
SIEMENS
Crimp snap-in
16
max.
bus units
flat ribbon
Number of terminals
10 per slot
Conductor cross
sectional area
- stranded
0.5 to 1.5 mm2
Insulation rating
VDE 0160
(+9 V to
- insulation group
- tested with
12 V AC
1×B
500 V AC
Current consumption
- from +9 V (CPU)
typ.
Dimensions
W×H×D in mm
in.
Weight
2
4
6
8 1 0
2
4
6
3
5
7
1
3
5
7
91.5×135×39
3.6×5.3×1.5
approx.
250 g (8.8 oz.)
8 1 0
1
1 mA
9
9
+9V
GND
Data
1 nF
14-11
Module Spectrum
S5-100U
Bus Unit with Interrupt Capability
(6ES5 700-8MB11)
Type of connection
SIGUT (screw-type
terminals)
Number of plug-in
units
2
Number of bus modules
per programmable
controller
max. 16 *
SIEMENS
12 V AC
1×B
500 V AC
Conductor crosssectional area
- stranded **
- solid
ALARM
flat ribbon
10
VDE 0160
(+9 V to )
- Insulation group
- tested with
ALARM
bus modules
Number of terminals
Insulation rating
2×0.5 to 1.5 mm2
2×0.5 to 2.5 mm2
Current consumption
- from+9 V (CPU)
Dimensions
(WxHxD) in mm
in.
Weight
2
4
6
8 1 0
2
4
6
8 1 0
1
3
5
7
1
3
5
7
9
9
typ. 11 mA
91.5×162×39
3.6 x 6.4 x 1.5
approx. 320 g (9.8 oz)
Only the bus unit (and only with 4-channel digital
input modules or comparator modules) directly
adjacent to the CPU has interrupt capability
** With core end sleeves
1
3
2
CPU
5
4
7
6
9
8
1
10
3
2
5
4
7
6
9
8
10
+9V
GND
Data
Alarm
1 nF
14-12
S5-100U
Module Spectrum
(6ES5 700-8MB21)
Type of connection
Crimp-snap-in
Number of plug-in
units
2
per programmable
controller
max. 16 *
bus modules
flat ribbon
Number of terminals
10 per slot
SIEMENS
- stranded
VDE 0160
(+9 V to
- insulation group
- tested with
ALARM
ALARM
0.5 to 1.5 mm2
Insulation rating
12 V AC
1×B
500 V AC
Current consumption
- from+9 V (CPU)
Dimensions
(WxHxD) in mm
in.
Weight
2
4
6
8 1
0
2
4
6
8 1 0
1
3
5
7
9
1
3
5
7
CPU
9
typ. 11 mA
91.5×135×39
3.6 x 5.3 x 1.5
approx. 270 g (9.5 oz)
adjacent to the CPU 103 has interrupt capability
+9V
GND
Data
Alarm
1 nF
14-13
Module Spectrum
14.5
S5-100U
Interface Modules
IM 315 Interface Module
(6ES5 315-8MA11)
OUT
SIEMENS
SIMATIC S5
INTERFACE MODULE
6ES5 315-8MA11
IN
MADE IN GERMANY
+9V
Current supply to the
expansion unit
max.
2.5 A
Number of interface
modules per PLC
GND
Data
max.
1
Permissible potential
difference between
(IM 315) and central
ground point (CPU)
input
output
+9V
GND
Data
±1 V
Insulation rating
1 nF
VDE 0160
(+9 V to
- insulation group
- tested with
12 V AC
1×B
500 V AC
Dimensions
W×H×D in mm
in.
2×(45.4×135×39)
2×(1.8×5.3×1.5)
Current consumption
- from +9 V (CPU)
typ.
Weight
approx. 280 g (9.8 oz.)
1 mA
1 nF
14-14
S5-100U
Module Spectrum
IM 316 Interface Module
(6ES5 316-8MA12)
expansion unit
max.
2.5 A
Number of interface
modules per PLC
max.
4
OUT
SIEMENS
Cable connectors for the
IM 316
- Cable connector
(0.5 m/1.6 ft.)
- Cable connector
(2.5 m/8.2 ft.)
- Cable connector
(5.0 m/16.4 ft.)
- Cable connector
(10 m/33 ft.)
6ES5 712-8CB00
SIMATIC S5
INTERFACE MODULE
6ES5 316-8MA12
Cable insulation in ducts
permissible
difference between
(IM 316) and central
ground point (CPU)
±1 V
Insulation rating
VDE 0160
(+9 V to )
- insulation group
12 V AC
1×B
Dimensions
W×H×D in mm
in.
45.4×135×39
1.8×5.3×1.5
MADE IN GERMANY
IN
6ES5 712-8AF00
6ES5 712-8BC50
6ES5 712-8BF00
Current consumption
- from +9 V (CPU)
typ.
27 mA
Weight
approx.
120 g (4.2 oz.)
+9V
GND
output
1 nF
input
Data
14-15
Module Spectrum
14.6
S5-100U
Digital Modules
14.6.1 Digital Input Modules
Digital Input Module 4 × 24 V DC
(6ES5 420-8MA11)
Number of inputs
Galvanic isolation
- in groups of
F
2
3
.0
.4
Input voltage L+
- rated value
- ”0” signal
- ”1” signal
L+
M
1
4
no
4
24 V DC
0 to 5 V
13 to 33 V
Input current at ”1”
signal
typ.
7 mA
6
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
typ.
typ.
2.5 ms
5 ms
.2
.6
7
Length of cable
- unshielded
max.
100 m (330 ft.)
.3
.7
9
4
5
.1
.5
8
Insulation rating
Rated insulation voltage *
(+9 V to
- insulation group
12 V AC
1×B
Fault LED (red)
10
VDE 0160
no input
voltage L+
Permissible ambient
temperature of module
4
Connection of 2-wire
BERO proximity switches
- residual current
DIGITAL INPUT
4 x 24 V DC
6ES5 420-8MA11
1
2
3
4
5
6
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
possible
1.5 mA
Current consumption
- from +9 V (CPU)
3
2
L+
Power loss of the
module
typ.
0.8 W
approx.
205 g (7.2 oz.)
7
6
9
8
10
M
X.0
14-16
5
4
16 mA
* Relevant only for isolated assembly in the
ET 100/200U
180 K
1
typ.
Weight
+9 V
GND
Data
X.1
X.2
X.3
S5-100U
Module Spectrum
Digital Input Module 8 × 24 V DC
(6ES5 421-8MA12)
Number of inputs
Galvanic isolation
- in groups of
1
Input voltage L+
- rated value
- ”0” signal
- ”1” signal
L+
F
2
8
no
8
24 V DC
0 to 5 V
13 to 33 V
M
.0
4
.1
3
.2
6
.3
5
.4
8
.5
7
.6
10
.7
9
signal
typ.
7 mA at 24 V
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
typ.
typ.
2.3 ms
3.5 ms
Length of cable
- unshielded
max.
100 m (330 ft.)
Insulation rating
VDE
(+9 V to )
- insulation group
12 V AC
1×B
Fault LED (red)
no input voltage
L+/M
Permissible ambient
4
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
DIGITAL INPUT
- residual current
8 x 24 V DC
6ES5 421-8MA12
1
2
3
4
5
6
possible
1.5 mA
Current consumption
from +9 V (CPU)
3
2
L+
5
4
34 mA
Power loss of the
module
typ.
1.6 W
approx.
190 g (6.7 oz.)
ET 100/200U
180 K
1
typ.
Weight
+9 V
GND
Data
7
6
9
8
10
M
X.1 X.0 X.3 X.2 X.5 X.4 X.7 X.6
14-17
Module Spectrum
S5-100U
Digital Input Module 16 × 24 V DC
(6ES5 422-8MA11)
(6ES5 490-8MA13/-8MA03)
(6ES5 490-8MB11)
Number of inputs
Galvanic isolation
DIGITAL
Input voltage L+
- rated value
- ”0” signal
- ”1” signal
IN
16xDC 24 V
n+1
n
F
16
no
24 V DC
0 to 5 V
13 to 30 V
Input protection
- against polarity reversal
no, fuse trips
- against overvoltage
up to 33 V
L+
n+1
.0
1
1
2
2
.1
3
3
.2
4
4
5
5
6
6
7
7
8
8
9
9
10
10
11
11
12
12
.1
13
13
.2
14
14
.3
15
15
.4
16
16
.5
17
17
18
18
19
19
20
20
.3
.4
.5
.6
Input current at
”1” signal
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
Length of cable
- unshielded
typ.
4.5 mA
typ.
typ.
4 ms
3 ms
100 m
NC
NC
n
.0
.6
6
.7
1 2 3
M
6ES5 422-8MA11
(+9 V to )
- insulation group
12 V AC
1×B
EMC/noise immunity to
VDE 801-4, severity level 3
2 kV
Fault LED
(red)
on L+/M interruption
Connection of 2-wire BERO
proximity switches
- residual current
possible
1.5 mA
Current consumption
- from +9 V (CPU)
typ.
50 mA
Power loss of
the module
typ.
4.5 W
Weight
.7
ca.
190 g (6.7 oz.)
+9 V
GND
Data
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
180 K
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
X.0
X.1
X.2
X.3
X.4
X.5
X.6
X.7
NC
NC
X.0
X.1
X.2
X.3
X.4
X.5
X.6
X.7
M L+
14-18
S5-100U
Module Spectrum
Digital Input Module 4 × 24 to 60 V DC
(6ES5 430-8MB11)
Number of inputs
Galvanic isolation
- in groups of
F
M
2
3
.0
.4
Input voltage L+
- rated value
- ”1” signal
- ”0” signal
L+
1
6
4.5 to 7.5 mA
typ.
typ.
3 ms (1.4 to 5 ms)
3 ms (1.4 to 5 ms)
Fault LED (red)
8
9
no input voltage L+
proximity switches
- residual current
7
.3
.7
typ.
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
5
.2
.6
24 to 60 V DC
13 to 72 V
- 33 to 8 V
signal
4
.1
.5
4
yes (optocoupler)
4
possible
1.5 mA
Permissible ambient
10
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
4
Length of cable
- unshielded
max.
100 m (330 ft.)
Insulation rating
4 x 24 - 60 V DC
6ES5 430-8MB11
1
2
3
4
5
6
+9 V
GND
Data
VDE 0160
(+9 V to )
- insulation group
- tested with
DIGITAL INPUT
12 V AC
1×B
500 V AC
(+9 V to L+)
- insulation group
- tested with
60 V AC
2×B
1250 V AC
Current consumption
- from +9 V (CPU)
- from L+
5
4
L+
M
X.0
7
6
X.1
2W
approx.
200 g (7 oz.)
9
8
X.2
max.
Weight
3
5 mA
35 mA
Power loss of the
module
1
max.
10
X.3
14-19
Module Spectrum
S5-100U
Digital Input Module 4 × 115 V AC
(6ES5 430-8MC11)
Number of inputs
Galvanic isolation
- in groups of
Input voltage L1
- rated value
- ”0” signal
- ”1” signal
- frequency
L1
1
N
2
3
.0
.4
4
yes (optocoupler)
4
115 V AC/DC
0 to 40 V
85 to 135 V
47 to 63 Hz
signal
4
5
typ.
typ.
14 mA at 115 V AC
6 mA at 115 V DC
6
.2
.6
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
typ.
typ.
10 ms
20 ms
7
.1
.5
Length of cable
- unshielded
max.
100 m (330 ft.)
8
Insulation rating
.3
.7
2
4 x 115 V AC
6ES5 430-8MC11
2
3
4
5
12 V AC
1×B
500 V AC
Permissible ambient
DIGITAL INPUT
1
125 V AC
2×B
1250 V AC
(+9 V to )
- insulation group
- tested with
10
VDE 0160
(+9 V to L1)
- insulation group
- tested with
9
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
6
- residual current
+9 V
GND
Data
possible
5 mA
3
L1
14-20
N X.0
5
4
7
6
X.1
typ.
2.8 W
approx.
210 g (7.4 oz.)
9
8
X.2
16 mA
Weight
2
typ.
Power loss
of the module
1
Current consumption
- from +9 V (CPU)
10
X.3
S5-100U
Module Spectrum
Digital Input Module 4 × 230 V AC
(6ES5 430-8MD11)
Number of inputs
Galvanic isolation
- in groups of
Input voltage L1
- rated value
- ”0” signal
- ”1” signal
- frequency
L1
1
N
2
3
.0
.4
7
16 mA at 230 V
typ.
typ.
10 ms
20 ms
Length of cable
- unshielded
6
typ.
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
5
.2
.6
230 V AC
0 to 70 V
170 to 264 V
47 to 63 Hz
signal
4
.1
.5
4
yes (optocoupler)
4
max.
100 m (330 ft.)
8
VDE 0160
9
.3
.7
Insulation rating
(+9 V to L1)
- insulation group
- tested with
250 V AC
2×B
1500 V AC
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
10
2
Permissible ambient
DIGITAL INPUT
4 x 230 V AC
6ES5 430-8MD11
1
2
3
4
5
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
6
- residual current
possible
5 mA
1
3
2
L1
N X.0
5
4
7
6
X.1
typ.
16 mA
Power loss
of the module
typ.
2.5 W
approx.
210 g (7.4 oz.)
9
8
X.2
Current consumption
- from +9 V (CPU)
Weight
+9 V
GND
Data
10
X.3
14-21
Module Spectrum
S5-100U
Digital Input Module 8 x 24 V DC
(6ES5 431-8MA11)
Number of inputs
Galvanic isolation
- in groups of
Input voltage L+
- rated value
- " 0 " signal
- " 1 " signal
1 L+
M
2
.0
4
.1
3
.3
.5
10
typ
typ.
5.5 ms
4.5 ms
max.
100 m (330 ft.)
7
.6
8.7 mA
Length of cable
- unshielded
8
typ.
Inherent delay
- from " 0 " to " 1 "
- from " 1 " to " 0 "
5
.4
24 V DC
0 to 5 V
13 to 33 V
Input current at
" 1 " signal
6
.2
8
yes (optocoupler)
8
Insulation rating
(+ 9 V to )
- insulation group
- tested with
4
12 V AC
2xB
500 V AC
(+ 9 V to L+)
- insulation group
- tested with
9
.7
VDE 0160
30 V AC
2xB
500 V AC
Permissible ambient
8 x 24 V DC
6ES5 431-8MA11
1
2
3
4
5
6
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
- residual current
DIGITAL INPUT
possible
1.5 mA
1
3
2
L+
5
4
7
6
Current consumption
- from + 9 V (CPU)
typ.
32 mA
Power loss of
the module
typ.
2W
Weight
+9 V
GND
Data
approx.
190 g (6.7 oz.)
9
8
10
M
14-22
EWA 4NEB 812 6120-02b
S5-100U
Module Spectrum
Digital Input Module 8 × 115 V ACV
(6ES5 431-8MC11)
Number of inputs
Galvanic isolation
- in groups of
1
2
.0
N
4
.1
Input voltage L1
- rated value
- ”0” signal
- ”1” signal
- frequency
L1
3
115 V AC/DC
0 to 40 V
85 to 135 V
47 to 63 Hz
signal
typ.
typ.
12 mA at 115 V AC
2.5 mA at 115 V DC
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
6
.2
8
yes (optocoupler)
8
typ.
typ.
10 ms
20 ms
max.
100 m (330 ft.)
.3
5
.4
8
Length of cable
- unshielded
.5
7
Insulation rating
VDE 0160
.6
10
(+9 V to L1)
- insulation group
- tested with
125 V AC
2×B
1250 V AC
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
9
.7
2
Permissible ambient
DIGITAL INPUT
8 x 115 V AC
6ES5 431-8MC11
1
2
3
4
5
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
6
+9 V
GND
Data
- residual current
possible
4 mA
3
5
4
7
6
32 mA
typ.
2.5 W
Weight
2
typ.
Power loss
of the module
1
Current consumption
- from +9 V (CPU)
approx.
260 g (9 oz.)
9
8
10
N
L1
14-23
Module Spectrum
S5-100U
Digital Input Module 8 × 230 V AC
(6ES5 431-8MD11)
Number of inputs
Galvanic isolation
- in groups of
1
2
Input voltage L1
- rated value
- ”0” signal
- ”1” signal
- frequency
L1
N
4
.0
5
.3
typ.
typ.
16 mA at 230 V AC
1.8 mA at 230 V DC
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
6
.2
230 V AC/DC
0 to 95 V
195 to 253 V
47 to 63 Hz
signal
3
.1
8
yes (optocoupler)
8
typ.
typ.
10 ms
20 ms
max.
100 m (330 ft.)
.4
8
Length of cable
- unshielded
.5
7
Insulation rating
VDE 0160
.6
10
(+9 V to L1)
- insulation group
- tested with
250 V AC
2×B
1500 V AC
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
9
.7
2
Permissible ambient
DIGITAL INPUT
8 x 230 V AC
6ES5 431-8MD11
1
2
3
4
5
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
6
+9 V
GND
Data
- residual current
possible
5 mA
3
5
4
7
6
32 mA
typ.
3.6 W
Weight
2
typ.
Power loss
of the module
1
Current consumption
- from +9 V (CPU)
approx.
260 g (9 oz.)
9
8
10
N
L1
14-24
S5-100U
Module Spectrum
Digital Input Module 8 x 5 to 24 V DC
(6ES5 433-8MA11)
Number of inputs
Galvanic isolation
- in groups of
1
2
4
.0
.1
8
.5
7
.6
10
.7
4.7 k to L+ or M;
reversible on the back
of the module *
5
.4
4.5 to 30 V
Input resistance
6
.3
Permissible range
M
5 to 24 V DC
Vin approx. 25% L+
Vin approx. 45% L+
3
.2
Input voltage L+
- rated value
- " 0 " signal
- " 1 " signal
L+
8
yes (optocoupler)
8
9
The LED displays
the evaluated signal
Inherent delay
approx.
1 ms or 10 ms;
of the module *
Length of cable
- unshielded
max.
100 m (330 ft.)
Insulation rating
(+ 9 V to L+)
- insulation group
- tested with
30 V AC
2xB
500 V AC
(+ 9 V to )
- insulation group
- tested with
L+
M
12-
VDE 0160
12 V AC
2xB
500 V AC
8
DIGITAL INPUT
8 x 5 ... 24 V DC
6ES5 433-8MA11
1
2
3
4
5
Permissible ambient
6
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
+9 V
GND
Data
typ.
typ.
6 mA
60 mA
Power loss of the
module
typ.
2.4 W
Weight
S2
Current consumption
- from + 9 V (CPU)
- from L+
approx.
225 g (8 oz.)
S1
* reversible in groups of 8
4,7 k
1
3
2
5
4
7
6
9
8
10
14-25
Module Spectrum
S5-100U
14.6.2 Digital Output Modules
Digital Output Module 4 × 24 V DC/0.5 A
(6ES5 440-8MA12)
1
F
2
3
.0
.4
Number of outputs
Galvanic isolation
- in groups of
Load voltage L+
- rated value
- permissible range
(including ripple)
- value at t & lt; 0.5 s
Output current
for ”1” signal
- rated value
- permissible range
- lamp load
L+
M
4
Residual current
at ”0” signal
Output voltage
- ”1” signal
5
.1
.5
6
7
.2
.6
8
9
4
no
4
24 V DC
20 to 30 V
35 V
0.5 A
5 to 500 mA
max. 5 W
max. 0.5 mA
max. L+ (- 0.6 V)
short-circuit protected
output with autom.
switch on when the
short-circuit does not
exist any more
Fault LED (red)
Voltage induced on circuit
interruption (internal) limited to
Switching frequency
- resistive load
max.
- inductive load
max.
Total permissible
current of outputs
DIGITAL OUTPUT
4 x 24 V DC/0.5 A
6ES5 440-8MA12
2
3
possible
10
5
1
short-circuit/
no load voltage L+
Error diagnostics
.3
.7
4
5
Driving of digital input
Paralleling of outputs
- maximum current
6
+9 V
GND
Data
100 Hz
2 Hz
2A
possible
possible
0.8 A
Permissible ambient
temperature
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
Length of cable
- unshielded
- 15 V
max. 100 m (330 ft.)
Insulation rating
VDE 0160
(+9 V to )
- insulation group
12 V AC
Current consumption
- from +9 V (CPU)
- from L+(without load)
1×B
3
2
L+
7
6
9
8
10
Power loss
of the module
typ.
1.5 W
approx. 200 g (7 oz.)
M
X.0
14-26
5
4
15 mA
25 mA
Weight
1
typ.
typ.
X.1
X.2
X.3
ET 100/200U
S5-100U
Module Spectrum
Digital Output Module 4 × 24 V DC/2 A
(6ES5 440-8MA22)
Number of outputs
Galvanic isolation
- in groups of
Load voltage L+
- rated value
- permissible range
F
2
3
.0
.4
4
Residual current at
”0” signal
Output voltage
- ”1” signal
5
.1
.5
6
.2
.6
7
.3
.7
24 V DC
20 to 30 V
Output current
for ”1” signal
- rated value
- permissible range
- lamp load
L+
M
1
4
no
4
2A
5 mA to 2 A
max. 10 W
max. 1 mA
max. L+ (- 0.8 V)
output with autom.
switch on when the
exist any more
9
8
Fault LED (red)
Error diagnostics
10
Switching frequency
- resistive load
max.
- inductive load
max.
Total permissible
current of outputs
5
- maximum current
Permissible ambient
DIGITAL OUTPUT
4 x 24 V DC/2 A
6ES5 440-8MA22
1
2
3
4
5
short-circuit/
no load voltage L+
possible
6
+9 V
GND
Data
1
3
2
L+
5
4
7
6
9
8
4A
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
VDE 0160
Rated insulation voltage*
(+9 V to )
- insulation group
Current consumption
- from +9 V (CPU)
typ.
- from L+ (without load)
typ.
Power loss
of the module
typ.
Weight
100 Hz
2 Hz
possible
possible
3.2 A
Length of cable
- unshielded
Insulation rating
- 15 V
12 V AC
1×B
15 mA
25 mA
3W
10
ET 100/200U
M
X.0
X.1
X.2
X.3
14-27
Module Spectrum
S5-100U
Digital Output Module 8 × 24 V DC/0.5 A
(6ES5 441-8MA11)
Number of outputs
Galvanic isolation
- in groups of
1
2
Load voltage L+
- rated value
- permissible range
(including ripple)
L+
M
4
.0
6
.2
8
.5
- permissible range
- lamp load
7
.4
Residual current at
”0” signal
Output voltage
- ”1” signal
10
.6
Switching frequency
- resistive load
- inductive load
Total permissible
current of outputs
5
DIGITAL OUTPUT
8 x 24 V DC/0.5 A
6ES5 441-8MA11
1 2
3
4
5
6
C
3
L+
5
4
max. L+ (- 0.5 V)
7
6
9
8
10
M
- 15 V
4A
possible
possible
0.8 A
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
VDE 0160
(+9 V to
- insulation group
Current consumption
- from +9 V (CPU)
typ.
typ.
Power loss
of the module
typ.
Weight
none
max. 100 Hz
max. 2 Hz
Permissible ambient
temperature of PLC
Length of cable
- unshielded
Insulation rating
2
max. 1.0 mA
Paralleling of 2 outputs
- maximum current
+9 V
GND
Data
1
0.5 A at 60 °C (140 °F)/
1 A at 30 °C (86 °F)
5 mA to 1 A
max. 5 W
9
.7
35 V
Warning
Output current for
”1” signal
- rated value
5
.3
24 V DC
20 to 30 V
Capacitor remains loaded
after switch off of L+
3
.1
8
no
8
12 V AC
1×B
14 mA
15 mA
2W
approx. 220 g (7.7 oz.)
* Relevant only for isolated assembly in the ET 100/200U
14-28
S5-100U
Module Spectrum
Digital Output Module 4 × 24 to 60 V DC/0.5 A
(6ES5 450-8MB11)
L+
M
1
F
2
3
.0
.4
Number of outputs
Galvanic isolation
- in groups of
Load voltage L+
- rated value
- permissible range
Output current for
”1” signal
- rated value
- permissible range
- lamp load
Residual current at
”0” signal
4
5
.1
.5
6
7
.2
.6
8
10
5
short circuit/
no load voltage L+
possible
2A
possible
- maximum current
Permissible ambient
4 x 24 - 60 V DC/0.5A
6ES5 450-8MB11
3 4
max. 1 mA
output with autom.
switch on when the
exist any more
Total permissible current
of outputs
DIGITAL OUTPUT
2
0.5 A
5 mA to 0.5 A
max. 5 to 12 W
Error diagnostics
interruption (internal) limited to - 30 V
Switching frequency
- resistive load
max. 100 Hz
- inductive load
max. 2 Hz
5
1
24 to 60 V DC
20 to 72 V
Fault LED (red)
9
.3
.7
4
yes (optocoupler)
4
6
+9 V
GND
Data
possible
2×0.4 A
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
Length of cable
- unshielded
Insulation rating
3
5
7
9
60 V AC
2×B
500 V AC
(+9 V to )
- insulation group
- tested with
1
VDE 0160
- (+9 V to L+)
- insulation group
- tested with
12 V AC
1×B
500 V AC
L+
4
6
8
10
M
X.0
X.1
X.2
X.3
Current consumption
- from +9 V (CPU)
typ.
typ.
15 mA
30 mA (at 60 V)
Power loss of the
module
typ.
5W
Weight
2
14-29
Module Spectrum
S5-100U
Digital Output Module 4 × 115 to 230 V AC/1 A
(6ES5 450-8MD11)
6
Number of outputs
Galvanic isolation
- in groups of
Load voltage L1
- rated value
- frequency
- permissible range
Output current for
”1”signal
- rated value
- permissible range
- lamp load
Contact current closing
rating:
7
Residual current at
”0” signal
max. 3/5 mA
Output voltage
- ”1” signal
Signal status display
(green LEDs)
max. L1 (- 7 V)
only with load
connected
L1
1
F
2
3
.0
.4
N
4
5
.1
.5
.2
.6
8
9
.3
.7
10
4
yes
4
115 to 230 V AC
max. 47 to 63 Hz
85 to 264 V
1A
50 mA to 1 A
max. 25/50 W
determined by the
size of the fuse
fuse
(10 A extra fast)
(Wickmann No.
19231, or
6ES5 980-3BC41)
FF
10A
Fault LED (red)
Switching frequency
Permissible current
of all outputs
3
DIGITAL OUTPUT
4x115/230V AC/1A
6ES5 450-8MD11
1
2
3 4
5
6
3
L1
5
4
7
6
9
8
10
N
X.0
X.1
X.2
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
Length of cable
- unshielded
2
4A
possible
not possible
Permissible ambient
+9 V
GND
Data
1
fuse blown *
max. 10 Hz
Insulation rating
(+9 V to L1)
- insulation group
- tested with
(+9 V to )
- insulation group
- tested with
Current consumption
- from +9 V (CPU)
Power loss of the
module
Weight
VDE 0160
250 V AC
2×B
1500 V AC
12 V AC
1×B
500 V AC
typ.
14 mA
typ. 3.5 W
approx. 315 g (11 oz.)
X.3
* Indication only given if load voltage is
applied and at least one load is connected
14-30
S5-100U
Module Spectrum
Digital Output Module 8 x 24 V DC/1 A
(6ES5 451-8MA11)
Number of outputs
Galvanic isolation
- in groups of
1
F
2
Load voltage L+
- rated value
- permissible range
(including ripple)
L+
Output current for
" 1 " signal
- rated value
- permissible range
- lamp load
Residual current at
" 0 " signal
Output voltage
- at " 1 " signal
Short-circuit
protection
M
4
.0
3
.1
6
.2
5
.3
8
.4
10
.6
Fault LED (red)
Voltage induced on
circuit interruption
Switching frequency
- resistive load
- inductive load
9
.7
5
20 to 30 V
35 V
1A
5 mA to 1A
max. 10 W
max. 0.5 mA
max. L+ (- 0.6 V)
output with autom.
switch on when the
exist any more
short-circuit
8 x 24 V DC/1 A
6ES5 451-8MA11
4
5
-15 V
max. 100 Hz
max. 2 Hz
Permissible current
of all outputs
Driving of
digital input
DIGITAL OUTPUT
3
24 V DC
7
.5
1 2
8
yes (optocoupler)
8
6
+9 V
GND
Data
6A
possible
Paralleling of 2
outputs
- maximum current
Permissible ambient
paarweise possible
1.8 A
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
1
3
2
L+
5
4
7
6
9
8
10
M X.1 X.0 X.3 X.2 X.5 X.4 X.7 X.6
Length of cable
- unshielded
Insulation rating
(+ 9 V to L+)
- insulation group
- tested with
(+ 9 V to )
- insulation group
- tested with
Current consumption
- from +9 V (CPU)
Power loss
of the module
Weight
VDE 0160
24 V AC
2xB
500 V AC
12 V AC
1xB
500 V AC
typ.
typ.
35 mA
50 mA
typ. 3 W
approx. 230g (8 oz.)
14-31
Module Spectrum
S5-100U
Digital Output Module 8 × 115 to 230 V AC/0.5 A
(6ES5 451-8MD11)
1
L1
2
Number of outputs
Galvanic isolation
- in groups of
Load voltage L1
- rated value
- frequency
- permissible range
Output current for
”1” signal
- rated value
- permissible range
- lamp load
Contact current
closing rating:
N
4
.0
3
.1
6
.2
5
.3
Residual current at
”0” signal
Output voltage
- at ”1” signal
Signal Status Display
(green LEDs)
8
.4
7
.5
10
.6
8
yes (optocoupler)
8
115 to 230 V AC
47 to 63 Hz
85 to 264 V
max.
0.5 A
50 mA to 0.5 A
25/50 W
max.
determined by the
size of the fuse
max.
3/5 mA
max.
L1 (-7 V)
only with load
connected
fuse
(10 A extra fast)
(Wickmann No.
19231, or
6ES5 980-3BC41)
max.
10 Hz
9
.7
FF
10A
Switching frequency
Permissible current
of all outputs
3
DIGITAL OUTPUT
8 x 115/230 V AC/0.5 A
6ES5 451-8MD11
1 2
3
4
5
4A
possible
not possible
Permissible ambient
6
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
+9 V
GND
Data
1
3
2
L1
14-32
N
5
4
7
6
9
8
10
Length of cable
- unshielded
max.
Insulation rating
(+9 V to L1)
- insulation group
- tested with
(+9 V to
- insulation group
- tested with
Current consumption
- from +9 V (CPU)
typ.
Power loss of the
module
typ.
Weight
100 m (330 ft.)
VDE 0160
250 V AC
2×B
1500 V AC
12 V AC
1×B
500 V AC
25 mA
3.5 W
approx.
270 g (9 oz.)
S5-100U
Module Spectrum
Digital Output Module 8 × 5 to 24 V DC/0.1 A
(6ES5 453-8MA11)
Number of outputs
Galvanic isolation
- in groups of
2
Load voltage L+
- rated value
- permissible range
(including ripple)
Output voltage
6
.2
none
- 19 V (at 24 V)
Switching frequency
- resistive load
- inductive load
3
.1
100 mA
4
.0
TTL-compatible 1
Output current for
”1” signal
- rated value
L+
M
5 to 24 V DC
4.75 to 30 V
1
8
yes
8
100 Hz
2 Hz
35 V
5
.3
8
.4
7
.5
10
.6
Paralleling of
2 outputs
9
.7
max.
max.
possible
Permissible ambient
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
8
Length of cable
- unshielded
DIGITAL OUTPUT
8 x 5...24 V DC/0,1 A
6ES5 453-8MA11
1 2
3
4
5
max.
100 m (330 ft.)
Insulation rating
VDE 0160
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
6
+9 V
GND
Data
Current consumption
- from +9 V (CPU)
- from L+
(without load)
typ.
20 mA
typ.
28 mA
Power loss of the
module
typ.
1W
Weight
approx.
220 g (8 oz.)
43 V
1
1
3
2
L+
5
4
7
6
transistor with open collector,
switching to M potential
9
8
10
M
14-33
Module Spectrum
S5-100U
Relay Output Module 8 x 30 V DC/230 V AC
Crimp Snap-in Connector, 40-pin
Screw Plug Connector, 20-pin
Screw Plug Connector, 40-pin
(6ES5 451-8MR12)
(6ES5 490-8MB21)
(6ES5 490-8MB11)
Outputs
Galvanic isolation
- in groups of
RELAY OUTPUT
F
8×30 V DC
1
3
4
.0
5
5
5
7
7
.1
.5
9
9
6
7
8
5
8
11
17
17
M
19
7
.+24V
19
1 2 3
17
18
19
20
.7
16
19
.3
15
18
15
15
14
17
13 13
20
B
1
1
3
3
5
7
9
9
11
11
13
13
15
15
17
max.
100 m (330 ft.)
VDE 0160
250 V AC
2xB
1500 V AC
12 V AC
1xB
500 V AC
250 V AC
2xB
1500 V AC
24 V DC
3.6 V
max.
19
X.1
X.2
X.3
M
14-34
Length of cable
- unshielded
Insulation rating
(+ 9 V to L 1)
- insulation group
- tested with
(+ 9 V to )
- insulation group
- tested with
(between contacts)
- insulation group
- tested with
Supply voltage L+
(for the relay)
- rated value
- ripple VPP
- permissible range
(ripple included)
- value to t & lt; 0.5 s
Current consumption
- from + 9 V (CPU)
- from L+
Power loss
of the module
Weight
17
19
X.4
5
7
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
+9 V
GND
Data
A
1 x 106
0.5 x 106
10 Hz
no input voltage
13
16
13
13
12
15
.6
11
13
11
9
14
11
max.
3 A at 250 V AC
1.5 A at 30 V DC
0.5 A at 250 V AC
0.5 A at 30 V DC
Operating cycles of
the contacts according to
VDE 0660, part 200
- AC - 11
- DC - 11
Switching frequency
max.
Fault LED (red)
Permissible ambient
10
12
11
11
9
10
.2
- inductive load
5
7
.4
max.
4
5
3
3
6
3
3
2
3
1
Continuous current Ith
Relay type
Switching capacity
of the contacts
- resistive load
1
2
1
X.0
8 relay outputs,
contact switching
varistor SIOVS07-K275
yes
2 with signal
status display
3A
Dold OW 5699
X.5
X.6
20 to 30 V
35 V
typ.
typ.
30 mA
70 mA
typ.
approx.
1.6 W
300 g (11 oz.)
X.7
L+
S5-100U
Module Spectrum
Relay Output Module 4 x 30 V DC/230 V AC
(6ES5 452-8MR11)
Outputs
1
2
4 relay outputs,
contact switching
varistor SIOV-S07K275
yes (optocoupler)
1
Galvanic isolation
- in groups of
L+
M
5A
Siemens
V 23127-D 0006A402
Relay type
3
.0
.4
Switching capacity
of the contacts
- resistive load
.1
.5
6
7
.2
.6
max.
Operating cycle of
VDE 0660, part 200
- AC-11
- DC-11
Switching frequency
max.
8
9
.3
.7
max.
- inductive load
4
5
Permissible ambient
10
RELAY OUTPUT
6ES5 452-8MR11
1
2
3
4
5
6
+9 V
GND
Data
1
3
2
L+
5
4
7
6
9
8
10
M
X.0
X.1
X.2
max.
Insulation rating
(+ 9 V to L1)
- insulation group
- tested with
(+ 9 V to )
- insulation group
- tested with
(between contacts)
- insulation group
- tested with
Supply voltage L+
(for the relay)
- rated value
- ripple Vpp
max.
- permissible range
(ripple included)
Current consumption
- from + 9 V (CPU)
- from L+
Power loss of
the module
Weight
1.5 x 106
0.5 x 106
10 Hz
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
7
Length of cable
- unshielded
5 A at 250 V AC
2.5 A at 30 V DC
1.5 A at 250 V AC
0.5 A at 30 V DC
100 m (330 ft.)
VDE 0160
250 V AC
2xB
1500 V AC
12 V AC
1xB
500 V AC
250 V AC
2xB
1500 V AC
24 V DC
3.6 V
20 to 30 V
35 V
typ.
typ.
14 mA
100 mA
typ.
approx.
2W
240 g (8 oz.)
X.3
14-35
Module Spectrum
S5-100U
14.6.3 Digital Input/Output Modules
Digital Input/Output Module with LED Display
OUT
DIGITAL
(6ES5 482-8MA13)
(6ES5 490-8MB11)
IN
32x24V DC
n+1
n
F
F
n+1
n
.0
L+
n+1
.0
L+
n+1
.0
.1
.1
0.5A
.2
.2
.3
.3
1
1
2
2
3
3
4
4
5
5
.4
.4
.5
.5
6
6
.6
7
7
.7
8
8
.7
.6
.7
.0
NC
NC
n
9
9
10
10
11
11
.0
.0
12
12
.1
.1
13
13
.2
14
14
15
15
16
16
17
17
18
18
19
19
20
20
M
L+
n
0.5A
.2
.7
.3
.3
.4
.4
.5
.5
.6
.6
.7
6
M
1 2 3
.7
M
+9 V
GND
Data
M L+
X.0
X.1
X.2
X.3
500
X.4
mA X.5
X.6
X.7
M L+
X.0
X.1
X.2
500X.3
X.4
mA
X.5
X.6
X.7
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
180 K
1
2
3
4
5
6
7
8
9
10
11
12
13
14
15
16
17
18
19
20
X.0
X.1
X.2
X.3
X.4
X.5
X.6
X.7
NC
NC
X.0
X.1
X.2
X.3
X.4
X.5
X.6
X.7
M
14-36
L+
S5-100U
Module Spectrum
Digital Input/Output Module with LED Display (continued)
(6ES5 482-8MA13)
Output side
Cable length
- unshielded
100 m (330 ft.)
(+9 V to )
- insulation group
12 V AC
1xB
Power loss of the
module
typ.
Weight
approx. 190 g (7 oz.)
4.5 W
Input side
Number of inputs
Galvanic isolation
- in groups of
16
no
16
Input voltage L+
- rated value
- for ”0” signal
- for”1” signal
24 V DC
0 to 5 V
13 to 30 V
Number of outputs
Galvanic isolation
- in groups of
16
no
8
Load voltage L+
- rated value
- permissible range
(ripple included)
24 V DC
20 to 30 V
35 V
Output current IN
for ”1” signal
- rated value
- permissible range
Residual current
for ”0” signal
500 mA
5 to 500 mA
max.
0.5 mA
yes
Short-circuit indication
red LED
Output voltage for
”1” signal
L+(- 0.6 V)
Input current
for ”1” signal
typ.
4.5 mA
limited to
- 15 V
Inherent delay
- from ”0” to ”1”
- from ”1” to ”0”
typ.
typ.
4 ms
3 ms
Switching frequency with
- resistive load
- inductive load
100 Hz
2 Hz
indicates
interruption of
L+/M supply
Permissible total current
of the outputs
6A
Driving of a digital input
possible
- maximum current
possible in pairs
(0.8×IN)
Fault LED (red)
Connection of
two-wire BERO
proximity switches
- residual current
possible
1.5 mA
typ.
50 mA
Current consumption
- from +9 V (CPU)
typ.
typ.
10 mA
100 mA
Lamp load
Current consumption
- from +9 V (CPU)
max.
5W
14-37
Module Spectrum
14.7
S5-100U
Analog Modules
Analog Input Module 4 x ±50 mV
(6ES5 464-8MA11)
broken wire
4
3
2
1
operating
mode
1+
Comp.
23+
Ch.0
45+
Ch.1
67+
Ch.2
89+
Ch.3
10 -
6
ANALOG INPUT
4 x±50 mV
6ES5 464-8MA11
1
2
3
4
5
6
+9 V
GND
Data
broken
wire
1
3
5
2
7
4
8
10
Cu Cu
Compensating
box
Fe Ko
Ch.0
14-38
9
6
Ch.1
Ch.2
Terminal box
Ch.3
S5-100U
Module Spectrum
Analog Input Module 4 × ±50 mV (continued)
(6ES5 464-8MA11)
Input ranges
(rated values)
±50 V
Number of inputs
1, 2 or 4
(selectable)
Galvanic isolation
yes (inputs to
grounding point;
not between inputs)
Input resistance
10 M
Connection method
of sensors
two-wire
connection
Digital representation
of input signal
12 bits+sign
(2048 units
= rated value)
Measured value
representation
two's complement
(left-justified)
Measuring principle
integrating
Conversion principle
voltage-time
conversion
(dual slope)
Integration time
(adjustable for optimum
noise suppression)
20 ms at 50 Hz
16.6 ms at 60 Hz
Encoding time
per input
- for 2048 units
- for 4095 units
Noise suppression
for f=nx
(50/60 Hz±1%);
n=1, 2, ...
- common-mode
rejection
(Vpp=1 V)
- series-mode rejection
(peak value of noise
& lt; rated value of
input range)
min.
86 dB
min.
40 dB
Basic error limits
±0.15 %
Operational error limits
(0 to 60 °C)
(32 to 140 °F)
±0.4 %
Single errors
- linearity
- tolerance
- polarity reversal error
±0.05 %
±0.05 %
±0.05 %
Temperature error
- final value
- zero point
±0.01 %/K
±0.002 %/K
Length of cable
- shielded
max.
50 m (164 ft.)
60 ms at 50 Hz
50 ms at 60 Hz
80 ms at 50 Hz
66.6 ms at 60 Hz
none
Connection of compensating box
max.
max.
max.
max.
Supply voltage L+
possible
Insulation rating
VDE 0160
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
60 V AC
1×B
500 V AC
Permissible voltage
difference
- between inputs
- between inputs and
central ground point
max. 75 V DC/60 V AC
Permissible
input voltage
(destruction limit)
(inputs to+9 V)
- insulation group
- tested with
max. 24 V DC
Current consumption
- from+9 V (CPU)
typ.
70 mA
Power loss of the
module
typ.
0.7 W
Weight
approx.
230 g (8 oz.)
Fault indication for
- range exceeded
max. ±1V
yes
(more than
4095 units)
- sensor wire break
yes (selectable)
- general indication of wire
break
red LED
14-39
Module Spectrum
S5-100U
(6ES5 464-8MA21)
broken wire
8
7
6
5
4
3
2
operating 1
mode
1+
Comp.
23+
Ch.0
45+
Ch.1
67+
Ch.2
89+
Ch.3
10 -
6
ANALOG INPUT
4 x±50 mV
6ES5 464-8MA21
1
2
3
4
5
6
+9 V
GND
Data
broken
wire
1
3
5
2
7
4
9
6
8
10
Cu Cu
Comp.
Fe Ko
Ch.0
14-40
Ch.1
Ch.2
Ch.3
S5-100U
Module Spectrum
Analog Input Module 4 x ±50 mV (continued)
(6ES5 464-8MA21)
Input range
(rated values)
± 50 mV
Number of inputs
1, 2 or 4
(selectable)
Galvanic isolation
yes (inputs to
grounding point;
not between
inputs)
Noise suppression
for f = nx
(50/60 Hz±1%)
n = 1, 2, ...
- common mode rejection
(Vpp = 1 V)
- series mode rejection
input range)
Input resistance
10 M
Basic error limits
±0.15%
Connection method
of sensors
two-wire
connection
Operating error limits
(0 to 60 °C)
(32 to 140 °F)
±0.4%
of input signal
12 bits + sign
(2048 units =
rated value)
Measured value
representation
two's complement
(left-justified)
Measuring principle
integrating
voltage-time
conversion
(dual slope)
Integration time
noise suppression)
20 ms at 50 Hz
16.6 ms at 60 Hz
Encoding time
per input
- for 2048 units
- for 4095 units
Permissible voltage
difference
- between inputs
max.
max.
max.
max.
60 ms at 50 Hz
50 ms at 60 Hz
80 ms at 50 Hz
66.6 ms at 60 Hz
max.
±1 V
max.
75 V DC/60 V AC
min. 86 dB
min. 40 dB
Single errors
- linearity
- tolerance
±0.05%
±0.05%
±0.05%
Temperature error
- final value
- zero point
±0.01 %/K
±0.002 %/K
Linearization exactness
for rated range
(for types J,K,L)
±1 °C (1.8 °F)
Characteristic linearization for the following
thermoelements
- Nickel-Chromium/
Nickel-Aluminium (Type K)
- Iron/Copper-Nickel (Type J)
- Iron/Copper-Nickel (Type L)
IEC 584
IEC 584
DIN 43710
Length of cable
- shielded
50 m (164 ft.)
max.
Supply voltage L+
none
- range exceeded
- sensor wire break
of wire break
max.
24 V DC
yes (more than
4095 units)
yes (selectable)
red LED
possible
Insulation rating
Permissible
input voltage
(destruction limit)
Connection of
compensating box
VDE 0160
(+9 V to )
- insulation group
- tested with
12 V AC
1xB
500 V DC
(inputs to + 9 V)
- insulation group
- tested with
60 V AC
1xB
500 V AC
Current consumption
- from + 9 V (CPU)
100 mA
Power loss of the
module
typ.
0.7 W
Weight
typ.
approx.
230 g (8 oz.)
14-41
Module Spectrum
S5-100U
Analog Input Module 4 x ±1 V
(6ES5 464-8MB11)
broken wire
4
3
2
1
operating
mode
3+
Ch.0
45+
Ch.1
67+
Ch.2
89+
Ch.3
10 -
6
ANALOG INPUT
4 ×± 1V
6ES5 464-8MB11
1
2
3
4
5
6
+9 V
GND
Data
broken
wire
1
3
5
2
Ch.0
14-42
7
4
9
6
Ch.1
8
Ch.2
10
Ch.3
S5-100U
Module Spectrum
Analog Input Module 4 x ±1 V (continued)
(6ES5 464-8MB11)
Input ranges
(rated values)
±1V
Number of inputs
1, 2 or 4
(selectable)
Galvanic isolation
yes (inputs to
grounding
point; not between
inputs)
Input resistance
10 M
Connection method
of sensors
two-wire
connection
of input signal
12 bits+sign
(2048 units
= rated value)
Measured value
representation
two's complement
(left-justified)
Measuring principle
integrating
voltage-time
conversion
(dual slope)
Integration time
noise suppression)
Encoding time
per input
- for 2048 units
20 ms at 50 Hz
16.6 ms at 60 Hz
Noise suppression
for f=nx
(50/60 Hz±1%);
n=1, 2, ...
- common-mode
rejection (Vpp=1 V)
input range)
min.
min.
86 dB
40 dB
Basic error limits
±0.1 %
(0 to 60 °C)
(32 to 140 °F)
±0.35 %
Single errors
- linearity
- tolerance
±0.05 %
±0.05 %
±0.05 %
Temperature error
- final value
- zero point
±0.01 %/K
±0.002 %/K
Length of cable
- shielded
max.
200 m (660 ft.)
Supply voltage L+
none
not possible
Insulation rating
VDE 0160
- for 4095 units
max.
max.
max.
max.
60 ms at 50 Hz
50 ms at 60 Hz
80 ms at 50 Hz
66.6 ms at 60 Hz
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
Permissible voltage
difference
- between inputs
max.
± 1V
max.
75 V DC/60 V AC
(inputs to +9 V)
- insulation group
- tested with
60 V AC
1×B
500 V AC
Permissible
input voltage
(destruction limit)
- range exceeded
- sensor wire break
wire break
Current consumption
- from+9 V (CPU)
max.
24 V DC
yes (more than
4095 units)
yes (selectable)
typ.
70 mA
Power loss of the
module
typ.
0.7 W
Weight
approx.
230 g (8 oz.)
red LED
14-43
Module Spectrum
S5-100U
Analog Input Module 4 x ±10 V
(6ES5 464-8MC11)
4
3
2
1
operating
mode
3+
Ch.0
45+
Ch.1
67+
Ch.2
89+
Ch.3
10 -
6
ANALOG INPUT
4 x ± 10 V
6ES5 464-8MC11
1
2
3
4
5
6
+9 V
GND
Data
2,5 k
47 k
1
3
5
2
Ch.0
14-44
7
4
9
6
Ch.1
8
Ch.2
10
Ch.3
S5-100U
Module Spectrum
Analog Input Module 4 x ±10 V (continued)
(6ES5 464-8MC11)
Input ranges
(rated values)
±10 V
Number of inputs
1, 2 or 4
(selectable)
Galvanic isolation
yes (inputs to
grounding point;
not between inputs)
Input resistance
50 k
Connection method
of sensors
two-wire
connection
of input signal
12 bits+sign
(2048 units =rated
value)
Measured value
representation
two's complement
(left-justified)
Measuring principle
integrating
voltage-time
conversion
(dual slope)
Integration time
noise suppression)
20 ms at 50 Hz
16.6 ms at 60 Hz
Encoding time
per input
- for 2048 units
- for 4095 units
Noise suppression
for f=nx
(50/60 Hz±1%);
n=1,2, ...
- common-mode
rejection (Vpp=1 V)
input range)
min.
86 dB
min.
40 dB
Basic error limits
±0.2 %
(0 to 60 °C)
(32 to 140 °F)
±0.45 %
Single errors
- linearity
- tolerance
±0.05 %
±0.05 %
±0.05 %
Temperature error
- final value
- zero point
±0.01 %/K
±0.002 %/K
Length of cable
- shielded
max.
200 m (660 ft.)
60 ms at 50 Hz
50 ms at 60 Hz
80 ms at 50 Hz
66.6 ms at 60 Hz
none
Connection of
compensating box
max.
max.
max.
max.
Supply voltage L+
not possible
Insulation rating
VDE 0160
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
60 V AC
1×B
500 V AC
Permissible voltage
difference
- between inputs
max.
±1 V
max.
75 V DC/60 V AC
Permissible
input voltage
(destruction limit)
(inputs to +9 V)
- insulation group
- tested with
max.
50 V DC
Current consumption
- from +9 V (CPU)
typ.
70 mA
yes (more than
4095 units)
no
Power loss of the
module
typ.
0.7 W
Weight
approx.
230 g (8 oz.)
- range exceeded
- sensor wire break
wire break
no
14-45
Module Spectrum
S5-100U
Analog Input Module 4 x ±20 mA
(6ES5 464-8MD11)
4
3
2
1
operating
mode
3+
Ch.0
45+
Ch.1
67+
Ch.2
89+
Ch.3
10 -
6
ANALOG INPUT
4 x ± 20 mA
6ES5 464-8MD11
1
2
3
4
5
6
+9 V
GND
Data
+9 V
GND
Data
25
25
1
3
2
U
7
1
9
6
8
3
2
10
5
7
4
Ch.1
Ch.2
9
6
8
Four-wire transducer
Ch.0
14-46
5
4
10
Two-wire transducer
Ch.3
U
U
S5-100U
Module Spectrum
Analog Input Module 4 x ±20 mA (continued)
(6ES5 464-8MD11)
Input ranges
(rated values)
±20 mA
Number of inputs
1, 2 or 4
(selectable)
Galvanic isolation
yes (inputs to
grounding point; not
between inputs)
Input resistance
25
Connection method
of sensors
two-wire
connection
of input signal
12 bits+sign
(2048 units
=rated value)
Measured value
representation
two's complement
(left-justified)
Measuring principle
integrating
voltage-time
conversion
(dual slope)
Integration time
noise suppression)
20 ms at 50 Hz
16.6 ms at 60 Hz
Encoding time
per input
- for 2048 units
- for 4095 units
Noise suppression
for f=nx
(50/60 Hz±1%);
n=1,2, ...
- common-mode
rejection (Vpp=1 V)
input range)
min.
min.
86 dB
40 dB
Basic error limits
±0.2 %
(0 to 60 °C)
(32 to 140 °F)
±0.45 %
Single errors
- linearity
- tolerance
±0.05 %
±0.05 %
±0.05 %
Temperature error
- final value
- zero point
±0.01 %/K
±0.002 %/K
Length of cable
- shielded
max.
200 m (660 ft.)
Supply voltage L+
none
not possible
max.
max.
max.
max.
60 ms at 50 Hz
50 ms at 60 Hz
80 ms at 50 Hz
66.6 ms at 60 Hz
Insulation rating
VDE 0160
(+9 V to
- insulation group
- tested with
12 V AC
1×B
500 V AC
60 V AC
1×B
500 V AC
Permissible voltage
difference
- between inputs
max.
±1 V
max.
75 V DC/60 V AC
Permissible
input voltage
(destruction limit)
(inputs to +9 V)
- insulation group
- tested with
max.
80 mA
Current consumption
- from +9 V (CPU)
typ.
70 mA
Power loss of the
module
typ.
0.7 W
Weight
approx.
230 g (8 oz.)
- range exceeded
- sensor wire break
break
yes (more than
4095 units)
no
no
14-47
Module Spectrum
S5-100U
Analog Input Module 4 x 4 to 20 mA
(6ES5 464-8ME11)
4
3
2
1
operating
mode
L+
1
M
2
24V
3+
Ch.0
45+
Ch.1
67+
Ch.2
89+
Ch.3
10 -
6
ANALOG INPUT
4 x 4 ... 20 mA
6ES5 464-8ME11
1
2
3
4
5
6
+9 V
GND
Data
+9 V
GND
Data
31,2
1
3
2
14-48
M
5
4
L+
31,2
7
6
9
8
1
10
3
2
Ch.1
7
6
9
8
10
Ch.0
5
4
Ch.2
Ch.3
U
S5-100U
Module Spectrum
Analog Input Module 4 x 4 to 20 mA (continued)
(6ES5 464-8ME11)
Input ranges
(rated values)
4 to 20 mA
Number of inputs
1, 2 or 4
(selectable)
Galvanic isolation
yes (inputs to
between inputs)
Input resistance
31.25
Connection method
of sensors
two-wire connection
for 2/4 wire transducers
of input signal
12 bits+sign
(2048 units
=rated value)
Measured value
representation
two's complement
(left-justified)
Measuring principle
integrating
voltage-time
conversion
(dual slope)
Integration time
noise suppression)
Encoding time
per input
- for 2048 units
- for 4095 units
Permissible voltage
difference
- between inputs
Permissible
input voltage
(destruction limit)
20 ms at 50 Hz
16.6 ms at 60 Hz
max.
max.
max.
max.
60 ms at 50 Hz
50 ms at 60 Hz
80 ms at 50 Hz
66.6 ms at 60 Hz
max.
±1 V
max.
Noise suppression
for f=nx
(50/60 Hz±1%);
n=1, 2, ...
- common-mode
rejection (Vpp=1 V)
input range)
min.
86 dB
min.
40 dB
Basic error limits
±0.15 %
(0 to 60 °C)
(32 to 140 °F)
±0.4 %
Single errors
- linearity
- tolerance
±0.05 %
±0.05 %
Temperature error
- final value
- zero point
±0.01 %/K
±0.002 %/K
Length of cable
- shielded
max.
200 m (660 ft.)
Supply voltage L+
for 2-wire transducers
- rated value
- ripple Vpp
- permissible range
24 V DC
3.6 V
20 to 30 V
not possible
Insulation rating
VDE 0160
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
(inputs to +9 V)
- insulation group
- tested with
60 V AC
1×B
500 V AC
75 V DC/60 V AC
max.
- range exceeded
80 mA
yes (more than
4095 units)
no
Current consumption
- from +9 V (CPU)
- from L+
no
70 mA
80 mA
Power loss of the
module
- for 2-wire transducers typ.
- for 4-wire transducers typ.
1.0 W
0.7 W
Weight
- sensor wire break
break
typ.
typ.
230 g (8 oz.)
approx.
14-49
Module Spectrum
S5-100U
Analog Input Module 2 x PT 100/±500 mV
(6ES5 464-8MF11)
broken wire
4
3
2
1
operating
mode
IC+
7
M+
3
Ch.0
4
8
MIC-
9
5
IC+
M+
Ch.1
6
10
MIC-
6
ANALOG INPUT
2×Pt100
6ES5 464-8MF11
1
2
3
4
5
6
+9 V
GND
Data
broken
wire
1
3
5
2
7
4
9
6
8
10
2×PT100
Ch.0
14-50
Ch.1
IC0
IC1
S5-100U
Module Spectrum
Analog Input Module 2 × PT 100/±500 mV (continued)
(6ES5 464-8MF11)
Input range
(rated values)
- resistance
sensor (PT 100)
0 to 200
(max. 400 )
± 500 mV
- voltage sources
Number of inputs
1 or 2
(selectable)
Galvanic isolation
yes (inputs to
between inputs)
Input resistance
10 M
Connection method
of sensors
two or four-wire
connection
of input signal
12 bits + sign
(2048 units
= rated value)
Measured value
representation
two's complement
(left-justified)
Measuring principle
integrating
voltage-time
conversion
(dual slope)
Noise suppression
for f = nx
(50/60 Hz±1%)
n = 1, 2, ...
- common mode
rejection (Vpp=1 V)
& lt; rated value
of input range)
min.
min.
86 dB
40 dB
Basic error limits
± 0.15%
(0 to 60 °C)
(32 to 140 °F)
± 0.4%
Single errors
- linearity
- tolerance
± 0.05%
± 0.05%
± 0.05%
Temperature error
- final value
- zero point
± 0.01 %/K
± 0.002 %/K
Length of cable
- shielded
max.
200 m (660 ft.)
Supply voltage L+
Auxiliary current
for PT 100
none
2.5 mA
Resistance sensor
- tolerance
- temperature error
- load dependency
± 0.05%
± 0.006%/K
± 0.02%/100
Integration time
(adjustable for optimum noise suppression)
20 ms at 50 Hz
16.6 ms at 60 Hz
Encoding time per input
- for 2048 units
max.
max.
- for 4095 units
max.
max.
Insulation rating
VDE 0160
60 ms at 50 Hz
50 ms at 60 Hz
80 ms at 50 Hz
66.6 ms at 50 Hz
(+9 V to )
- insulation group
- tested with
12 V AC
1xB
500 V AC
max.
±1V
max.
75 V DC/60 V AC
(inputs to + 9 V)
- insulation group
- tested with
60 V AC
1xB
500 V AC
Permissible voltage
difference
- between inputs
Permissible
input voltage
(destruction limit)
- range exceeded
- sensor wire break
of wire break
Current consumption
- from + 9 V (CPU)
max.
24 V DC
yes (more than
4095 units)
yes (selectable)
typ.
70 mA
Power loss of
the module
typ.
0.9 W
Weight
approx.
230 g (8 oz.)
red LED
14-51
Module Spectrum
S5-100U
(6ES5 464-8MF21)
broken wire
8
7
6
5
4
3
2
1
operating
mode I +
C
7
M+
3
Ch.0
4
8
MIC-
9
5
IC+
M+
Ch.1
6
10
MIC-
6
ANALOG INPUT
2×Pt100
6ES5 464-8MF21
1
2
3
4
5
6
+9 V
GND
Data
broken
wire
1
3
5
2
7
4
9
6
8
10
2×PT100
Ch.0
14-52
Ch.1
IC0
IC1
S5-100U
Module Spectrum
(6ES5 464-8MF21)
Input range
(rated values)
- resistance sensor (PT 100)
- voltage source
0 to 200
(max. 400 )
± 500 mV
Number of inputs
1 or 2
(selectable)
Galvanic isolation
yes (inputs to
between inputs)
Input resistance
10 M
Connection method
of sensors
two or four-wire
connection
of input signal
12 bits + sign
(2048 units = rated
value)
Measured value
representation
two's complement
(left-justified)
Measuring principle
integrating
voltage-time conversion (dual slope)
Integration time
noise suppression)
20 ms at 50 Hz
16.6 ms at 60 Hz
Encoding time
per input
- for 2048 units
- for 4095 units
Permissible voltage
difference
- between inputs
Permissible input
voltage
(destruction limit)
- range exceeded
- sensor wire break
of wire break
Noise suppression for f = nx
(50/60Hz ± 1%);
n = 1, 2, ...
- common mode
rejection
(V = 1 V)
min.
PP
- series-mode rejection min.
& lt; rated value
of input range)
86 dB
40 dB
Basic error limits
±0.15%
(0 to 60 °C)
(32 to 140 °F)
±0.4 %
Single errors
- linearity
- tolerance
±0.05%
±0.05%
±0.05%
Temperature error
- final value
- zero point
±0.01%/K
± 0.002%/K
in rated range
±0.5 °C
(0.9 °F)
60 ms at 50 Hz
50 ms at 60 Hz
80 ms at 50 Hz
66.6 ms at 60 Hz
max.
±1V
max.
75 V DC/60 V AC
max.
24 V DC
yes (more than
4095 units)
yes (selectable)
DIN IEC 751
Length of cable
- shielded
max.
max.
max.
max.
of PT 100-characteristic curve
200 m (660 ft.)
max.
Supply voltage L +
Auxiliary current for PT 100
none
2.5 mA
Resistance-type sensor
- tolerance
- temperature error
- influence of load variation
±0.05%
±0.006%/K
±0.02%/100
Insulation rating
VDE 0160
(+9 V to )
- insulation group
- tested with
12 V AC
1xB
500 V AC
(inputs to + 9V)
- insulation group
- tested with
60 V AC
1xB
500 V AC
typ.
100 mA
typ.
0.9 W
Weight
Current consumption
- from + 9 V (CPU)
Power loss of the
module
red LED
approx.
230 g (8 oz.)
14-53
Module Spectrum
S5-100U
Analog Input Module 4 × +0 to 10 V
(6ES5 466-8MC11)
3+
Ch.0
45+
Ch.1
67+
Ch.2
89+
Ch.3
10 -
6
ANALOG INPUT
4 x 0 ...10 V
6ES5 466-8MC11
1
2
3
4
5
6
+9 V
GND
Data
D
A
10 k
90 k
1
3
5
2
Ch.0
14-54
7
4
9
6
Ch.1
8
Ch.2
10
Ch.3
S5-100U
Module Spectrum
Analog Input Module 4 × +0 to 10 V (continued)
(6ES5 466-8MC11)
Input ranges
(rated values)
+0 to 10 V
Number of inputs
4
Galvanic isolation
no
Input resistance
100 k
Connection for the
signal sensor
2-wire connection
Basic error limits
Digital representation of
the input signal
Representation of the
measured value
±0.6%
Single errors
- linearity
- tolerance
±0.1%
±0.1%
Temperature error
- final value
- zero point
±0.01% K
±0.01% K
Length of cable
- shielded
max.
200 m (660 ft.)
binary *
Encoding time
per input
Current consumption
- from + 9 V (CPU)
typ.
100 mA
100 µs
Conversion time
Supply voltage L+
successive
approximation
Measuring principle
Permissible voltage
difference
- between inputs
(0 to 60 °C)
(32 to 140 °F)
8 bits (256 units
= rated value)
±0.4%
Power loss
of the module
typ.
0.9 W
Weight
approx.
200 g (7 oz.)
5 ms
max.
none
±1 V
Permissible input voltage
(destruction limit)
max.
60 V DC
- range exceeded
- sensor wire break
of wire break
no
no
no
Noise suppression
- common mode
interference (V =1 V) min.
PP
86 dB
Bit
7 6 5 4 3 2 1 0
27 26 25 24 23 22 21 20
Units
Input voltage
in V
255
254
9.961
9.922
1
1
1
1
1
1
1
1
1
1
1
1
1
1
1
0
192
191
7.500
7.461
1
1
1
0
0
1
0
1
0
1
0
1
0
1
0
1
128
127
5.000
4.961
1
0
0
1
0
1
0
1
0
1
0
1
0
1
0
1
64
63
2.500
2.461
0
0
1
0
0
1
0
1
0
1
0
1
0
1
0
1
1
0
0.039
0.000
0
0
0
0
0
0
0
0
0
0
0
0
0
0
1
0
14-55
Module Spectrum
S5-100U
14.7.2 Analog Output Modules
Analog Output Module 2 x ±10 V
(6ES5 470-8MA12)
Output range
(rated values)
±10 V
Number of outputs
2
Galvanic isolation
yes (outputs to
grounding point and
between outputs)
Input resistance
L+
1
2
R
5
6 MANA
8
7 S+
yes
±30 mA
Permissible voltage
difference to ground
and between outputs
max.
75 V DC/60 V AC
Basic error limits
6
+9 V
GND
Data
0V
- 15V
+15V
±0.6%
Single errors
- linearity
- temperature error
2 x± 10 V
6ES5 470-8MA12
±0.3%
(0 to 60 °C)
(32 to 140 °F)
ANALOG OUTPUT
5
25%
Short-circuit current
6
4
0.15 ms
R
Ch.1
S-
R 3,3k
3
max.
Permissible overload
10 MANA
1 2
two's complement
(left-justified)
Conversion time
(0 to 100%)
QV
9
11 bits + sign
(1024 units =
rated value)
Measured value
representation
24 V
4
3 S+
Ch.0
S-
3.3 k
two or four-wire
connection
of output signal
M
QV
min.
Connection method
±0.2%
±0.1%
±0.01%/K
Length of cable
- shielded
max.
200 m (660 ft.)
Supply voltage L+
(peripheral)
- rated value
- ripple V
PP
- permissible range
(ripple included)
24 V DC
3.6 V
20 to 30 V
3
2
5
4
7
6
9
8
S+ QV S- MA S+ QV S- MA
10
VDE 0160
(+9 V to )
- insulation group
- tested with
1
Insulation rating
12 V AC
1xB
500 V AC
(Output to L +, between
outputs, output to + 9V)
- insulation group
- tested with
60 V AC
1xB
500 V AC
Current consumption
- from + 9 V (CPU)
- from L +
L+
M
Ch.0
Legend:
QV: Analog output ”voltage”
14-56
Ch.1
typ.
typ.
120 mA
100 mA
Power loss
of the module
typ.
3.1 W
Weight
approx.
220 g (8 oz.)
S5-100U
Module Spectrum
Analog Output Module 2 x ±20 mA
(6ES5 470-8MB12)
Output range
(rated values)
±20 mA
Number of outputs
2
Galvanic isolation
yes (outputs to
grounding point and
between outputs)
Input resistance
L+
1
2
4
24 V
R
Ch.0
6
8
11 bits + sign
(1024 units =rated
value)
Measured value
representation
Conversion time
(0 to 100%)
MANA
300
two-wire connection
of output signal
M
QI
max.
Connection method
two's complement
(left-justified)
max.
0.15 ms
QI
R 300
6
5
6
+9 V
GND
Data
0V
- 15V
+15V
1
3
2
±0.6%
±0.2%
±0.1%
±0.01%/K
max.
Supply voltage L+
- rated value
- ripple V
PP
- permissible range
(ripple included)
200 m (660 ft.)
24 V DC
3.6 V
20 to 30 V
Insulation rating
5
MANA
7
6
9
8
+QI
MANA
10
VDE 0160
(+9 V to )
- insulation group
- tested with
4
+QI
Length of cable
- shielded
75 V DC/60 V AC
±0.3%
(0 to 60 °C)
(32 to 140 °F)
Single errors
- linearity
- temperature error
2 x± 20 mA
6ES5 470-8MB12
4
max.
Basic error limits
ANALOG OUTPUT
3
± 12 V
Permissible voltage
difference to central
ground point and
between outputs
10 M
ANA
1 2
yes
Leerlaufspannung
R
Ch.1
25%
12 V AC
1xB
500 V AC
(output to L+, between
outputs, output to + 9 V)
- insulation group
- tested with
60 V AC
1xB
500 V AC
Ch.0
120 mA
130 mA
typ.
3.8 W
Weight
M
typ.
typ.
Power loss of the
module
L+
Current consumption
- from + 9 V (CPU)
- from L +
approx.
220 g (8 oz.)
Ch.1
Legend:
QI: Analog output ”current”
14-57
Module Spectrum
S5-100U
Analog Output Module 2 x 4 to 20 mA
(6ES5 470-8MC12)
Output range
(rated value)
4 to 20 mA
Number of outputs
2
Galvanic isolation
yes (outputs to
grounding point and
between outputs)
Load resistance
1
2
4
8
300
Connection method
L+
QI
two-wire connection
of output signal
M
24 V
R
Ch.0
6
max.
11 bits + sign
(1024 units = rated
value)
Measured value
representation
Conversion time
(0 to 100%)
MANA
QI
two's complement
(left-justified)
max.
0.15 ms
10 M
ANA
yes
Leerlaufspannung
Ch.1
25%
R
±12 V
Permissible voltage
ground point and
between outputs
R 300
6
max.
75 V DC/60 V AC
Basic error limits
2 x 4 ... 20 mA
6ES5 470-8MC12
1 2
3
4
5
6
+9 V
GND
Data
±0.6%
Single errors
- linearity
- temperature error
ANALOG OUTPUT
±0.2%
(0 to 60 °C)
(32 to 140 °F)
±0.2%
±0.01%/K
Length of cable
- shielded
max.
200 m (660 ft.)
1
3
2
5
4
+QI
7
6
MANA
9
8
+QI
MANA
10
VDE 0160
(+9 V to
- insulation group
- tested with
+15V
24 V DC
3.6 V
20 to 30 V
Insulation rating
0V
- 15V
Supply voltage L+
- rated value
- ripple VPP
- permissible range
(ripple included)
12 V AC
1xB
500 V AC
(outputs to L+,
between outputs,
output to + 9 V )
- insulation group
- tested with
60 V AC
1xB
500 V AC
Current consumption
- from + 9 V (CPU)
- from L+
L+
M
Ch.0
Legend:
14-58
Ch.1
typ.
typ.
120 mA
130 mA
Power loss of
the module
typ.
3.8 W
Weight
approx.
220 g (8 oz.)
S5-100U
Module Spectrum
Analog Output Module 2 x 1 ... 5 V
(6ES5 470-8MD12)
Output range
(rated values)
Number of outputs
Galvanic isolation
Input resistance
Connection method
1
L+
M
2
4 QV
of output signal
Measured value
representation
Conversion time
(0 to 100%)
R
Ch.0
8
SMANA
QV
7 S+
Permissible voltage
ground point and
between outputs
Basic error limits
(0 to 60 °C)
(32 to 140 °F)
R
Ch.1
9
10
SMANA
R 3,3k
6
ANALOG OUTPUT
3
4
5
6
+9 V
GND
Data
0V
- 15V
+15V
1
3
5
7
two's complement
(left-justified)
max.
9
0.15 ms
25%
yes
±30 mA
max.
75 V DC/60 V AC
±0.2%
±0.6%
Single errors
- linearity
- temperature error
2 x 1 ... 5 V
6ES5 470-8MD12
1 2
11 bits + sign
(1024 units=rated
value)
24 V
3 S+
5
6
min.
1 to 5 V
2
yes (outputs to
grounding point and
between outputs)
3.3 k
two or four-wire
connection
±0.2%
±0.01%/K
Length of cable
- shielded
max.
Supply voltage L+
- rated value
- ripple VPP
- permissible range
(ripple included)
Insulation rating
(+9 V to )
- insulation group
- tested with
(outputs to L+,
between outputs,
output to +9 V)
- insulation group
- tested with
200 m (660 ft.)
24 V DC
3.6 V
20 to 30 V
VDE 0160
12 V AC
1xB
500 V AC
60 V AC
1xB
500 V AC
L+
Current consumption
- from +9 V (CPU)
- from L+
typ.
typ.
120 mA
100 mA
Power loss of
the module
Weight
10
2
4
6
8
typ.
approx.
3.1 W
220 g (8 oz.)
M
Ch.0
Ch.1
14-59
15
Function Modules
15.1
Comparator Module 2 × 1 to 20 mA/0.5 to 10 V
15.2
Timer Module 2 × 0.3 to 300 s
15.3
Simulator Module . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15 - 7
15.4
Diagnostic Module . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15 - 9
15.5
Counter Module 2 × 0 to 500 Hz
15 - 12
15.6
15.6.1
15.6.2
15.6.3
15.6.4
15.6.5
15 - 1
15 - 4
Counter Module 25/500 kHz . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Installation Guidelines . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Data Transfer . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Functional Description of the Counter Mode . . . . . . . . . . . . . . . . .
Functional Description of the Position Decoder . . . . . . . . . . . . . . .
Entering New Setpoints for the Counter and
Position Decoder . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15.6.6 Addressing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15
15
15
15
15
15.7
Closed-Loop Control Module IP 262
15 - 41
15.8
IP 263 Positioning Module
15.9
IP 264 Electronic Cam Controller Module . . . . . . . . . . . . . . . . . . .
15 - 49
15.10
IP 265 High Speed Sub Control
15 - 52
15.11
Positioning Module IP 266
15 - 55
15.12
Stepper Motor Control Module IP 267
17
20
25
27
29
15 - 38
15 - 39
15 - 45
15 - 59
15.13 Communications Modules . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15.13.1 Printer Communications Module CP 521 . . . . . . . . . . . . . . . . . . .
15.13.2 Communications Module CP 521 BASIC . . . . . . . . . . . . . . . . . . .
15 - 62
15 - 62
15 - 65
Figures
15-1
15-2
15-3
15-4
15-5
15-6
Scanning the Comparator Module . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Scanning the Timer Module . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Scanning the Simulator Module as a Digital Input . . . . . . . . . . . . . . . . . .
Setting the Input Voltage Range on the Counter Module (500 Hz)
Scanning the Counter Module (500 Hz) . . . . . . . . . . . . . . . . . . . . . . . . .
Timing Diagram: Setting and Resetting an Output of the
Counter Module (500 Hz) . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-7
Switch Positions on the Operating Mode Switch . . . . . . . . . . . . . . . . . . .
15-8
Pin Assignment of the 15-Pin Sub-D Female Connector . . . . . . . . . . . . .
15-9
Connecting a Counting Pulse Sensor for 5-V Differential Signal to RS 422
15-10 Connecting a Counting Pulse Sensor for 24 V DC . . . . . . . . . . . . . . . . .
15-11 Connecting a 5-V Position Sensor to RS 422 . . . . . . . . . . . . . . . . . . . . .
15-12 Connecting a 24-V DC Position Sensor . . . . . . . . . . . . . . . . . . . . . . . . .
15-13 Signal Sequence for Up-Counting . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-14 Assignment Diagram for the Terminal Block . . . . . . . . . . . . . . . . . . . . . .
15-15 Diagnostic Byte . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-16 Switching the Outputs Dependent on the Status of the Counter and
the Enable Input . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-17 Position of the Reference Point (SYNC Bit 0 -- & gt; 1) within the
Reference Signal Range . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-18 Position of the Reference Point (SYNC Bit 0 -- & gt; 1) after the Reference
Signal . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-19a Synchronization (SYNC Bit 0 -- & gt; 1) during a Reversal of Direction
before Reaching the Reference Pulse in a Positive Direction . . . . . . . . . .
15-19b No Synchronization during a Reversal of Direction before
Reaching the Reference Pulse in a Positive Direction . . . . . . . . . . . . . . .
15-20 Schematic of a Reference Point Approach Operation . . . . . . . . . . . . . . .
15-21 Enabling the Outputs - Reaching the Setpoints - Resetting the Outputs
15-22 Approaching a Setpoint in Up-Count Direction . . . . . . . . . . . . . . . . . . . .
15-23 Approaching a Setpoint in Down-Count Direction . . . . . . . . . . . . . . . . . .
15-24 Approaching a Setpoint in Up-Count Direction and Consecutive
Reversal of Direction . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-25 Requirement for New Setpoints . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-26 Positioning with the IP 263 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-27 Units of Measurement that IP 266 Can Process for Circular Axis
and Linear Axis . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15-28 Course of a Following Error during a Positioning Operation . . . . . . . . . . .
15-29 Velocity Profile of the IP 267 . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15
15
15
15
15
- 2
- 5
- 8
- 14
- 15
15
15
15
15
15
15
15
15
15
15
15
19
20
21
21
22
22
23
24
26
15 - 28
15 - 32
15 - 32
15 - 33
15
15
15
15
15
33
33
34
35
36
15 - 36
15 - 38
15 - 48
15 - 56
15 - 57
15 - 60
Tables
15-1
15-2
15-3
15-4
15-5
15-6
15-7
15-8
Sending Data from the Programmable Controller to the Counter Module . . .
Sending Data from the Counter Module to the Programmable Controller
Pulse Evaluation . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Example for a Traversing Range . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Reaction of the Counter Module during Transfer of the Setpoints . . . . . . . .
Slot Addressing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Meaning of the Address Bytes of a Slot Address (Example: Slot 1) . . . . . .
Designation of the Operating Modes . . . . . . . . . . . . . . . . . . . . . . . . . . . .
15
15
15
15
15
15
15
15
25
25
30
31
38
39
39
58
S5-100U
Function Modules
15
Function Modules
15.1
(6ES5 461-8MA11)
Technical Specifications
Channels
Galvanic isolation
Current or voltage
measurement
no measuring
Display
green LED for actual
value setpoint
Setpoint adjustment
with potentiometer
Setting error
0
switch-selectable
Switch position “0”
±10%
Reproducibility
±2%
Hysteresis
3
2
yes
10%
4
U
O
I
9
“V” measuring range
0.5 to 10 V DC
10
Input resistance
47 k
1
Inherent delay
5 ms
Input voltage
U
O
I
typ.
max.
100 V DC
( 0.5 s)
“I” measuring range
Input resistance
2
3
4
5
6
+9 V
GND
Data
30 V AC
2×B
500 V AC
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
Length of cable
- shielded
- unshielded
1
VDE 0160
Rated insulation
voltage
(+9 V to measuring
circuit and between
measuring circuits)
- insulation
- tested with
COMPARATOR
100%
Insulation rating
0.5 to 10V/1 to 20mA
6ES5 461-8MA11
500
Overload capability
6
0.5 to 20 mA
200 m (660 ft.)
100 m (330 ft.)
Current consumption
- from +9 V (CPU)
3
5
4
V
7
6
typ.
0.3 W
Weight
2
35 mA
Power losses
of the module
1
typ.
9
8
10
I
15-1
Function Modules
S5-100U
Function
The module has two isolated comparators for voltage or current measurement (selector switch with
positions U/0/I). When the preset value is reached, the LED of the respective channel lights up and
sends a “1” signal to the programmable controller.
The module must be removed or the measuring circuit disconnected before you select the function.
In switch position “0”, the comparator is switched off; if scanned, a “0” signal results.
The response threshold of the comparator is set by a selector on the front panel. The selector has
scale divisions to simplify adjustment.
Installation
The comparator module is mounted on a bus unit like any other input or output module
(see chapter 3).
Wiring
See schematic diagram. Unused inputs can be left open.
Addressing
The comparator module is addressed like a 2-channel digital input module (channel “0” or “1”).
Scan
(examples)
A
O
I
I
x.0
x.1
Channel “0”
Channel “1”
Channel number
Slot address
Figure 15-1. Scanning the Comparator Module
15-2
S5-100U
Function Modules
Typical Application
A comparator module is mounted at slot 4. The current source is connected to channel 1. If the
Schmitt trigger 1 detects that the current has exceeded the preset value, output 5.1 is to be set.
Terminal Connections
1
3
2
5
4
7
6
9
8
10
STL
A
I
Q
Explanation
4.1
5.1
As soon as the limit is reached or exceeded, input 4.1
becomes " 1 " ; this sets output 5.1 to " 1 " .
15-3
Function Modules
15.2
S5-100U
(6ES5 380-8MA11)
Number of timers
Time setting
Range extension factor
±10%
Reproducibility
±3%
Temperature influence
+1%/10 °C (50 °F)
of set time
Insulation rating
VDE 0160
(+ 9 V to )
- insulation group
- tested with
1
green LED
Setting error
x 0.3s
x 3s
x 30s
0.3 to 3 s
×10, ×100
Function indication
0
2
12 V AC
1×B
500 V AC
Current consumption
- from +9 V (CPU)
typ.
Weight
10 mA
x 0.3s
x 3s
x 30s
6
TIMER
2 x 0.3-300s
6ES5 380-8MA11
1
2
3
4
5
6
+9 V
GND
Data
0.3 s
1
300 s
3
2
15-4
5
4
X.0
0.3 s
300 s
7
6
9
8
10
X.1
S5-100U
Function Modules
Function
The module contains two pulse timers. While a timer runs, the LED of the respective channel is lit
and a “1” is reported to the CPU.
The pulse duration is preselected with the time range selector “x 0.3 s / x 3 s / x 30 s” in a definite
range and then set to the exact value by means of a potentiometer on the front panel. This selector
has scale divisions to simplify setting.
(time value=time range x scale value)
Example:
Time range:
Scale value:
Set time:
x3s
7
7 x 3 s=21 s
Installation
The counter is inserted into a bus unit like any other input or output module (see chapter 3).
Wiring
No wiring is required.
Addressing
A timer module is addressed like a two-channel digital module (channel “0” or “1”).
The timer module is addressed like a digital output module for starting, resetting, or interrupting the
pulse. The signal status is scanned like a digital input module.
Starting the pulse
S
S
Q
Q
x.0
x.1
Interrupt/
Reset
R
R
Q
Q
x.0
x.1
Scan
“1” = timer running
A
A
I
I
Channel “0”
Channel “1”
x.0
x.1
Channel number
Slot address
Figure 15-2. Scanning the Timer Module
15-5
Function Modules
S5-100U
Typical Application as “On-Delay Timer”
A timer module is mounted at slot 5. A time of 270 s is set on channel “0” of this module by means
of the time-range selector and the potentiometer. The timer is started when input 0.0 is “1”.
A lamp lights up (output 4.0) when the timer has run down.
No process peripherals are connected to this
module.
Unlike the internal timers, times can be set or
modified using a timer module without
making any program modifications.
STL
A
I
0.0
AN I
A F
S Q
A I
= F
AN I
5.0
65.0
0.0
R
A
15-6
5.0
65.0
4.0
4.0
0.0
5.0
Q
I
Q
Explanation
The timer must not be scanned in the program scan cycle in which it was
enabled since the CPU would not receive the acknowledgement that the
timer had started until one program scan later.
If flag 65.0 is “1” and the timer has run down (AN I 5.0), output 4.0 is set
to “1”.
If the “Timer started” message has been sent to the CPU, the flag is set.
If I 0.0 is “0”, the lamp is switched off.
The timer is started if I 0.0 is “1”.
S5-100U
15.3
Function Modules
Simulator Module
(6ES5 788-8MA11)
Function selection
- simulation of 8 input
signals
- display of 8 output
signals
IN
selected by switch
on rear of module
Function indication
yellow LED
OUT
“0”/“1” input signals
.4
.5
.6
green LEDs
Current consumption
- from +9 V (CPU)
.3
12 V AC
1×B
500 V AC
Signal status display for
input/output
.2
VDE 0160
Rated insulation
voltage
(+9 V to )
- insulation group
- tested with
.1
switch-selectable
Insulation rating
.0
30 mA
Power loss of the
module
.7
Weight
typ.
0.3 W
190 g (6.7 oz.)
SIMULATOR
INPUT/OUTPUT
6ES5 788-8MA11
1
2
3
4
5
6
+9 V
GND
Data
OUT
3
IN
1
2
5
4
7
6
9
8
10
15-7
Function Modules
S5-100U
Function
Simulator modules are 8-channel modules that can simulate digital input signals and display output
signals.
The type of module to be simulated (input or output) is selected by means of a switch on the rear of
the module and indicated by two LEDs on the front panel.
The module cannot simulate interrupt inputs.
Installation
The simulator module is inserted into a bus unit like any other input or output module (see
chapter 3). The module does not have a coding key and can therefore replace any digital module.
The coding element on the bus unit does not have to be readjusted.
Wiring
There is no electrical connection between the module and the terminal block. It can therefore be
inserted into slots that have already been wired and connected to the power supply.
Addressing
A simulator module is addressed like an 8-channel digital module (channels 0 to 7).
Scan
(examples)
A
O
I
Q
0.0
1.1
Channel “0”
Channel “1”
Channel number
Slot address
Figure 15-3. Scanning the Simulator Module as a Digital Input
Typical Application
The CPU is in the RUN mode, the green LED is lit but the programmable controller is malfunctioning. You have also discovered that the fault must be in a particular I/O module. If the
module has no fault indicator, check to see if:
The power supply is connected.
The bus connections and interface modules are plugged in correctly.
Then, try to access the module via the process image (STATUS or STATUS VAR). If this
procedure is not successful, replace the module with the simulator module. Perform a second
check with the STATUS or STATUS VAR function. If the simulator performs, the input/output
module you replaced is defective.
15-8
S5-100U
15.4
Function Modules
Diagnostic Module
(6ES5 330-8MA11)
Insulation rating
VDE 0160
(+9 V to )
- insulation group
- tested with
12 V AC
1×B
500 V AC
U1 8V
Voltage monitor
- undervoltage
- voltage ok
red LED
green LED
U1 & gt; 8V
control signals
yellow LEDs
Current consumption
- from+9 V (CPU)
25 mA
DATA
DATA-N
Power loss of
the module
LATCH
typ.
Weight
IDENT
approx. 175 g (6.1 oz.)
0.3 W
CLOCK
CLEAR
BUS SIGNAL
DISPLAY
6ES5 330-8MA11
1
2
3
4
5
6
+9 V
GND
Data/Bus signals
VRef
+1024
1
3
2
5
4
7
6
9
8
10
15-9
Function Modules
S5-100U
Function
The diagnostic module is used for monitoring the S5-100U I/O bus. LEDs on the front panel display
the signal states of the control lines and the supply voltage for the I/O bus.
IDENT
The programmable controller executes an IDENT run after each change from STOP to RUN. It
executes an IDENT run after any changes in the configuration in order to determine the current
configuration. The IDENT LED lights up briefly. If the LED lights up in the RUN mode, this
indicates that a faulty I/O module has been plugged in.
CLEAR
The CLEAR signal line is “1” only in the STOP mode in normal operation.
The outputs of the output modules are disabled.
If CLEAR is “1” in the RUN mode, the control line itself may be defective (no contact).
LATCH/CLOCK
These two control lines control data interchange between the CPU, the I/O bus, and the I/O
modules.
During normal operation, both LEDs must flash (programmable controller in RUN mode).
The flashing frequency provides information on the speed of the serial bus.
If both LEDs show a steady light in the RUN mode, the bus unit that the diagnostic module is
plugged into is defective.
DATA/DATA-N
The alternate lighting up of the DATA and DATA-N LEDs indicates data flow on the I/O bus.
If these two LEDs show a steady light (as in the case of the LATCH and CLOCK LEDs), this
indicates that the bus unit that the diagnostic module is plugged into is defective.
U1 8 V
If the supply voltage of a slot remains at a value U1 8 V, proper functioning of the I/O
modules is no longer guaranteed. The low supply voltage can be explained by an excessively
high bus load ( & gt; 1 A).
If this LED flickers, noise pulses are superimposed on the supply voltage U1 (e.g., by the
coupling of noise pulses).
The LED lights up briefly if the programmable controller is switched on or off.
U1 & gt; 8 V
The supply voltage of the I/O bus is functioning correctly.
15-10
S5-100U
Function Modules
Installation
The diagnostic module is plugged into a bus unit like any other input or output module (see
chapter 3). The module has no mechanical coding. The coding element on the bus unit does not
have to be reset.
Note
The module can be plugged in and removed regardless of the operating status of the
Wiring
No wiring is required. Existing wiring does not have to be removed.
Addressing
There is no addressing since the module cannot be addressed by the programmable controller.
15-11
Function Modules
15.5
S5-100U
(6ES5 385-8MA11)
F
Q0
Q1
Ch.0
Ch.1
5V/24 V
Ch.0
Ch.1
6
COUNTER
500 Hz
6ES5 385-8MA11
1 2
3
4
5
6
+9 V
GND
Data
-0
-0
5V
24 V
1
3
2
15-12
5
4
7
6
9
8
10
S5-100U
Function Modules
Number of Inputs
2
Galvanic isolation
yes
1A
Driving a digital input
possible
5 V/24 V DC
0 to 0.8/-33 to 5 V
3 to 5 V/13 to 33 V
Input voltage
- rated value
- for “0” signal
- for “1” signal
of outputs
- max. current
possible
0.5 A
Permissible ambient
temperature for the unit
- horizontal arrangement
- vertical arrangement
0 to 60 °C (32 to 140 °F)
0 to 40 °C (32 to 104 °F)
Input current for
“1” signal
typ.
1.5/8.5 mA
Inherent delay
typ.
180 µs
Input frequency
max. 500 Hz
Connection of 2-wire BERO
proximity switches
(24 V DC)
- quiescent current
Length of cable
- unshielded
max.
100 m (330 ft.)
Insulation rating
possible
1.5 mA
max. 50 m (165 ft.)
Number of Outputs
2
Galvanic isolation
yes
Supply voltage L+
(for load)
- rated value
- permissible range
(including ripple)
Length of cable
- unshielded
24 V DC
20 to 30 V
Output current
for “1” signal
- rated value
- permissible range
- lamp load
Current consumption
- from+9 V (CPU)
typ.
20 mA
Power loss of the
module
typ.
2.5 W
Weight
max. 1 mA
Output voltage
- for “0” signal
- for “1” signal
60 V AC
1×B
1250 V AC
0.5 A
5 to 500 mA
max. 5 W
Residual current
at “0” signal
VDE 0160
(inputs and outputs to
each other and to
input to +9 V)
- insulation group
- tested with
max. 3 V
max. L+-2.5 V
Short-circuit protection
electronic
Fault indication (red LED)
short-circuit
limited to
L+-47 V
Switching frequency
- resistive load
- inductive load
EWA 4NEB 812 6120-02b
max. 100 Hz
max. 2 Hz
15-13
Function Modules
S5-100U
Function
The module consists of two independent down counters with isolated inputs and outputs. It counts
input signals up to a frequency of 500 Hz from a set value down to the value 0. When 0 is reached,
the 24-V DC output of the module is energized.
At the same time, a green LED on the module lights up and the input signal (I x.0 or I x.1) is set
to “1”.
The setpoint (0 to 999) can be entered via the three-digit thumbwheel switches on the front panel of
the module.
The input voltage ranges can be set for 5 V DC or 24 V DC using rocker switches on the front
panel.
Channel 0
Channel 0
Channel 1
Channel 1
5 V DC (TTL)
24 V DC
Figure 15-4. Setting the Input Voltage Range on the Counter Module (500 Hz)
Installation
The counter module is plugged into a bus unit like any other module (see chapter 3).
Wiring
See schematic diagram for the counter module.
15-14
S5-100U
Function Modules
Addressing
A counter module can be addressed like a two-channel digital module (channel “0” or “1”). For
enabling and resetting the counter, you address the module like a digital output module. The
counter reading is scanned in the same way as a digital input module.
Counter enable
(Set to start value)
S
S
Q
Q
x.0
x.1
Counter reset
R
R
Q
Q
x.0
x.1
Scan
“1” = Counter at zero
A
A
I
I
Channel “0”
Channel “1”
x.0
x.1
Channel number
Slot address
Figure 15-5. Scanning the Counter Module (500 Hz)
Timing Diagram
S Q x.0
R Q x.0
1
0
Enable
1
0
Counting
pulses
6
0
1
0
Output Q
Time
Figure 15-6.
15-15
Function Modules
S5-100U
Typical Application
A counter module is plugged into slot 2. A value of 100 is set on channel “0” of this module using
the three-digit thumbwheel switches. The incoming pulses are counted once the counter has been
enabled by the control program. As soon as 100 pulses have been counted, a signal (output 4.0) is
released.
Connection Diagram
1
3
2
STL
S
2.0
A
I
2.0
15-16
Q
Q
4.0
5
4
7
6
9
8
10
Explanation
During the counting operation, input I 2.0 is “0”. When
the counter status is “0”, input I 2.0 is set to “1”.
Output Q 4.0 is then also set. Direct output at terminals
5 and 6 is possible.
S5-100U
15.6
Function Modules
(6ES5 385-8MB11)
F
PD
SV
24 V
6
HIGH SPEED
COUNTER 25/500 kHz
6ES5 385-8MB11
1 2
3
4
5
6
+9 V
GND
Data
1
+5 V
24 V
3
4
5
8
1
3
2
5
4
7
6
9
8
10
15-17
Function Modules
S5-100U
Power supply for sensor
Operating mode
(switch-selectable)
- position decoder
- counter
24 V from L+
(PTC thermistor)
PD
C
Output current
Sensor inputs
1 sensor 5 V
(differential input) or
1 sensor 24 V DC
Digital Inputs
reference and
enabling
Rated input voltage
24 V DC
Digital inputs
2; reference and
enabling
Input voltage
- “0” signal
- “1” signal
- 33 to +5 V DC
+13 to 33 V DC
Digital outputs
2; setpoints reached 1
and 2
Galvanic isolation
no
max.
300 mA, shortcircuit proof
two's complement
(KF) - 32768 to
+32767
unipolar representation
(KH) 0 to 65535
- counter
typ.
8.5 mA
Input frequency
Counting range
Operating mode
- position decoder
Rated input current for
“1” signal and at 24 V
max.
100 Hz
Inherent delay
typ.
3 ms (1.4 to 5 ms)
Cable length (unshielded) max.
100 m (330 ft.)
Digital Outputs
setpoints 1 and 2
Output current
(resistive, inductive load)
5 mA to 0.5 A
Counting mode
- position decoder
- counter
up/down
up
Setpoint input
via program
Residual current for
“0” signal
5-V Sensor Input
15-pin Cannon subminiature D connector
Switching current
for lamps
differential signals
to RS 422
A A-N, B B-N, R R-N
A A-N
Limitation of inductive
interrupting voltage
Input signals
- position decoder
- counter
max.
0.5 mA
0.22 A (5 W)
to
-15 V
min.
max.
L+ - 2.2 V
3V
Counting frequency
max. 500 kHz
Output voltage
- “1” signal
- “0” signal
Cable length (shielded)
max. 50 m (165 ft.)
100 m (330 ft.)
(cable impedance up to 15 )
electronic
(short-circuit to M)
red LED
Power supply for decoder
Output current
5 V from L+via voltage
transformer
max. 300 mA, short-circuitproof
24-V Sensor Input
Rated input voltage
24 V DC
Input signals
- position decoder
- counter
A, B, R
A
Input voltage
- “0” signal
- “1” signal
- 33 to 5 V DC
+13 to 33 V DC
Rated input current
for “1” signal
typ.
Counting frequency
max. 100 m (330 ft.)
15-18
8.5 mA
max.
Fuse (internal)
24 V DC
3.6 V
20 to 30 V DC
T 5 A (slow blow)
Current consumption
- from L+
without sensor supply
without load
- internal (+9 V)
max. 25 kHz
Supply voltage L+
- rated value
- ripple Vpp
- permissible range
(including ripple)
30 mA
70 mA
Power consumption
of the module
typ.
Weight
approx. 250 g (9 oz.)
1.9 W+total output
current (IA)×1.1 V
S5-100U
Function Modules
Function
The counter module can be used as an up-counter or as an up/down counter for a position decoder.
The counting pulses are supplied by a sensor that you can connect to the 15-pin subminiature D
female connector of the module. You can choose from two types of sensors that fulfill the following
requirements:
5-V error voltages according to RS 422 (up to 500 kHz)
24-V signals (up to 25 kHz)
As additional inputs, the module has an enable input and a reference input.
By using the STEP 5 program, you can assign two setpoints via the I/O bus. Once the counter
status reaches one of these values, the respective output completes the circuit at terminal block
(Q 0 or Q 1). The status of the outputs is displayed in the diagnostic byte.
You can also read the following values by using the STEP 5 program:
The updated count
The diagnostic byte
You can preselect the following items on the operating mode switch:
The function mode
The position resolution
The input voltage range of the sensor
Position decoding (PD)
Counter (C)
Pos. resolution
Pos. resolution
PD
double
Pos. resolution
quadruple
24 V
SV
single
not allowed
Sensor connection
5V
Sensor connection
24 V
Figure 15-7. Switch Positions on the Operating Mode Switch
15-19
Function Modules
S5-100U
15.6.1 Installation Guidelines
Installing and Removing the Module
Plug the counter module into a bus unit like other I/Os.
The counter module can only be plugged into slots 0 through 7.
Set the coding key to number 6 on the bus unit.
Installing or Removing the Sensor
Disconnect the 24-V DC power supply (terminals 1 and 2 of the terminal block) before connecting or
disconnecting the sensor cables.
Warning
Connecting or disconnecting the 5-V sensor cable while the module is energized can
cause damage to the sensor.
Connection of Pulse and Position Sensors
Connect pulse and position sensors on the front plate by means of a 15-pin sub-D female
connector. The correct cable connectors are listed in Appendix D. The module can supply the
sensors (5 V DC or 24 V DC).
Basically, all sensors can be connected if they fulfill the requirements of the system signals and
supply voltage. Sensors with OPEN-COLLECTOR outputs cannot be connected to the module.
The shield connection of the sensors must be connected to the metallic front connector cover.
Pin
1
2
1
9
2
10
3
4
5
Assignment
5 V Supply voltage
5 V Sensor line
Ground
12
5
13
6
14
7
15
8
Rectangular-wave signal A-N (5 V)
Rectangular-wave signal A (5 V)
Supply voltage (24 V)
9
10
11
Rectangular-wave signal B (5 V)
Rectangular-wave signal B-N (5 V)
Reference pulse R (5 V)
Reference pulse R-N (5 V)
Rectangular-wave signal A (24 V)
Rectangular-wave signal B (24 V)
15
11
4
6
7
8
12
13
14
3
Reference pulse R (24 V)
Figure 15-8. Pin Assignment of the 15-Pin Sub-D Female Connector
15-20
S5-100U
Function Modules
Connecting Counting Pulse Sensors for 5-V Differential Signal to RS 422
Module
Electronic light
5V
1
Sensor line
5V
2
L+
3
0V
4
5V 5V 0V
24 V
M
5
6
5-V
Va
Pulse
sensor
A-N
7
A
8
9
10
11
12
13
16
15
Shield
Shell of subminiature D connector
Figure 15-9. Connecting a Counting Pulse Sensor for 5-V Differential Signal to RS 422
Module
1
2
3
4
M
5
0V
6
7
0V
8
L+
9
DC
DC 24V
10
24-V
Pulse
sensor
11
12
13
A
16
15
Shield
Figure 15-10. Connecting a Counting Pulse Sensor for 24 V DC
15-21
Function Modules
S5-100U
Module
Electronic light
5V
1
Sensor line
5V
2
L+
3
0V
4
5V 5V 0V
24 V M
5
6
5-V
Position
sensor
A-N
7
Va1
A
8
9
11
B
B-N
R
12
Va2
R-N
10
Va0
13
16
15
Shield
Figure 15-11. Connecting a 5-V Position Sensor to RS 422
Module
1
2
3
4
M
5
Electronic light source
0V
6
7
8
24 V
L+
9
0V
24 V
10
24-V
Position
sensor Va1
11
12
13
A
16
Va2
Va0
B
R
15
Shield
Figure 15-12. Connecting a 24 V DC Position Sensor
15-22
S5-100U
Function Modules
Sensor Requirements
The following requirements must be satisfied by the sensor signals to the module inputs:
Signal sequence for up-counting
t1
Sensor
signals: Va1
(A, A-N/A)
t
Va2
(B, B-N/B)
t
t
t
t1
t2
Va0
(R, R-N/R)
Figure 15-13. Signal Sequence for Up-Counting
Pulse time of the sensors
5-V Sensors
24-V Sensors
Pulses
t
10 µs
Va1 = Position decoder count pulses (A)
t1
2 µs
40 µs
Va2 = Position decoder count pulses (B)
t2
500 ns
500 ns
10 µs
Va0 = Position decoder ref. pulse (R)
Minimum edge steepness
5 V - differential signals according to RS 422A (A, A-N, B, B-N, R, R-N):
24 V - count pulses and reference pulse (A, B, R):
24 V - enable and reference signal:
5 V/µs
0.3 V/µs
0.3 mV/µs
15-23
Function Modules
S5-100U
Terminal Block
Proximity switches can be connected (contacts, two-wire BERO proximity limit switches) to the
inputs on the terminal block.
Terminal
Terminal Assignment
1
2
5
7
9
1
3
5
7
9
2
4
6
8
10
2
4
6
8
10
24-V DC supply for enable signal
DI enable signal
5
6
DQ 24 V/0.5 A setpoint (Q0)
Ground
24-V DC supply for reference signal
DI reference signal
9
10
3
3
4
7
8
1
24-V DC supply for the module
Ground
DQ 24-V/0.5 A setpoint 2 (Q1)
Ground
Figure 15-14. Assignment Diagram for the Terminal Block
Assignment of Inputs on the Terminal Block
Two-wire BERO proximity limit switches can be connected to the reference input. The enable
input can also be driven by a 24-V DC digital output module.
Outputs on the Terminal Block
There are two short-circuit protected 24-V DC digital outputs on the terminal block.
Short-Circuit Indication
A shorted output is indicated by the red LED on the front panel.
15-24
S5-100U
Function Modules
15.6.2 Data Transfer
The data is transmitted via the I/O bus. Four bytes are used.
Examples of data transfer are shown in section 15.6.6.
Transfer from the Programmable Controller to the Counter Module (PIQ)
The control program transfers two setpoints to the counter module by means of transfer operations.
Table 15-1. Sending Data from the Programmable Controller to the Counter Module
Byte 0
Byte 1
Byte 2
Setpoint 1
High byte
Byte 3
Setpoint 2
Low byte
High byte
Low byte
Transfer from the Counter Module (PII) to the Programmable Controller
The counter module transfers the diagnostic byte and the current counter status. In the control
program, this data can be read in by means of load operations and then evaluated.
Table 15-2. Sending Data from the Counter Module to the Programmable Controller
Byte 0
Irrelevant
Byte 1
Diagnostic
byte
Byte 2
Byte 3
Actual value
High byte
Low byte
15-25
Function Modules
S5-100U
Diagnostic Byte (Byte 1)
The diagnostic byte is byte 1 of the first input word. Byte 0 has no significance.
The diagnostic byte provides information on the following items:
- Preset position resolution
- Preset mode
- Status of setpoints
- Signal status of the sync bit for position decoding
Bit No.:
7
6
5
R
R
0
1
1
0
4
3
1
0
1
0
P/C OV
2
1
0
S2
S1
Sy
Position resolution
single
double
quadruple
not possible
Mode
Position decoding
Counter
1
0
Counter overflow
No counter overflow
1
0
Setpoint 2 reached
Setpoint 2 not reached
1
0
Setpoint 1 reached
Setpoint 1 not reached
1
0
Sync bit set
Sync bit not set *
1
0
X = irrelevant
If the sync bit is not set, a reference point approach must be implemented before operation
can continue in the Position Decoding mode.
Figure 15-15. Diagnostic Byte
15-26
S5-100U
Function Modules
15.6.3 Functional Description of the Counter Mode
In the operation mode “Counter”, the module works as a “port-controlled” up-counter and counts
the positive edges of the counting pulses while the enable input is active. If the counter reaches a
preselected setpoint, the respective output is enabled.
Initial Settings
Use the operating mode switch to make the following selections:
“Counter” (C)
Signal level of counting pulses (5 V or 24 V)
The position of the switches for the position resolution is irrelevant.
For this operation, you need a counting pulse sensor (e.g., BERO). The pulses can be applied as
5-V differential signals according to RS 422A (up to 500 kHz) or as 24-V signals (up to 25 kHz).
The sensor is connected to the sub-D connector of the module.
Loading Setpoints
The control program can transfer two setpoints to the module. These setpoints must be between 0
and 65,535.
The transfer of the setpoints via the module depends on whether the “setpoint 1 (setpoint 2)
reached” bit is set in the diagnostic byte (S1 and S2).
If the bit is not set, which means the existing setpoint has not been reached or has not been exceeded, the new setpoint is transferred immediately and is immediately valid.
If the bit is set, which means the existing setpoint has been reached or exceeded, the new setpoint
is valid only after a positive edge occurs at the enable input.
If you do not specify a setpoint, a setpoint of “0” applies.
Enabling the Counter
The signal state of the enable input (terminal 3 on the terminal block) determines the function of the
counter.
A positive edge at the enable input
Sets the counter to 0
Resets the diagnostic bits for “setpoint reached”
Resets the outputs
Enables the counter
Note
The enable input should be set to “1” only after the setpoint has been transferred.
Otherwise, the outputs are enabled automatically when the first positive edge occurs.
15-27
Function Modules
S5-100U
Disabling the Counter
A negative edge at the enable input disables the counter. The outputs, diagnostic bits, and the
counter are not reset. You can continue reading the current count. A positive edge at the enable
input resets the outputs and the diagnostic bytes.
Reaching the Setpoints - Setting the Outputs - Resetting the Outputs
If setpoints have been preselected and the counter is enabled, the module counts the positive edges
at the counter input. The count is incremented by “1” with every leading edge.
After setpoint 1 has been reached, output Q 0 is enabled. At the same time, status bit S1 is set.
After setpoint 2 has been reached, output Q 1 is enabled. At the same time, status bit S2 is set.
As long as the enable input is active, the counter counts the pulses. After the enable command has
been cancelled, the counter is disabled. The actual value remains constant.
You can read the current count in the STEP 5 program. The actual value is displayed as an
unsigned whole number and must be between 0 and 65,535.
Note
If no setpoint is preselected, the respective value “0” is assigned. The corresponding
output is enabled with the positive edge of the enable input.
Example: Setpoints S1=2 and S2=4 are entered into the counter
Counter status
0
1
2
3
4
5
5 0 1
2
Counting pulses
Enable
input
Output Q 0
(setpoint 1
reached)
Output Q 1
(setpoint 2
reached)
Figure 15-16.
Pulse is not counted because
counter is disabled by enable
input=0.
The count is " frozen " to the
current value.
the Enable Input
When the programmable controller goes from RUN to STOP, outputs Q 0 and Q 1 are reset.
15-28
S5-100U
Function Modules
Performance during Overflow
If the enabled counter exceeds the counter range limit 65,535 the following occurs:
Bit 3 (overflow) in the diagnostic byte is set to “1”.
The outputs and diagnostic bits for “setpoint reached” are disabled, but they remain unchanged.
The counting function continues. Thus the actual value is constantly updated.
You can continue to read all data from the module in the STEP 5 program:
The updated count
The status of the outputs at the time of the overflow (This status remains unchanged until the
overflow bit is reset.)
The set overflow bit
After an overflow, the counter can be reset by one of the following actions:
An overall reset of the programmable controller (STOP to RUN mode)
Note
After a cold restart of the programmable controller, the outputs are disabled. These
outputs can be enabled via a positive edge to the enable input.
15.6.4 Functional Description of the Position Decoder
In the operation mode “position decoder” the module works as an up/down-counter and counts the
pulses of the connected position encoder. Because of the phase offset of the two decoder signals
A and B, the counter determines the counting direction. If the counter reaches a preselected setpoint, the respective output is then turned on.
Settings
Set the following items on the operating mode switch:
“Position decoding” (PD) function
The desired position resolution (single, double, or quadruple)
The signal level of the counting pulses (5 V or 24 V)
15-29
Function Modules
S5-100U
Connect the sub-D interface female connector to an incremental position encoder that has to deliver
the following signals:
Two counting pulses offset by 90 degrees
A reference pulse
The pulses can be supplied as 5-V differential signals according to RS 422 (up to 500 kHz) or as
24-V DC signals.
Connect a switch to the enable input. This switch must deliver a 24-V signal. In the same way, the
reference pulse has to deliver a 24-V signal to the reference input.
Position Resolution
Counter capacity
The 16-bit up/down-counter permits a resolution of 65,536 units between -32,768 and +32,767.
The traversing range depends on the resolution of the position encoders.
Pulse evaluation
The counting pulses, which are offset by 90 degrees, can be subjected to single, double, or
quadruple evaluation. The necessary setting is made on the operating mode switch (see
section 15.6).
The accuracy of the traversing path increases accordingly if double or quadruple pulse evaluation is
used. However, the traversing range then available is reduced by the factor 2 or 4.
Table 15-3. Pulse Evaluation
Single
Evaluation
Double
Evaluation
Quadruple
Evaluation
0
0
01234
Counting pulse A
Counting pulse B
Count
15-30
1
1
2
S5-100U
Function Modules
Example:
A rotary incremental position encoder produces 1000 pulses per revolution.
The spindle has a pitch of 50 mm/revolution. The position encoder therefore produces 1000 pulses
for a traversing path of 50 mm (1 revolution).
The resolution of the encoder is therefore 50 mm/1000 pulses.
The counter can handle up to 65,536 pulses. With the above resolution, the following traversing
ranges are obtained:
Table 15-4. Example for a Traversing Range
Pulse evaluation
Single
Double
Quadruple
Traversing range
3.25 m (10.7 ft.)
1.625 m (5.3 ft.)
0.81 m (2.7 ft.)
Distance travelled/
pulse
50 µm
25 µm
12.5 µm
Loading Setpoints
In the STEP 5 program, two setpoints can be transferred to the module. These setpoints must lie
between -32768 and +32767.
The acceptance of the setpoints by the module depends on whether the “setpoint 1 (setpoint 2)
reached” bit has been set in the diagnostic byte.
If the bit is not set, which means the existing setpoint is not reached or not exceeded, the new
setpoint is immediately accepted and is immediately valid.
If the bit is set, which means the existing setpoint is reached or exceeded, the new setpoint is not
valid until a positive edge occurs at the enable input.
Synchronization of the Actual Value Detection (Reference Point Approach)
The synchronization of the actual value detection is necessary after Power ON and after a counter
overflow.
Synchronization performs one of the following functions:
The count (actual value) is set to “0” and the SYNC bit (bit 0 in the diagnostic bit) is set after
Power ON.
The overflow bit (bit 3 in the diagnostic byte) is reset after an overflow.
15-31
Function Modules
S5-100U
Prerequisites for a Synchronization
1. The reference signal
The sensor for the reference signal is connected to terminals 7 and 8 of the terminal block.
Synchronization is enabled with the leading edge (0 to 1) at terminal 8. If the signal was
already on “1” when the module was switched on, then the reference signal must be turned off
to restart the synchronization.
If the reference signal lies in the normal traversing range, the actual value will be constantly
resynchronized by the reference signal. To prevent the unwanted resynchronizing, you have to
mask out the reference signal after the first reference point approach.
2. The traversing direction after a positive edge of the reference signal
After the reference signal has been reached, the module has to recognize a positive traversing
path (up-counting) while the reference signal is still active (1). This means, you have to input
the reference signal with increasing actual value to synchronize the module.
3. The reference pulse
The reference pulse is generated by the position encoder at least once per revolution.
• The first reference pulse that the module recognizes after a leading edge of the reference
signal synchronizes the module (see figures 15.17 and 15.19a).
• If the reference signal changes from ”1” to ”0” before the reference pulse is reached, the
module is only synchronized if a positive traversing path is recognized after the falling edge
of the reference signal (see figure 15.18).
The module is not synchronized, if a negative traversing path is recognized after the falling
edge of the reference signal (see figure 15.19b).
The figures 15.17, 15.18 and 15.19a illustrate different possibilities for a reference traversing
path. Figure 15.19b illustrates a reference traversing path, which is terminated without
synchronization:
Positive direction of traverse
Reference
signal
Reference pulse
of the sensor
Sync. bit
Figure 15-17.
Position of the Reference Point (SYNC Bit 0 -- & gt; 1) within the Reference
Signal Range
Reference
signal
Reference pulse
of the sensor
Sync. bit
Figure 15-18. Position of the Reference Point (SYNC Bit 0 -- & gt; 1) after the Reference Signal
15-32
S5-100U
Function Modules
Reference
signal
Reference pulse
of the sensor
Change of direction
Change of direction
Reference
signal
Reference pulse
of the sensor
Synchronization
Sync. bit
No synchronization
Figure 15-19a. Synchronization (SYNC Bit 0 -- & gt; 1)
15-19b. No Synchronization
during a Reversal of Direction before Reaching the Reference Pulse in a
Positive Direction
Example:
Transporting objects from point A to point B on a conveyor belt.
A rotary position encoder is used, together with a BERO proximity switch as reference
transmitter. The conveyor belt is marked at a definite point. As soon as this mark
comes within the range of the BERO, the BERO produces a reference signal.
Following the reference point approach, the enable input is set via a digital output module.
Rotary position
encoder
PS
CPU
DQ
Operation range
of reference
transmitter
Conveyor belt
Counting-up
direction
Mark
BERO as reference transmitter
Traversing path
Enable input
Reference input
Traversing range
Figure 15-20. Schematic of a Reference Point Approach Operation
15-33
Function Modules
S5100U
Starting the Counter
The counter is reset and started by setting the SYNC bit in the diagnostic byte during the reference
point approach operation. The active pulses are counted according to the rotation direction of the
position encoder. The count value is incremented during a positive count direction, and decremented during a negative count direction.
The two outputs are enabled for switching by a positive pulse edge at the enable input.
An output and the associated diagnostic bit “setpoint reached” are set if all of the following
statements are true:
The position decoder was synchronized (SYNC bit=1 and overflow bit=0).
The enable signal (terminal 3 on the terminal block) is set to “1” signal.
The actual value corresponds to the selected setpoint.
The setpoint can be reached in the up-count or down-count direction.
Up-count direction
SYNC bit is set to begin
Counter status
0
1
2
3
4
5
6
7
Down-count direction
SYNC bit is constantly set
8
7
9
10
-10
-9
-8
7
-7
-6
-5
-4
-3
-2
-1
0
1
Counting
pulses
SYNC bit
(in diagnostic
byte)
Enable
input
Output Q0
(setpoint 1
reached)
Output Q1
(setpoint 2
reached)
Measured counting pulse
Counter is still disabled
Figure 15-21. Enabling the Outputs - Reaching the Setpoints - Resetting the Outputs
After reaching setpoint 1, the output Q 0 is energized and the status bit S1 is set. After reaching
setpoint 2, the output Q 1 is energized and status bit S2 is set.
As long as the enable input is active, the outputs are switchable through the module. If the enable
command is cancelled, the outputs are switched off and the diagnostic bits are reset. The current
actual value is still being measured and incremented or decremented depending on the direction of
rotation.
15-34
S5-100U
Function Modules
You can read the current count in the STEP 5 program. The actual value is displayed as a signed
whole number in two's complement and lies in the range - 32,768 to +32,767.
Note
Before you enable the outputs to be switched on by setting the enable input to “1”,
make sure the following conditions exist:
Both setpoints were transferred.
The overflow bit=0.
The SYNC bit=1.
If you ignore these prerequisites, the outputs are switched on directly when the actual
value=0.
The diagnostic bit and the output are reset with the “0” signal at the enable input. Outputs Q 0 and
Q 1 are also reset when the programmable controller goes from RUN to STOP.
The following examples show the switching on of the output at the selected setpoint. There are
three possibilities:
Reaching the setpoint in the direction of a rising actual value
Reaching the setpoint in the direction of a falling actual value
Reaching the setpoint in the direction of a rising actual value, then a reversal of direction and a
reapproaching of the setpoint in the opposite direction
Example 1:
Enable input
Direction of traverse
Output,
diagnostic bit
setpoint reached
Example of
actual value
Setpoint
1000
2000
3000
4000
5000
6000
7000
Figure 15-22. Approaching a Setpoint in Up-Count Direction
Actual value=1000: The enable input is set to “1”.
Actual value=3000: The setpoint is reached, output and diagnostic bit “setpoint reached” are
set.
Actual value=6000: The enable input is set to “0”, output and diagnostic bit are reset.
15-35
Function Modules
Example 2:
S5100U
Enable input
Output,
diagnostic bit
setpoint reached
Setpoint
Example of
actual value
1000
2000
3000
4000
5000
6000
7000
Figure 15-23. Approaching a Setpoint in Down-Count Direction
Actual value=7000: The enable input is set to “1”.
Actual value=3000: The setpoint is reached, the output and the diagnostic bit “setpoint
reached” are set.
Actual value=1000: The enable input is set to “0”, the output and the diagnostic bit are reset.
Example 3:
Reversal of Direction after Approaching a Setpoint
Enable input
Output,
diagnostic bit
setpoint reached
Example of
actual value
Setpoint
1000
2000
Figure 15-24.
3000
Change of direction
4000
5000
6000
7000
Consecutive Reversal of Direction
reached” are set.
Actual value=4500: The traversing path is reversed.
Note
Set outputs can be reset only via a “0” signal to the enable input.
15-36
S5-100U
Function Modules
If the counter leaves the counting range of -32,768 to + 32,767, then the following occurs:
The outputs of the counter module are disabled.
The enable input (terminal 4 of the terminal block) must be set to “0”, in order to switch off active
outputs.
After an overflow, a new reference point approach operation has to be executed for synchronization
of the actual value detection. After reaching the synchronization, bit 3 in the diagnostic byte is again
set to “0”, and the outputs along with the active enable input can be turned on.
Note
During an overflow, active outputs are not switched off, and the SYNC bit (bit 0 in the
diagnostic byte) is not reset.
15-37
Function Modules
S5100U
15.6.5 Entering New Setpoints for the Counter and Position Decoder
Entering new setpoints is always possible via the PIQ. However, a setpoint is only valid if the
respective output is not switched on. The status of the outputs is displayed with diagnostic bits S1
and S2.
Diagnostic bit S1 (bit 1 in the diagnostic byte)=1:
Diagnostic bit S2 (bit 2 in the diagnostic byte)=1:
setpoint 1 is reached and output 1 is switched
on.
setpoint 2 is reached and output 2 is switched
on.
Table 15-5. Reaction of the Counter Module during Transfer of the Setpoints
Diag. Bit
Response
S1 = 0
S2 = 0
New setpoint 1 is transferred and is valid immediately.
New setpoint 2 is transferred and is valid immediately.
S1 = 1
New setpoint 1 only becomes active if a positive edge has appeared at the
enable input.
New setpoint 2 only becomes active if a positive edge has appeared at the
enable input.
S2 = 1
Example:
You want to control a drive by using the outputs of the counter module. After a run of positioning,
both setpoints are reached and both outputs are turned on. You can enter the new setpoints by
using the following sequence:
Enable input
Output Q 0/
Diag. bit S 1
Output Q 1/
Diag. bit S 2
S 1old
S 2old
S 1new
S 2new
Figure 15-25. Requirement for New Setpoints
Transfer the new setpoints to the module. Since both diagnostic bits S1 and S2 are set to “1”,
the actual values are not yet accepted.
Switch the signal now at the enable input to “0”. With the falling edge, the outputs are switched
Switch the signal at the enable input again to “1”. The new setpoints are accepted and are
now active.
After reaching the new setpoints, the respective output is switched on again.
15-38
S5-100U
Function Modules
15.6.6 Addressing
The counter module is addressed like an analog module (see section 6.3).
The module may only be plugged into slots 0 to 7.
The address range extends from byte 64 to byte 127.
In both process image tables, eight bytes are reserved per slot and of these eight bytes only the
first four are used.
Slot Addressing
Table 15-6. Slot Addressing
Slot
0
1
2
3
4
5
6
7
Address
PII/PIQ
64
to
71
72
to
79
80
to
87
88
to
95
96
to
103
104
to
111
112
to
119
120
to
127
Meaning of the Bytes of a Slot Address (Example: Slot 1)
Table 15-7.
Byte
Number
Byte
Address
Meaning in PII
0
72
Irrelevant
High
byte
Diagnostic byte
Low
byte
1
73
2
74
High
byte
3
75
Low
byte
4 to 7
76 to 79
Meaning in PIQ
High
byte
Actual value
Setpoint 1
Setpoint 2
Low
byte
Irrelevant
15-39
Function Modules
S5100U
Examples for Data Exchange between the Programmable Controller and the Counter Module
Example 1:
The counter module is plugged into slot 4. If you now wish to check whether your system for
position decoding has been synchronized by a reference point approach, you must scan the sync bit
in the diagnostic byte (bit 0). If this bit is set, a branch is to be made to FB20. The position
decoding operation is started in FB20.
STL
A
I
JC
Description
Read in bit 0 of the diagnostic byte (sync bit).
If this bit is set, a branch is made to FB20.
If the bit is not set, program scanning is continued
with the statement following the block call.
97.0
FB 20
Example 2:
Transferring the setpoints stored in flag words 0 and 2 to the counter module inserted into slot 7.
The module has only to accept the setpoints when the old setpoints have been reached or
exceeded.
STL
Description
AN
JC=
L
121.1
T
AN
JC=
L001
I
L001
FW
QW
I
L002
120
121.2
FW
QW
2
122
L
T
BE
L002
0
If setpoint 1 has not yet been reached (bit 1=0), a
branch is made to label 1.
Read in setpoint 1
and transfer it to the counter module.
If setpoint 2 has not yet been reached (bit 2=0), a
branch is made to label 2.
Read in setpoint 2
Block end
15-40
S5-100U
15.7
Function Modules
(6ES5 262-8MA12)
(6ES5 262-8MB12)
STATUS
S1
1
2
3
4
on
off
6
CLOSED LOOP
CONTROLLER
6ES5 262-8MA12
1 2
3
4
5
6
15-41
Function Modules
S5-100U
Controller
Analog outputs of the constant controller
(6ES5 262-8MA12)
Total cycle time
(equals scan time)
Resolution of the
open-loop controller
100 to 200 ms
5 ms at 50 Hz
4.2 ms at 60 Hz
Number of outputs
Galvanic isolation
Output signal range
Maximum permissible load
No load voltage
Analog Inputs
Number of inputs
4 (suited for
current, thermocouple, or resistance thermometer),
voltage with
external switching
Additional input for
reference temperature
1 (resistance
thermometer)
Galvanic isolation
no
Binary outputs for the open-loop controller
(6ES5 262-8MB11)
Number of outputs
Galvanic isolation
Signal state “0”
Signal state “1”
Maximum load current
Wiring method
front side via
15-pin subminiature
D connector
Connectable are
PG 605, PG 635,
PG 675, PG 685,
PG 695,
PG 730, PG 750,
OP 393, OP 396,
OP 395
Analog and binary inputs
front side via
25-pin subminiature D
connector
0 to 50 mV or
- 8.9 to 41.1 mV
(type J, K, L, S)
Analog and binary outputs
via terminal block of the
bus unit
30 per wire
General data
18.49
219.12
30 per wire
Input voltage
- rated value
- permissible range
- permissible range with
the PG 605/OP 393
- 1 V to +1 V
of the input signal
11 bits+sign
Current input
- input signal range
- 1 V to +1 V
0 to 20 mA or
4 to 20 mA
24.3 ±0.1%
- input resistance
mV Input (for thermocouple)
Cable impedance
Resistance thermometer
- start
- end
- permissible cable impedance
Binary Inputs
Signal state “1”
Input resistance
15-42
8
no
& lt; 1.5 V
(L+) - 3.8 V
100 mA short-circuit
proof
Programmer (PG)
Operator panel (OP)
SINEC L1 network connection
Permissible voltage difference
- between inputs
- between inputs and
central ground point
Number of inputs
Galvanic isolation
Signals state “0”
3
no
0 to 20 mA or
4 to 20 mA
600
(L+) - 2 V
4
no
- 30 to+4.5 V
or open
+13 to +30 V
(signal state
invertible)
approx. 4 k
Current consumption
- internal (from
the CPU; 9 V)
- external (for 24 V;
without load)
without load;
with PG 605/OP 393)
Ambient temperature
24 V DC
18 to 34 V DC
18 to 27 V DC
approx. 20 mA
approx. 180 mA
approx. 340 mA
0 ° to 55 °C
(32 to 131°F)
S5-100U
Function Modules
Function
The S5-100U programmable controller offers different solutions for individual closed-loop control
tasks. First there is a software solution for CPU 103, version 8MA02 and higher, via function blocks.
Second, there is a control module solution (for example, a module that can solve PID control tasks
simply and in a time saving manner). The basis, in both cases, is a PID control algorithm.
The closed-loop control module IP 262 can be used with the S5-90U, S5-95U, and S5-100U
programmable controllers. It can be used without COM software.
The module relieves the programmable controller from closed-loop control tasks. The IP 262 also
works with its own power supply in a stand-alone operation. The module can function independently
without a programmable controller and can handle up to four closed-loop control circuits.
Two interfaces are located on the front panel of the module.
An interface for the connection of a programmer (PG) or an operator panel (OP) or the
SINEC L1 Network (under development)
An interface for the connection of analog and binary inputs
In addition, the following items are available:
A selector switch for each channel for current and voltage (thermocouples or PT 100)
A status LED for RUN (a continuously lit green light), transducer malfunction (blinking light), and
module malfunction (off)
The module is well suited to take over control-loop tasks in the area of industrial processing
technology, for example, temperature control, pressure and flow control, continuous injection
functions, and non-time-critical closed-loop rpm controls.
Modules
There are two IP 262 modules.
... - 8MA12 with 3 analog outputs for continuous controllers with analog output signals
... - 8MB12 with 8 binary outputs for continuous controllers with pulse time-interval signals or for
step-action controllers
Additionally, the module provides the following inputs:
4 analog inputs for direct feed of setpoint and actual values
4 binary inputs for control variables
Installation
The closed-loop control module is plugged into a bus unit like any other input or output module
(see chapter 3).
The module can only be plugged into slots 0 to 7.
The connections for power supply and the analog and binary output signals are located on the
terminal block of the bus unit.
The analog and binary inputs are connected to the module with a 25-pin sub-D female
connector.
15-43
Function Modules
S5-100U
Addressing
The module is addressed like a four-channel analog module.
Operating Modes
Since transducers and sensors are directly wired to the module, the module can work independently
from a programmable controller in stand-alone operation, provided that the setpoints and the 24-V
power supply voltage are fed directly to the IP 262. This means that the module executes the
control and the output of the manipulated variable and can work alone or be controlled via the
SINEC L1 by a master unit.
Besides this, the IP 262 has its own back-up, which means that the module can continue to work
alone in the event the master CPU (e.g., S5-135U with R64) fails. It uses the last setpoint received
from the CPU or the predefined back-up setpoint.
Two operating modes are possible:
DDC Operation (Direct Digital Control)
The control is executed entirely from the CPU. The IP only outputs the manipulated variable. If
the CPU fails, the module can continue to control independently with a predefined back-up
setpoint.
SPC Operation (SetPoint Control)
The module receives only the setpoint from the CPU; the control task is carried out
independently of the CPU. If the CPU fails, the IP continues to control using the last setpoint
received from the CPU. It is also possible to use a predefined back-up setpoint here.
15-44
S5-100U
15.8
Function Modules
RUN
(6ES5 263-8MA13)
FAULT 1
FAULT 2
E
N
C
O
D
E
R
E
N
C
O
D
E
R
1
2
F 3.15 A
6
Positioning/Counter Module IP 263
6ES5 263-8MA13
1
2
3 4
5
6
15-45
Function Modules
S5-100U
Digital Inputs
Encoders
Input voltage range
Galvanic isolation
0 signal
1 signal
Permissible zero-signal current
at 0 signal
Input current at 24 V
Position decoder
Maximum traversing range
- with incremental encoders
- with absolute encoders
Signal voltages
- Differential inputs
- Asymmetrical inputs
Supply votlage for encoders
(short-circuit-proof,
no overload)
incremental, absolute
(SSI interface)
224 increments
8192 increments per
revolution × 2048
revolutions
5 V to RS 422
24 V (only
incremental
encoders)
5 V/300 mA
24 V/300 mA
Input frequency and cable
length
Symmetrical encoders
(5 V signals):
- with 5 V encoder supply
- with 24 V encoder supply
Asymmetrical encoders
(24 V signale):
Data transmission rate and
cable length with
absolute encoders
Input signals
- Incremental
- 3 V to + 30 V
no
- 3 V to +5 V
+13 V to+30 V
1.1 mA
typ. 5 mA
Other: If the digital inputs are used, they must always
be connected to a defined potential (0 V, 24 V) and
must not be kept open.
Digital Outputs
Output voltage range
Galvanic isolation
Output current at 1 signal
+20 V to+30 V
no
max. 500 mA
Short-circuit-proof
output
max. 100 m (328 ft.)
Cable length, shielded
Supply Voltage
max. 200 kHz for
32 m (105 ft.) cable,
shielded
max. 200 kHz for
100 m (328 ft.)
cable, shielded
max. 100 kHz for
25 m (82 ft.) cable,
shielded
max. 25 kHz for
100 m (328 ft.)
cable, shielded
Logic voltage from 24 V
supply produced with switchedmode power supply
4.9 V to 5.1 V
Current consumption from 24 V
without outputs and encoder
typ. 120 mA
Undervoltage monitoring
Vinternal & lt; 4.65 V
Power Loss
typ. 4 W
62.5 kHz
(selectable
in steps)
125 kHz (160 m/
525 ft. shielded)
250 kHz
500 kHz
1 MHz (32 m/
105 ft. shielded)
2 pulse trains
displaced by 90°
1 zero pulse
- 24 V initiator (BERO)
- SSI
1 pulse train
Absolute value
Input currents
-5V
- 24 V
to RS 422
typ. 5 mA
15-46
S5-100U
Function Modules
A separate manual is available for the IP 263 positioning module. It can be ordered under the order
number 6ES5 998-5SK21.
The IP 263 is suitable for positioning of two independent axes.
Assignments of Outputs
The IP 263 is a two-channel module: 4 digital outputs are assigned to each channel for the control of
drives;
Rapid traverse
Creep speed
Anti-clockwise rotation
Clockwise rotation
Both incremental and absolute encoders (SSI - synchronous serial interface) can be connected for
actual position encoding.
They transmit the machine data, such as
Software limit switches
Resolution
Cutoff difference
Switchover difference
Zero-speed control
The syntax for the data block which has to be created for this purpose is simple and is described in
the manual.
Positioning
The only thing that remains to be done is to specify the desired target and then the module is ready
for the positioning procedure.
The IP 263 then carries out positioning automatically. When the target has been reached, it sends a
message to the IM 318-B interface module and thus to the CPU.
Figure 15-26 shows the positioning procedure with the IP 263: After the start, a rapid traverse
towards the target takes place first. When the switchover/cutoff point has been reached, a switchover to creep speed or cutoff takes place. Afterwards, the IP 263 monitors approach of the target.
When the axis has reached the target range, a signal is sent to the IM 318-B interface module.
15-47
Function Modules
S5-100U
Switchover point
VRapid traverse
Cutoff point
Target range
VCreep
Rapid traverse
Creep speed
Clockwise
Anti-clockwise
Fig. 15-26. Positioning with the IP 263
During reference point travel, the digital input of the module senses the speed reducing cam
(reference point switch).
In the ”Length measurement” operating mode, the module senses encoder pulses as long as this
input has a ”1” signal.
Installation
As other I/O modules, the IP 263 is mounted on the bus unit (see chapter 3).
Addressing
The IP 263 is addressed like a 4-channel analog module.
15-48
S5-100U
15.9
Function Modules
RUN
6ES5 264-8MA12
ACTIVE
FAULT
E
N
C
O
D
E
R
E
N
C
O
D
E
R
I
N
O
U
T
F 10 A
6
Cam Controller Module IP 264
6ES5 264-8MA12
1
2
3 4
5
6
15-49
Function Modules
S5-100U
Digital Inputs
Encoders
Input voltage range
-3 V to + 30 V
Galvanic isolation
0 signal
1 signal
at 0 signal
no
- 3 V to +5 V
+13 V to+30 V
Actual value sensing
Signal voltages
Supply voltage for encoders
no overload)
(SSI interface)
216 increments
216 encoders
5 V to RS 422
24 V (only
incremental
encoders)
5 V/300 mA
24 V/300 mA
Digital Outputs
length
(5 V signals):
(24 V signal):
cable length with absolute
encoders (selectable in steps)
Input signals
- Incremental
1.1 mA
typ. 5 mA
Galvanic isolation
max. 200 kHz for
shielded
max. 200 kHz for
100 m (328 ft.)
cable, shielded
max. 100 kHz for
shielded
max. 25 kHz for
100 m (328 ft.)
cable, shielded
125 kHz (160 m/
525 ft. shielded)
250 kHz
500 kHz
1 MHz (32 m/
105 ft. shileded)
2 pulse trains
displaced by 90°
1 zero pulse
- SSI
Supply Voltage
4.9 V to 5.1 V
without outputs and sensors
typ. 120 mA
Power Loss
typ. 4 W
Module Cycle Time (incl.
dead-time compensation)
Separate cam programs with
max. 32 cams each for forwards
and backwards
(incl. dead-time compensation) 57.6 µs
”Common” cam program with
max. 32/64 cams for forwards
and backwards
57.6/115.2 µs
1 pulse train
Absolute value
Input currents
-5V
- 24 V
+20 V to+30 V
no
max. 300 mA
Short-circuit-proof
output
to RS 422
typ. 5 mA
15-50
S5-100U
Function Modules
A separate manual is available for the electronic cam controller. It can be ordered under the order
number 6ES5 998-5SL21.
The IP 264 can be used both for rotary and linear axes.
The IP 264 electronic cam controller makes electronic processing of cams economical even for
applications in the lower performance range.
32 cams which can be allocated as desired to 16 tracks have a switching accuracy of better than 1
degree at 2400 revolutions per minute. This corresponds to a response time of less than 60 µs. For
applications with low precision requirements it is even possible to program 64 cams.
It is also possible to integrate 32 cams each into a cam program for ”forwards” and a cam program
for ”backwards”. Switchover between these two programs is carried out by automatic direction
sensing of the IP 264 or it is controlled by the SIMATIC S5.
All cams can be defined either as path-path cams or as path-time cams.
Dead Time Compensation
Through the speed-dependent, dynamic shift, each individual cam compensates the dead time of the
actuator connected (e.g. pneumatic valve) at a scanning rate of 60 µs. This enables the utmost
accuracies to be achieved even at changing drive speeds.
Direct Process Connection
In order to be able to pass on the short response time of the IP 264 directly to the process, a digital
output (24 V, 0.3 A) is available on the module for each track. Generally, the units to be controlled
can be connected directly. Auxiliary contactors are required only for actuators with a higher current
consumption.
The sensors to be connected can be incremental encoders, absolute SSI encoders (SSI=
synchronous serial interface) or simple 24 V signal sensors (e.g. BEROs). The sensor data can be
looped through to further modules via the additional sensor output, without separating the sensor
cables mechanically or using additional fan-out units.
Installation
Addressing
The IP 264 is addressed like a 4-channel analog module.
15-51
Function Modules
15.10
S5-100U
IP 265 High Speed Sub Control
(6ES5 265-8MA01)
STOP RUN
I
O
I
N
P
u
T
I
N
T
E
R
F
A
C
E
O
U
T
P
u
T
6
HIGH SPEED
L+
SUB CONTROL
24 V
M
6ES5 265-8MA01
1 2 3
15-52
S5-100U
Function Modules
+9 V (CPU)
Digital 24 V outputs (9-pin sub D socket
connector)
& lt; 175 mA
Number of outputs
8
only for 24 V inputs
and 24 V outputs
(green LEDs)
Galvanic isolation
no
Status display
Yes, on 5 V side
Operating status display
STOP (red LED)
RUN (green LED)
Yes, electronic clock
cycle
Memory submodule
EPROM/EEPROM
Power loss
typ. 2.3 W
Weight
approx. 300 g
(10.6 oz.)
Load voltage L+
- Rated value
- Permissible range
24 V DC
20 to 30 V
Output current at ”1” signal
0.5 A at 60 °C
Permissible total current of
output
2 A at 60 °C
Digital 24 V Inputs (9-pin sub D connector)
Number of inputs
8
Galvanic isolation
no
Status display
Yes, on 5 V side
Input votlage L+
- Rated value
- for ”0” signal
- for ”1” signal
Connection of outputs in
parallel
24 V DC
0 to 5 V
11 to 30 V (IEC 65A)
possible in pairs
(Ioutp=0.8×Irated)
Output frequency at ohmic
load
max. 1 kHz at
15 mA load*
max. 2 kHz at
50 mA load*
max. 4 kHz at
500 mA load*
Cable length
Lamp load
max. 2 W
possible
(zero signal current
1.5 mA)
Residual current at ”0” signal
max. 1 mA
Voltage drop at ”1” signal
max. 1 V
Input frequency
max. 10 kHz
cut-off voltage
-15 V
Input current at ”1” signal
Delay time of input circuit
- Rising edge
- Falling edge
typ. 6.5 mA
(IEC 65 A)
typ. 15 µs
typ. 10 µs
Delay time of output circuit
- Rising edge
- Falling edge, depending on
ohmic load:
5 V differential inputs
(15-pin D sub HD socket connector)
Number and type of input
signals
3 differential signals
RS 422
Input frequency
max. 58 kHz
Pulse length
- ”Low” level
- ”High” level
min. 8.6 µs
min. 8.6 µs
max. 32 m (105 ft.)
typ. 10 µs
typ. 150 µs at
15 mA load*
typ. 90 µs at
50 mA load*
typ. 70 µs at
500 mA load*
Expansion input and outputs
Number of inputs and outputs
8 (any desired
mixture of I/Os can
be configured)
Connector for 24 V load voltage (2-pin)
Permissible cross-sections of cables
- Flexible cable H07V-K
with end sleeve
0.5 to 1.5 mm2
- Solid cable H07V-U
0.5 to 2.5 mm2
* Peak value (no effective value specified)
15-53
Function Modules
S5-100U
The IP 265 High Speed Sub Control is a powerful, user-programmable I/O module which relieves the
CPU's of the SIMATIC S5-100 systems of automation tasks which place great demand on speed
and reproducibility.
A separate manual is available for the IP 265. It can be ordered under the order number 6ES5 9985SH21.
Function
The IP 265 High Speed Sub Control is available with a COM software package which is required to
determine the function of the module.
The use of the IP 265 in an S5 system enables rapid I/O processing in the millisecond range. By
implementation of an FPGA (Field Programmable Gate Array) in the IP 265 it is possible to process
process signals in parallel and very fast.
The IP 265 user program consists of elementary basic functions such as logic operations, counters,
timers or comparators. The structure of the IP 265 user program is based on the CSF5 type of
representation.
The following can be used:
Either a user-programmed user program
or
a fixed-programmed standard program from SIEMENS.
The COM 265 is available for user-programming of the IP 265. Besides it being programmable, the
IP 265 can also be used to implement the special ”counter” function with a fixed-program standard
program. For this purpose, SIEMENS AG offers a memory submodule for the IP 265 with the
standard ”counter” function.
The IP 265 user program is automatically processed by the IP 265. It conditions process input
signals to process output signals. The IP 265 can read 11 process inputs (8 x 24 V inputs, 3 x 5
differential inputs) and set 8 process outputs (24 V outputs).
The program capacity of the FPGA and the number of process inputs/outputs of one IP 265 are
limited. The IP 265 is therefore used for rapid sub controls. By adding one IP 265 to another,
complex sub-processes can be controlled with this module.
Installation
As other I/O modules, the IP 265 High Speed Sub Control is mounted on a bus unit.
Adressing
The module is addressed like a 4-channel analog module.
15-54
S5-100U
Function Modules
15.11 Positioning Module IP 266
(6ES5 266-8MA11)
Technical Specifications
Analog Output
Output signal range
Digital signal representation
Short-circuit proof
Reference potential of the
Cable length shielded
Pulse Input
Position decoder
Traverse range
FAULT
ANALOG
OUT
max.
P
G
6
Input Frequency and
Cable Length
Symmetrical sensors (5 V) max.
max.
Asymmetrical sensors
(24 V)
max.
max.
POSITIONING CONT.
MODULE IP 266
6ES5 266-8MA11
1 2
3
4
5
Input Signals
6
Digital Inputs
Input voltage range
Galvanic isolation
“0” signal
“1” signal
Permissible zero signal
current at “0” signal
Typ. input current at 24 V
Digital Outputs
Galvanic isolation
Max. output current at
“1” signal
Short-circuit protector
max.
Supply Voltage
Logic voltage from 24-V
ext. supply produced
with switched-mode
power supply
24-V supply without outputs and 24-V sensor
typ.
analog ground of the
power section
32 m (105 ft.)
incremental
±32767.999 mm/
0.1 inch/degree
Input voltages for the tracks
- differential inputs
- asymmetrical inputs
Supply voltage for
the sensor
(short-circuit proof)
E
N
C
O
D
E
R
±10 V
13 bits plus sign
yes
5 V/RS 422
24 V/typ. 7.3 mA
5 V/350 mA
24 V/350 mA
500 kHz,
30 m (98 ft.) shielded
cable length
100 kHz for
25 m (82 ft.) cable
length shielded
25 kHz for 100 m
(330 ft.) cable length
shielded
2 pulse series 90
degrees out of phase
1 zero pulse
±30 V
no
- 30 V to +5 V
13 V to 30 V
1.5 mA
7.3 mA
20 V to 30 V
no
100 mA
short-circuit proof output
100 m (330 ft.)
4.7 V to 5.5 V
180 mA
15-55
Function Modules
S5-100U
Because of its performance capability and the complexity of its description, the IP 266 has its own
manual that you can order separately. The order number is: 6ES5 998-5SC21. The positioning
control module IP 266 expands the field of application for “positioning operations” of the S5-100U.
As an “intelligent I/O module”, it allows you to use open-loop as well as closed-loop control
positioning.
The positioning operations are processed independently of the execution times of the user programs
in the programmable controller. Thus the CPU is not burdened with positioning jobs constantly
being processed. You can plug the IP 266 into slots 0 to 7 on the S5-100U. The IP 266 is assigned
addresses in the analog address area of the programmable controller.
Operation Principle of the IP 266
The IP 266 enables you to control the positioning operation of your drive exactly.
The module delivers a voltage setpoint in the range of±10 V via an analog output for the control of
a power section for servo motors.
The IP 266 needs exact data about your drive system in order to calculate speed, acceleration, or
traverse residual distances. This data can be stored in an EEPROM that is permanently installed in
the programmable controller. By using its own start-up routine, this data can be accessed
immediately after you switch on the programmable controller and can be processed directly.
The IP 266 allows you to select between a linear axis and a circular axis. You can also select the
unit of measurement for processing the data: either [mm], [in.] or [deg].
Linear Axis
Circular Axis
Beginning/end of traversing range
Table
Rotary table
Continuous
belt
Possible parameter units: [mm], [in.]
Figure 15-27.
15-56
Possible parameter units: [deg], [mm], [in.]
Units of Measurement that IP 266 Can Process for Circular Axis and Linear
Axis
S5-100U
Function Modules
Besides purely traversing movements, other operating modes allow offset generation of axis
coordinates or drift compensation in the system.
In addition, the IP 266 offers operating modes to read data such as positioning actual value or
residual traversing distances.
In order to use the IP 266 in an automatic manufacturing process, it is possible to combine individual
traversing applications, positioning corrections, offsets or dwell times in a “traversing program”.
These traversing programs can be called up via two special operating modes and processed automatically or semi-automatically.
Such a traversing program can be created by using the “learning capable” “Teach-in mode” for
positioning applications. The information from single positioning applications can be stored at the
end of an operation in a traversing program.
Positioning
For the positioning operation, the IP 266 calculates the setpoint from the selected end data and
velocity data in conjunction with the programmed machine data. The actual value follows the
selection. The deviation (following error) that occurs reaches a constant value after the short
start-up phase and must reach zero at the end of the positioning operation.
S(t)
a = Setpoint function
b = Actual value function
S = Following error
s
a
b
t
S
s = const
t
Figure 15-28. Course of a Following Error during a Positioning Operation
15-57
Function Modules
S5-100U
Overview of the Operation Modes
Table 15-8. Designation of the Operating Modes
List of the Operating Modes
JOG 1
JOG 2
CONTROLLED JOG
FOLLOW-UP MODE
REFERENCE POINT
INCREMENTAL ABSOLUTE
INCREMENTAL RELATIVE
AUTOMATIC
AUTOMATIC SINGLE BLOCK
TEACH-IN ON
TEACH-IN OFF
ZERO OFFSET ABSOLUTE
ZERO OFFSET RELATIVE
CLEAR ZERO OFFSET
TOOL OFFSET ON
TOOL OFFSET OFF
ACKNOWLEDGE ERROR
DRIFT COMPENSATION ON
DRIFT COMPENSATION OFF
RAM EEPROM
READ ACTUAL POSITION
READ FOLLOWING ERROR
READ DISTANCE TO GO
SYNCHRONIZE IP
The COM 266 software package offers user friendly operation and programming. The IP 266
exchanges all data with the programmable controller via a serial interface. All tasks written in 8-byte
messages are sent to the IP 266 during the program cycle via the process output image table (PIQ).
The IP 266 transmits feedback messages cyclically via the process image input table (PII). These
messages can be about the actual value position, remaining traversing distance, or following error as
well as a status byte, error byte, the current operation mode, and special data from the traversing
program.
Installation
1. Plug the IP 266 into a bus unit like any other I/O module (see chapter 3).
2. Insert the IP 266 only into slots 0 to 7.
3. Connect the external switches to the digital inputs of the IP 266 via the terminal block. These
switches are used to limit the traversing range. They also allow you to intervene at any time into
the processing of the module.
- The IP 266 can bypass the STEP 5 OB1 cycle, via three digital outputs, and send signals
directly to external I/Os. The controller must, however, be enabled (function signal enable
controller, FUM) and must be connected to the power section of the drive.
4. Connect the servo motor's power section to the 9-pin subminiature D female connector.
5. Connect the incremental encoder to the left 15-pin subminiature D female connector ENCODER.
You can connect a programmer with screen to the 15-pin subminiature D female connector on the
right side to operate the IP 266 via the COM software.
15-58
S5-100U
Function Modules
15.12 Stepper Motor Control Module IP 267
(6ES5 267-8MA11)
Supply voltage (BUS)
Current consumption
9V
approx. 150 mA
Special voltage VS
5 V to 30 V
Digital Inputs
ABT
Rated input voltage
RDY
no
Input voltage:
“0” signal
“1” signal
ACT
24 V
Galvanic isolation
US
5V
- 33 V to 5 V
13 V to 33 V
Input current
typ.
Supply voltage for
two-wire BEROs
8.5 mA
22 V to 30 V
9-pin Subminiature D Connector
Output voltage
with 5-V supply
“0” signal
“1” signal
0.4 V
4.5 V
With special supply
voltage VS
(5 V to 30 V)
“0” signal
“1” signal
6
max.
min.
max.
min.
0.4 V
VS - 0.4 V
Output current
20 mA
STEPPER MOTOR
MODUL IP 267
6ES5 267-8MA11
3
4
5
Output frequency
max.
204 kHz
Increment number
of steps
1 2
max.
220 - 1 pulses/
job
Permissible cable length
max.
50 m (165 ft.) at
50 kHz
(twisted pair cable)
6
+9 V
GND
Data
US 5 V - L
9V
5V
24 V
f
RDY
5V
ACT
ABT
t
G
ASIC
1
3
2
5
4
7
6
+24 V
9
8
10
+US
15-59
Function Modules
S5-100U
Because of its performance capability and the complexity of its description, the IP 267 has its own
manual that you can order separately. The order number is: 6ES5 998-5SD21. The IP 267 Stepper
Motor Control Module expands the field of application as an intelligent I/O module (IP) of the
S5-100U and S5-95U programmable controllers for “closed-loop control positioning " . The IP 267
controls positioning processes independently of the run time of user programs in the programmable
controller. The CPU is not loaded with processing positioning job operations.
You can plug the IP 267 into slots 0 to 7 in the programmable controller. It then occupies addresses
Principle of Operation
The IP 267 generates pulses for the stepper motor power section. The number of output pulses
determines the length of the traversing path. The pulse frequency is a measure of the velocity.
Each pulse causes the stepper motor shaft to turn through a certain angle. In the case of
high-speed pulse trains, this step movement becomes a constant rotational movement. Stepper
motors can reproduce all movement sequences only as long as no steps are lost. Step losses can
be caused when load variations occur or when the programmed pulse trains exceed motor-specific
values.
To enable the IP 267 to generate these pulse trains, the user must enter the following data:
Configuration data: This data describes the individual stepper motors and the technical characteristics of the drive system.
Positioning data: This data describes the individual traverse jobs and indicates the velocities,
directions, and lengths of the configured paths.
The IP exchanges data with the programmable controller via the serial interface. During the program
scans, all necessary information is sent from the process image output table (PIQ) to the IP 267 in
4-byte messages. The IP 267 cyclically transmits feedback signals on the remaining distance to go
and various status bits to the process image input table (PII).
Using the configuration and positioning data settings, the IP 267 generates a symmetrical traverse
profile consisting of an acceleration ramp, a constant velocity range, and a deceleration ramp.
f
fA
fss
1. Acceleration ramp
2. Constant stepping
rate/velocity range
fss = Start/stop rate; fA = Stepping rate
3. Deceleration ramp
t
Figure 15-29. Velocity Profile of the IP 267
15-60
S5-100U
Function Modules
Using a limit switch on the digital inputs, IP 267 can monitor the limits of a traversing range and stop
the traversing movement when the permissible range limit is exceeded.
The activated input “external stop” causes a calculated decelerating of the traversing movement.
An emergency limit switch can be installed at input “IS” (pulse inhibit). When this switch responds,
the pulse output is interrupted immediately.
For a reference point approach operation, an additional switch can be connected at input REF that
lies within the traversing zone. The reference point approach operation is also possible without this
switch.
Status LEDs provide you with the following information:
The IP 267 is configured
RDY
Pulse outputs during a positioning operation
ACT
Interruption of the positioning operation
ABT
There are four operating modes:
STOP
START FORWARDS
START BACKWARDS
NEUTRAL
Installation
1. Plug the IP 267 into a bus unit like any other I/O module (see chapter 3).
2. Insert the IP 267 module only into slots 0 to 7.
3. Connect the external switches to the DIs of the IP 267 via the terminal block.
4. Connect the stepper motor's power section to the 9-pin subminiature D female connector.
Addressing
The IP 267 is addressed like an analog module.
EWA 4NEB 812 6120-02b
15-61
Function Modules
S5-100U
15.13 Communications Modules
15.13.1 Printer Communications Module CP 521SI
(6ES5 521-8MA22)
Galvanic isolation
TTY signals are
isolated
Memory submodule
RXD
Asynchronous
10-bit character
frame/11-bit character
frame
Transmission rate
Battery
3,4 V
V.24/TTY passive
(active)
Transmission
TXD
EPROM/EEPROM
Serial interface
110 to 9600 baud
- V.24
- TTY
850 mAh
RTS
BATT
15 m (49.2 ft.)
Results from:
(Voltage drop on
cable)+
(Receiver-typ. voltage
drop 1.5 V) or
(transmitter-typ. voltage
drop 0.9 V)
max. 1000 m (3281 ft.)
LED displays
- TxD (green)
- RxD (green)
- RTS (green)
- BATT (yellow)
Back-up battery
Lithium 1/2 AA
1
2
3
4
5
typ. 140 mA
Power loss of module
typ. 1.2 W
Weight
CP 521 SI
SERIAL INTERFACE
6ES5 521-8MA22
3.6 V/850 mAh
Current consumption
from +9 V
6
Transmitting
Receiving
Ready to send
Battery failure
approx. 500 g (1.1 lb.)
6
+9 V
GND
Data
V.24
module
TTY
1
3
2
15-62
5
4
7
6
9
8
10
S5-100U
Function Modules
The CP 521 SI (Serial Interface) communications module is a powerful I/O module with its own
central processor.
A separate manual is available for this module. It can be ordered under the order number 6ES5 9981UD21.
The following is an overview of the module's mode of operation.
Function
The CP 521 SI can be used for unidirectional and bidirectional data exchange.
Unidirectional Data Exchange
For unidirectional data traffic, the CP 521 is provided with a printer driver. If the printer driver is
used, the following must be connected to the serial interface of the CP 521 SI:
A printer with TTY interface (active) or
A printer with V.24 (RS 232C) interface.
This enables you to log process states and process disturbances. The output of messages on the
printer does not extend the response time of the programmable controller.
The following messages and texts can be output:
Message texts, which you have configured on a memory submodule in data blocks DB 2 to 63.
Time of day and date, which are provided by the module's own clock
Values for variables which are transmitted to the CP 521 SI via the I/O bus.
The message texts are stored on an EPROM or EEPROM memory submodule (up to 8/16 Kbytes).
Bidirectional Data Exchange
The following drivers are implemented for the bidirectional data exchange:
ASCII driver, transparent
ASCII driver, interpreting mode I and interpreting mode II
”3964(R)” driver
SINEC L1 driver, master (point-to-point)
SINEC L1 driver, slave
Terminal driver
The use of these drivers enables the transmission of data frames between the CPU and an I/O
device connected to the CP 521 SI.
15-63
Function Modules
S5-100U
The maximum data flow rate is 6 bytes of user data per 2 program cycles; i.e. at a program cycle
time of, for example, 50 ms a maximum of 60 bytes per second can be transmitted.
The following terminals and communications devices can be used as I/O devices:
Keyboard
Terminal
Another CP 521 SI
CP 523
S5-95U with second serial interface
CP 524/CP 525-2 (in connection with special driver 6ES5 897-2AB11)
CPU 944 (with ASCII driver, 3964(R) driver)
Other I/O devices with serial interface, e.g. bar code readers
Which of the I/O devices and transmission modes are used depends on the intended application of
data transmission. In the bidirectional data exchange mode of the module you are, for example, able
to network programmable controllers (point-to-point link).
I/O devices and CP 521 SI are connected with each other via a serial interface. Either a passive
TTY interface or a 24 V voltage interface are available (programmable).
Parameterizing (matching) of the I/O interface and configuring of the message texts are supported by
the DB editor of programmers. The parameters of the I/O interface are stored either on a memory
submodule in DB1 or are directly transmitted in the user program. The CP 521 SI can be
programmed and operated wihtout the COM software.
Integrated Real-Time Clock
The CP 521 SI has it's own real-time clock which is battery-backed when the module is in the deenergized state. Independent of the type of function selected for the CP 521 SI, the clock data can
be read from the CPU and can be used in the user program for date and time-dependent tasks.
Installation
As other I/O modules, the CP 521 SI is mounted on the bus unit (see chapter 3).
Plug the module only into slots 0 to 7.
The module has no connection to the terminal block.
Connect the printer to the module via a 25-pin sub-D female connector.
Adressing
The CP 521 SI is addressed like a 4-channel analog module.
15-64
S5-100U
Function Modules
15.13.2
Communications Module CP 521 BASIC
(6ES5 521-8MB12)
Galvanic isolation
Memory submodule
EPROM/EEPROM/
RAM
Serial interface
RUN
TTY signals are
isolated
V.24
(RS-232-C)/TTY,
passive
Real-time clock
- accuracy
±1 s/day at 25 °C
(77 °F)
PROG
- variation due to
temperature change tV
(ambient temperature TA in °C)
Battery
3,4V
RXD
TXD
850mAh
RTS
BATT
Quartz frequency
-10 to +70 °C
1 s to -11 s
according to data
sheet
14.7456 MHz
Transmission mode
Baud rate
2
3
4
5
6
+9 V
GND
Data
BASIC
Interpreter
3.4 V/850 mAh
1 year minimum
Degree of protection
1
1.5 V+
0.9 V
15 m (50 ft.)
Back-up battery
lithium AA
Life expectancy
CP-521 BASIC
send data
receive data
ready to send
battery low
Permiss. length of cable
- TTY dependent on:
voltage drop on the +line
- typical for receiver
- typical for sender
- V.24
SERIAL INTERFACE
6ES5 521-8MB12
110 to 9600 Bd
LEDs
- TXD
- RXD
- RTS
- BATT (yellow)
6
asynchronous
10-bit character
frame
IP20
Permiss. ambient
temperature
- horizontal arrangement
- vertical arrangement
Relative humidity
0 to 60 °C
(32 to 140 °F)
0 to 40 °C
(32 to 104 °F)
15% to 95%
Current consumption
from+9 V (CPU)
1
3
2
5
4
7
6
9
8
10
180 mA
typ.
1.6 W
Weight
module
TTY
typ.
Power loss of the
module
V.24
approx.
500 g (1 lb. 1.5 oz.)
Note:
It is only possible to run the CP 521 with the interrupt
processing if the interrupts are disabled at the end of
the OB1 cycle and enabled again at the beginning of
the OB1 cycle.
15-65
Function Modules
S5-100U
The CP 521 BASIC is a powerful peripheral module that can be used with the SIMATIC systems
S5-90U, S5-95U, and the S5-100U. It has its own central processor (cannot be used with the
CPU 100, version 8MA01).
A separate manual for this module is available. The order number is 6ES5 998-0UW21.
A brief overview of the functions of this module follows.
Function
This module comes with a special COM software package that is required for generating and storing
BASIC programs (on a floppy disk or an EPROM submodule).
Since the CP 521 includes a basic interpreter, you can create and run BASIC programs that exchange data with a CPU and a connected peripheral device. Use a programmer or a PC terminal
and the COM software to program the BASIC interpreter.
You can store the BASIC programs in the module’s own battery backed-up RAM or on a plug-in
memory submodule.
Connect programmers or PC terminals to the CP 521 via a serial interface. You can choose (by
setting parameters) between a passive TTY current-loop interface or a RS-232 C V.24 interface to
connect a programmer or terminal. Connect a printer to the unidirectional V.24 interface of the
module to print listings or messages.
Change parameter settings for the peripheral interface by using a BASIC command or by using the
BASIC program.
The CP 521 has an integral real-time clock that can be backed up by a battery. You can use the
clock data in unidirectional data traffic to log process statuses or process malfunctions.
Installation
1. Install the communications module on the bus module like any other I/O module (see chapter 3).
2. Plug the module only into slots 0 to 7.
3. The module has no connection to the terminal block.
4. Connect the printer to the module via a 25-pin sub-D female connector.
Addressing
15-66
Appendices
Appendix A
Appendix B
Appendix C
Appendix D
Appendix E
Appendix F
Operations List, Machine Code and List of Abbreviations
Dimension Drawings
Active and Passive Faults in Automation Equipment /
Guidelines for Handling Electrostatic Sensitive Devices
Information for Ordering Accessories
Reference Materials
Siemens Addresses Worldwide
A
A.1
A.1.1
A.1.2
A.1.3
A.1.4
Operations List . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Basic Operations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
Supplementary Operations
System Operations, for CPU 102 and Higher . . . . . . . . . . . . . . . . .
Evaluation of CC 1 and CC 0 . . . . . . . . . . . . . . . . . . . . . . . . . . . .
A
A
A
A
A
- 1
- 1
- 8
- 13
- 14
A.2
Machine Code Listing . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
A
- 15
A.3
List of Abbreviations . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
A
- 18
S5-100U
A
Operations List, Machine Code and Abbreviations
A.1
Operations List
A.1.1
Basic Operations
For organization blocks (OB)
For function blocks (FB)
For program blocks (PB)
For sequence blocks (SB)
Operation
Permissible
Operands
(STL)
Execution Time in µs
RLO*
CPU 100
1
2
CPU 102
typ.
70
4
3
Function
CPU 103
MA02 MA03
Boolean Logic Operations
A
I, Q
N
Y
N
F
N
Y
N
T
N
Y
N
C
N
Y
N
I, Q
N
Y
N
F
N
Y
N
T
N
Y
N
Z
N
Y
N
I, Q
N
Y
N
F
N
Y
N
T
N
Y
N
C
N
Y
N
I, Q
N
Y
N
F
N
Y
N
T
N
Y
N
C
N
Y
N
O
N
Y
Y
41
A(
N
Y
Y
O(
N
Y
N
AN
O
ON
1.6
0.8
Scan operand for “1” and
combine with RLO through
logic AND.
1.6
0.8
Scan operand for “0” and
logic AND.
1.6
0.8
logic OR.
1.6
0.8
logic OR.
7
1.6
0.8
Combine AND operations
through logic OR.
61
6
1.6
0.8
Combine expressions enclosed
in parentheses through logic
AND (6 nesting levels).
Y
64
6
1.6
0.8
OR (6 nesting levels).
Y
N
51
13
1.6
0.8
Close parentheses (conclusion
of a parenthetical expression).
typ.
70
7
1.6
0.8
Set operand to “1”.
7
typ.
75
4
9
typ.
75
4
7
typ.
80
4
9
Set/Reset Operations
S
Y
N
Y
F
I, Q
Y
N
Y
1 RLO dependent ?
2 RLO affected ?
3 RLO reloaded ?
A-1
Operation
Permissible
Operands
(STL)
S5-100U
RLO*
Function
CPU 100
1
2
CPU 102
typ.
70
7
1.6
0.8
Reset operand to “0”.
typ.
70
6
1.6
0.8
Assign value of RLO to
operand.
3
CPU 103
MA02 MA03
Set/Reset Operations (cont.)
R
Y
N
Y
F
Y
N
Y
I, O
N
N
Y
F
I, O
N
N
Y
Load Operations
L
N
N
N
59
14
1.6
0.8
Load an input byte from the PII
into ACCU 1.
L
QB
N
N
N
63
14
1.6
0.8
Load an output byte from the
PIQ into ACCU 1.
L
IW
N
N
N
59
17
1.6
0.8
Load an input word from the
PII into ACCU 1:
byte n ACCU 1 (bits 8-15);
byte n+1 ACCU 1 (bits 0-7)
L
QW
N
N
N
63
17
1.6
0.8
Load an output word from the
PIQ into ACCU 1:
L
PY
N
91
68
Permissible in OB2 and OB13.
Load an input byte of the
digital/analog inputs from the
interrupt PII into ACCU 1.
L
PW
N
92
69
L
FY
N
N
N
64
14
1.6
0.8
Load a flag byte into ACCU 1.
L
FW
N
N
N
71
17
1.6
0.8
Load a flag word into ACCU 1:
byte n+1 ACCU 1 (bits 0-7).
L
DL
N
N
N
65
39
82
1.7
Load a data word (left-hand
byte) of the current data block
into ACCU 1.
L
DR
N
N
N
65
41
83
1.7
Load a data word (right-hand
into ACCU 1.
L
IB
DW
N
N
N
66
43
85
2.0
Load a data word of the current data block into ACCU 1:
1 RLO dependent ?
A-2
2 RLO affected ?
3 RLO reloaded ?
S5-100U
Operation
Permissible
Operands
(STL)
RLO*
CPU 100
1
2
CPU 102
3
Function
CPU 103
MA02 MA03
Load Operations (cont.)
L
KB
N
N
N
54
7
59
1.45
Load a constant (1-byte
number) into ACCU 1.
L
KS
N
N
N
57
7
1.6
0.8
Load a constant (2 characters
in ASCII format) into ACCU 1.
L
KF
N
N
N
57
7
1.6
0.8
Load a constant (fixed-point
L
KH
N
N
N
57
7
1.6
0.8
Load a constant (hexadecimal
code) into ACCU 1.
L
KM
N
N
N
57
7
1.6
0.8
Load a constant (bit pattern)
into ACCU 1.
L
KY
N
N
N
57
7
1.6
0.8
Load a constant (2-byte
L
KT
N
N
N
57
7
1.6
0.8
Load a constant (time in BCD)
into ACCU 1.
L
KC
N
N
N
57
7
1.6
0.8
Load a constant (count in
BCD) into ACCU 1.
L
T, C
N
N
N
typ.
70
19
1.6
0.8
Load a time or count (in binary
code) into ACCU 1.
LC
T
N
N
N
125
69
154
1.8
C
N
N
N
Load times or counts (in BCD)
into ACCU 1.
Transfer Operations
T
N
N
N
51
5
1.6
0.8
Transfer the contents of
ACCU 1 to an input byte (into
the PII).
T
QB
N
N
N
54
5
1.6
0.8
ACCU 1 to an output byte (into
the PIQ).
T
IW
N
N
N
53
11
1.6
0.8
ACCU 1 to an input word (into
the PII):
ACCU 1 (bits 8-15) byte n;
ACCU 1 (bits 0-7) byte n+1.
T
QW
N
N
N
56
11
1.6
0.8
ACCU 1 to an output word (into
the PIQ):
T
IB
PY
N
60
37
ACCU 1 to the interrupt PIQ
with updating of the PIQ.
1 RLO dependent ?
2 RLO affected ? 3 RLO reloaded ?
A-3
Operation
Permissible
Operands
RLO*
CPU 100
(STL)
1
2
S5-100U
CPU 102
3
Function
CPU 103
MA02 MA03
Transfer Operations (cont.)
T
PW
N
T
FY
N
N
N
55
T
FW
N
N
N
T
DL
N
N
T
DR
N
T
DW
N
67
51
5
1.6
0.8
ACCU 1 to a flag byte.
64
11
1.6
0.8
ACCU 1 to a flag word (into the
PIQ):
N
53
31
75
1.15
ACCU 1 to a data word
(left-hand byte).
N
N
57
33
78
1.15
ACCU 1 to a data word (righthand byte).
N
N
59
36
81
1.4
ACCU 1 to a data word.
Timer Operations
SP
T
Y
N
Y
125
74
147
1.9
Start a timer (stored in
ACCU 1) as a signalcontracting pulse.
SE
T
Y
N
Y
125
74
147
1.9
ACCU 1) as extended pulse
(signal contracting and
stretching).
SD
T
Y
N
Y
127
76
150
1.9
Start an on-delay timer (stored
in ACCU 1).
SS
T
Y
N
Y
127
76
150
1.9
Start a stored on-delay timer
(stored in ACCU 1).
SF
T
Y
N
Y
125
74
144
1.9
Start an off-delay timer (stored
in ACCU 1).
R
T
N
Y
126
75
96
1.9
Reset a timer.
Y
Counter Operations
CU
Y
N
Y
79
42
105
1.9
Counter counts up 1.
CD
C
C
Y
N
Y
92
31
117
1.9
Counter counts down 1.
1 RLO dependent ?
A-4
2 RLO affected ?
3 RLO reloaded ?
S5-100U
Operation
Permissible
Operands
RLO*
CPU 100
(STL)
1
2
CPU 102
3
Function
CPU 103
MA02 MA03
Counter Operations (cont.)
S
C
R
Y
C
Y
N
Y
118
67
141
1.9
Set counter.
N
Y
69
12
96
1.9
Reset counter.
Arithmetic Operations
+F
N
N
N
55
26
1.6
0.8
Add two fixed-point numbers:
ACCU 1+ACCU 2.
CC 1/CC 0/OV are affected.
-F
N
N
N
58
23
1.6
0.8
Subtract one fixed-point
number from another:
ACCU 2 - ACCU 1.
Comparison Operations
!=F
Y
N
79
24
1.6
0.8
Compare two fixed-point
numbers for “equal to”: If
ACCU 2=ACCU 1, the RLO
is “1”.
CC 1/CC 0 are affected.
& gt; & lt; F
N
Y
N
82
27
1.6
0.8
numbers for “not equal to”: If
ACCU 2 ACCU 1, the RLO
is “1”.
& gt; F
N
Y
N
79
24
1.6
0.8
numbers for “greater than”:
If ACCU 2 & gt; ACCU 1, the
RLO is “1”. CC 1/CC 0 are
affected.
& gt; =F
N
Y
N
79
24
1.6
0.8
numbers for “greater than or
equal to”: If ACCU 2
ACCU 1, the RLO is “1”.
& lt; F
N
Y
N
82
27
1.6
0.8
numbers for “less than”:
If ACCU 2 & lt; ACCU 1, the
affected.
& lt; =F
N
N
Y
N
82
27
1.6
0.8
numbers for “less than or equal
to”: If ACCU 2 ACCU 1, the
affected.
1 RLO dependent ?
2 RLO affected ?
3 RLO reloaded ?
A-5
Operation
Permissible
Operands
(STL)
RLO*
CPU 100
1
S5-100U
2
CPU 102
3
Function
CPU 103
MA02 MA03
Block Call Operations
JU
PB
N
N
Y
125
49
185
3.35
Jump unconditionally to a
program block.
JU
FB
N
N
Y
147
49
187
3.35
function block.
JU
SB
N
N
Y
185
3.35
sequence block.
JC
PB
Y Y1)
Y
130
53
190
3.35
Jump conditionally to a
program block.
JC
FB
Y Y1)
Y
152
53
196
3.35
function block.
JC
SB
Y Y1)
Y
194
3.35
sequence block.
C
DB
N
N
N
70
28
79
1.75
Call a data block.
G
DB
N
N
Y
233
182
Generate or delete a data
block.
N
N
Y
88
36
119
2.5
Block end (termination of a
block)
BEC
Y Y1)
Y
90
38
121
2.5
Block end, conditional
BEU
N
N
Y
88
36
119
2.5
Block end, unconditional (BEU
cannot be used in organization
blocks.)
NOP 0
N
N
N
35
0
1.6
0.8
No operation (all bits reset)
NOP 1
N
N
N
35
0
1.6
0.8
No operation (all bits set)
N
N
N
35
1
53
25
Stop: scanning is still completed before a stop. Error ID
“STS” is set in the ISTACK.
Return Operations
BE
“No” Operations
Stop Operations
STP
Display Generation Operations
BLD
130
N
N
N
35
0
1.6
0.8
Display generation operation
for the programmer: carriage
return generates blank line.
BLD
131
N
N
N
35
0
1.6
0.8
for the programmer: switch to
statement list (STL).
* 1 RLO dependent ?
1) RLO is set to “1”.
A-6
2 RLO affected ?
3 RLO reloaded ?
S5-100U
Operation
Permissible
Operands
(STL)
RLO*
1
2
CPU 100
CPU 102
3
Function
CPU 103
MA02 MA03
Display Generation Operations (cont.)
BLD
132
N
N
35
0
1.6
0.8
control system flowchart (CSF).
BLD
133
N
N
N
35
0
1.6
0.8
ladder diagram (LAD).
BLD
255
N
N
N
N
35
0
1.6
0.8
for the programmer:
terminate a segment.
1 RLO dependent ?
2 RLO affected ?
3 RLO reloaded ?
A-7
S5-100U
A.1.2 Supplementary Operations
Operation
Permissible
Operands
(STL)
RLO*
CPU 100
1
2
CPU 102
3
Function
CPU 103
MA02 MA03
A=
Formaloperand
I, Q, F, T, C
N
Y
N
202
151
AND operation: scan formal
operand for “1”.
(Data type: BI)
AN=
Formal
operand
I, Q, F, T, C
N
Y
N
202
151
operand for “0”.
(Data type: BI)
O=
Formal
operand
I, Q, F, T, C
N
Y
N
202
151
OR operation: scan formal
operand for “1”.
(Data type: BI)
ON=
Formal
operand
I, Q, F, T, C
N
Y
N
202
151
operand for “0”.
(Data type: BI)
AW
N
N
N
53
19
1.6
0.8
Combine contents of ACCU 2
and ACCU 1 through logic
AND (word operation).
Result is stored in ACCU 1.
OW
N
N
N
53
19
1.6
0.8
and ACCU 1 through logic OR
(word operation).
XOW
N
N
N
51
19
1.6
0.8
EXCLUSIVE OR (word operation).
Bit Operations
TB
N
Y
N
187
123
Test a bit of a timer or counter
word for “1”.
TB
D
N
Y
N
187
144
Test a bit of a data word
for “1”.
TB
RS
N
Y
N
185
121
Test a bit of a data word in the
system data area for “1”.
TBN
T, C
T, C
N
Y
N
188
124
word for “0”.
1 RLO dependent ?
A-8
2 RLO affected ?
3 RLO reloaded ?
S5-100U
Operation
Permissible
Operands
(STL)
RLO*
CPU 100
1
2
CPU 102
3
Function
CPU 103
MA02 MA03
Bit Operations (cont.)
TBN
D
N
Y
N
188
145
for “0”.
TBN
RS
N
Y
N
186
122
system data area for “0”.
SU
T, C
N
N
Y
180
125
Set a bit of a timer or counter
word unconditionally.
SU
D
N
N
Y
183
146
Set a bit of a data word unconditionally.
RU
T, C
N
N
Y
189
124
Reset a bit of a timer or
counter word unconditionally.
RU
D
N
N
Y
189
146
Reset a bit of a data word
unconditionally.
S=
Formal
operand
I, Q, F
Y
N
Y
202
151
Set a formal operand
(when RLO=1).
(Data type: BI)
RB=
Formal
operand
I, Q, F
Y
N
Y
203
152
Reset a formal operand
(when RLO=1).
(Data type: BI)
RD=
Formal
operand
T, C
Y
N
Y
197
147
(digital) (when RLO=1).
Formal
operand
I, Q, F
N
N
Y
202
151
Assign the value of the RLO to
the status of the formal
operand.
(Data type: BI)
FR
T, C
Y
N
Y
98
1.9
Enable a timer/counter for cold
restart. If RLO=“1”,
- “FR T” restarts the timer
- “FR C” sets, decrements, or
increments the counter.
FR=
Formal op. T,
C
Y
N
Y
194**
145**
Enable formal operand (timer/
counter) for cold restart (for
detailed description, see “FR”
operation).
SP=
Formal op. T
Y
N
Y
194**
145**
Start a timer (formal operand)
as pulse with the value stored
in ACCU 1.
* 1 RLO dependent ?
2 RLO affected ?
** +Execution of the substituted command
3 RLO reloaded ?
A-9
Operation
Permissible
Operands
(STL)
RLO*
CPU 100
1
2
S5-100U
CPU 102
3
Function
CPU 103
MA02 MA03
Timer and Counter Operations (cont.)
SD=
Formal op.
T
Y
N
Y
194**
145**
Start an on-delay timer (formal
operand) with the value stored
in ACCU 1.
SEC
Formal op.
T, C
Y
N
Y
194**
145**
as an extended pulse with the
value stored in ACCU 1, or
set a counter (formal operand)
with the next count value
indicated.
SSU
Formal op.
T, C
Y
N
Y
194**
145**
(formal operand) with the
increment a counter (formal
operand).
SFD=
Formal op.
T, C
Y
N
Y
194**
145**
Start an off-delay timer (formal
in ACCU 1, or decrement a
counter (formal operand).
148** Load the value of the formal
operand into ACCU 1.
Data type: BY, W
Additional actual operands:
DL, DR, DW
Load and Transfer Operations
L=
Formal
operand
I, Q, F, T, C
N
N
N
142**
L
RS
N
N
N
77
LD=
Formal
operand
T, C
N
N
N
194**
LW=
Formal
operand
N
N
N
152
T=
Formal
operand
I, Q, F
N
N
N
195**
* 1 RLO dependent ?
2 RLO affected ?
** +Processing time for the substituted command
A-10
61
Load a word from the system
data area into ACCU 1.
145** Load the value of the formal
operand in BCD code into
ACCU 1.
76
Load a formal operand bit
pattern into ACCU 1.
Data type: D
Parameter type:
KC, KF, KH, KM, KS, KT, KY
149** Transfer the contents of
ACCU 1 to the formal operand.
Data type: BY, W
DR, DL, DW
3 RLO reloaded ?
S5-100U
Operation
Permissible
Operands
(STL)
RLO*
CPU 100
1
2
CPU 102
3
Function
CPU 103
MA02 MA03
Conversion Operations
CFW
N
N
N
42
4
1.6
0.8
Form the one's complement of
ACCU 1.
CSW
N
N
N
60
23
1.6
0.8
Form the two's complement of
ACCU 1. CC 1/CC 0 and OV
are affected.
Shift Operations
SLW
Parameter
n=0 to 15
N
N
N
47+
n·10
12+
n·10
1.6
0.8
Shift the contents of ACCU 1
to the left by the value
specified in the parameter.
Unassigned positions are
padded with zeros.
SRW
Parameter
n=0 to 15
N
N
N
47+
n·10
12+
n·10
1.6
0.8
to the right by the value
padded with zeros.
N
N
62
2
1.6
0.8
Jump unconditionally to the
symbolic address.
Jump Operations
JU=
Symbolic
address max.
4 characters
N
JC=
Symbolic
address max.
4 characters
Y Y1)
Y
65
5
1.6
0.8
Jump conditionally to the
symbolic address. (If the RLO
is “0”, it is set to “1”.)
JZ=
Symbolic
address max.
4 characters
N
N
N
69
6
1.6
0.8
Jump if the result is zero. The
jump is made only if CC 1=0
and CC 0=0. The RLO is not
changed.
JN=
Symbolic
address max.
4 characters
N
N
N
69
10
1.6
0.8
Jump if the result is not zero.
The jump is made only if
CC 1 CC 0. The RLO is not
changed.
JP=
Symbolic
address max.
4 characters
N
N
N
71
6
1.6
0.8
Jump if the sign of the result is
“+”. The jump is made only if
CC 1=1 and CC 0=0. The
RLO is not changed.
JM=
Symbolic
address max.
4 characters
N
N
N
71
6
1.6
0.8
“-”. The jump is made only if
CC 1=0 and CC 0=1. The
RLO is not changed.
JO=
Symbolic
address max.
4 characters
N
N
N
65
4
1.6
0.8
Jump on overflow. The jump is
made only if the OVERFLOW
bit is set. The RLO is not
changed.
* 1 RLO dependent ?
2 RLO affected ?
3 RLO reloaded ?
A-11
Operation
Permissible
Operands
(STL)
S5-100U
RLO*
CPU 100
CPU 102
Function
CPU 103
MA02 MA03
1
2
3
IA
N
N
N
58
24
Disable interrupt. Input/
output interrupt or timer OB
processing is disabled.
RA
N
N
N
58
26
Enable interrupt.
This operation cancels the
effect of IA.
D
N
N
N
49
0,9
Decrement the low byte (bits 0
to 7) of ACCU 1 by the
value n (n=0 to 255).
I
N
N
N
49
0,9
Increment the low byte (bits 0
Other Operations
DO=
Formal
operand
N
N
Y
252**
188**
Process a block.
(Only C DB, JU OB, J U PB,
JU FB, JU SB can be
substituted.)
Actual operands: C DB,
JU OB, JU PB, JU FB, JU SB
DO
DW***
N
N
N
229
171
Process data word. The next
operation is combined with the
parameter specified in the data
word (OR operation) and then
carried out.
DO
FW***
N
N
N
179
138
Process flag word. The next
parameter specified in the flag
carried out.
1 RLO dependent ?
2 RLO affected ?
Permissible operations:
A, AN, O, ON
S, R=;
FR T, RT, SF T, SD T, SP T, SS T, SE T;
FR C, RC, SC, CU, CD C;
A-12
3 RLO reloaded ?
L, LC, T;
JU, JC, JZ, JN, JP, JM, JO, SLW, SRW;
D, I;
C DB, T RS, TNB
S5-100U
A.1.3 System Operations, for CPU 102 and Higher
Operation
Permissible
Operands
(STL)
RLO*
CPU 100
1
2
CPU 102
3
Function
CPU 103
MA02 MA03
Set Operations
SU
RS
N
N
Y
167
123
Set bit in system data area
unconditionally.
RU
RS
N
N
Y
167
123
Reset bit in system data area
unconditionally.
LIR
N
N
N
105
76
Load the contents of a memory
word (addressed by ACCU 1)
indirectly into the register
(0: ACCU 1; 2: ACCU 2).
TIR
N
N
N
85
61
Transfer the register contents
indirectly into the memory
word (addressed by ACCU 1).
N
N
N
97+
n·21
75+
n·16
N
N
N
71
59
TNB
T
Parameter
n=0 to 255
RS
1 RLO dependent ?
2 RLO affected ?
13+n·19
(48+n·19)
Transfer a field byte by byte
(number of bytes 0 to 255).
Transfer a word to the system
data area.
3 RLO reloaded ?
A-13
Operation
Permissible
Operands
(STL)
RLO*
CPU 100
1
2
S5-100U
CPU 102
3
Function
CPU 103
MA02 MA03
Block Call Operations and Return Operations
JU
OB
N
N
Y
187
3.35
Call an organization block
unconditionally.
JC
OB
Y Y1)
Y
194
3.35
conditionally.
N
N
131
82
Jump at random within a
function block (jump distance
-32768 to + 32767)
Jump Operation
JUR
N
ADD
BF
N
N
N
58
35
Add byte constant (fixed point)
to ACCU 1.
ADD
KF
N
N
N
104
68
Add fixed-point constant
(word) to ACCU 1.
STS
N
N
N
TAK
N
N
N
Other Operations
* 1 RLO dependent ?
A.1.4
2 RLO affected ?
74
57
Swap the contents of ACCU 1
and ACCU 2.
3 RLO reloaded ?
CC 1 CC 0
Arithmetic
Operations
Digital
Logic
Operations
Comparison
Operations
Shift
Operations
Result
=0
ACCU 2
= ACCU 1
shifted
bit = 0
0
0
Result
=0
0
1
Result
& lt; 0
1
0
Result
& gt; 0
A-14
Stop operation. Program processing is interrupted immediately after this operation.
ACCU 2
& lt; ACCU 1
Result
0
ACCU 2
& gt; ACCU 1
Conversion
Operations
Result
& lt; 0
shifted
bit = 1
Result
& gt; 0
S5-100U
A.2
Machine Code
B0
B1
Machine Code
B2
L
R
L
R
0
0
0
0
0
1
0
0
2
0d
0
3
0
4
0
5
0
L
Operation
B3
L
R
B0
B1
B2
L
R
NOP 0
1
E
0c
0c
SEC=
0
CFW
1
F
0c
0c
0d
L
2
0
0f
0f
C
0l
0l
TNB
2
1
2
0
& gt; F
0d
0d
FR
2
1
4
0
& lt; F
0
0
BEC
2
1
6
0
& gt; & lt; F
6
0c
0c
FR=
2
1
8
0
!=F
0
7
0c
0c
A=
2
1
A
0
& gt; =F
0
8
0
0
IA
2
1
C
0
& lt; =F
0
8
8
0
RA
2
2
0g
0g
L
DL
0
9
0
0
CSW
2
3
0g
0g
T
DL
0
A
0a
0a
L
FY
2
4
0d
0d
SD
T
0
B
0a
0a
T
FY
2
5
0i
0i
JM=
0
C
0d
0d
LC
T
2
6
0c
0c
SD=
0
D
0i
0i
JO=
2
7
0c
0c
AN=
0
E
0c
0c
LC=
2
8
0e
0e
L
KB
0
F
0c
0c
0
2
A
0g
0g
L
DR
1
0
8
2
BLD
130
2
B
0g
0g
T
DR
1
0
8
3
BLD
131
2
C
0d
0d
SS
T
1
0
8
4
BLD
132
2
D
0i
0i
JU=
1
0
8
5
BLD
133
2
E
0c
0c
SSU=
1
0
F
F
BLD
255
2
F
0c
0c
ON=
1
1
0n
0n
I
3
0
0
1
0e
0e
0e
0e
L
KC
1
2
0a
0a
L
FW
3
0
0
2
0e
0e
0e
0e
L
KT
1
3
0a
0a
T
FW
3
0
0
4
0e
0e
0e
0e
L
KF
1
4
0d
0d
SF
T
3
0
1
0
0e
0e
0e
0e
L
KS
1
5
0i
0i
JP=
3
0
2
0
0e
0e
0e
0e
L
KY
1
6
0c
0c
SFD=
3
0
4
0
0e
0e
0e
0e
L
KH
1
7
0c
0c
S=
3
0
8
0
0e
0e
0e
0e
L
KM
1
9
0n
0n
D
3
2
0g
0g
L
DW
1
C
0d
0d
SE
T
3
3
0g
0g
T
DW
1
D
0f
0f
JC
FB
3
4
0d
0d
SP
T
T
R
L
Operand
R
T
L
Operation
B3
L
R
Operand
R
DB
A-15
S5-100U
Machine Code
B0
B1
Machine Code
B2
L
R
L
R
3
5
0i
6
0c
B3
0i
3
L
Operation
R
L
Operand
R
B0
B1
B2
L
Operation
B3
R
L
Operand
L
R
L
R
R
JN=
5
C
0o
0o
S
C
0c
SI=
5
D
0f
0f
JC
SB
3
7
0c
0c
RB=
6
1
0h
0h
SLW
3
C
0d
0d
R
T
6
2
0g
0g
L
RS
3
D
0f
0f
JU
FY
6
3
0g
0g
T
RS
3
E
0c
0c
RD=
6
5
0
0
BE
3
F
0c
0c
LW=
6
5
0
1
BEU
4
0
0
0k
LIR
6
6
0c
0c
T=
4
1
0
0
AW
6
9
0h
0h
SRW
4
2
0o
0o
L
C
6
C
0o
0o
CU
C
4
4
0o
0o
FR
C
6
D
0f
0f
JU
OB
4
5
0i
0i
JZ=
6
E
0g
0g
DO
DW
4
6
0c
0c
L=
7
0
0
0
STS
4
8
0
0k
TIR
7
0
0
2
TAK
4
9
0
0
OW
7
0
0
3
C
0
0o
0o
STP
4
A
0a
0a
L
IB
7
0
1
5
8
0
0o
0o
TB
C
4
A
8a
0a
L
QB
7
0
1
5
4
0
0o
0o
TBN
C
4
B
0a
0a
T
IB
7
0
1
5
0
0
0o
0o
SU
C
4
B
8a
0a
T
QB
7
0
1
5
C
0
0d
0d
RU
C
4
C
0o
0o
LC
C
7
0
2
5
8
0
0d
0d
TB
T
4
D
0f
0f
JC
OB
7
0
2
5
4
0
0d
0d
TBN
T
4
E
0g
0g
DO
FW
7
0
2
5
0
0
0d
0d
SU
T
BF
7
0
2
5
C
0b
0g
0g
RU
T
7
0
4
6
8
0b
0g
0g
TB
D
5
0
0e
0e
ADD
5
1
0
0
XOW
5
2
0a
0a
L
IW
7
0
4
6
4
0b
0g
0g
TBN
D
5
2
8a
0a
L
QW
7
0
4
6
0
0b
0g
0g
SU
D
5
3
0a
0a
T
IW
7
0
4
6
C
0b
0g
0g
RU
D
5
3
8a
0a
T
QW
7
0
5
7
8
0b
0g
0g
TB
RS
5
4
0o
0o
CD
C
7
0
5
7
4
0b
0g
0g
TBN
RS
5
5
0f
0f
JC
PB
7
0
5
7
0
0b
0g
0g
SU
RS
5
8
0
0
ADD
KF
7
0
5
7
RU
RS
5
9
0
0
-F
A-16
0e
0e
0e
0e
S5-100U
Machine Code
B0
B1
Machine Code
B2
L
Operation
B3
L
R
L
R
7
2
0a
0a
L
7
3
0a
0a
7
5
0f
7
6
7
7
B2
PY
B
F
0
0
T
PY
C
0b
0a
0a
A
I
0f
JU
PY
C
0b
8a
0a
A
Q
0c
0c
DO=
C
8b
0a
0a
O
I
8
0
5
C
8b
8a
0a
O
Q
9
0
0
+F
D
0b
0a
0a
S
I
7
A
0a
0a
L
PW
D
0b
8a
0a
S
Q
7
B
0a
0a
T
PW
D
8b
0a
0a
I
7
C
0o
0o
R
C
D
8b
8a
0a
Q
7
D
0f
0f
JU
SB
E
0b
0a
0a
AN
I
7
E
0
0
DI
E
0b
8a
0a
AN
Q
8
0b
0a
0a
A
F
E
8b
0a
0a
ON
I
8
8b
0a
0a
O
F
E
8b
8a
0a
ON
Q
9
0b
0a
0a
S
F
F
0b
0a
0a
R
I
G
DB
R
L
Operand
R
0f
L
Operation
B3
L
0f
R
B1
R
0
L
B0
L
0
R
Operand
R
9
8b
0a
0a
F
F
0b
8a
0a
R
Q
A
0b
0a
0a
AN
F
F
8
0d
0d
A
T
A
8b
0a
0a
ON
F
F
9
0d
0d
O
T
B
0b
0a
0a
R
F
F
A
0i
0i
JC=
B
8
0o
0o
A
C
F
B
0
0
O
B
9
0o
0o
O
C
F
C
0d
0d
AN
T
B
A
0
0
A(
F
D
0d
0d
ON
T
B
B
0
0
O(
F
F
F
F
NOP 1
B
C
0o
0o
AN
C
B
D
0o
0o
ON
C
Explanation of the Indices
a
b
c
d
e
f
g
+ byte address
+ bit address
+ parameter address
+ timer number
+ constant
+ block number
+ word address
h
i
k
l
m
n
o
+ number of shifts
+ relative jump address
+ register address
+ block length in bytes
+ jump displacement (16 bits)
+ value
+ counter number
A-17
Operations List, Machine Code and List of Abbreviabrations
A.3
S5-100U
Permissible Operand Value Range for
Abbreviation
Explanation
CPU 100
ACCU 1
Accumulator 1
ACCU 2
Byte constant (fixed-point number)
C
Counter
- retentive
- non-retentive
- for the “Bit Test” and “Set” supplementary
operations
CPU 103
(- 127 to +127)
(- 127 to +127)
(- 127 to +127)
(0 to 7)
(8 to 15)
(0 to 15)
(0 to 7)
(8 to 127)
(0 to 127)
(0 to 7)
(8 to 127)
(0 to 127)
(0.0 to 127.15)
Accumulator 2
BF
CPU 102
(When accumulator 1 is loaded,
any existing contents are shifted
into accumulator 2.)
CC 0/CC 1
Condition code 0/Condition code 1
CF
DB1 parameter: input correction factor (integral
real-time clock)
CLK
DB1 parameter: clock data location
CPU
Central processing unit of programmable
controller
CSF
STEP 5 control system flowchart method of
representation
D
Data (1 bit)
DB
Data block
(2 to 63)
(2 to 63)
(2 to 255)
DL
Data word (left-hand byte)
(0 to 255)
(0 to 255)
(0 to 255)
DR
Data word (right-hand byte)
(0 to 255)
(0 to 255)
(0 to 255)
DW
Data word
(0 to 255)
(0 to 255)
(0 to 255)
EF
DB1 parameter: SINEC L1, position of receive
mailbox
F
Flag
(0.0 to 63.7)
(64.0 to 127.7)
(0.0 to 63.7)
(64.0 to 127.7)
(0.0 to 63.7)
(64.0 to 255.7)
FB
Function block
(0 to 63)
(0 to 63*)
(0 to 255)
FB/FY
Flag byte
(0 to 63)
(64 to 127)
(0 to 63)
(64 to 127)
(0 to 63)
(64 to 255)
Formal
operand
Expression with a maximum of 4 characters. The
first character must be a letter of the alphabet.
FW
Flag word
(0 to 62)
(64 to 126)
(0 to 62)
(64 to 126)
(0 to 62)
(64 to 254)
I
Input
(0.0 to 127.7)
(0.0 to 127.7)
(0.0 to 127.7)
IB
Input byte
(0 to 127)
(0 to 127)
(0 to 127)
IW
Input word
(0 to 126)
(0 to 126)
(0 to 126)
KB
Constant (1 byte)
(0 to 255)
(0 to 255)
(0 to 255)
(0.0 to 255.15)
- retentive
- non-retentive
- retentive
- non-retentive
- retentive
- non-retentive
* +integrated FBs such as CPU 103
A-18
S5-100U
Abbreviation
Explanation
CPU 100
CPU 102
CPU 103
(0 to 999)
(0 to 999)
(0 to 999)
KBE
DB1 parameter: SINEC L1, position of the
“Receive” coordination byte
KBS
“Send” coordination byte
KC
Constant (count)
KF
Constant (fixed-point number)
(- 32,768 to
+32,767)
(- 32,768 to
+32,767)
(- 32,768 to
+32,767)
KH
Constant (hexadecimal code)
(0 to FFFF)
(0 to FFFF)
(0 to FFFF)
KM
Constant (2-byte bit pattern)
(arbitrary bit
pattern: 16 bit)
(arbitrary bit
pattern: 16 bit)
(arbitrary bit
pattern: 16 bit)
KS
Constant (2 characters)
(any two
alphanumeric
characters)
(any two
alphanumeric
characters)
KT
Constant (time)
(0.0 to 999.3)
(0.0 to 999.3)
(0.0 to 999.3)
KY
Constant (2 bytes)
(0 to 255 each
byte)
(0 to 255 each
byte)
(0 to 255 each
byte)
LAD
STEP 5-Ladder Diagram
NT
DB1 parameter: number of timers being
processed
OB
Organization block
for special applications:
1, 3, 13, 21, 22, 31, 34, 251
(0 to 63)
(0 to 63)
(0 to 255)
OB13
DB1 parameter: interval (ms) within which OB13
is called and processed
OHE
DB1 parameter: enable operating hours counter
OHS
DB1 parameter: set operating hours counter
OP
Operator panel
OV
Overflow. This condition code bit is set if, e.g., a
numerical range is exceeded during arithmetic
operations.
PII
Process image input table
PIQ
Process image output table
PB
Program block
(with block call and return operations)
(0 to 63)
(0 to 63)
(0 to 255)
PY
Peripheral byte
PG
Programmer
PW
Peripheral word
Q
Output
QB
QW
(0 to 127)
(0 to 126)
(0.0 to 127.7)
(0.0 to 127.7)
(0.0 to 127.7)
Output Byte
(0 to 127)
(0 to 127)
(0 to 127)
Output word
(0 to 126)
(0 to 126)
(0 to 126)
A-19
S5-100U
Abbreviation
Explanation
CPU 100
RLO
The RLO is affected/not affected
by the operation.
RLO
dependent?
Y
Y /Y
N
CPU 103
Result of logic operation
RLO affected?
Y/N
CPU 102
The statement is executed only if the RLO is “1”.
The statement is executed only on
positive/negative edge change of the RLO.
The statement is always executed.
RLO reloaded? When the next binary operation takes place, the
Y/N
RLO is reloaded/not reloaded (e.g. A I 0.0).
RS
System data area
- for load operations (supplementary operations)
and transfer operations (system operations)
- for bit test and set operations (system
operations)
SAC
DB1 parameter: Clock time after last switch from
STOP RUN or save from last Power OFF
SB
Sequence block
SDP
DB1 block ID for system data parameters
SET
DB1 parameter: Set clock/date
SF
DB1 parameter: SINEC L1, position of send
mailbox
SL1
DB1 block ID for SINEC L1
SLN
DB1 parameter: SINEC L1, slave number
STL
STEP 5 statement list method of representation
STP
DB1 parameter: update the clock while in the
STOP state.
STW
DB1 parameter: status word location (integral
real-time clock)
T
Timer
operations
TFB
DB1 block ID for timer function block
TIS
DB1 parameter: set prompt time
WD
(0.0 to 255.15)
STEP address counter
SAV
(0 to 255)
DB1 parameter: set scan time monitoring
(0 to 255)
(0 to 15)
(0 to 31)
(0 to 127)
(0.0 to 127.15)
A-20
B
Dimension Drawings
Figures
B-1
B-2
B-3
B-4
B-5
B-6
B-7
Cross Sections of Standard Mounting Rails . . . . . . . . . . . . . . . . . . . . . . . .
Dimension Drawing of the 483-mm (19-in.) Standard Mounting Rail . . . . . . .
Dimension Drawing of the 530-mm (20.9-in.) Standard Mounting Rail . . . . . .
Dimension Drawing of the 830-mm (32.7-in.) Standard Mounting Rail . . . . . .
Dimension Drawing of the 2-m (6.6-ft.) Standard Mounting Rail . . . . . . . . . .
Dimension Drawing of the S5-100U (CPU) . . . . . . . . . . . . . . . . . . . . . . . .
Dimension Drawing of the Bus Unit (Crimp Snap-in Connections)
with I/O Module . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . . .
B-8 Dimension Drawing of the Bus Unit (SIGUT Screw-type Terminals)
B-9 Dimension Drawing of the IM 315 Interface Module . . . . . . . . . . . . . . . . . .
B-10 Dimension Drawing of the IM 316 Interface Module (6ES5 316-8MA12) . . . .
B-11 Dimension Drawing of the PS 930 and PS 931 Power Supply Modules
B
B
B
B
B
B
1
1
2
2
2
3
B
4
B
B
B
B
5
6
7
8
S5-100U
B
Dimension Drawings
Dimension Drawings
Dimensions are indicated in millimeters. The approximate equivalent in inches is indicated in
parentheses. (1 mm=0.039 in. rounded off to the nearest tenth or hundredth of an inch)
15°
15°
Deburred
1
2.5 (0.1)
2.5 (0.1)
R 1.2 (0.05)
R 1.2 (0.05)
Centerline
for oblong
hole
Deburred
1
R 1.2 (0.05)
R 1.2 (0.05)
19 (0.8)
19 (0.8)
24 (1.0)
24 (1.0)
35 (1.4)
Deburred
oblong
hole
35 (1.4)
15 (0.6)
15 (0.6)
Figure B-1. Cross Sections of Standard Mounting Rails
8.7 (0.3)
465.1 (18.3)
163.8 (6.5)
155 (6.1)
7 (0.3)
482.6 (19.0)
11
(0.4)
Figure B-2. Dimension Drawing of the 483-mm (19-in.) Standard Mounting Rail
B-1
Dimension Drawings
S5-100U
15 (0.6)
20 x 25=500 (0.8 x 1.0=19.7)
25 (1.0)
5.2 (0.2)
18 (0.7)
530 (20.9)
Figure B-3. Dimension Drawing of the 530-mm (20.9-in.) Standard Mounting Rail
15 (0.6)
32 x 25=800 (1.26 x 1.0=31.5)
25 (1.0)
5.2 (0.2)
18 (0.7)
830 (32.7)
Figure B-4. Dimension Drawing of the 830-mm (32.7-in.) Standard Mounting Rail
2000 mm (6.6 ft.)
Figure B-5. Dimension Drawing of the 2-m (6.6-ft.) Standard Mounting Rail
B-2
S5-100U
Dimension Drawings
81 (3.2)
91.5 (3.6)
63.5 (2.5)
35 (1.4)
135 (5.3)
120 127
(4.1) (5)
40 (1.6)
10.8 (0.4)
Figure B-6.
Dimension Drawing of the S5 100U (CPU)
B-3
Dimension Drawings
S5-100U
135 (5.3)
85 (3.4)
127 (5)
81 (3.2)
135 (5.3)
with crimp snap-in connection (6ES5 700-8MA22)
Standard
mounting rail
EN 50022-35 x 15
91.5
(3.6)
45.75
(1.8)
Figure B-7. Dimension Drawing of the Bus Unit (Crimp Snap-in Connections)
with I/O Module
B-4
S5-100U
Dimension Drawings
135 (5.3)
85 (3.4)
127 (5)
81 (3.2)
162 (6.4) with screw type terminals (6ES5 700-8MA11)
Standard mounting rail
EN 50022-35 x 15
91.5
(3.6)
45.75
(1.7)
Figure B-8. Dimension Drawing of the Bus Unit (SIGUT Screw-type Terminals)
with I/O Module
B-5
Dimension Drawings
S5-100U
135
(5.3)
min. 210 (8.3)
max. 570 (22.4)
81 (3.2)
135
(5.3)
13.5 (0.5)
45.4 (1.8)
26 (1)
35 (1.4)
Figure B-9.
B-6
S5-100U
Dimension Drawings
45.4
(1.8)
min. 210 (8.3)
max. 10000 (39.4)
81 (3.2)
135 (5.3)
13.5 (0.5)
26 (1)
35 (1.4)
Figure B-10. Dimension Drawing of the IM 316 Interface Module (6ES5 316-8MA12)
B-7
Dimension Drawings
S5-100U
135 (5.3)
120 (4.7)
127 (5)
81 (3.2)
EN 50022-35×15
45.4 (1.8)
Figure B-11. Dimension Drawing of the PS 930 and PS 931 Power Supply Modules
B-8
C
S5-100U
C
Active and Passive Faults in Automation Equipment/ESD Guidelines
Equipment / Guidelines for Handling
Depending on the particular task for which the electronic automation equipment is used, both
active as well as passive faults can result in a dangerous situation. For example, in drive
control, an active fault is generally dangerous because it can result in an unauthorized startup of
the drive. On the other hand, a passive fault in a signalling function can result in a dangerous
operating state not being reported to the operator.
The differentiation of the possible faults and their classification into dangerous and nondangerous faults, depending on the particular task, is important for all safety considerations in
respect to the product supplied.
Warning
In all cases where a fault in automation equipment can result in severe personal injury or
substantial property damage, i.e., where a dangerous fault can occur, additional external
measures, additional external measures must be taken or equipment provided to ensure
or force safe operating conditions even in the event of a fault (e.g., by means of
independent limit monitors, mechanical interlocks, etc.).
Procedures for Maintenance and Repair
If you are carrying out measurement or testing work on an active unit, you must adhere to the rules
and regulations contained in the “VGB 4.0 Accident Prevention Regulations“ of the German
employers liability assurance association (“Berufsgenossenschaften“). Pay particular attention to
paragraph 8, “Permissible exceptions when working on live parts.“
Do not attempt to repair an item of automation equipment. Such repairs may only be carried out by
Siemens service personnel or repair shops Siemens has authorized to carry out such
repairs.
The information in this manual is checked regularly for updating and correctness and may be modified without prior notice. The
information contained in this manual is protected by copyright. Photocopying and translation into other languages is not permitted
without express permission from Siemens.
C-1
S5-100U
Guidelines for Handling Electrostatic Sensitive Devices (ESD)
What is ESD?
All electronic modules are equipped with large-scale integrated ICs or components. Due to their
design, these electronic elements are very sensitive to overvoltages and thus to any electrostatic
discharge.
These Electrostatic Sensitive Devices are commonly referred to by the abbreviation ESD.
Electrostatic sensitive devices are labelled with the following symbol:
Caution
Electrostatic sensitive devices are subject to voltages that are far below the voltage
values that can still be perceived by human beings. These voltages are present if you
touch a component module without previously being electrostatically discharged. In most
cases, the damage caused by an overvoltage is not immediately noticeable and results in
total damage only after a prolonged period of operation.
C-2
S5-100U
Electrostatic charging of objects and persons
Every object with no conductive connection to the electrical potential of its surroundings can be
charged electrostatically. In this way, voltages up to 15000 V can build up whereas minor charges,
i.e. up to 100 V, are not relevant.
Examples:
Plastic covers
Plastic cups
Plastic-bound books and notebooks
Desoldering device with plastic parts
Walking on plastic flooring
Sitting on a padded chair
Walking on a carpet (synthetic)
up to 5000 V
up to 5000 V
up to 8000 V
up to 8000 V
up to 12000 V
up to 15000 V
up to 15000 V
Limits for perceiving electrostatic discharges
An electrostatic discharge is
perceptible from 3500 V
audible from 4500 V
visible from 5000 V
A fraction of those voltages is capable of destroying or damaging electronic devices.
Carefully note ad apply the protective measures described below to protect and prolong the life of
your modules and components.
General protective measures against electrostatic discharge damage
Keep plastics away from sensitive devices. Most plastic materials have a tendency to build up
electrostatic charges easily.
Make sure that the personnel, working surfaces and packaging are sufficiently grounded when
handling electrostatic sensitive devices.
If possible, avoid any contact with electrostatic sensitive devices. Hold modules without touching
the pins of components or printed conductors. In this way, the discharged energy cannot affect
the sensitive devices.
C-3
S5-100U
Additional precautions for modules without housings
Note the following measures that have to be taken for modules that are not protected against
accidental contact:
Touch electrostatical sensitive devices only
- if you wear a wristband complying with ESD specifications or
- if you use special ESD footwear or ground straps when walking ona an ESD floor.
Persons working on electronic devices should first discharge their bodies by touching grounded
metallic parts (e.g. bare metal parts of switchgear cabinets, water pipes, etc.)
Protect the modules against contact with chargeable and highly insulating materials, such as
plastic foils, insulating table tops or clothes made of plastic fibres.
Place electrostatic sensitive devices only on conductive surfaces:
- Tables with ESD surfaces
- Conductive ESD foam plastic (ESD foam plastic ismostly coloured black)
- ESD bags
Avoid direct contact of eletrostatic sensitive devices with visual display units, monitors or TV
sets (minimum distance to screen & gt; 10 cm).
C-4
S5-100U
The following Figures once again illustrates the precautions for handling electrostatically sensitive
devices.
a
b
c
d
e
f
g
Conductive flooring material
Table with conductive, grounded surface
ESD footwear
ESD smock
Gounded ESD writstband
Grounded connection of switchgear cabinet
Grounded chair
d
b
e
g
c
f
a
Figure C-1. ESD Measures
Taking measurements and working on ESD modules
Measurements may be taken on electrostatic sensitive devices only if
the measuring device is grounded (e.g. via protective conductor) or
the tip of the isolated measuring tool has previously been discharged (e.g. by briefly touching
grounded metal parts).
C-5
D
S5-100U
D
Order Numbers
Standard 35 mm Mounting Rail
for 19-in. cabinets, length 483 mm
for 600 mm cabinets, length 530 mm
for 900 mm cabinets, length 830 mm
Length 2000 mm, without holes
Power supply module PS 930
115/230 V AC; 1 A
Replacement fuse (3A extra-fast)
Power supply module PS 931
115/230 V AC; 24 V DC; 2 A
(with electronic circuit protection)
Power supply module PS 935
24 V DC; 9 V DC, 2.5 A
Load power supply 6EW1
115/230 V AC; 24 V DC; 4 A
115/230 V AC; 24 V DC; 10 A
Bus Units
Bus unit with SIGUT screw-type terminals
Bus unit with crimp snap-in terminals
Interrupt bus unit, with SIGUT screw-type terminals
Interrupt bus unit with crimp snap-in terminals
Accessories
Extracting tool
for crimp snap-in connections
Crimp snap-in contacts, 250 pieces
Crimping tool
for attaching the crimp contacts
Interface Modules
IM 315 interface module
IM 316 interface module
- Cable connectors (0.5 m/1.6 ft.)
- Cable connectors (2.5 m/8.2 ft.)
- Cable connectors (5.0 m/16.5 ft.)
- Cable connectors (10 m/33 ft.)
6ES5 710-8MA11
6ES5 710-8MA21
6ES5 710-8MA31
6ES5 710-8MA41
6ES5 930-8MD11
6ES5 980-3BC61
6ES5 931-8MD11
6ES5 935-8ME11
6EW1 380-1AB
6EW1 380-4AB01
6ES5 700-8MA11
6ES5 700-8MA22
6ES5 700-8MB11
6ES5 700-8MB21
6ES5 497-8MA11
6XX3 070
6XX3 071
6ES5 315-8MA11
6ES5 316-8MA12
6ES5 712-8AF00
6ES5 712-8BC50
6ES5 712-8BF00
6ES5 712-8CB00
D-1
S5-100U
Order Numbers
Central Processing Units (CPUs)
CPU 100
CPU 102
CPU 103
6ES5 100-8MA02
6ES5 102-8MA02
6ES5 103-8MA03
S5-100U System Manual (CPU 100, CPU 102, CPU 103)
German
English
French
Spanish
Italian
6ES5 998-0UB13
6ES5 998-0UB23
6ES5 998-0UB33
6ES5 998-0UB43
6ES5 998-0UB53
Accessories for the CPUs
Back-up battery lithium AA; 3.4 V/850 mAh
6ES5 980-0MB11
Memory submodule (EPROM)
Memory submodule (EEPROM)
D-2
4096 statements
8192 statements
16384 statements
1024 statements
2048 statements
4096 statements
8192 statements
6ES5 375-1LA15
6ES5 375-1LA21
6ES5 375-1LA41
6ES5 375-0LC11
6ES5 375-0LC21
6ES5 375-0LC31
6ES5 375-0LC41
S5-100U
Order Numbers
Manual for IP 262 Closed-Loop Control Module
German
English
French
Italian
6ES5 998-5SG11
6ES5 998-5SG21
6ES5 998-5SG31
6ES5 998-5SG51
German
English
6ES5 998-5SK11
6ES5 998-5SK21
German
English
6ES5 998-5SL11
6ES5 998-5SL21
German
English
French
6ES5 998-5SH11
6ES5 998-5SH21
6ES5 998-5SH31
German
English
6ES5 998-5SC11
6ES5 998-5SC21
German
English
French
Spanish
6ES5 998-5SD11
6ES5 998-5SD21
6ES5 998-5SD31
6ES5 998-5SD41
Manual for IP 263 Positioning Module
Manual for IP 264 Electronic Cam Controller Module
Manual for IP 265 Closed-Loop Control Module
Manual for IP 266 Positioning Module
Manual for IP 267 Stepper Motor Module
Digital Input Modules
8 x 5 to 24 V DC
4 x 24 V DC
8 x 24 V DC
16 x 24 V DC
8 x 24 V DC
4 x 24 to 60 V DC
4 x 115 V AC
8 x 115 V AC
4 x 230 V AC
8 x 230 V AC
Digital Output Modules
8 x 5 to 24 V DC/0.1 A
4 x 24 V DC/0.5 A
4 x 24 V DC/2 A
8 x 24 V DC/0.5 A
8 x 24 V DC/0.5 A
4 x 24 to 60 V DC/0.5 A
4 x 115 to 230 V AC/1 A
8 x 115 to 230 V AC/0.5 A
4 relays x 30 V DC/230 V AC
8 relays x 30 V DC/230 V AC
isolated
isolated
isolated
isolated
isolated
isolated
isolated
isolated
isolated
isolated
isolated*
isolated*
* Replacement fuse (10 A extra-fast)
6ES5 433-8MA11
6ES5 420-8MA11
6ES5 421-8MA12
6ES5 422-8MA11
6ES5 431-8MA11
6ES5 430-8MB11
6ES5 430-8MC11
6ES5 431-8MC11
6ES5 430-8MD11
6ES5 431-8MD11
6ES5 453-8MA11
6ES5 440-8MA12
6ES5 440-8MA22
6ES5 441-8MA11
6ES5 451-8MA11
6ES5 450-8MB11
6ES5 450-8MD11
6ES5 451-8MD11
6ES5 452-8MR11
6ES5 451-8MR12
6ES5 980-3BC11
D-3
S5-100U
Order Numbers
Digital Input/Output Module
24 V DC 16 inputs/16 outputs
Accessories
Front connector, 40-pin for crimp snap-in connection
– with crimp contacts
– without crimp contacts
Front connector, 40-pin for screw-type connection
– standard
– increased EMC strength
6ES5 490-8MB11
6ES5 490-8FB11
Analog Input Modules
4 x ± 50 mV
4 x ± 50 mV
4x±1V
4 x ± 10 V
4 x ± 20 mA
4 x + 4 to 20 mA
2 x PT 100/± 500 mV
2 x PT 100/± 500 mV
4 x + 0 to 10 V
isolated
isolated
isolated
isolated
isolated
isolated
isolated
isolated
isolated
6ES5 464-8MA11
6ES5 464-8MA21
6ES5 464-8MB11
6ES5 464-8MC11
6ES5 464-8MD11
6ES5 464-8ME11
6ES5 464-8MF11
6ES5 466-8MF21
6ES5 466-8MC11
Analog Output Modules
2 x ± 10 V
2 x ± 20 mA
2 x + 4 to 20 mA
2 x + 1 to 5 V
isolated
isolated
isolated
isolated
6ES5 470-8MA12
6ES5 470-8MB12
6ES5 470-8MC12
6ES5 470-8MD12
Function Modules
IP 262 Closed-loop control module
– with 3 analog outputs
– with 8 binary outputs
IP 263 Positioning module
IP 264 Electronic cam controller module
IP 266 Positioning module
IP 267 Stepper motor control module
Diagnostic module 330
Timer module 380 2 x 0.3 to 300 s
Counter module 2 x 0 to 500 Hz
Counter module 385B 1 x 25/500 KHz
Comparator module 461 2 x 1 to 20 mA/0.5 to 10 V
CP 521 SI Printer output module
CP 521 BASIC communications module
Simulator 788 (digital input/output signals)
D-4
6ES5 482-8MA13
6ES5 490-8MA13
6ES5 490-8MA03
6ES5 262-8MA12
6ES5 262-8MB12
6ES5 263-8MA13
6ES5 264-8MA12
6ES5 265-8MA01
6ES5 266-8MA11
6ES5 267-8MA11
6ES5 330-8MA11
6ES5 380-8MA11
6ES5 385-8MA11
6ES5 385-8MB11
6ES5 461-8MA11
6ES5 521-8MA22
6ES5 521-8MB12
6ES5 788-8MA11
S5-100U
Order Numbers
Operator Panels and Programmers
OP 393-III Operator Panel
with connecting cable
OP 393-III Operator guide, German
PG 605U Programmer
PG 605U Operator guide, German
PG 720 Programmer
PG 720 C Programmer
PG 740 Programmer
PG 760 Programmer
(– & gt; Catalog ST 59)
Cable connector for connecting the OP 393-III to the CPU
3m
10 m
20 m
Special lengths
up to 1000 m
(– & gt; Catalog ST 80)
6ES5 393-0UA15
6ES5 998-0UQ12
6ES5 605-0UA11
6ES5 998-0UP11
6ES7 720-0AB00-0YA0
6ES7 720-1AB00-0YB0
6ES7 740-0AA00-0YA0
6ES7 760-1AA00-0YA0
6ES5 728-0BD00
6ES5 728-0CB00
6ES5 728-0CC00
Program Packages
Basic Functions Program Package
with description in German, English, and French
for the S5-DOS operating system
for the MS-DOS, S5-DOS/MT operating system
6ES5 848-8AA01
6ES5 848-7AA01
Floating Point Arithmetic Program Package
6ES5 845-8GP01
6ES5 845-7GP01
GRAPH 5 Program Package
6ES5 886-1FA01
GRAPH 5 Mini Program Package
German
English
French
Spanish
Italian
6ES5 886-1SE11
6ES5 886-1SE21
6ES5 886-1SE31
6ES5 886-1SE41
6ES5 886-1SE51
German
English
Italian
6ES5 840-4BC11
6ES5 840-4BC21
6ES5 840-4BC51
S5-100U Program Package
with description in
STEP 5 Package for Mini PLCs for PC
Documentation for STEP 5 Package, German
6ES5 866-0MA02
6ES5 896-0MY11
D-5
E
Reference Materials
S5-100U
E
Reference Materials
Reference Materials
The following reference material can be ordered from your local Siemens Company or your
local bookshop:
Automating with the SIMATIC® S5-115U
Programmable Controllers
Hans Berger
Siemens AG, Berlin and Munich, 1989 (2nd Edition)
(Order No.: ISBN 3-8009-1530-8)
Basic Concepts
Siemens AG, 1992 (Order No.: A19100-L531-F914-X-7600)
Programming Primer for the SIMATIC® S5-90/95U
Practical Exercises with the PG 710 Programmer
Siemens AG, Berlin and Munich, 1992
Order No.: A19100-L531-F550-X-7600
E-1
F
S5-100U
F
European Companies and Representatives
Austria
Siemens AG Österreich
Vienna
Bregenz
Graz
Innsbruck
Klagenfurt
Linz
Salzburg
Federal Republic
of Germany (continued)
Hanover
Leipzig
Mannheim
Munich
Nuremberg
Saarbrücken
Stuttgart
Belgium
Siemens S.A.
Brussels
Liège
Siemens N.V.
Brussels
Antwerp
Gent
Finland
Siemens Osakeyhtiö
Helsinki
Bulgaria
RUEN office of the
INTERPRED corporation,
agency of the
Siemens AG Sofia
Sofia
Czechoslovakia
EFEKTIM
Engineering Consultants,
Siemens AG
Prague
Denmark
Siemens A/S
Copenhagen, Ballerup
Hojbjerg
Federal Republic
of Germany
Branch offices of the
Siemens AG
Berlin
Bremen
Cologne
Dortmund
Düsseldorf
Essen
Frankfurt/Main
Hamburg
France
Siemens S.A.
Paris, Saint-Denis
Lyon, Caluire-et-Cuire
Marseilles
Metz
Seclin (Lille)
Strasbourg
Great Britain
Siemens Ltd.
London, Sunbury-onThames
Birmingham
Bristol, Clevedon
Congleton
Edinburgh
Glasgow
Leeds
Liverpool
Newcastle
Greece
Siemens A.E.
Athens
Thessaloniki
Hungary
SICONTACT GmbH
Budapest
Iceland
Smith & Norland H/F
Reykjavik
Ireland
Siemens Ltd.
Dublin
Italy
Siemens S. p. A.
Milan
Bari
Bologna
Brescia
Casoria
Florence
Genoa
Macomer
Padua
Rome
Turin
Luxemburg
Siemens S.A.
Luxembourg
Malta
J.R. Darmanin & Co., Ltd.
Valletta
Netherlands
Siemens Nederland N.V.
The Hague
Norway
Siemens A/S
Oslo
Bergen
Stavanger
Trondheim
Poland
PHZ Transactor S.A.
Warsaw
Gda sk-Letnica
Katowice
Portugal
Siemens S.R.A.L.
Lisbon
Faro
Leiria
Porto
F-1
Romania
Siemens birou de
consulta ii tehnice
Bukarest
Spain
Siemens S.A.
Madrid
Sweden
Siemens AB
Stockholm
Eskilstuna
Göteborg
Jönköping
Luleå
Malmö
Sundsvall
S5-100U
Switzerland
Siemens-Albis AG
Zürich
Bern
Siemens-Albis S.A.
Lausanne, Renens
Turkey
ETMA
Istanbul
Adana
Ankara
Bursa
Izmir
Samsun
USSR
Siemens AG Agency
Moscow
Yugoslavia
General Export
OOUR Zastupstvo
Belgrade
Ljubljana
Rijeka
Sarajewo
Skopje
Zagreb
Non-European Companies and Representatives
Africa
Algeria
Siemens Bureau
Alger
Algier
Angola
Tecnidata
Luanda
Burundi
SOGECOM
Bujumbara
Egypt
Siemens Resident
Engineers
Cairo-Mohandessin
Alexandria
Centech
Zamalek-Cairo
Ethiopia
Addis Electrical
Engineering Ltd.
Addis Abeba
F-2
Ivory Coast
Siemens AG
Succursale Côte d'Ivoire
Abidjan
Namibia
Siemens Resident
Engineer
Windhoek
Kenya
Achelis (Kenya) Ltd.
Nairobi
Nigeria
Electro Technologies
Nigeria Ltd. (Eltec)
Lagos
Libya
Siemens AG
Branch Office Libya
Tripoli
Mauritius
Rey & Lenferna Ltd.
Port Louis
Morocco
SETEL
Société Electrotechnique
et de Télécommunications S.A.
Casablanca
Mozambique
Siemens Resident
Engineer
Maputo
Rwanda
Etablissement Rwandais
Kigali
Simbabwe
Corporation (Pvt.) Ltd.
Harare
South Africa
Siemens Ltd.
Johannesburg
Cape Town
Durban
Middleburg
Newcastle
Port Elizabeth
Pretoria
S5-100U
Sudan
National Electrical &
Commercial Company
(NECC)
Khartoum
Swaziland
Siemens (Pty.) Ltd.
Mbabane
Tanzania
Tanzania Electrical
Services Ltd.
Dar-es-Salaam
Tunesia
Sitelec S.A.
Tunis
Zaire
SOFAMATEL S.P.R.L.
Kinshasa
Zambia
Electrical Maintenance
Lusaka Ltd.
Lusaka
Mining projects:
General Mining
Industries Ltd.
Kitwe
Brazil
Siemens S.A.
São Paulo
Belém
Belo Horizonte
Brasília
Campinas
Curitiba
Florianópolis
Fortaleza
Porto Alegre
Recife
Rio de Janeiro
Salvador de Bahía
Vitoria
Canada
Siemens Electric Ltd.
Montreal, Québec
Toronto, Ontario
Chile
INGELSAC
Santiago de Chile
Colombia
Siemens S.A.
Bogotá
Baranquilla
Cali
Medellín
Costa Rica
Siemens S.A.
San José
America
Argentina
Siemens S.A.
Buenos Aires
Bahía Blanca
Córdoba
Mendoza
Rosario
Bolivia
Sociedad Comercial e
Industrial Hansa Ltd.
La Paz
Ecuador
Siemens S.A.
Quito
OTESA
Guayaquil
Quito
Honduras
Representaciones Electroindustriales S. de R.L.
Tegucigalpa
Mexico
Siemens S.A.
México, D.F.
Culiacán
Gómez Palacio
Guadalajara
León
Monterrey
Puebla
Nicaragua
Siemens S.A.
Managua
Paraguay
Rieder & Cia., S.A.C.I.
Asunción
Peru
Siemsa
Lima
Uruguay
Conatel S.A.
Montevideo
Venezuela
Siemens S.A.
Caracas
Valencia
United States
of America
Siemens Industrial
Automation Inc.
Alpharetta, Georgia
El Salvador
Siemens S.A.
San Salvador
Guatemala
Siemens S.A.
Ciudad de Guatemala
F-3
Asia
Bahrain
Transitec Gulf
Manama
or
Siemens Resident Engineer
Abu Dhabi
Bangladesh
Siemens Bangladesh Ltd.
Dhaka
Hong Kong
Jebsen & Co., Ltd.
Hong Kong
India
Siemens India Ltd.
Bombay
Ahmedabad
Bangalore
Calcutta
Madras
New Dehli
Secundarabad
Indonesia
P.T.Siemens Indonesia
Jakarta
P.T. Dian-Graha Elektrika
Jakarta
Bandung
Medan
Surabaya
Iran
Siemens Sherkate
Sahami Khass
Teheran
Iraq
Samhiry Bros. Co. (W.L.L.)
Baghdad
or
Siemens AG (Iraq Branch)
Baghdad
Japan
Siemens K.K.
Tokyo
F-4
S5-100U
Jordan
Siemens AG (Jordan
Branch)
Amman
or
A.R. Kevorkian Co.
Amman
Korea (Republic)
Siemens Electrical
Engineering Co., Ltd.
Seoul
Pusan
Kuwait
National & German
Electrical and Electronic
Service Co. (INGEECO)
Kuwait, Arabia
Lebanon
Ets. F.A. Kettaneh S.A.
Beirut
Malaysia
Siemens AG
Malaysian Branch
Kuala Lumpur
Oman
Waleed Associates
Muscat
or
Siemens Resident
Engineers
Dubai
Pakistan
Siemens Pakistan
Karachi
Islamabad
Lahore
Peshawer
Quetta
Rawalpindi
People's Republic of China
Siemens Representative Office
Beijing
Guangzhou
Shanghai
Philippine Islands
Maschinen & Technik Inc.
(MATEC)
Manila
Qatar
Trags Electrical Engineering
and
Air Conditioning Co.
Doha
or
Abu Dhabi
Saudi Arabia
Arabia Electric Ltd.
(Equipment)
Jeddah
Damman
Riyadh
Sri Lanka
Dimo Limited
Colombo
Syria
Siemens AG
(Damascus Branch)
Damascus
Taiwan
Siemens Liaison Office
Taipei
TAI Engineering Co., Ltd.
Taipei
Thailand
B. Grimm & Co., R.O.P.
Bangkok
United Arab Emirates
Electro Mechanical Co.
Abu Dhabi
or
Abu Dhabi
Scientechnic
Dubai
or
Dubai
S5-100U
Asia (continued)
Yemen (Arab Republic)
Tihama Tractors &
Engineering Co.o., Ltd.
Sanaa
or
Sanaa
Australia
Australia
Siemens Ltd.
Melbourne
Brisbane
Perth
Sydney
New Zealand
Auckland
F-5
Index
S5-100U
Index
Index
A
Accumulator
Actual operand
Addition
Address
- absolute
- relative
Address assignment
- in RAM
- in the system data area
AM flag
Analog input module
Analog modules
- addressing
Analog output module
Analog value
- conversion
- output of (FB251)
- read in (FB250)
- scaling (FB250)
Argument
Arithmetic operations
- comparison
- system
Arithmetic unit
ASCII mode
Assigning parameters
Automation equipment
- fault
8-10, 8-12
7-14
8-31
5-9
5-10
6-7
6-15
6-16
12-10
11-1, 11-11
6-5
11-20
11-22
9-14, 11-25,
9-14, 11-17,
11-22
9-14, 11-22
9-5
8-30
8-67
2-5
15-63
9-1
C-1
B
Back-up battery
BASIC
- creating a program in
Basic operations
Battery
- failure (OB34)
Binary coded representation
(BCD)
Binary divider
Binary scaler
Bit pattern
Bit test operation
4-8
15-66
8-1
4-8
9-14
7-31, 7-32
8-71
8-71
11-11
8-42
Block
- call operations
- end symbol
- header
- ID
- length
- parameters
- programming
- structure
- type
Boolean logic operation
Broken wire
BSTACK
Bus cable
Bus terminal
Bus unit
- installing
8-33
9-4
7-8
9-1, 9-5, 9-10
7-7
7-14
7-8
7-6 - 7-8
7-5
8-2
11-7
5-11
13-1
13-1
2-2
3-3
C
CE marking
Central Processing Unit (CPU)
Circuit diagram
Clock data
- 12-hour mode
- 24-hour mode
- area
- range definition
Clock pulse generator
Clock time correction factor
Code converter
- : 16
- : B4
Comment
- symbol
Communications module
- CP 521 Basic
- CP 521 SI
Comparator module
Comparison
- operation
Complement
- one's
- two's
COMPRESS
Condition code generation
14-1
2-1, 3-2
7-3
12-10
12-10
12-8, 12-9,
12-15
12-10
8-73
12-7, 12-35
15-41
9-12
9-12
9-6
9-6
15-62
15-65
15-62
15-1
8-30
8-50
8-50
7-30
8-69
1
Index
Control
- deviation
- system flowchart (CSF)
- variable
- word
Controller
- continuous action
Controller DB
Conversion operation
Coordination byte Receive (KBE)
Coordination byte Send (KBS)
Correction rate
- algorithm
Correction value
Counter
- loading
- operation
- resetting
- scanning
- setting
Counter module
- 25/500 kHz
- 2×0 to 500 Hz
Counting pulse sensor
- connection of
CPU
Crimp-snap-in
- connection method
S5-100U
9-21
7-2
9-12
9-19
9-15
9-15, 9-19
8-50
13-2, 13-10
13-2, 13-8
9-18
12-35
2-4, 8-26 - 8-29
8-25
8-25
8-28, 8-29
8-26
8-28, 8-29
15-17
15-12
15-21
2-1
3-10
D
Data block
- calling
- deleting
- generating
Data cycle
- interupt
Data exchange
DB1
- function
DB1 parameter
- transfering
- setting
Decimal format
Default DB1
Derivative action time
Design
- modular
Diagnostic
- module
Digital input module
Digital input/output module
- address assignment
Digital logic operation
2
7-5, 7-16
8-33, 8-35
8-33, 8-35
8-33, 8-35
2-7
2-7
13-7
9-1, 12-2
7-17
9-10, 12-2
9-9
9-10
7-32
9-1, 13-5
9-19, 9-21
1-2
15-9
3-13
3-18, 6-4
6-7
8-44
Divider : 16
DO operation
8-39
9-13
8-54
E
Electromagnetic interference
Enable operation
Equipotential bonding
Error
- address
- analysis
- indication
- remedy
- parameter error
Expansion capability
- maximum
3-22
15-49
8-41
3-31
5-9
5-1, 5-4, 5-5
5-1
5-4, 5-5
9-4, 9-8
2-8
F
Fault
- automation equipment
FB250
FB251
Field transfer
Filler
Flags
FORCE VAR
Formal operand
Four wire circuit
Function module
- addressing
Function block
- calling
- header
- integrated
- setting parameters
C-1
11-22, 11-23
11-25
8-66
9-1, 9-5
2-4, 7-3
12-19
8-58
11-6
6-7
7-5, 7-11
7-14
7-12
9-11
7-12, 7-15
G
GRAPH 5
Grounding
7-1
3-30
H
Hexadecimal representation
7-31
I
IM
IM 315
IM 316
Increment operation
Input
Input/output module
2-2
3-5
3-5
8-52
7-3
2-2
S5-100U
Installation of the S5-100U
- electrical
- horizontally
- mechanical
- mechanical, with external
I/Os
- vertical
Integral action time (TN)
Interface
- module
- serial
Interrupt
- disable
- PII
- PIQ
- reaction time
Interrupt data cycle
I/O bus
I/O modules
Index
3-1
3-20, 3-21
3-7
3-1
3-4
3-8
9-19
2-2, 3-5, 3-6
2-4
8-53
7-29, 10-3
7-29, 10-3
10-7
2-7
2-5, 2-6, 15-10
3-13, 5-12
J
Jump
- processing
- operation
8-57
8-56
L
Ladder diagram (LAD)
Leap year
Lightning protection
Linerization
Load operation
Loading a time
7-1
12-10
3-30
11-8
8-10, 8-11, 8-40,
8-64
8-14
M
Mode change
Modular design
Momentary contact relay/edge
evaluation
Monitoring
Mounting rail
- standard
Multiplier: 16
7-21
1-2
8-71
5-10
2-2
9-16
N
Nesting depth
" NO " operation
Normal mode
Number
- format
7-6
8-38
7-19
O
OB2
OB13
OB21
OB22
On-delay
- stored
- timer
Operand
- areas
- ID
Operating hours counter
Operating mode
- changing
- display
- panel
- start-up
- switch
Operating system
Operation
- basic
- Boolean logic
- set/reset
- supplementary
- system
Organization block
- integrated
Output
Overall reset
10-1, 10-4
7-28
7-24
7-24
8-22, 8-23
8-23
15-6
7-1
7-3
7-1
12-7, 12-30
4-2
4-1
4-2
4-2
4-1
2-7
7-1, 8-1
8-1
8-2 - 8-7
8-7 - 8-9
8-1
8-1
7-5, 7-9, 7-18
9-14
7-3
4-2
P
Parameter
- function block
Parameter block
Parameter error
- correction
- locating
- recognizing
Parameter error code
- scanning
Parameter name
PID control algorithm
(OB251)
PM flag
Position
- decoding
- resolution
7-12
9-1, 9-5
9-4
9-6
9-8
9-8
9-2, 9-7
9-6
9-5
9-15
12-10
15-29
15-19, 15-26,
15-30
7-31
3
Index
Position sensor
- connecting
Positioning
- algorithm
- closed-loop controlled
- open-loop controlled
Positioning module
- IP 263
- IP 266
Power supply
- frequency
- module
Printer communications module
CP521
Printer mode
Process image (PII, PIQ)
Process image I/O tables
- interrupt
- PII
- PIQ
Processor
Program
- block
- memory
- structured
Program check
Program processing
- cyclical
- interrupt-driven
- time-controlled
Programmable controller
- design
Programming
- linear
- structured
Prompt time
Proportional gain
PT 100
Pulse generator
- connection of
Pulse timer
- extended
S5-100U
15-20, 15-2
15-57
9-18
15-60
15-56
15-45
15-55
11-7
2-1, 3-2, 3-12
3-20
15-62
15-63
2-4, 7-29
10-4
6-12
6-8, 6-10, 10-3
6-8, 6-11, 10-3
2-5
7-5, 7-11
2-4, 7-30
8-33
4-11
7-18
7-26
6-12, 7-29, 10-1
6-12, 7-28
2-1
7-4
7-5
12-6, 12-25
9-19
11-6
15-21
8-20
8-21
R
Reaction time
- interrupt
4
10-5
Real-time clock
- integral
- reading
- setting
Receive Mailbox (EF)
Reference
- point approach
- pulse
- signal
- variable
Reference potential
Register contents
- loading and transfering
Removing the S5-100U
Response time
Retentive characteristics
Retriggering
- OB31
RLO
12-1
12-21
12-5, 12-21
13-2
15-31
15-32
15-32
9-21
11-1
8-65
3-1, 3-2
7-27
2-5
8-33
8-33
S
Sampling interval
Scan cycle time trigger
Scan monitoring time
Screw-type
- connection method
SEARCH
- function
Send Mailbox (SF)
Sensor lines
Serial interface
Sequence block
Set operation
Set/reset operation
Setpoint
Set time
Setting parameters
- for function blocks
Shielding
Shift operation
Shift register
- length
Shunt resistor
Simulator
- module
SINEC L1
- local area network
9-18, 9-21
7-26
7-26
3-18
3-9
5-11
4-11
13-2
11-19
2-4
7-5, 7-11
8-64
8-7 - 8-9
9-19, 9-21
15-5
7-15
3-29
8-48
2-6
2-8
11-5
15-7
13-1
EWA 4NEB 812 6120-02b
S5-100U
Slave
Slot addressing
SONAR BERO
Start ID
START-UP
Starting up
Statement list (STL)
STATUS
STATUS VAR
Status word
STOP operation
Substitution operation
Subtraction operation
Supplimentary operation
System
- data
- operations
- parameters
System data area
System data word
System characteristics
- defining in DB1
Index
13-3, 13-5
6-1
11-23
9-4, 9-5
4-1, 7-24
4-4
7-1
4-8
4-9
12-12, 12-15
15-59
8-39
8-58
8-31
8-1, 8-31
U
USTACK
5-1
W
Wiring
- arrangement
Wiring method
- crimp-snap-in terminals
- screw-type terminals
3-29
3-10
3-9
6-16
8-1, 8-64 - 8-67
5-14
12-15
13-2
9-11
T
Terminal block
Temperature
- compensation
Test function
- STATUS
Test mode
Thermocouples
Time
- base
- loading
Time constant
- dominant
Timer
- module
- operation
- reset
- starting
Transfer
- operation
Transfering a time
Two's complement
3-10
11-3
11-8
4-8
7-19
11-2
8-17
8-16, 8-17
8-14, 8-17
9-21
8-15 - 8-24
15-4
8-15
8-15
8-15, 8-19
8-12
8-10, 8-11, 8-64
8-14
11-11
5
Siemens AG
A & D AS E 148
Postfach 1963
D-92209 Amberg
Federal Republic of Germany
Your Name:
Your Title:
Company Name:
Street:
City, Zip Code:
Country:
Phone:
Please check any industry that applies to you:
Automotive
Pharmaceutical
Chemical
Plastic
Electrical Machinery
Pulp and Paper
Food
Textiles
Instrument and Control
Transportation
Nonelectrical Machinery
Other
Petrochemical
Remarks Form
Your comments and recommendations will help us to improve the quality and usefulness of our
publications. Please take the first available opportunity to fill out this questionnaire and return it
to Siemens.
Title of Your Manual:
Order No. of Your Manual:
Edition:
Please give each of the following questions your own personal mark within the range from 1
(very good) to 5 (poor).
1.
Do the contents meet your requirements?
2.
Is the information you need easy to find?
3.
Is the text easy to understand?
4.
Does the level of technical detail meet your requirements?
5.
Please rate the quality of the graphics/tables:
Additional comments: